[TRNSYS-users] minmassflowrate
Marion Hiller
hiller at transsolar.com
Thu Jun 21 00:14:22 PDT 2012
Michael,
The min. mass flow rate calcualted by TRNbuild may differ from the
calculated during the simulation
If there it switches from turblent to laminar flow. However, this isn’t
your problem.
I had a quick look at your file
When I open your file b17 I get an error message for surface 15 (the
one with active layer):
The adjacent surface numbers of surface 12 and 15 are wrong!!
ZONE Z02
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE Z02
WALL =IW01 : SURF= 11 : AREA= 40.66 : INTERNAL
WALL =ID01 : SURF= 12 : AREA= 44.87 : ADJACENT=Z02 :
ADJ_SURF=5 : FRONT : INTEMP = INPUT 1*Z02_TABS_TETA_SW : MFLOW = INPUT
1*Z02_TABS_MASSFLOW : NLOOP = 6 : MFLOWMIN = 15
WALL =ID02 : SURF= 13 : AREA= 5.09 : BOUNDARY=IDENTICAL
WALL =ID03 : SURF= 14 : AREA= 12.69 : BOUNDARY=0
WALL =ID01 : SURF= 15 : AREA= 44.87 : ADJACENT=Z02 :
ADJ_SURF=1 : BACK : INTEMP = INPUT 1*Z02_TABS_TETA_SW : MFLOW = INPUT
1*Z02_TABS_MASSFLOW : NLOOP = 6 : MFLOWMIN = 15
WALL =ID05 : SURF= 16 : AREA= 12.69 : BOUNDARY=IDENTICAL
I assume you edit the file manually.
If I delete the wrong ADJ_SURF, and I reopen it TRNbuild it assigns the
the correct numbers.
Marion
Dipl.-Ing. Marion Hiller
TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes Bauen
und Nutzerkomfort in Gebäude
Munich - New York - Stuttgart + 49.711.67976.0
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart
Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.:
DE152272639
Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher
-----Ursprüngliche Nachricht-----
Von: Michael Döbele [mailto:michael.doebele at hochschule-bc.de]
Gesendet: Montag, 18. Juni 2012 23:25
An: trnsys-users at engr.wisc.edu
Betreff: [TRNSYS-users] minmassflowrate
Dear TRNSSYS User,
i am trying to run an active layer with an specific massflow rate of 15
kg/h m² (absolute value 654.15 kg/h). TRNBuild calculates a minimum
allowed massflow rate of 10.25 kg/h. (446 kg/h) ....so far so good.
But when I set this massflow rate in TRNSYS Studio via Input to the
wanted 654.15 kg/h I get following error
"specific fluid mass flow of active layer in surface 2 below minimum
value of16.26/m2h, increase the minimum mass flow rate or use
autosegmentation feature of TRNBuild for subdividing the surface."
This is a really strange behavior. The massflow criteria varies and
seems to depend on the inlet temperature.. I also tried autosegmentation
- I didn´t help, I got the same error message.
Please help me out here..
Thank you
Michael Döbele
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120621/3f1c4b8b/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 10538 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120621/3f1c4b8b/attachment-0001.jpg>
More information about the TRNSYS-users
mailing list