[TRNSYS-users] cold bridge
Karol Bandurski
karol.bandurski at put.poznan.pl
Fri Jul 13 01:22:50 PDT 2012
Dear Marion,
so cold bridge module is not useful in this case – am I right?
Regards,
Karol
From: Marion Hiller [mailto:hiller at transsolar.com]
Sent: Friday, July 13, 2012 10:13 AM
To: karol.bandurski
Cc: trnsys-users
Subject: AW: RE: [TRNSYS-users] cold bridge
Dear Karol,
1) You recommend to set resistance of whole wall (include cold bridge) in “cold bridge window” (hmK/kJ) or resistance of “massless wall” (hm^2K/kJ). It doesn't matter which way will be chosen, dimension of element will be the same and only units will change m<->m^2.
No, you need the thermal mass. The adjustment really depend on your wall construction.
It is more adjusting the u-value of layer (if poassible) and thereby of a wall.
For a wall with insulation I would increase the u-value for the insulation such that it includes the loss of the cold bridge.
Best regards,
Marion
Dipl.-Ing. Marion Hiller
TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes Bauen und Nutzerkomfort in Gebäude
Munich - New York - Stuttgart + 49.711.67976.0
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart
Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.: DE152272639
Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer, Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher
_____
Von: Karol Bandurski [mailto:karol.bandurski at put.poznan.pl]
Gesendet: Freitag, 13. Juli 2012 10:06
An: Marion Hiller
Cc: 'trnsys-users'
Betreff: RE: [TRNSYS-users] cold bridge
Dear Marion,
Thank you very much for your explanation!
If I understand:
1) You recommend to set resistance of whole wall (include cold bridge) in “cold bridge window” (hmK/kJ) or resistance of “massless wall” (hm^2K/kJ). It doesn't matter which way will be chosen, dimension of element will be the same and only units will change m<->m^2.
2) In both case element will be massless. So what can I do to account mass and heat capacity of wall and cold bridge?
Regards,
Karol
-----Original Message-----
From: Marion Hiller [mailto:hiller at transsolar.com]
Sent: Friday, July 13, 2012 9:03 AM
To: karol.bandurski
Cc: trnsys-users
Subject: AW: [TRNSYS-users] cold bridge
Dear Karol,
If you define a "cold bridge" in TRNbuild the following happens:
- Instead of defining layers as for a wall you define a "thermal resistance"
(without mass effects)
- Instead of setting an area as for a wall you define a lenght
However, in the end this cold bridge is treated as "a massless wall".
If you use a detailed radiation mode, you can't add surfaces (and a cold bridge would be surface somehow) in order to keep the geometry consistent.
It is not recommended to draw very small surfaces in T3d to represent the cold bridge unless you need the inside surface temperature because very small surfaces may cause trouble for matrix generation.
Therefore, the recommendation is to integrate the losses of a cold bridge into the wall by adjusting the u-value of a wall as previously mentioned by Adrien.
I hope this helps.
Best regards,
Marion
Dipl.-Ing. Marion Hiller
TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes Bauen und Nutzerkomfort in Gebäude Munich - New York - Stuttgart + 49.711.67976.0
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.:
DE152272639
Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer, Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher
-----Ursprüngliche Nachricht-----
Von: Karol Bandurski <mailto:%5bmailto:karol.bandurski at put.poznan.pl%5d> [mailto:karol.bandurski at put.poznan.pl]
Gesendet: Donnerstag, 12. Juli 2012 18:25
An: <mailto:trnsys-users at cae.wisc.edu> trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] cold bridge
_______________________________________________
TRNSYS-users mailing list
<mailto:TRNSYS-users at cae.wisc.edu> TRNSYS-users at cae.wisc.edu
<https://mailman.cae.wisc.edu/listinfo/trnsys-users> https://mailman.cae.wisc.edu/listinfo/trnsys-users
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120713/b11d9f30/attachment-0001.htm>
More information about the TRNSYS-users
mailing list