[TRNSYS-users] Fatal Error of type 56
David BRADLEY
d.bradley at tess-inc.com
Mon Nov 7 07:51:20 PST 2011
Wang,
If you have variable convection coefficients on either the inside or
outside surface of that particular window, turn them off in favor of
constant values (11 kJ/h.m2.K for the inside, 64 for the outside). If
the problem still occurs, unfortunately, you are going to have to adjust
the thermal properties of your window. If you created the window using
LBNL's Window 5 software, you can change it yourself. If you are using a
standard window, then you will need to send your project to your
distributor for assistance.
Regards,
David
On 11/7/2011 06:55, 王洋 wrote:
> Dear all,
> I met an Fatal Error as follows, which experts could deal with it?
> Please tell me in detail.
> *** Fatal Error at time : 0.010000
> Generated by Unit : 2
> Generated by Type : 56
> Message : Zone 3 surface 18 pane temperature
> calculation is diverging at time 0.01000TDIF: NaN
> ITPANE: 31 ITCALC: 51
> Many thanks in advance!
> br
> wang
>
> 2011/11/6 <trnsys-users-request at cae.wisc.edu
> <mailto:trnsys-users-request at cae.wisc.edu>>
>
> Send TRNSYS-users mailing list submissions to
> trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
>
> To subscribe or unsubscribe via the World Wide Web, visit
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
> or, via email, send a message with subject or body 'help' to
> trnsys-users-request at cae.wisc.edu
> <mailto:trnsys-users-request at cae.wisc.edu>
>
> You can reach the person managing the list at
> trnsys-users-owner at cae.wisc.edu
> <mailto:trnsys-users-owner at cae.wisc.edu>
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of TRNSYS-users digest..."
>
> Today's Topics:
>
> 1. Re: about the chilled ceiling below the roof room (Matt Duffy)
> 2. Re: command line to generate dck from tpf (Matt Duffy)
>
>
> ---------- 已转发邮件 ----------
> From: "Matt Duffy" <duffy at tess-inc.com <mailto:duffy at tess-inc.com>>
> To: ilyt2000 at gmail.com <mailto:ilyt2000 at gmail.com>,
> trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
> Date: Sun, 6 Nov 2011 16:20:10 -0600 (CST)
> Subject: Re: [TRNSYS-users] about the chilled ceiling below the
> roof room
>
> Dear Leona,
>
> I am not exactly sure what you mean by, “there is a roof room
> above”. If there is indeed a thermal zone above your room, that
> would require an adjacent wall and not a boundary wall.
>
> Best regards,
>
> Matt Duffy
>
>
>
> *----- Original Message -----*
> *From:* "ͫͫ" <ilyt2000 at gmail.com <mailto:ilyt2000 at gmail.com>>
> *Sent:* Fri, November 4, 2011 9:45
> *Subject:* [TRNSYS-users] about the chilled ceiling below the roof
> room
>
> !
> Dear all,
> i want to add a chilled ceiling ,but there is a roof room above,
> and i have made the boundary temperatur of the wall type "
> ceiling" as 35 °C. Wenn i use the chilled ceiling ,it seems like
> something is wrong,
> Does someone know, what i should change?
> best regards from Leona
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
>
> ---------- 已转发邮件 ----------
> From: "Matt Duffy" <duffy at tess-inc.com <mailto:duffy at tess-inc.com>>
> To: "Keech, Richard" <richard.keech at gmail.com
> <mailto:richard.keech at gmail.com>>, trnsys-users at cae.wisc.edu
> <mailto:trnsys-users at cae.wisc.edu>
> Date: Sun, 6 Nov 2011 16:23:47 -0600 (CST)
> Subject: Re: [TRNSYS-users] command line to generate dck from tpf
>
> Dear Richard,
>
> To the best of my knowledge, you cannot do this from the command
> line. However, you could perhaps implement an Auto HotKey
> application that would create all of the input *.dck files from
> many *.tpf Studio projects.
>
> Best regards,
>
> Matt Duffy
>
>
>
>
> *----- Original Message -----*
> *From:* "Keech, Richard" <richard.keech at gmail.com
> <mailto:richard.keech at gmail.com>>
> *Sent:* Fri, November 4, 2011 20:23
> *Subject:* [TRNSYS-users] command line to generate dck from tpf
>
> Is it possible to generate a TRNSYS input "dck" file from a TRNSYS
> Studio "tpf" file straight from the command line?
>
> --
> Richard Keech +61 419 036 463 <tel:%2B61%20419%20036%20463>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu <mailto:TRNSYS-users at cae.wisc.edu>
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111107/2a8db683/attachment-0001.htm>
More information about the TRNSYS-users
mailing list