    Esteban,<br>
      I have had some success in contacting manufacturer's
    representatives and asking them to generate a few additional
    performance points. These days more and more manufacturers rely on
    software to generate performance estimates rather than on catalogs
    so it is hard to find a complete map in *.pdf form!<br>
    <br>
     If that tactic does not work then you may be able to use the
    example data file for your off-design points. Some HVAC equipment
    normalizes very well; in other words if you look at the performance
    of an air cooled chiller at a given operating point divided by the
    performance at the rated point, it looks quite the same as a lot of
    other air cooled chillers and even like other sizes of air cooled
    chiller. Other HVAc equipment does not normalize so well (absorption
    chillers are a good example). I have never looked directly at
    cooling coils so I am afraid that I can't offer any very specific
    advice there.<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    On 4/2/2012 15:52, Esteban De Jesus Quintana Miranda wrote:
    <blockquote cite="mid:SNT129-W52E44D185AB13DBA8172879E4C0@phx.gbl"
      type="cite">
      <style><!--
.hmmessage P
{
margin:0px;
padding:0px
}
body.hmmessage
{
font-size: 10pt;
font-family:Tahoma
}
--></style>
      <div dir="ltr">
        <div>
          <div>hi , i want simulate a abosortion system with a fan
            coils, but i dont know how generate the data files of the
            air temperture because in the catalog that i find only
            appears the performance for a pair of db and wb temperture,
             no data for a constant dry bulb temperture for a wet bulb
            variable temperature, how can i generate this file?</div>
          <div><br>
          </div>
          <div>thanks</div>
          <br>
          <div align="center"><font style="font-size:16pt"
              color="#002060" face="Comic Sans MS" size="4">"la santidad
              consiste en estar siempre alegres" san Juan Bosco</font><br>
          </div>
          <font style="" face="Comic Sans MS"><br>
            Esteban De Jesús Quintana Miranda<br>
          </font></div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>