The min. mass flow rate calcualted by TRNbuild may differ from the
calculated during the simulation
If there it switches from turblent to laminar flow. However, this isn’t
your problem.
I had a quick look at your file
When I open your file b17 I get an error message for surface 15 (the
one with active layer):
The adjacent surface numbers of surface 12 and 15 are wrong!!
ZONE Z02
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE Z02
WALL =IW01 : SURF= 11 : AREA= 40.66 : INTERNAL
WALL =ID01 : SURF= 12 : AREA= 44.87 : ADJACENT=Z02 :
ADJ_SURF=5 : FRONT : INTEMP = INPUT 1*Z02_TABS_TETA_SW : MFLOW = INPUT
1*Z02_TABS_MASSFLOW : NLOOP = 6 : MFLOWMIN = 15
WALL =ID02 : SURF= 13 : AREA= 5.09 : BOUNDARY=IDENTICAL
WALL =ID03 : SURF= 14 : AREA= 12.69 : BOUNDARY=0
WALL =ID01 : SURF= 15 : AREA= 44.87 : ADJACENT=Z02 :
ADJ_SURF=1 : BACK : INTEMP = INPUT 1*Z02_TABS_TETA_SW : MFLOW = INPUT
1*Z02_TABS_MASSFLOW : NLOOP = 6 : MFLOWMIN = 15
WALL =ID05 : SURF= 16 : AREA= 12.69 : BOUNDARY=IDENTICAL
I assume you edit the file manually.
If I delete the wrong ADJ_SURF, and I reopen it TRNbuild it assigns the
the correct numbers.
Marion
Dipl.-Ing. Marion Hiller
TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes Bauen
und Nutzerkomfort in Gebäude
Munich - New York - Stuttgart + 49.711.67976.0
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart
Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.:
DE152272639
Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher
-----Ursprüngliche Nachricht-----
Von: Michael Döbele [mailto:michael.doebele at hochschule-bc.de]
Gesendet: Montag, 18. Juni 2012 23:25
An: trnsys-users at engr.wisc.edu
Betreff: [TRNSYS-users] minmassflowrate
Dear TRNSSYS User,
i am trying to run an active layer with an specific massflow rate of 15
kg/h m² (absolute value 654.15 kg/h). TRNBuild calculates a minimum
allowed massflow rate of 10.25 kg/h. (446 kg/h) ....so far so good.
But when I set this massflow rate in TRNSYS Studio via Input to the
wanted 654.15 kg/h I get following error
"specific fluid mass flow of active layer in surface 2 below minimum
value of16.26/m2h, increase the minimum mass flow rate or use
autosegmentation feature of TRNBuild for subdividing the surface."
This is a really strange behavior. The massflow criteria varies and
seems to depend on the inlet temperature.. I also tried autosegmentation
- I didn´t help, I got the same error message.
Please help me out here..
Thank you
Michael Döbele
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120621/3f1c4b8b/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 10538 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120621/3f1c4b8b/attachment-0005.jpg>
More information about the TRNSYS-users
mailing list