Alex,
I would use an integrator component (Type24) to integrate the energy
use over the entire year, then pass its output to an equation that
divides by 3600 (to get kWh) and by 330 (to get energy per m2.)
Best,
David
On 3/28/2012 04:49, Alex Rachid wrote:
>
> Hi All,
>
> I am simulating a Cooling System:TYP92 with TYPE56
>
> I stored the energy removed in KWh in an excel sheet for every hour
> (simulation step)
>
> QCool in KWh =QCool KJ/h/3600
>
> how do I calculate using the output I am attaching the cooling energy
> in : KWh /m2/year
>
> Cooled area: 330 m2
>
> (what happens if the simulation step is 0.5 hr instead of 1 hour)
>
> Thanks in advance..
>
> Regards
>
> Alex
>
>
>