<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Aleck,<br>
      The steps that you are seeing in some of the temperature plots are
    probably a result of timebase that you have chosen for the walls in
    your building. Wall response factors are computed for a series of
    discrete times extending backwards through the history of the wall.
    If you use a simulation time step that is less than the wall
    timebase then the conduction transfer function has a constant value
    for a few timesteps until the end of the next timebase is reached,
    then they change and you end up seeing that stepped response. The
    ideal solution is to use a wall timebase that is as close as
    possible to your simulation timestep. That is not always feasible
    though; so I typically use a 0.25hr timebase and a 1 or 5 minute
    time step.<br>
    best,<br>
     david<br>
    <br>
    <br>
    On 6/21/2012 10:40, Yujun TAO wrote:
    <blockquote
      cite="mid:1340293259.59055.YahooMailNeo@web133204.mail.ir2.yahoo.com"
      type="cite">
      <div style="color:#000; background-color:#fff; font-family:times
        new roman, new york, times, serif;font-size:12pt">
        <div>Dear trnsys users,</div>
        <div>I have a problem about the two tempreatures simulated:
          TiZONE1 and TiZONEPLATRE, in the graphic of TRNEXE, the two
          curves follow well at the big tendance with the
          experimentation's results, but at detail's view, there are
          somes escalades, i don't understand.</div>
        <div>Could someone tell me why?</div>
        <div>Here are jointed files to check<br>
        </div>
        <div>Kind regards<br>
        </div>
        <div>Aleck TAO<br>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>