Esteban,
I have had some success in contacting manufacturer's representatives
and asking them to generate a few additional performance points. These
days more and more manufacturers rely on software to generate
performance estimates rather than on catalogs so it is hard to find a
complete map in *.pdf form!
If that tactic does not work then you may be able to use the example
data file for your off-design points. Some HVAC equipment normalizes
very well; in other words if you look at the performance of an air
cooled chiller at a given operating point divided by the performance at
the rated point, it looks quite the same as a lot of other air cooled
chillers and even like other sizes of air cooled chiller. Other HVAc
equipment does not normalize so well (absorption chillers are a good
example). I have never looked directly at cooling coils so I am afraid
that I can't offer any very specific advice there.
Kind regards,
David
On 4/2/2012 15:52, Esteban De Jesus Quintana Miranda wrote:
> hi , i want simulate a abosortion system with a fan coils, but i dont
> know how generate the data files of the air temperture because in the
> catalog that i find only appears the performance for a pair of db and
> wb temperture, no data for a constant dry bulb temperture for a wet
> bulb variable temperature, how can i generate this file?
>
> thanks
>
> "la santidad consiste en estar siempre alegres" san Juan Bosco
>
> Esteban De Jesús Quintana Miranda
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120409/ddf05467/attachment-0001.htm>
More information about the TRNSYS-users
mailing list