[TRNSYS-users] Problems with Trnsys3d
jeannieboef
jeannieboef at gmail.com
Tue Jul 3 03:36:31 PDT 2012
I don't think a window subsurface is possible on a ground bounded
surface. I would draw the light shaft as zone or split the surface off
around the window (this means splitting the surface into 5 parts) and
assign Outdoors as boundry.
As for 2. save the idf using the plugin. it is forbidden to save
a .skp file at all... just don't. Then load the idf into a new just
opened sketchup. If I remember right, all construction lines are
errased. If you really have zones with 2 verticies, I would use a text
edditor to find and elliminate them.
Sent from my iPhone
On 03.07.2012, at 11:20, Anne-Kathrin.Albrecht at ise.fraunhofer.de wrote:
> Hallo everybody,
> I have several problems with Trnsys3d:
>
> 1. I am working on a building that has a cellar with windows.
> When I convert the idf-file into a TRNBuild-file (b17 idf-file) the
> cellar walls are shown with a wrong area (takes the net area = gross
> area minus windows instead of the gross area) and the windows are
> missing. Is it not possible to include windows in walls that have
> the ground as a boundary? Of course the house has a light well, but
> I thought I could solve the problem by just drawing the windows and
> setting them to a high shading factor.
>
> 2. Is it possible to list all the drown surfaces in a
> building? I´ve always used the surface search so far but I have two
> lines (drown by accident) that are recognized as walls with an area
> of 0.001 m² and I don´t know where they are, so it´s like
> searching for a needle in a haystack...
>
> Best regards,
>
> Anne-Kathrin Albrecht
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120703/4b2276ca/attachment-0001.htm>
More information about the TRNSYS-users
mailing list