Dear TRNSSYS User,
i am trying to run an active layer with an specific massflow rate of 15
kg/h m² (absolute value 654.15 kg/h). TRNBuild calculates a minimum
allowed massflow rate of 10.25 kg/h. (446 kg/h) ....so far so good.
But when I set this massflow rate in TRNSYS Studio via Input to the
wanted 654.15 kg/h I get following error
"specific fluid mass flow of active layer in surface 2 below minimum
value of16.26/m2h, increase the minimum mass flow rate or use
autosegmentation feature of TRNBuild for subdividing the surface."
This is a really strange behavior. The massflow criteria varies and
seems to depend on the inlet temperature.. I also tried autosegmentation
- I didn´t help, I got the same error message.
Please help me out here..
Thank you
Michael Döbele
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Heizkurve.tpf
Type: application/octet-stream
Size: 124538 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120618/58272ccd/attachment-0005.obj>
-------------- next part --------------
*********************************************************************************************************************************************************************************************************
* TRNBuild 2.0.167
*********************************************************************************************************************************************************************************************************
* BUILDING DESCRIPTIONS FILE TRNSYS
* FOR BUILDING: E:\01 Thesis\04 Simulation TRNSYS\06 Typraum an R133_R134 (überarbeitet)\04 Ermitteln der Heiz- und Kühlkurven\DCK4_20120615.b17
* GET BY WORKING WITH TRNBuild 1.0 for Windows
*********************************************************************************************************************************************************************************************************
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* C o m m e n t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* P r o j e c t
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*+++ PROJECT
*+++ TITLE=TYPRAUM FÜR UBB VERFAHREN IN TRNSYS
*+++ DESCRIPTION=ERSTELLUNG EINES GEBÄUDEMODELLS FÜR BELIEBIGE BÜROGEBÄUDE
*+++ CREATED=MICHAEL DÖBELE MIT OPENOFFICECALC
*+++ ADDRESS=UNDEFINED
*+++ CITY=88400 BIBERACH
*+++ SWITCH=UNDEFINED
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* P r o p e r t i e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
PROPERTIES
DENSITY=1.204 : CAPACITY=1.012 : PRESSURE=101325.000 : HVAPOR=2454.0 : SIGMA=2.041e-007 : RTEMP=293.15
*--- alpha calculation -------------------
KFLOORUP=7.2 : EFLOORUP=0.31 : KFLOORDOWN=3.888 : EFLOORDOWN=0.31
KCEILUP=7.2 : ECEILUP=0.31 : KCEILDOWN=3.888 : ECEILDOWN=0.31
KVERTICAL=5.76 : EVERTICAL=0.3
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
TYPES
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* L a y e r s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
LAYER TABS1
PSPACING= 0.15 : PDIAMETER= 0.022 : PWALLTHICKNESS= 0.0023 : PCONDUCTIVITY= 1.44 : CPFLUID= 4.18
LAYER BE_NORMALBETON_21
CONDUCTIVITY= 7.56 : CAPACITY= 1 : DENSITY= 2100
LAYER BE_LEICHTBETON_049
CONDUCTIVITY= 1.764 : CAPACITY= 1 : DENSITY= 1000
LAYER PME_ZE14
CONDUCTIVITY= 5.04 : CAPACITY= 1 : DENSITY= 2000
LAYER PME_GP07
CONDUCTIVITY= 2.52 : CAPACITY= 1 : DENSITY= 2000
LAYER WD_MW035
CONDUCTIVITY= 0.126 : CAPACITY= 1 : DENSITY= 200
LAYER WD_MW045
CONDUCTIVITY= 0.162 : CAPACITY= 1 : DENSITY= 200
LAYER WD_PS040
CONDUCTIVITY= 0.144 : CAPACITY= 1 : DENSITY= 200
LAYER WD_PUR025
CONDUCTIVITY= 0.09 : CAPACITY= 1.4 : DENSITY= 50
LAYER PL_GKPL025
CONDUCTIVITY= 0.9 : CAPACITY= 1 : DENSITY= 900
LAYER PL_OSB013
CONDUCTIVITY= 0.468 : CAPACITY= 1.7 : DENSITY= 650
LAYER PL_TRESTR
CONDUCTIVITY= 1.8 : CAPACITY= 1 : DENSITY= 1200
LAYER SO_TEPPICH
CONDUCTIVITY= 0.198 : CAPACITY= 1.3 : DENSITY= 200
LAYER SO_PVC
CONDUCTIVITY= 0.144 : CAPACITY= 1.2 : DENSITY= 1390
LAYER SO_LUFT003
RESISTANCE= 0.153
LAYER SO_EINFACHGLAS
CONDUCTIVITY= 5.04 : CAPACITY= 0.75 : DENSITY= 2200
LAYER SO_GIPSKARTON
CONDUCTIVITY= 11.664 : CAPACITY= 1 : DENSITY= 900
LAYER HW_SPLANPLATTE
CONDUCTIVITY= 0.313 : CAPACITY= 2.7 : DENSITY= 800
LAYER HW_HDFPLATTE
CONDUCTIVITY= 0.648 : CAPACITY= 1.7 : DENSITY= 1000
LAYER WD_FIBER_ISULATING
CONDUCTIVITY= 0.18 : CAPACITY= 1.4 : DENSITY= 250
LAYER PME_PUTZ_070
CONDUCTIVITY= 3.6 : CAPACITY= 1 : DENSITY= 200
LAYER WD_MW040
CONDUCTIVITY= 0.144 : CAPACITY= 1 : DENSITY= 200
LAYER SO_LUFT020
RESISTANCE= 0.044
LAYER TABS2
PSPACING= 0.15 : PDIAMETER= 0.022 : PWALLTHICKNESS= 0.0023 : PCONDUCTIVITY= 1.44 : CPFLUID= 4.18
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* I n p u t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
INPUTS Z01_TABS_TETA_SW Z01_TABS_MASSFLOW SHADE_SE SHADE_SW SHADE_NW SHADE_NE Z01_QGAIN Z02_TABS_TETA_SW Z02_TABS_MASSFLOW Z02_QGAIN Z01_VENT_AIRCHANGE Z01_VENT_ZULUFTTEMP Z02_VENT_AIRCHANGE ;
Z02_VENT_ZULUFTTEMP
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* S c h e d u l e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
SCHEDULE MONTAG_MAX
HOURS =0.000 7.000 13.000 14.000 17.000 24.0
VALUES=0 0.9 0 0.9 0 0
SCHEDULE DIENSTAG_FREITAG_MIN
HOURS =0.000 7.000 14.000 24.0
VALUES=0 0.35 0 0
SCHEDULE MONTAG_MIN
HOURS =0.000 7.000 13.000 14.000 17.000 24.0
VALUES=0 0.35 0 0.35 0 0
SCHEDULE DIENSTAG_FREITAG_MAX
HOURS =0.000 6.000 7.000 14.000 24.0
VALUES=0 0 0.9 0 0
SCHEDULE WOCHENENDE
HOURS =0.000 6.000 24.0
VALUES=0 0 0
SCHEDULE GESAMTWOCHE_MIN
DAYS=1 2 3 4 5 6 7
HOURLY=MONTAG_MIN DIENSTAG_FREITAG_MIN DIENSTAG_FREITAG_MIN DIENSTAG_FREITAG_MIN DIENSTAG_FREITAG_MIN WOCHENENDE WOCHENENDE
SCHEDULE GESAMTWOCHE_MAX
DAYS=1 2 3 4 5 6 7
HOURLY=MONTAG_MAX DIENSTAG_FREITAG_MAX DIENSTAG_FREITAG_MAX DIENSTAG_FREITAG_MAX DIENSTAG_FREITAG_MAX WOCHENENDE WOCHENENDE
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* W a l l s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
WALL AW01
LAYERS = BE_NORMALBETON_21 WD_FIBER_ISULATING SO_EINFACHGLAS
THICKNESS= 0.1 0.2 0.01
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = VERTICAL : HBACK= 72
WALL ID01
LAYERS = BE_NORMALBETON_21 TABS1 BE_NORMALBETON_21 SO_TEPPICH
THICKNESS= 0.175 0 0.175 0.005
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = CEILING : HBACK= FLOOR
WALL ID02
LAYERS = BE_NORMALBETON_21 SO_TEPPICH
THICKNESS= 0.35 0.01
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = CEILING : HBACK= FLOOR
WALL ID03
LAYERS = SO_GIPSKARTON WD_MW040 SO_LUFT020 BE_NORMALBETON_21 SO_TEPPICH
THICKNESS= 0.012 0.02 0 0.35 0.005
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = CEILING : HBACK= 11
WALL ID04
LAYERS = SO_TEPPICH BE_NORMALBETON_21 TABS1 BE_NORMALBETON_21
THICKNESS= 0.005 0.175 0 0.175
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = FLOOR : HBACK= CEILING
WALL ID05
LAYERS = SO_TEPPICH BE_NORMALBETON_21 SO_LUFT020 WD_MW040 SO_GIPSKARTON
THICKNESS= 0.005 0.35 0 0.02 0.01
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = FLOOR : HBACK= 11
WALL ID06
LAYERS = SO_TEPPICH BE_NORMALBETON_21
THICKNESS= 0.005 0.35
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = FLOOR : HBACK= CEILING
WALL IT01
LAYERS = HW_SPLANPLATTE
THICKNESS= 0.05
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = VERTICAL : HBACK= VERTICAL
WALL IW01
LAYERS = SO_GIPSKARTON WD_PS040 SO_GIPSKARTON
THICKNESS= 0.03 0.1 0.03
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = VERTICAL : HBACK= VERTICAL
WALL AW02
LAYERS = BE_NORMALBETON_21 WD_FIBER_ISULATING PME_PUTZ_070
THICKNESS= 0.25 0.2 0.015
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = VERTICAL : HBACK= 72
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* W i n d o w s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
WINDOW ATSTD
WINID=12007 : HINSIDE=39.6 : HOUTSIDE=230.4 : SLOPE=90 : SPACID=1 : WWID=0.77 : WHEIG=1.08 : FFRAME=0.15 : UFRAME=29.41 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0 : REFLOSHADE=0 : ;
CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
WINDOW AFTRH
WINID=12007 : HINSIDE=10.98 : HOUTSIDE=72 : SLOPE=90 : SPACID=4 : WWID=1.16 : WHEIG=1 : FFRAME=0.22 : UFRAME=5.04 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=1 : REFLOSHADE=1 : CCISHADE=0.5 :;
EPSFRAME=0.9 : EPSISHADE=0.9
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* D e f a u l t G a i n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* O t h e r G a i n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
GAIN Z01_KEINE_LAST
CONVECTIVE=87.0175 : RADIATIVE=130.526 : HUMIDITY=0
GAIN Q_GAIN_Z01_ITC
CONVECTIVE=INPUT 0.4*Z01_QGAIN : RADIATIVE=INPUT 0.6*Z01_QGAIN : HUMIDITY=0
GAIN Z02_KEINE_LAST
CONVECTIVE=88.3523 : RADIATIVE=132.528 : HUMIDITY=0
GAIN Q_GAIN_Z02_ITC
CONVECTIVE=INPUT 0.4*Z02_QGAIN : RADIATIVE=INPUT 0.6*Z02_QGAIN : HUMIDITY=0
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* C o m f o r t
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* I n f i l t r a t i o n
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
INFILTRATION STANDARD
AIRCHANGE=0.1
INFILTRATION KEINE_INF
AIRCHANGE=0
INFILTRATION GMS
AIRCHANGE=0.024
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* V e n t i l a t i o n
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
VENTILATION Z01_VENT_INPUT
TEMPERATURE=INPUT 1*Z01_VENT_ZULUFTTEMP
AIRCHANGE=INPUT 1*Z01_VENT_AIRCHANGE
HUMIDITY=0
VENTILATION Z02_VENT_INPUT
TEMPERATURE=INPUT 1*Z02_VENT_ZULUFTTEMP
AIRCHANGE=INPUT 1*Z02_VENT_AIRCHANGE
HUMIDITY=0
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* C o o l i n g
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* H e a t i n g
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONES Z01 Z02
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* O r i e n t a t i o n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ORIENTATIONS HORIZONTAL NORTHEAST NORTHWEST SOUTHEAST SOUTHWEST
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
BUILDING
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e Z01 / A i r n o d e Z01
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE Z01
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE Z01
WALL =IW01 : SURF= 1 : AREA= 63.99 : INTERNAL
WALL =ID01 : SURF= 2 : AREA= 43.61 : ADJACENT=Z01 : ADJ_SURF=5 : FRONT : INTEMP = INPUT 1*Z01_TABS_TETA_SW : MFLOW = INPUT 1*Z01_TABS_MASSFLOW : NLOOP = 6 : MFLOWMIN = 15
WALL =ID02 : SURF= 3 : AREA= 5.63 : BOUNDARY=IDENTICAL
WALL =ID03 : SURF= 4 : AREA= 13.56 : BOUNDARY=IDENTICAL
WALL =ID01 : SURF= 5 : AREA= 43.61 : ADJACENT=Z01 : ADJ_SURF=2 : BACK : INTEMP = INPUT 1*Z02_TABS_TETA_SW : MFLOW = INPUT 1*Z02_TABS_MASSFLOW : NLOOP = 6 : MFLOWMIN = 15
WALL =ID05 : SURF= 6 : AREA= 12.94 : BOUNDARY=IDENTICAL
WALL =ID06 : SURF= 7 : AREA= 6.26 : BOUNDARY=IDENTICAL
WALL =IT01 : SURF= 8 : AREA= 2.27 : BOUNDARY=IDENTICAL
WALL =AW01 : SURF= 9 : AREA= 9.28 : EXTERNAL : ORI=SOUTHEAST : FSKY=0.5
WINDOW=AFTRH : SURF= 10 : AREA= 18.72 : EXTERNAL : ORI=SOUTHEAST : FSKY=0.5 : ESHADE=INPUT 0.8*SHADE_SE
REGIME
GAIN = Z01_KEINE_LAST : SCALE= 0 : GEOPOS= 0
GAIN = Q_GAIN_Z01_ITC : SCALE= 1 : GEOPOS= 0
INFILTRATION= GMS
VENTILATION = Z01_VENT_INPUT
CAPACITANCE = 233.77 : VOLUME= 194.81 : TINITIAL= 0 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e Z02 / A i r n o d e Z02
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE Z02
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE Z02
WALL =IW01 : SURF= 11 : AREA= 40.66 : INTERNAL
WALL =ID01 : SURF= 12 : AREA= 44.87 : ADJACENT=Z02 : ADJ_SURF=5 : FRONT : INTEMP = INPUT 1*Z02_TABS_TETA_SW : MFLOW = INPUT 1*Z02_TABS_MASSFLOW : NLOOP = 6 : MFLOWMIN = 15
WALL =ID02 : SURF= 13 : AREA= 5.09 : BOUNDARY=IDENTICAL
WALL =ID03 : SURF= 14 : AREA= 12.69 : BOUNDARY=0
WALL =ID01 : SURF= 15 : AREA= 44.87 : ADJACENT=Z02 : ADJ_SURF=1 : BACK : INTEMP = INPUT 1*Z02_TABS_TETA_SW : MFLOW = INPUT 1*Z02_TABS_MASSFLOW : NLOOP = 6 : MFLOWMIN = 15
WALL =ID05 : SURF= 16 : AREA= 12.69 : BOUNDARY=IDENTICAL
WALL =ID06 : SURF= 17 : AREA= 5.09 : BOUNDARY=IDENTICAL
WALL =IT01 : SURF= 18 : AREA= 2.27 : BOUNDARY=IDENTICAL
WALL =AW01 : SURF= 19 : AREA= 10.46 : EXTERNAL : ORI=SOUTHEAST : FSKY=0.5
WINDOW=AFTRH : SURF= 20 : AREA= 18.75 : EXTERNAL : ORI=SOUTHEAST : FSKY=0.5 : ESHADE=INPUT 0.8*SHADE_SE
WALL =AW02 : SURF= 21 : AREA= 30.14 : EXTERNAL : ORI=NORTHEAST : FSKY=0.5
WINDOW=AFTRH : SURF= 22 : AREA= 0.01 : EXTERNAL : ORI=NORTHEAST : FSKY=0.5 : ESHADE=INPUT 0.8*SHADE_NE
REGIME
GAIN = Z02_KEINE_LAST : SCALE= 0 : GEOPOS= 0
GAIN = Q_GAIN_Z02_ITC : SCALE= 1 : GEOPOS= 0
INFILTRATION= GMS
VENTILATION = Z02_VENT_INPUT
CAPACITANCE = 233.77 : VOLUME= 194.81 : TINITIAL= 0 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* O u t p u t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
OUTPUTS
TRANSFER : TIMEBASE=1.000
AIRNODES = Z01
NTYPES = 75 : QTSABS - total solar radiation absorbed at all inside surfaces of airnode
= 25 : TOP - obsolete use new comfort outputs (Version 16: Operative temperature)
AIRNODES = Z02
NTYPES = 75 : QTSABS - total solar radiation absorbed at all inside surfaces of airnode
= 25 : TOP - obsolete use new comfort outputs (Version 16: Operative temperature)
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* T R N S F L O W Multizone Airflow Network (Model COMIS 3.1)
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
MULTIZONE_AIRFLOW_NETWORK
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
CALCFLOWS=0
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* A d d T R N S F L O W C o m m a n d s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
POLLUTANTS
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
LINKTYPES
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* C r a c k s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* F a n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* S t r a i g h t D u c t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* F l o w C o n t r o l l e r s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* L a r g e V e r t i c a l Openings (Windows+Doors)
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* T e s t D a t a C o m p o n e n t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
NODETYPES
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* E x t e r n a l N o d e s (CP VALUES)
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* A u x i l i a r y N o d e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* T h e r m a l Z o n e N o d e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* W i n d v e l o c i t y p r o f i l e
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
WIND_VELOPROF
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* A i r l i n k N e t w o r k
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
AIRLINK_NETWORK
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* E n d
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
END
_EXTENSION_WINPOOL_START_
WINDOW 4.1 DOE-2 Data File : Multi Band Calculation
Unit System : SI
Name : TRNSYS15 WINDOW LIB
Desc : Pilkington OPTITHERM Besch.#2#5 4/16/4/16/4
Window ID : 12007
Tilt : 90.0
Glazings : 3
Frame : 11 TRNSYS WIN - 1 2.270
Spacer : 1 Class1 2.330 -0.010 0.138
Total Height: 1600.0 mm
Total Width : 1250.0 mm
Glass Height: 1460.3 mm
Glass Width : 1110.3 mm
Mullion : None
Gap Thick Cond dCond Vis dVis Dens dDens Pr dPr
1 Argon 16.0 0.01620 5.000 2.110 6.300 1.780 -0.0060 0.680 0.00066
2 Argon 16.0 0.01620 5.000 2.110 6.300 1.780 -0.0060 0.680 0.00066
3 0 0 0 0 0 0 0 0 0
4 0 0 0 0 0 0 0 0 0
5 0 0 0 0 0 0 0 0 0
Angle 0 10 20 30 40 50 60 70 80 90 Hemis
Tsol 0.387 0.386 0.382 0.376 0.367 0.348 0.304 0.216 0.086 0.000 0.321
Abs1 0.186 0.187 0.188 0.191 0.194 0.199 0.206 0.214 0.206 0.000 0.196
Abs2 0.077 0.078 0.079 0.081 0.084 0.088 0.092 0.095 0.081 0.000 0.085
Abs3 0.079 0.080 0.081 0.081 0.079 0.076 0.072 0.059 0.029 0.000 0.072
Abs4 0 0 0 0 0 0 0 0 0 0 0
Abs5 0 0 0 0 0 0 0 0 0 0 0
Abs6 0 0 0 0 0 0 0 0 0 0 0
Rfsol 0.270 0.270 0.270 0.270 0.275 0.288 0.326 0.417 0.598 1.000 0.316
Rbsol 0.327 0.326 0.325 0.326 0.332 0.349 0.394 0.497 0.690 1.000 0.379
Tvis 0.643 0.642 0.637 0.628 0.612 0.576 0.492 0.339 0.138 0.000 0.530
Rfvis 0.152 0.151 0.152 0.155 0.165 0.195 0.269 0.417 0.639 1.000 0.237
Rbvis 0.152 0.151 0.151 0.155 0.167 0.199 0.275 0.427 0.667 1.000 0.242
SHGC 0.501 0.501 0.499 0.494 0.485 0.465 0.419 0.321 0.158 0.000 0.433
SC: 0.50
Layer ID# 4060F 4046 4068 0 0 0
Tir 0.000 0.000 0.000 0 0 0
Emis F 0.840 0.840 0.090 0 0 0
Emis B 0.090 0.840 0.840 0 0 0
Thickness(mm) 4.0 4.0 4.0 0 0 0
Cond(W/m2-C ) 225.0 225.0 225.0 0 0 0
Spectral File None None None None None None
Overall and Center of Glass Ig U-values (W/m2-C)
Outdoor Temperature -17.8 C 15.6 C 26.7 C 37.8 C
Solar WdSpd hcout hrout hin
(W/m2) (m/s) (W/m2-C)
0 0.00 12.25 3.21 7.25 0.73 0.73 0.66 0.66 0.69 0.69 0.72 0.72
0 6.71 25.47 3.19 7.26 0.75 0.75 0.68 0.68 0.70 0.70 0.73 0.73
783 0.00 12.25 3.43 7.95 0.80 0.80 0.84 0.84 0.86 0.86 0.88 0.88
783 6.71 25.47 3.32 7.87 0.81 0.81 0.84 0.84 0.87 0.87 0.91 0.91
*** END OF LIBRARY ***
***************************************************************************************************
*WinID Description Design U-Value g-value T-sol Rf-sol T-vis
***************************************************************************************************
12007 Pilkington OPTITHERM Besch.#2#5 4/16/4/16/4 4/16/4/16/4 0.7 0.501 0.387 0.27 0.643
_EXTENSION_WINPOOL_END_
_EXTENSION_BuildingGeometry_START_
_EXTENSION_BuildingGeometry_END_
_EXTENSION_ExternalShadingGeometry_START_
_EXTENSION_ExternalShadingGeometry_END_
_EXTENSION_GeoPositionGeometry_START_
_EXTENSION_GeoPositionGeometry_END_
-------------- next part --------------
TRNSYS - the TRaNsient SYstem Simulation program
The Solar Energy Lab at the University of Wisconsin - Madison, USA
Le Centre Scientifique et Technique du Batiment, Sophia Antipolis, France
Transsolar Energietechnik GmBH, Stuttgart, Germany
Thermal Energy System Specialists, LLC, Madison Wisconsin, USA
Release 17.00.0019
Listing file for: "E:\01 Thesis\04 Simulation TRNSYS\06 Typräume an R133_R134 (überarbeitet)\04 Ermitteln der Heiz- und Kühlkurven\Heizkurve.dck"
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : The TRNSYS Executable (TRNExe.exe) and main DLL (TRNDll.dll) are located in "C:\PROGRA~1\Trnsys17\Exe"
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : 208
TRNSYS Message 75 : The Type referenced below requires descriptors instead of initial values.
Reported information : Type 208
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : 535
TRNSYS Message 75 : The Type referenced below requires descriptors instead of initial values.
Reported information : Type 535
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : 580
TRNSYS Message 76 : The following Type has been identified as allowing the unit specifications (kg/h for example) after the input specifications and intial values for the inputs. The critical parameter number, and the value of this critical parameter that indicates that the units will be supplied is also listed. This information was retrieved from the VarUnits.dat file loacted in the \Exe directory of your TRNSYS 16 installation.
Reported information : Type 580, Critical Parameter 11, Parameter Value 1
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : 580
TRNSYS Message 88 : The following Type has been identified as allowing FORMAT statements. This information was retrieved from the Formats.dat file loacted in the \Exe directory of your TRNSYS 16 installation.
Reported information : Type 580
*** Pre-Processing the TRNSYS EQUATIONs and CONSTANTs to check for fatal errors.
*** Pre-Processing of EQUATIONs and CONSTANTs completed with no fatal errors found.
*** Evaluating the EQUATIONs and CONSTANTs to determine their initial values.
*** Finished evaluating the EQUATIONs and CONSTANTs and ready to begin processing the remainder of the TRNSYS input file.
VERSION 17
*******************************************************************************
*** TRNSYS input file (deck) generated by TrnsysStudio
*** on Montag, Juni 18, 2012 at 16:50
*** from TrnsysStudio project: E:\01 Thesis\04 Simulation TRNSYS\06 Typräume an R133_R134 (überarbeitet)\04 Ermitteln der Heiz- und Kühlkurven\Heizkurve.tpf
***
*** If you edit this file, use the File/Import TRNSYS Input File function in
*** TrnsysStudio to update the project.
***
*** If you have problems, questions or suggestions please contact your local
*** TRNSYS distributor or mailto:software at cstb.fr
***
*******************************************************************************
*******************************************************************************
*** Units
*******************************************************************************
*******************************************************************************
*** Control cards
*******************************************************************************
* START, STOP and STEP
CONSTANTS 3
START=0
STOP=8760
STEP=1
* User defined CONSTANTS
! Start time End time Time step
SIMULATION 0.0000000000000000E+00 8.7600000000000000E+03 1.0000000000000000E+00
! Integration Convergence
TOLERANCES 1.0000000000000002E-03 1.0000000000000002E-03
! Max iterations Max warnings Trace limit
LIMITS 30 500 51
! TRNSYS numerical integration solver method
DFQ 1
! TRNSYS output file width, number of characters
WIDTH 80
! NOLIST statement
LIST
! MAP statement
! Solver statement Minimum relaxation factor Maximum relaxation factor
SOLVER 0
1.000000000000000
1.000000000000000
! Nan DEBUG statement
NAN_CHECK 0
! Overwrite DEBUG statement
OVERWRITE_CHECK 0
! disable time report
TIME_REPORT 0
! EQUATION SOLVER statement
EQUATION SOLVING METHOD 0
* EQUATIONS "Randbedingung äquivalente Wärmegewinnschranke"
*
EQUATIONS 2
Z01_Q_ELB = 1.4*62.8*3.6
Z02_Q_ELB = 1.5*62.6*3.6
*$UNIT_NAME Randbedingung äquivalente Wärmegewinnschranke
*$LAYER Main
*$POSITION 299 319
*------------------------------------------------------------------------------
* EQUATIONS "Randbedingung Technik"
*
EQUATIONS 6
Z01_TABS_MASSFLOW = 750
Z02_TABS_MASSFLOW = 750
Z01_VENT_AIRCHANGE = 0.18
Z02_VENT_AIRCHANGE = 0.18
Z01_VENT_ZULUFTTEMP = 21
Z02_VENT_ZULUFTTEMP = 21
*$UNIT_NAME Randbedingung Technik
*$LAYER Main
*$POSITION 300 244
*------------------------------------------------------------------------------
* EQUATIONS "Randbedingung Wetter"
*
EQUATIONS 4
TAMB = 10
RELHUMAMB = 0
TSGRD = 0
TSKY = 0
*$UNIT_NAME Randbedingung Wetter
*$LAYER Main
*$POSITION 297 148
*------------------------------------------------------------------------------
* Model "Type56" (Type 56)
*
UNIT 5 TYPE 56
*$UNIT_NAME Type56
*$MODEL \Programme\Trnsys17\Studio\lib\Updates\Type56.tmf
*$POSITION 479 258
*$LAYER Main #
*$#
PARAMETERS 3
! 1 Logical unit for building description file (.bui)
! 2 Star network calculation switch
! 3 Weighting factor for operative temperature
5.5000000000000000E+01 0.0000000000000000E+00 5.0000000000000000E-01
INPUTS 36
! Randbedingung Wetter:TAMB -> 1- TAMB
! Randbedingung Wetter:RELHUMAMB -> 2- RELHUMAMB
! Randbedingung Wetter:TSKY -> 3- TSKY
! Randbedingung Wetter:TSGRD -> 4- TSGRD
! [unconnected] 5- AZEN
! [unconnected] 6- AAZM
! [unconnected] 7- IT_HORIZONTAL
! [unconnected] 8- IT_NORTHEAST
! [unconnected] 9- IT_NORTHWEST
! [unconnected] 10- IT_SOUTHEAST
! [unconnected] 11- IT_SOUTHWEST
! [unconnected] 12- IB_HORIZONTAL
! [unconnected] 13- IB_NORTHEAST
! [unconnected] 14- IB_NORTHWEST
! [unconnected] 15- IB_SOUTHEAST
! [unconnected] 16- IB_SOUTHWEST
! [unconnected] 17- AI_HORIZONTAL
! [unconnected] 18- AI_NORTHEAST
! [unconnected] 19- AI_NORTHWEST
! [unconnected] 20- AI_SOUTHEAST
! [unconnected] 21- AI_SOUTHWEST
! [unconnected] 22- GRDREF
! R133:Control signal -> 23- Z01_TABS_TETA_SW
! Randbedingung Technik:Z01_TABS_MASSFLOW -> 24- Z01_TABS_MASSFLOW
! [unconnected] 25- SHADE_SE
! [unconnected] 26- SHADE_SW
! [unconnected] 27- SHADE_NW
! [unconnected] 28- SHADE_NE
! Randbedingung äquivalente Wärmegewinnschranke:Z01_Q_ELB -> 29- Z01_QGAIN
! R134:Control signal -> 30- Z02_TABS_TETA_SW
! Randbedingung Technik:Z02_TABS_MASSFLOW -> 31- Z02_TABS_MASSFLOW
! Randbedingung äquivalente Wärmegewinnschranke:Z02_Q_ELB -> 32- Z02_QGAIN
! Randbedingung Technik:Z01_VENT_AIRCHANGE -> 33- Z01_VENT_AIRCHANGE
! Randbedingung Technik:Z01_VENT_ZULUFTTEMP -> 34- Z01_VENT_ZULUFTTEMP
! Randbedingung Technik:Z02_VENT_AIRCHANGE -> 35- Z02_VENT_AIRCHANGE
! Randbedingung Technik:Z02_VENT_ZULUFTTEMP -> 36- Z02_VENT_ZULUFTTEMP
TAMB RELHUMAMB TSKY TSGRD CONST
CONST CONST CONST CONST CONST
CONST CONST CONST CONST CONST
CONST CONST CONST CONST CONST
CONST CONST 10,1 Z01_TABS_MASSFLOW CONST
CONST CONST CONST Z01_Q_ELB 9,1
Z02_TABS_MASSFLOW Z02_Q_ELB Z01_VENT_AIRCHANGE Z01_VENT_ZULUFTTEMP Z02_VENT_AIRCHANGE
Z02_VENT_ZULUFTTEMP
*** INITIAL INPUT VALUES
0.0000000000000000E+00 0.0000000000000000E+00 0.0000000000000000E+00 0.0000000000000000E+00 0.0000000000000000E+00
0.0000000000000000E+00 0.0000000000000000E+00 0.0000000000000000E+00 0.0000000000000000E+00 0.0000000000000000E+00
0.0000000000000000E+00 0.0000000000000000E+00 0.0000000000000000E+00 0.0000000000000000E+00 0.0000000000000000E+00
0.0000000000000000E+00 0.0000000000000000E+00 0.0000000000000000E+00 0.0000000000000000E+00 0.0000000000000000E+00
0.0000000000000000E+00 0.0000000000000000E+00 0.0000000000000000E+00 0.0000000000000000E+00 0.0000000000000000E+00
0.0000000000000000E+00 0.0000000000000000E+00 0.0000000000000000E+00 0.0000000000000000E+00 0.0000000000000000E+00
0.0000000000000000E+00 0.0000000000000000E+00 0.0000000000000000E+00 0.0000000000000000E+00 0.0000000000000000E+00
0.0000000000000000E+00
*** External files
ASSIGN DCK4_20120615.b17 55
*|? Building description file (*.bui) |1000
*------------------------------------------------------------------------------
* Model "Type65d-2" (Type 65)
*
UNIT 6 TYPE 65
*$UNIT_NAME Type65d-2
*$MODEL .\Output\Online Plotter\Online Plotter Without File\Type65d.tmf
*$POSITION 893 191
*$LAYER Main #
PARAMETERS 12
! 1 Nb. of left-axis variables
! 2 Nb. of right-axis variables
! 3 Left axis minimum
! 4 Left axis maximum
! 5 Right axis minimum
! 6 Right axis maximum
! 7 Number of plots per simulation
! 8 X-axis gridpoints
! 9 Shut off Online w/o removing
! 10 Logical unit for output file
! 11 Output file units
! 12 Output file delimiter
2.0000000000000000E+00 2.0000000000000000E+00 0.0000000000000000E+00 1.0000000000000000E+02 0.0000000000000000E+00
1.0000000000000000E+02 1.0000000000000000E+00 1.2000000000000000E+01 0.0000000000000000E+00 -1.0000000000000000E+00
0.0000000000000000E+00 0.0000000000000000E+00
INPUTS 4
! Type56: 2- TOP_Z01 ->Left axis variable-1
! Type56: 4- TOP_Z02 ->Left axis variable-2
! R133:Control signal ->Right axis variable-1
! R134:Control signal ->Right axis variable-2
5,2 5,4 10,1 9,1
*** INITIAL INPUT VALUES
R133_TOP R134_TOP R133_Vorla uftempeatur R134_ Vorlauftemperatur
LABELS 3
operative Raumtemperatur in °C
Vorlauftemperatur TABS in °C
Graph 1
*------------------------------------------------------------------------------
* Model "TOP TABS_TETA_SW" (Type 25)
*
UNIT 7 TYPE 25 TABS_TETA_SW
*$UNIT_NAME TOP TABS_TETA_SW
*$MODEL .\Output\Printer\User-Supplied Units\Type25b.tmf
*$POSITION 895 93
*$LAYER Main #
PARAMETERS 10
! 1 Printing interval
! 2 Start time
! 3 Stop time
! 4 Logical unit
! 5 Units printing mode
! 6 Relative or absolute start time
! 7 Overwrite or Append
! 8 Print header
! 9 Delimiter
! 10 Print labels
1.0000000000000000E+00 0.0000000000000000E+00 9.4320000000000000E+03 5.6000000000000000E+01 1.0000000000000000E+00
0.0000000000000000E+00 -1.0000000000000000E+00 -1.0000000000000000E+00 0.0000000000000000E+00 1.0000000000000000E+00
INPUTS 4
! Type56: 2- TOP_Z01 ->Input to be printed-1
! R133:Control signal ->Input to be printed-2
! Type56: 4- TOP_Z02 ->Input to be printed-3
! R134:Control signal ->Input to be printed-4
5,2 10,1 5,4 9,1
*** INITIAL INPUT VALUES
R133_TOP R133_TABS_TETA_ SW R134_TOP R134_ TABS_TETA_SW
- - - -
*** External files
ASSIGN Heizkurve.out 56
*|? Output file for printed results |1000
*------------------------------------------------------------------------------
* Model "R133" (Type 23)
*
UNIT 10 TYPE 23
*$UNIT_NAME R133
*$MODEL .\Controllers\PID Controller\Type23.tmf
*$POSITION 494 116
*$LAYER Main #
PARAMETERS 2
! 1 mode
! 2 Maximum number of oscillations
0.0000000000000000E+00 0.0000000000000000E+00
INPUTS 13
! [unconnected] Setpoint
! Type56: 2- TOP_Z01 ->Controlled variable
! [unconnected] On / Off signal
! [unconnected] Minimum control signal
! [unconnected] Maximum control signal
! [unconnected] Threshold for non-zero output
! [unconnected] Gain constant
! [unconnected] Integral time
! [unconnected] Derivative time
! [unconnected] Tracking time for anti-windup
! [unconnected] Fraction of ySet for proportional effect
! [unconnected] Fraction of ySet for derivative effect
! [unconnected] High-frequency limit on derivative
CONST 5,2 CONST CONST CONST
CONST CONST CONST CONST CONST
CONST CONST CONST
*** INITIAL INPUT VALUES
2.0000000000000000E+01 0.0000000000000000E+00 1.0000000000000000E+00 -1.0000000000000000E+06 1.0000000000000000E+06
0.0000000000000000E+00 1.0000000000000000E+00 1.0000000000000000E+00 0.0000000000000000E+00 -1.0000000000000000E+00
1.0000000000000000E+00 1.0000000000000000E+00 1.0000000000000000E+01
*------------------------------------------------------------------------------
* Model "R134" (Type 23)
*
UNIT 9 TYPE 23
*$UNIT_NAME R134
*$MODEL .\Controllers\PID Controller\Type23.tmf
*$POSITION 675 106
*$LAYER Main #
PARAMETERS 2
! 1 mode
! 2 Maximum number of oscillations
0.0000000000000000E+00 0.0000000000000000E+00
INPUTS 13
! [unconnected] Setpoint
! Type56: 4- TOP_Z02 ->Controlled variable
! [unconnected] On / Off signal
! [unconnected] Minimum control signal
! [unconnected] Maximum control signal
! [unconnected] Threshold for non-zero output
! [unconnected] Gain constant
! [unconnected] Integral time
! [unconnected] Derivative time
! [unconnected] Tracking time for anti-windup
! [unconnected] Fraction of ySet for proportional effect
! [unconnected] Fraction of ySet for derivative effect
! [unconnected] High-frequency limit on derivative
CONST 5,4 CONST CONST CONST
CONST CONST CONST CONST CONST
CONST CONST CONST
*** INITIAL INPUT VALUES
2.0000000000000000E+01 0.0000000000000000E+00 1.0000000000000000E+00 -1.0000000000000000E+06 1.0000000000000000E+06
0.0000000000000000E+00 1.0000000000000000E+00 1.0000000000000000E+00 0.0000000000000000E+00 -1.0000000000000000E+00
1.0000000000000000E+00 1.0000000000000000E+00 1.0000000000000000E+01
*------------------------------------------------------------------------------
END
TRANSIENT SIMULATION STARTING AT TIME = 0.0000000000000000E+00
STOPPING AT TIME = 8.7600000000000000E+03
TIMESTEP = 1 / 1
DIFFERENTIAL EQUATION ERROR TOLERANCE = 1.0000000000000002E-03
ALGEBRAIC CONVERGENCE TOLERANCE = 1.0000000000000002E-03
DIFFERENTIAL EQUATIONS SOLVED BY MODIFIED EULER
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
TRNSYS Message 90 : TRNDll.dll is compiled in release mode. External DLLs will be loaded from the .\UserLib\ReleaseDLLs\ directory.
Reported information : Not available
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : The following Types were loaded from TRNDll.dll: Type56, Type65, Type25, Type23
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "FileReader.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSApplicationsLibrary_ReleaseVersion204.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSApplicationsLibrary_v17.01_Release.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSArchiveDLL_v2.04_Release.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSControllersLibrary_v17.01_Release.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSControlsLibrary_ReleaseVersion204.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSElectricalLibrary_v17.01_Release.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSGHPLibraryType997_v17.01_Release.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSGHPLibrary_ReleaseVersion204.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSGHPLibrary_v17.01_Release.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSGreenBuildingLibrary_ReleaseVersion204.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSGroundCouplingLibrary_ReleaseVersion204.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSGroundCouplingLibrary_v17.01_Release.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSGroundCouplingType1244_v17.01_Release.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSGroundCouplingType1255_v17.01_Release.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSGroundCouplingType1256_v17.01_Release.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSGroundCouplingType957_v17.01_Release.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSGroundCouplingType993_v17.01_Release.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSHVACLibrary_ReleaseVersion204.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSHVACLibrary_v17.01_Release.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSHydronicsLibrary_ReleaseVersion204.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSHydronicsLibrary_v17.01_Release.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSLoadsAndStructuresLibrary_ReleaseVersion204.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSLoadsStructuresLibrary_v17.01_Release.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSOptimizationLibrary_ReleaseVersion204.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSOptimizationLibrary_v17.01_Release.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSSolarLibrary_ReleaseVersion204.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSSolarLibrary_v17.01_Release.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSStorageLibrary_ReleaseVersion204.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSStorageLibrary_v17.01_Release.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSUtilityLibrary_ReleaseVersion204.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "TESSUtilityLibrary_v17.01_Release.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "type127.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "Type157_demo_release.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "type320.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "type333.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "type334.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "type340.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "type360.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "type361.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "type362.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "type371.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "type372.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "type401.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "type451.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "type460.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "Type76Lib.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "type79-W.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "Type79Lib.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "Type82Lib.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "Type858-diffeqn.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
TRNSYS Message 199 : TRNSYS found at least one user DLL in the UserLib directory. (Note: Only DLL's including Types that are used in the simulation are loaded)
Reported information : 0 user DLLs were loaded after searching in "C:\PROGRA~1\Trnsys17\UserLib\ReleaseDLLs"
*** Notice at time : 0.000000
Generated by Unit : 5
Generated by Type : 56
Message : Shading mask file *.shm for external windows does not exist.
*** Notice at time : 0.000000
Generated by Unit : 5
Generated by Type : 56
Message : TRNFLOW multi zone air flow model integrated
*** Notice at time : 0.000000
Generated by Unit : 5
Generated by Type : 56
Message : Active layers and internal window calculations integrated
*** Notice at time : 0.000000
Generated by Unit : 5
Generated by Type : 56
Message : No internal humidity calculations are performed and no condensation warnings are printed. if any of the outputs ntype 9,10,11,26,29,40,41,47,48 or 49 is specified The humidity calculations, using an internal timestep, will be switched on and condensation checks are performed
*** Notice at time : 0.000000
Generated by Unit : 5
Generated by Type : 56
Message : Star network calculation: every iteration stepof TYPE 56
*** Warning at time : 0.000000
Generated by Unit : 10
Generated by Type : 23
TRNSYS Message 315 : The TRNSYS processor has reported a potential problem with the connections in your input file. In version 16, there is a very specific calling order after convergence has been reached at each timestep. One of your connections flows against this calling order - for example you may have the output of an integrator connected as an input to a standard component (one that is being called iteratively at each timestep). While this is not technically an ERROR - it may cause incorrect values to be passed to the component. For example, the input to an iterating component from an integrator will be from the previously converged timestep and not the current timestep. Refer to the TRNSYS Manual - Volume 1 - for more information on the calling order for TRNSYS components
Reported information : ** Reported by Exec.f90
*** Warning at time : 0.000000
Generated by Unit : 10
Generated by Type : 23
TRNSYS Message 315 : The TRNSYS processor has reported a potential problem with the connections in your input file. In version 16, there is a very specific calling order after convergence has been reached at each timestep. One of your connections flows against this calling order - for example you may have the output of an integrator connected as an input to a standard component (one that is being called iteratively at each timestep). While this is not technically an ERROR - it may cause incorrect values to be passed to the component. For example, the input to an iterating component from an integrator will be from the previously converged timestep and not the current timestep. Refer to the TRNSYS Manual - Volume 1 - for more information on the calling order for TRNSYS components
Reported information : ** Reported by Exec.f90
*** Warning at time : 0.000000
Generated by Unit : 10
Generated by Type : 23
TRNSYS Message 315 : The TRNSYS processor has reported a potential problem with the connections in your input file. In version 16, there is a very specific calling order after convergence has been reached at each timestep. One of your connections flows against this calling order - for example you may have the output of an integrator connected as an input to a standard component (one that is being called iteratively at each timestep). While this is not technically an ERROR - it may cause incorrect values to be passed to the component. For example, the input to an iterating component from an integrator will be from the previously converged timestep and not the current timestep. Refer to the TRNSYS Manual - Volume 1 - for more information on the calling order for TRNSYS components
Reported information : ** Reported by Exec.f90
*** Warning at time : 0.000000
Generated by Unit : 9
Generated by Type : 23
TRNSYS Message 315 : The TRNSYS processor has reported a potential problem with the connections in your input file. In version 16, there is a very specific calling order after convergence has been reached at each timestep. One of your connections flows against this calling order - for example you may have the output of an integrator connected as an input to a standard component (one that is being called iteratively at each timestep). While this is not technically an ERROR - it may cause incorrect values to be passed to the component. For example, the input to an iterating component from an integrator will be from the previously converged timestep and not the current timestep. Refer to the TRNSYS Manual - Volume 1 - for more information on the calling order for TRNSYS components
Reported information : ** Reported by Exec.f90
*** Warning at time : 0.000000
Generated by Unit : 9
Generated by Type : 23
TRNSYS Message 315 : The TRNSYS processor has reported a potential problem with the connections in your input file. In version 16, there is a very specific calling order after convergence has been reached at each timestep. One of your connections flows against this calling order - for example you may have the output of an integrator connected as an input to a standard component (one that is being called iteratively at each timestep). While this is not technically an ERROR - it may cause incorrect values to be passed to the component. For example, the input to an iterating component from an integrator will be from the previously converged timestep and not the current timestep. Refer to the TRNSYS Manual - Volume 1 - for more information on the calling order for TRNSYS components
Reported information : ** Reported by Exec.f90
*** Warning at time : 0.000000
Generated by Unit : 9
Generated by Type : 23
TRNSYS Message 315 : The TRNSYS processor has reported a potential problem with the connections in your input file. In version 16, there is a very specific calling order after convergence has been reached at each timestep. One of your connections flows against this calling order - for example you may have the output of an integrator connected as an input to a standard component (one that is being called iteratively at each timestep). While this is not technically an ERROR - it may cause incorrect values to be passed to the component. For example, the input to an iterating component from an integrator will be from the previously converged timestep and not the current timestep. Refer to the TRNSYS Manual - Volume 1 - for more information on the calling order for TRNSYS components
Reported information : ** Reported by Exec.f90
*** The TRNSYS components will be called in the following order:
Unit # 5 Type # 56
Unit # 6 Type # 65
Unit # 7 Type # 25
Unit # 10 Type # 23
Unit # 9 Type # 23
*** Notice at time : 8760.000000
Generated by Unit : 10
Generated by Type : 23
Message : The controller was stuck during 0 time steps, i.e. 0.000000000000000 % of the time (Note that you have set NStick < 1. In that case the controller is stuck when further oscillations would trigger the 'maximum number of iterations' warning. Use a large number if you do not want this behavior).
*** Notice at time : 8760.000000
Generated by Unit : 9
Generated by Type : 23
Message : The controller was stuck during 0 time steps, i.e. 0.000000000000000 % of the time (Note that you have set NStick < 1. In that case the controller is stuck when further oscillations would trigger the 'maximum number of iterations' warning. Use a large number if you do not want this behavior).
*********************************************************************************************************
The Following UNIT Numbers, TYPE Numbers, and Logical Units Were Used in the Supplied TRNSYS Input File:
5 23 4
6 25 6
7 56 9
9 65 55
10 56
57
58
59
60
*********************************************************************************************************
Total TRNSYS Calculation Time: 17.6300 Seconds