    Wang, <br>
      If you have variable convection coefficients on either the inside
    or outside surface of that particular window, turn them off in favor
    of constant values (11 kJ/h.m2.K for the inside, 64 for the
    outside). If the problem still occurs, unfortunately, you are going
    to have to adjust the thermal properties of your window. If you
    created the window using LBNL's Window 5 software, you can change it
    yourself. If you are using a standard window, then you will need to
    send your project to your distributor for assistance.<br>
    Regards,<br>
     David<br>
    <br>
    <br>
    On 11/7/2011 06:55, 王洋 wrote:
    <blockquote
cite="mid:CABF0dEsxdB1PovGMvpP9XzzzPJ_OoJ+c+NzrNu5N0E_hUR9txQ@mail.gmail.com"
      type="cite">
      <div> </div>
      <div>Dear all,</div>
      <div> </div>
      <div>I met an Fatal Error as follows, which experts could deal
        with it? Please tell me in detail.</div>
      <div> </div>
      <div>*** Fatal Error at time   :         0.010000<br>
            Generated by Unit     :     2<br>
            Generated by Type     :    56<br>
            Message               : Zone   3 surface   18 pane
        temperature calculation is diverging at time      0.01000TDIF: 
        NaN         ITPANE:   31 ITCALC:   51</div>
      <div> </div>
      <div>Many thanks in advance!</div>
      <div> </div>
      <div>br</div>
      <div> </div>
      <div>wang<br>
        <br>
      </div>
      <div class="gmail_quote">2011/11/6 <span dir="ltr"><<a
            moz-do-not-send="true"
            href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a>></span><br>
        <blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px
          0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Send
          TRNSYS-users mailing list submissions to<br>
                 <a moz-do-not-send="true"
            href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
          <br>
          To subscribe or unsubscribe via the World Wide Web, visit<br>
                 <a moz-do-not-send="true"
            href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
            target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
          or, via email, send a message with subject or body 'help' to<br>
                 <a moz-do-not-send="true"
            href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a><br>
          <br>
          You can reach the person managing the list at<br>
                 <a moz-do-not-send="true"
            href="mailto:trnsys-users-owner@cae.wisc.edu">trnsys-users-owner@cae.wisc.edu</a><br>
          <br>
          When replying, please edit your Subject line so it is more
          specific<br>
          than "Re: Contents of TRNSYS-users digest..."<br>
          <br>
          Today's Topics:<br>
          <br>
            1. Re: about the chilled ceiling below the roof room (Matt
          Duffy)<br>
            2. Re: command line to generate dck from tpf (Matt Duffy)<br>
          <br>
          <br>
          ---------- 已转发邮件 ----------<br>
          From: "Matt Duffy" <<a moz-do-not-send="true"
            href="mailto:duffy@tess-inc.com">duffy@tess-inc.com</a>><br>
          To: <a moz-do-not-send="true" href="mailto:ilyt2000@gmail.com">ilyt2000@gmail.com</a>,
          <a moz-do-not-send="true"
            href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
          Date: Sun, 6 Nov 2011 16:20:10 -0600 (CST)<br>
          Subject: Re: [TRNSYS-users] about the chilled ceiling below
          the roof room<br>
          <br>
          <p class="MsoNormal">Dear Leona,</p>
          <p class="MsoNormal"> </p>
          <p class="MsoNormal">I am not exactly sure what you mean by,
            “there is a roof room above”. If there is indeed a thermal
            zone above your room, that would require an adjacent wall
            and not a boundary wall.</p>
          <p class="MsoNormal"> </p>
          <p class="MsoNormal">Best regards,</p>
          <p class="MsoNormal"> </p>
          <p class="MsoNormal">Matt Duffy</p>
          <p class="MsoNormal"> </p>
          <br>
          <br>
          <div style="BACKGROUND-REPEAT: repeat-x"><strong>-----
              Original Message -----</strong><br>
            <strong>From:</strong> "ͫͫ" <<a moz-do-not-send="true"
              href="mailto:ilyt2000@gmail.com" target="_blank">ilyt2000@gmail.com</a>>
            <br>
            <strong>Sent:</strong> Fri, November 4, 2011 9:45<br>
            <strong>Subject:</strong> [TRNSYS-users] about the chilled
            ceiling below the roof room<br>
            <br>
            <table cellspacing="5" width="100%">
              <tbody>
                <tr>
                  <td>! </td>
                </tr>
                <tr>
                  <td>
                    <div>
                      <div>Dear all,</div>
                      <div> </div>
                      <div>i want to add a chilled ceiling ,but there is
                        a roof room above, and i have made the boundary
                        temperatur of the wall type " ceiling" as 35 °C.
                        Wenn i use the chilled ceiling ,it seems like
                        something is  wrong,</div>
                      <div> </div>
                      <div>Does someone know, what i should change?</div>
                      <div> </div>
                      <div>best regards from Leona</div>
                      <hr noshade="noshade" size="1">
                      <pre>_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true">TRNSYS-users@cae.wisc.edu</a>
<a moz-do-not-send="true" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
                    </div>
                  </td>
                </tr>
              </tbody>
            </table>
          </div>
          <br>
          <br>
          ---------- 已转发邮件 ----------<br>
          From: "Matt Duffy" <<a moz-do-not-send="true"
            href="mailto:duffy@tess-inc.com">duffy@tess-inc.com</a>><br>
          To: "Keech, Richard" <<a moz-do-not-send="true"
            href="mailto:richard.keech@gmail.com">richard.keech@gmail.com</a>>,
          <a moz-do-not-send="true"
            href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
          Date: Sun, 6 Nov 2011 16:23:47 -0600 (CST)<br>
          Subject: Re: [TRNSYS-users] command line to generate dck from
          tpf<br>
          <p class="MsoNormal"> </p>
          <p class="MsoNormal">Dear Richard,</p>
          <p class="MsoNormal">To the best of my knowledge, you cannot
            do this from the command line. However, you could perhaps
            implement an Auto HotKey application that would create all
            of the input *.dck files from many *.tpf Studio projects.</p>
          <p class="MsoNormal">Best regards,</p>
          <p class="MsoNormal"> </p>
          <p class="MsoNormal">Matt Duffy</p>
          <br>
          <br>
          <br>
          <div style="BACKGROUND-REPEAT: repeat-x"><strong>-----
              Original Message -----</strong><br>
            <strong>From:</strong> "Keech, Richard" <<a
              moz-do-not-send="true"
              href="mailto:richard.keech@gmail.com" target="_blank">richard.keech@gmail.com</a>>
            <br>
            <strong>Sent:</strong> Fri, November 4, 2011 20:23<br>
            <strong>Subject:</strong> [TRNSYS-users] command line to
            generate dck from tpf<br>
            <br>
            <table cellspacing="5" width="100%">
              <tbody>
                <tr>
                  <td>
                    <div>Is it possible to generate a TRNSYS input "dck"
                      file from a TRNSYS Studio "tpf" file straight from
                      the command line?   <br clear="all">
                      <br>
                      -- <br>
                      Richard Keech   <a moz-do-not-send="true"
                        href="tel:%2B61%20419%20036%20463"
                        target="_blank" value="+61419036463">+61 419 036
                        463</a><br>
                      <hr noshade="noshade" size="1">
                      <pre>_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true">TRNSYS-users@cae.wisc.edu</a>
<a moz-do-not-send="true" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
                    </div>
                  </td>
                </tr>
              </tbody>
            </table>
          </div>
          <br>
          _______________________________________________<br>
          TRNSYS-users mailing list<br>
          <a moz-do-not-send="true"
            href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
          <a moz-do-not-send="true"
            href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
            target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
          <br>
        </blockquote>
      </div>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>