[TRNSYS-users] TYPE 682
Matt Duffy
duffy at tess-inc.com
Thu Mar 31 08:19:15 PDT 2011
Dear Alessia,
Yes, you are on the right track using Type686 and Type682. Simply connect
the WWHP component's outputs to the other inputs (intlet Temperature and
Inlet Flowrate) of Type682.
For version 17, there was a new feature added to Type682 which is
described in the comment of the source code:
C DECEMBER 2008 - ADDED A CHECK FOR INLET CONDITIONS BELOW MINIMUM
HEATING CONDITION OR ABOVE MAXIMUM COOLING CONDITION
This also has a new modification in the *.tmf proforma. We apologize, but
the example has not been updated. Thank you for bringing that to our
attention. I have updated the example and attached it to this email.
Please let me know if you have any other questions or concerns.
Best regards,
Matt Duffy
----- Original Message -----
From: "" <aartecon at mta01.univpm.it>
Sent: Thu, March 24, 2011 11:24
Subject:[TRNSYS-users] TYPE 682
Dear TRNSYS users,
I have two questions:
1) I know the design cooling and heating loads of a building to be
satisfied by a heat pump (water to water). I want to simulate the
performance of the heat pump during a whole year, considering that the
loads vary during time.
How can I couple the thermal loads with the heat pump, whose requested
input is the load inlet temperature?
I have tried to generate the thermal loads in the whole year, starting
from the design values, with TYPE686.
Then I have coupled TYPE686 with TYPE682 to transfer the load to a fluid
and then I mean to couple the latter with the heat pump (load side). Does
it make sense?
Here the second question:
2) When I tried to use TYPE682 from TESS library 17, I get different
results than using TYPE682 from the available example (synthetic
building). They have slightly different output values ("Heat transfer"
instead of "Heating load met"). Which is the difference between these
otputs? Do they represent different things?
I attach a simple simulation with the comparison of the two types.
Has anyone experienced the same thing? Which one should I use?
Thanks for your help.
Regards.
Alessia
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu
https://mailman.cae.wisc.edu/listinfo/trnsys-users
----- End of original message -----
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Synthetic Building.tpf
Type: application/unknown
Size: 111206 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110331/c757e9a3/attachment-0005.bin>
More information about the TRNSYS-users
mailing list