    Mayank,<br>
     It is very hard to get matching results between two people using
    the same software package, let alone between two different packages;
    there are so many assumptions in modeling. Still, what you report is
    a quite significant difference in sensitivity. I think the first
    place to look is that in your *.bui, you have left the default
    thermal capacitance of the zone as <br>
    <br>
    VOLUME= 3027.33 m3<br>
    CAPACITANCE = 3632.79 kJ/K <br>
    <br>
    this accounts only for the thermal capacitance of the air in the
    zone. It neglects the thermal capacitance of the furnishings. A more
    typical value would be 18200 kJ/h (approximately 5 times the default
    value).<br>
    <br>
    Kind regards,<br>
     David<br>
    <br>
    On 2/14/2012 01:11, Mayank wrote:
    <blockquote cite="mid:4f3a0949.2139440a.48e8.5034@mx.google.com"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="Generator" content="Microsoft Word 12 (filtered
        medium)">
      <style>
<!--
 /* Font Definitions */
 @font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri","sans-serif";}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
span.EmailStyle17
        {mso-style-type:personal-compose;
        font-family:"Calibri","sans-serif";
        color:windowtext;}
.MsoChpDefault
        {mso-style-type:export-only;}
@page Section1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.Section1
        {page:Section1;}
-->
</style><!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1" />
 </o:shapelayout></xml><![endif]-->
      <div class="Section1">
        <p class="MsoNormal">Hello Everyone,<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">I have made a simple cooling load
          calculation model in
          TRNSYS v16 and similar setup in E-quest. There is vast
          variation in cooling
          load when I put into outdoor air in the room.<o:p></o:p></p>
        <p class="MsoNormal">In TRNSYS I used 2800 sqft area building
          having 150 person
          occupancy and according to ASHRAE 62 (ventilation rate
          procedure) I calculated
          1150 CFM outdoor air as fresh air. When I taking no outdoor
          air the cooling
          load is about 10 ton but when I put outdoor air through
          ventilation (2.46 ACH)
          the cooling load increases and reached at 42 ton.<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">And in E-quest it increase only 1 ton.<o:p></o:p></p>
        <p class="MsoNormal"> Can anyone help me to find out the reason?
          <o:p></o:p></p>
        <p class="MsoNormal">I attached bui. File and tpf file.<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Regards <o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Mayank <o:p></o:p></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>