[TRNSYS-users] control function for shading system
Adrien JEZEQUEL - ITF
a.jezequel at itf.biz
Wed Nov 23 08:10:13 PST 2011
Dear Rana,
If you use Type 2D,
1. connect radiation you need to Input 1 : Upper Input Value
2. connect Output Control Function to Input 4 Input Control Function
3. Put 0 in Parameters 1 to 4
4. Put 972 in Parameter 5 : Upper Dead Band => your control will be on
when irradiation > 270 W/m²
5. Put 972 in Parameter 6 : Lower Dead Band => your control will be off
when irradiation < 270W/m² (you may change this value to obtain an
hysteresis effect)
If you use TRNSYS 16, you may also have a look to examples
(building.tpf) and TRNSYS documentation. You may alos use wizard to see
how are used Type2 in studio.
Best regards
------------------------------------------------------------------------
www.itf.biz <http://www.itf.biz>
www.itf.biz <http://www.itf.biz>
Adrien JEZEQUEL
Simulations Thermiques Dynamiques
*ITF*
62, Rue du Bolliet
73230 St Alban Leysse
FRANCE
Phone :
Fax :
Mail:
+33(0) 479 750 029
+33(0) 479 852 122
a.jezequel at itf.biz ou aj at itf.biz
/Afin de contribuer au respect de l'environnement, merci de n'imprimer
cet e-mail que si nécessaire
Please, consider our environmental responsability before printing this email
/
Le 23/11/2011 16:08, Rana Mohsen a écrit :
> Hi all,
>
> i am having a building with internal and external shading system. the
> external shading system is on when it the irradiation on window
> reaches 270w/m2 or more, and if it is less it went off. and i want to
> put this in the simulation by using a control function and connect it
> to my input,,, so which control function could be used is it type 2d
> or the PID controler type 23..
> and if it is in the 2d, how to put this number.
>
> /Best Regards/,
> ***I*NG*.*| *_R_*ana Hanafy
> Master Student
> Hochschule für TechniK Stuttgart
> Tübingerstraße 93,
> 70178 Stuttgart, Germany
> 0049-176-59730029
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111123/44992eed/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: logo_itf_2010.jpg
Type: image/jpeg
Size: 17526 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111123/44992eed/attachment-0001.jpg>
More information about the TRNSYS-users
mailing list