[TRNSYS-users] trnsys3d pug-in sketchup8 : problem of adjacent wall for several others zones

Angela Dröscher angela.droescher at tugraz.at
Thu Mar 31 06:53:09 PDT 2011


Dear Pauline,

I think your problem is easy to solve: divide the surface (NOT the zone) that is adjacent to two different zones into two surfaces, exactly where the adjacent zones adjoin. It is important that the adjacent surfaces have the same number of vertices and that the vertices exactly line up. Now define the adjacents (now the surface matching tool should also do the job):
surface 1 of zone 1 to zone 2
surface 2 of zone 1to zone 3

I know this hint is included somewhere in the manuals, but I just can't find the section right now.

Hope that helps,
best regards
Angela

-- 
Institute of Thermal Engineering
Graz University of Technology
Inffeldgasse 25/B, A-8010 Graz, Austria
Tel.: (+43) 316 873 7307
Fax: (+43) 316 873 7305
http://www.iwt.tugraz.at



Am 30.03.2011 18:23, schrieb Pauline GELIN:
> SketchUp version:sketchup8
> Operating system:windows xp
>
>
> I am so sorry to ask a so easy question but I didn't find how to link a wall to several others zones.
> Indeed, in the object info we can only choose one zone.
> But, if I cut my zone into 2 parts and, for example, erase the adjacent wall to recreate it in trnbuild, after, there is no more interest to use sketchup and it would be quicker to do everything in trnbuild.
>
> Is there anyone who already met this problem?
> Do you have a solution ?
>
> Thanks a lot in advance for your help.
>
> Best regards,
>
> Pauline Gelin.
>




More information about the TRNSYS-users mailing list