[TRNSYS-users] Cooling load calculation
David BRADLEY
d.bradley at tess-inc.com
Tue Feb 14 10:31:30 PST 2012
Mayank,
It is very hard to get matching results between two people using the
same software package, let alone between two different packages; there
are so many assumptions in modeling. Still, what you report is a quite
significant difference in sensitivity. I think the first place to look
is that in your *.bui, you have left the default thermal capacitance of
the zone as
VOLUME= 3027.33 m3
CAPACITANCE = 3632.79 kJ/K
this accounts only for the thermal capacitance of the air in the zone.
It neglects the thermal capacitance of the furnishings. A more typical
value would be 18200 kJ/h (approximately 5 times the default value).
Kind regards,
David
On 2/14/2012 01:11, Mayank wrote:
>
> Hello Everyone,
>
> I have made a simple cooling load calculation model in TRNSYS v16 and
> similar setup in E-quest. There is vast variation in cooling load when
> I put into outdoor air in the room.
>
> In TRNSYS I used 2800 sqft area building having 150 person occupancy
> and according to ASHRAE 62 (ventilation rate procedure) I calculated
> 1150 CFM outdoor air as fresh air. When I taking no outdoor air the
> cooling load is about 10 ton but when I put outdoor air through
> ventilation (2.46 ACH) the cooling load increases and reached at 42 ton.
>
> And in E-quest it increase only 1 ton.
>
> Can anyone help me to find out the reason?
>
> I attached bui. File and tpf file.
>
> Regards
>
> Mayank
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120214/1788f16c/attachment-0001.htm>
More information about the TRNSYS-users
mailing list