[TRNSYS-users] Need helps to solve the absorption chiller (Type677) issue
David BRADLEY
d.bradley at tess-inc.com
Mon Feb 20 20:35:18 PST 2012
Billy,
I typically put a buffer storage tank in those loops instead of a
pipe. The idea is the same. The volume of the tank (or pipe) should be a
little more than the volume of fluid that the pump in the loop can
transfer in one timestep.
Best,
David
On 2/20/2012 22:16, coolbilly1999 at gmail.com wrote:
> Hi Matt,
> Thanks for the detailed explanation. I will try to shorten the
> timestep. Actually, I also tried adding a pipe between the cooling
> coil and chiller to store adequate flow as mentioned in the
> documentation which I neglected before. And it works pretty well and I
> will look into the other warnings you mentioned. Thanks for your help
> again.
> Best regards,
> Billy
> *From:* Matt Duffy <mailto:duffy at tess-inc.com>
> *Sent:* Monday, February 20, 2012 8:53 AM
> *To:* Billy Chen <mailto:coolbilly1999 at gmail.com> ;
> trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
> *Subject:* Re: [TRNSYS-users] Need helps to solve the absorption
> chiller (Type677) issue
> Billy,
>
> I looked at your listing file, and I noticed other important things
> about your simulation. First of all, the timestep you are using is
> much too large. You will notice in the TESS HVAC Solar Absorption
> example, the timestep is 5 minutes (note the equation in the control
> cards to implement this) in order to consider the control decisions
> and flow rates during that timestep. When using a large timestep, an
> extraordinary amount of fluid is being sent through your system, and
> if you are not simulating adequate capacitance or storage in that
> loop, it will lead to components not converging. Also, please note the
> other warnings at the end of your listing file about the independent
> variables being above or below the specified range in the performance
> data files. The TRNSYS data interpolation routine does not
> extrapolate, so if you send it an independent variable that is not
> within the specified range, it will use the dependent variable at that
> end(or beginning) of the range and not extrapolate.
>
> Best regards,
>
> Matt Duffy
>
>
> *----- Original Message -----*
> *From:* "Billy Chen" <coolbilly1999 at gmail.com>
> *Sent:* Fri, February 17, 2012 17:22
> *Subject:* [TRNSYS-users] Need helps to solve the absorption chiller
> (Type677) issue
>
> Hi TRNSYS users,
> I am building an absorption chiller model for a medium office, and I
> used the similar components from the TESS example (Restaurant with
> absorption chiller). However, when I ran the simulation, I got tons of
> warnings (from SYS Message 441), and the simulation terminated because
> it exceeded the limit of warnings. The warning said as below:
> *** Warning at time : 3717.000000
> Generated by Unit : Not applicable or not available
> Generated by Type : Not applicable or not available
> TRNSYS Message 441 : The inputs to the listed units have not
> converged at this timestep. The values at the last iteration will be
> used and the simulation will proceed.
> Reported information : UNITS: 12 13 18
> UNIT 12 is Type 677 double effect chiller
> UNIT 13 is Type 144 pump
> UNIT 18 is Type 697b cooling coil
> I checked the input units and I can't figure out the problem. Could
> someone give me some advice?
> And I also found out a problem when I ran the TESS Restaurant example,
> the chilled water outlet temperature is always going up over 100
> degree C. But the temperature from the air temperature from cooling
> coil looks reasonable. It confuses me a lot. Does anyone find this
> problem before and have any suggestion on that?
> I attached the LST file and the plot for the chiller water temp. I
> really appreciate any help.
> Best regards,
> Billy
> ------------------------------------------------------------------------
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu <javascript:bodyCreateMail('TRNSYS-users%40cae.wisc.edu')>
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com