Eva,
Quite a long time ago, there was a bug in Type668 that caused there to
be a power output even when the device was off. However, this was fixed
in 2005. You should contact your distributor and make sure that you have
a more recent version. Also, Type668 has two control signals; one for
heating and one for cooling. Make sure that both are switched to OFF.
Best,
David
On 8/21/2012 10:56, Eva gklezakou wrote:
> Dear Sirs,
>
> I think that something going wrong with the control signal of the type
> 668 because even though the signal from the controller is 0 and for
> this reason both COP (output of type 668) of the heat pump and the
> heat transfer to load (output of type 668) are 0 the heat pump power
> is not 0.
> Thank you for your help.
>
> Regards,
> Eva
>
>