[TRNSYS-users] [EnergyPlus_Support] Experimental Data for PCM Modeling Validation
CleanTech Analytics
jeremiah at cleantechanalytics.com
Sat Mar 3 08:18:00 PST 2012
Saleh,
My latest data on the BioPCM technology is attached in the document called
BioPCM Energy Plus Objects. It has temperature enthalpy sets for the
following melt temperatures: Q21, Q23, Q25, Q29.
I do not yet have data on the microtek, BASF, and DuPont products, but the
microtek is not commercially available yet, and the BASF & DuPont products
can not be installed in the USA because they are a fire hazard so the
BioPCM is the defacto only commercially viable product for the USA. I have
attached a file with info on the BioPCM technology as well as an image of
the BioPCMat product..
The ramp on the Q21 is .5C/min, and the others are 1C/min, all using
dynamic DSC testing. I have requested for each of the melt temps to be
tested using isothermal stepped DSC testing. Question-- Could/would you
want to do T history and/or isothermal stepped testing, if so I can have
samples of each sent to you on Monday, as the lab I have at my disposal is
saying that it may take 250 hours to do the isothermal stepped tests, and
my math says that it should take more like 20 hours (how long would you say
it should take?) I have also attached are three files on testing methods
for your review..
Also thank you for all the recent advise, I now have my model working for a
small room and did figure out how to get energy savings. What I did was use
the internal source sink layers construction object and change the
convergence limits and it now works very well.
Here is a link to my visualization of a recent simulation run for Denver CO
that shows 25.2% savings (The same file ran in Eugene Oregon shows 12.6%)
-
https://docs.google.com/spreadsheet/ccc?key=0Ag7cD5ZV9QwRdGdmMThETElEaGJNWUQ3ZGU1MEZRcEE
Lastly I have attached two files that I found to be very interesting with
regards to parametric modeling PCM's, one by Saylor on enhanced comfort in
passive house and the other on an office building and more.. (see pages
50+)
I figure these files may give you some ideas about possible parametric
analysis that might be done.
Best of luck on your code project, and I will send you the next data as
soon as I get it (hot of the DSC....:)
On Sat, Mar 3, 2012 at 7:11 AM, saleh saadi <salehsnjsaadi404 at yahoo.com>wrote:
> **
>
>
> Dear All
>
> I have been involved in modeling PCM as a part of my PhD work at
> University of Colorado Boulder. At this phase of my work, I'm looking for a
> reliable experimental data to validate the models that I have coded. If you
> are willing to share your experimental data or you know someone who has
> one, then I will appreciate you contacting me or send the data to me.
>
> I have done the literature and found many available studies and contacting
> authors but unfortunately wasn't successful in getting the data. I tried to
> extract data from those published papers but I don't think that would be
> accurate for validation(i.e. may be good for qualitative comparison) .
>
> I appreciate your cooperation for accurate PCM simulation.
>
> Regards,
> Saleh Al Saadi
>
> __._,_.___
> Reply to sender<salehsnjsaadi404 at yahoo.com?subject=Re%3A%20Experimental%20Data%20for%20PCM%20Modeling%20Validation>| Reply
> to group<EnergyPlus_Support at yahoogroups.com?subject=Re%3A%20Experimental%20Data%20for%20PCM%20Modeling%20Validation>| Reply
> via web post<http://groups.yahoo.com/group/EnergyPlus_Support/post;_ylc=X3oDMTJxNTI1cGU2BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lkAzIzOTI2BHNlYwNmdHIEc2xrA3JwbHkEc3RpbWUDMTMzMDc4NzQ5MA--?act=reply&messageNum=23926>| Start
> a New Topic<http://groups.yahoo.com/group/EnergyPlus_Support/post;_ylc=X3oDMTJldDBiY2Z2BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA250cGMEc3RpbWUDMTMzMDc4NzQ5MA-->
> Messages in this topic<http://groups.yahoo.com/group/EnergyPlus_Support/message/23926;_ylc=X3oDMTM2NzFvdHByBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lkAzIzOTI2BHNlYwNmdHIEc2xrA3Z0cGMEc3RpbWUDMTMzMDc4NzQ5MAR0cGNJZAMyMzkyNg-->(
> 1)
> Recent Activity:
>
> - New Members<http://groups.yahoo.com/group/EnergyPlus_Support/members;_ylc=X3oDMTJmamQyaXQyBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzMzA3ODc0OTA-?o=6>
> 17
>
> Visit Your Group<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJlNHBybjVuBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTMzMDc4NzQ5MA-->
> Primary EnergyPlus support is found at:
> http://energyplus.helpserve.com or send a message to
> energyplus-support at gard.com
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are currently allowed but be mindful that not everyone has a
> high speed connection. Limit attachments to small files.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> [image: Yahoo! Groups]<http://groups.yahoo.com/;_ylc=X3oDMTJkZ25kZHFkBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzMwNzg3NDkw>
> Switch to: Text-Only<EnergyPlus_Support-traditional at yahoogroups.com?subject=Change+Delivery+Format:+Traditional>,
> Daily Digest<EnergyPlus_Support-digest at yahoogroups.com?subject=Email+Delivery:+Digest>•
> Unsubscribe<EnergyPlus_Support-unsubscribe at yahoogroups.com?subject=Unsubscribe>• Terms
> of Use <http://docs.yahoo.com/info/terms/>
> .
>
> __,_._,___
>
--
*Jeremiah D. Crossett*
*CleanTech Analytics*
*503-688-8951*
*www.cleantechanalytics.com* <http://www.cleantechanalytics.com>
*
This document may contain valuable information proprietary to CleanTech
Analytics which is private and confidential. It may not be shared, copied,
stored or transmitted in any form without the prior written consent of
CleanTech Analytics
*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120303/7a41a438/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: BioPCM-Energy Plus Objects-V2.idf
Type: application/octet-stream
Size: 39045 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120303/7a41a438/attachment-0003.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: RoomStudy-BioPCM M27-Q21.idf
Type: application/octet-stream
Size: 50341 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120303/7a41a438/attachment-0004.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: RoomStudy-BASELINE.idf
Type: application/octet-stream
Size: 46020 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120303/7a41a438/attachment-0005.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Enthalpy of Phase Change Materials as a Function of Temperature Required Accuracy and Suitable Measurement Methods.pdf
Type: application/pdf
Size: 1265014 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120303/7a41a438/attachment-0006.pdf>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: konstantinidou.pdf
Type: application/pdf
Size: 6915086 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120303/7a41a438/attachment-0007.pdf>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Determination of the enthalpy of PCM as a function of temperature using a heatflux DSC A study of different.pdf
Type: application/pdf
Size: 398755 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120303/7a41a438/attachment-0008.pdf>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: saylorASME (1).pdf
Type: application/pdf
Size: 428985 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120303/7a41a438/attachment-0009.pdf>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: stocktonDSC-TEST-ADV.pdf
Type: application/pdf
Size: 356811 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120303/7a41a438/attachment-0010.pdf>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EMail-BioPCM_101811.pdf
Type: application/pdf
Size: 2771478 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120303/7a41a438/attachment-0011.pdf>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: PCM_Frt_Back_rgb.jpg
Type: image/jpeg
Size: 345582 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120303/7a41a438/attachment-0001.jpg>
More information about the TRNSYS-users
mailing list