[TRNSYS-users] TRNSYS and BESTEST validation
David BRADLEY
d.bradley at tess-inc.com
Tue Nov 15 09:47:54 PST 2011
Dapeng,
While BESTEST (and ASHRAE Standard 140 - which is identical to
BESTEST) try hard to be very clear about what assumptions you should
make in each of the test cases, there is still /a lot/ of room for
interpretation. Some years ago, we ran TRNSYS 16.1 through those test
cases as well and found that you can make quite legitimate
interpretations of the standard and come out with quite a variety of
results. I would recommend you have a look at a couple papers that we
wrote about the effort:
"Converging on a Recommended Set of Interpretations and Assumptions in
Applying Standard Tests to Energy Analysis Tools"
"Experiences with and Interpretations of Standard Test Methods of
Building Energy Analysis Tools"
both are available at http://www.tess-inc.com/pubs.
If my recollection is correct, we were within the range on the 600
cases. If anything, the annual cooling that modern versions of TRNSYS
predict is on the low end of the range and is sometimes below the range.
It is worth keeping in mind that the "acceptable range" of results does
not come from an analytical solution. It comes from the results
generated by a bunch of software tools and TRNSYS (version 13!) is one
of them. Other software developers have mentioned to me recently that
building science and cooling load algorithms have advanced since the
1980s and that more recent algorithms do predict lower cooling loads
than did the older algorithms. This is not reflected in the BESTEST or
Standard140 results; those ranges are still set by the older versions of
the tools.
Best,
David
On 11/14/2011 21:14, Dapeng Li wrote:
>
> Dear all users,
> Hello.
>
> I try to take a test by using BESTEST algorithm. I use TRNSYS version
> 16.01.003. I think I have taken my best to set up each parameters in
> TRNSYS's deck and TRNBUILD according to case 600's condition in the
> BESTEST documents which is downloaded from
> _http://www.nrel.gov/docs/legosti/old/6231.pdf?_But the annual heating
> load (5.997MWh) from TRNSYS is different from the value ranges (4.296
> to 5.709). The annual cooling load (6.519MWh) fit well. I wonder the
> reasons of this kind of difference. For convenience, I attached my
> project for your deep examine.
>
> Thank you for your help in advance.
>
> kindly regards,
> Dapeng Li
>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111115/840b9c76/attachment-0001.htm>
More information about the TRNSYS-users
mailing list