[TRNSYS-users] Error 50
David BRADLEY
d.bradley at tess-inc.com
Mon Sep 12 08:36:55 PDT 2011
Dear Ramkishore,
Increasing the number of surfaces that Type15 calculates adds a lot of
parameters to your simulation. So many, in this case that your
simulation exceeds the total number of parameters allowed per
simulation. In addition to your change in Type15.f90, you also need to
change TrnsysConstants.f90 as follows:
Integer, Parameter :: nMaxParameters = 4000 ! Maximum number
of Parameters 2000
in other words, increase the total number of allowed parameters, then
recompile the TRNDll.dll.
Kind regards,
David
On 9/9/2011 04:57, R.K. Singh wrote:
> Dear All,
> I am using type 15-6 and type 56 components for simulating a spherical
> building that is defined by 144 surfaces. I have connected
> successfully all requiered connection between two. One error 50 arrive
> at the time of running the model. Though, I have changed the
> *ns_max=200* from *25* in *Type 15.f90* [Parameter
> (ns_max=25,nitems_max=36,nout=52+8*ns_max)] file. The screen shot is
> attached herewith for your kind reference.
> I would be very thankful if anybody can help to resolve this problem.
> Regards,
> Ramkishore Singh
> Department of Energy & Environment
> TERI University
> Web: www.teriuniversity.ac.in <http://www.teriuniversity.ac.in>
>
>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110912/ebc559ca/attachment-0005.htm>
More information about the TRNSYS-users
mailing list