Aleck,
The steps that you are seeing in some of the temperature plots are
probably a result of timebase that you have chosen for the walls in your
building. Wall response factors are computed for a series of discrete
times extending backwards through the history of the wall. If you use a
simulation time step that is less than the wall timebase then the
conduction transfer function has a constant value for a few timesteps
until the end of the next timebase is reached, then they change and you
end up seeing that stepped response. The ideal solution is to use a wall
timebase that is as close as possible to your simulation timestep. That
is not always feasible though; so I typically use a 0.25hr timebase and
a 1 or 5 minute time step.
best,
david
On 6/21/2012 10:40, Yujun TAO wrote:
> Dear trnsys users,
> I have a problem about the two tempreatures simulated: TiZONE1 and
> TiZONEPLATRE, in the graphic of TRNEXE, the two curves follow well at
> the big tendance with the experimentation's results, but at detail's
> view, there are somes escalades, i don't understand.
> Could someone tell me why?
> Here are jointed files to check
> Kind regards
> Aleck TAO
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120621/b6658ebf/attachment-0001.htm>
More information about the TRNSYS-users
mailing list