[TRNSYS-users] QHEAT
王洋
wanghongyang1767 at gmail.com
Sun Mar 13 09:41:42 PDT 2011
Dear Mr. Bradley,
Many thanks for your reply!
Please see the ATTACHED! They are .tpf and .bui files. The living room is
the test room, its ambient room is kitchen.
To solar incident: Yes, I didn't define solar incident on my building.
To 2nd: I used the TRNBUILD Wall's default convective heat transfer
coefficient:11 kJ/h*m^2*K and 64 kJ/h*m^2*K to calculate the Q Heat loss.
I calculated the different u-value of different wall types based on the
test room's actual data.
To 3rd: The test room(living room) has no windows.
To 4th: Yes, there is no internal gains and no infiltration and ventilation
in my building.
To 5th: Yes, the living room's ambient room is kitchen. Kitchen's indoor air
temperature is also keeping 20°C from initial temperature.
To 6th: I defined all the wall and floor boundary temperature of the test
room (except the ambient wall next to the kitchen) are 10°C.
To 7th: I defined initial indoor air temperatures of the test room and
kitchen are 20°C, other wall's initial boundary temperature is 10°C
All in all, the result of QHEAT in TRNSYS is 6600 kJ/day, but the heat loss
by Heat transfer equations is 24000 kJ/day.
Please help me find the possible reasons.
MAny thanks!
Br.
wang
2011/3/10 David BRADLEY <d.bradley at tess-inc.com>
> Wang,
> QHEAT is the amount of sensible energy that has to be added to a space to
> maintain it at its set point temperature. I am highly skeptical that it is
> possible or even correct to try and "verify" Type56 using steady state hand
> calculations. Type56 takes into account hundreds of interdependent phenomena
> and holding something like indoor/outdoor temperature difference constant is
> no guarantee that all of them will be constant. A few comments about your
> test: I assume you do not have any solar incident on your building as that
> would have a significant impact on QHEAT. Second, Type56 dynamically
> calculates (and can output) the convective heat transfer coefficient on the
> inside and outside surface of each wall. Those coefficients impact the
> overall u-value of the wall; make sure that you are using the same u-value
> in your hand calc as Type56 is using. Third; windows pose an even more
> complex problem as they are modeled as having a frame u-value, and a center
> of glass u-value that I believe is derated to account for edge effects. Make
> certain that the u-value you are using in your hand calculations and the
> u-value that Type56 is calculating are the same. Fourth, I assume that you
> have no internal gains, infiltration, or ventilation in your building either
> as these also would impact QHEAT. Fifth, if your building has multiple
> zones, make certain that all of them are at the same temperature. Sixth, if
> you are modeling a floor that is coupled to a boundary temperature, there is
> probably energy transfer through that surface. Seventh, the Type56 zones all
> have initial conditions; make certain that your calculation is done long
> after the start of the simulation to avoid any leftover transient effects.
> David
>
>
>
> On 3/10/2011 10:58, 王洋 wrote:
>
> Dear all,
>
> I want to know what is the QHEAT caculation model in TRNSYS? Because I
> assumed a situation: The indoor and outdoor temperature keep the constant
> all the time, based on the Energy Balance the QHEAT must be equal to the
> heat loss through the walls. But the result of QHEAT in TRNSYS is 6600
> kJ/day, but the heat loss by Heat transfer equations is 24000 kJ/day. So I
> want to know what is the QHEAT caculation model in TRNSYS? Why both of them
> are so much defferent?
>
> Many thanks!
>
> br.
>
> wang
>
> 2011/3/10 <trnsys-users-request at cae.wisc.edu>
>
>> Send TRNSYS-users mailing list submissions to
>> trnsys-users at cae.wisc.edu
>>
>> To subscribe or unsubscribe via the World Wide Web, visit
>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>> or, via email, send a message with subject or body 'help' to
>> trnsys-users-request at cae.wisc.edu
>>
>> You can reach the person managing the list at
>> trnsys-users-owner at cae.wisc.edu
>>
>> When replying, please edit your Subject line so it is more specific
>> than "Re: Contents of TRNSYS-users digest..."
>>
>> Today's Topics:
>>
>> 1. problem in trnbuild (Serban Cristina)
>> 2. Re: problem in trnbuild (Matt Duffy)
>> 3. Type 927 W/W heat pump (Partenay, Vincent)
>> 4. Re: Type 927 W/W heat pump (Matt Duffy)
>> 5. Wall heat transfer model in TRNSYS (??)
>>
>>
>> ---------- 已转发邮件 ----------
>> From: Serban Cristina <cristina.serban at unitbv.ro>
>> To: <trnsys-users at cae.wisc.edu>
>> Date: Thu, 10 Mar 2011 12:33:42 +0200
>> Subject: [TRNSYS-users] problem in trnbuild
>> Dear trnsys users,
>>
>> I am a new user of TRNSYS and I have encountered some problems.
>>
>> I created a multizone building in simulation studio, and when I edited the
>> building in trnbuild I created a new wall but I haven't defined layers in
>> it.
>> Now when I try to edit the building to define the wall the error: no
>> layers defined in mtype13 appears. I click ok and trnbuild closes.
>> How can I define my wall? is there a way? or do I have to start over
>> again?
>>
>> My building has 4 zones but they are displayed on 2 levels (floors). Is
>> there a way to automatically create the building on 2 levels?
>> In trnbuild each zone has 5 walls. If I add a new wall type (e.g. ceiling)
>> to each zone will the building be with two levels?
>>
>>
>> P.S. I tried using the trnsys3d plugin but it doesn't work. It gives me
>> too many errors.
>>
>> PhD. Cristina SERBAN
>> Transilvania University of Brasov
>> Department of Renewable Energy Systems and Recycling
>>
>>
>>
>> ---------- 已转发邮件 ----------
>> From: Matt Duffy <duffy at tess-inc.com>
>> To: Serban Cristina <cristina.serban at unitbv.ro>
>> Date: Thu, 10 Mar 2011 06:25:48 -0600
>> Subject: Re: [TRNSYS-users] problem in trnbuild
>> Dear Cristina,
>>
>> Since you are a new user, I am going to suggest that you instead use and
>> learn the Trnsys3D plugin for Google SketchUp. There is a great tutorial
>> that will walk you through everything, it is simple to apply multiple zones,
>> add windows, and shading. After you import this Trnsys3d (*.idf) file into
>> TrnBuild, you can indeed change the wall constructions. Please give it a try
>> and let me know if you have any questions.
>>
>> Best regards,
>>
>> Matt Duffy
>> Thermal Energy Systems Specialists
>>
>>
>> Sent from my mobile wireless device. Please excuse any typos.
>>
>> On Mar 10, 2011, at 4:33 AM, Serban Cristina <cristina.serban at unitbv.ro>
>> wrote:
>>
>> > Dear trnsys users,
>> >
>> > I am a new user of TRNSYS and I have encountered some problems.
>> >
>> > I created a multizone building in simulation studio, and when I edited
>> the building in trnbuild I created a new wall but I haven't defined layers
>> in it.
>> > Now when I try to edit the building to define the wall the error: no
>> layers defined in mtype13 appears. I click ok and trnbuild closes.
>> > How can I define my wall? is there a way? or do I have to start over
>> again?
>> >
>> > My building has 4 zones but they are displayed on 2 levels (floors). Is
>> there a way to automatically create the building on 2 levels?
>> > In trnbuild each zone has 5 walls. If I add a new wall type (e.g.
>> ceiling) to each zone will the building be with two levels?
>> >
>> >
>> > P.S. I tried using the trnsys3d plugin but it doesn't work. It gives me
>> too many errors.
>> >
>> > PhD. Cristina SERBAN
>> > Transilvania University of Brasov
>> > Department of Renewable Energy Systems and Recycling
>> >
>> > _______________________________________________
>> > TRNSYS-users mailing list
>> > TRNSYS-users at cae.wisc.edu
>> > https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>
>>
>>
>> ---------- 已转发邮件 ----------
>> From: "Partenay, Vincent" <vincent.partenay at cstb.fr>
>> To: "trnsys-users at cae.wisc.edu" <trnsys-users at cae.wisc.edu>
>> Date: Thu, 10 Mar 2011 13:01:25 +0000
>> Subject: [TRNSYS-users] Type 927 W/W heat pump
>>
>> Dear all,
>>
>>
>>
>> I’m working with the new type 927 and I would like to get some information
>> about how it works
>>
>> Is there an available detailed documentation of Type 927 ?
>>
>>
>>
>> Thanks in advance,
>>
>>
>>
>>
>>
>>
>>
>> *Vincent PARTENAY*
>>
>> Energies Renouvelables - Département ESE
>>
>>
>>
>> *Centre Scientifique et Technique du Bâtiment*
>>
>> 290 Route des Lucioles BP 209 – F 06904 Sophia Antipolis Cedex
>>
>> Tél : +33-(0)4-93-95-67-21
>>
>> Fax : +33-(0)4-93-95-64-31
>>
>> *Évitez d’imprimer vos emails inutilement. Respectez l’environnement*
>>
>>
>>
>>
>> ---------- 已转发邮件 ----------
>> From: "Matt Duffy" <duffy at tess-inc.com>
>> To: "Partenay, Vincent" <vincent.partenay at cstb.fr>,
>> trnsys-users at cae.wisc.edu
>> Date: Thu, 10 Mar 2011 09:49:13 -0600 (CST)
>> Subject: Re: [TRNSYS-users] Type 927 W/W heat pump
>> Dear Vincent,
>>
>> The detailed documentation for that component is not quite available;
>> however, you may refer the the documentation for the previous version,
>> Type668.
>>
>> The Type927 WWHP is a fairly straightforward component. It references your
>> manufacturer's data in the performance map in the external file. Oppose to
>> Type668, the data file is normalized, so you can scale the power and the
>> capacity as parameters in Type927. If you have any other particular
>> questions about this component, please feel free to contact me.
>>
>>
>>
>> Best regards,
>>
>> Matt Duffy
>>
>> *----- Original Message -----*
>> *From:* "Partenay, Vincent" <vincent.partenay at cstb.fr>
>> *Sent:* Thu, March 10, 2011 7:01
>> *Subject:* [TRNSYS-users] Type 927 W/W heat pump
>>
>> Dear all,
>>
>>
>>
>> I’m working with the new type 927 and I would like to get some information
>> about how it works
>>
>> Is there an available detailed documentation of Type 927 ?
>>
>>
>>
>> Thanks in advance,
>>
>>
>>
>>
>>
>>
>>
>> *Vincent PARTENAY*
>>
>> Energies Renouvelables - Département ESE
>>
>> < /p>
>>
>> *Centre Scientifique et Technique du Bâtiment*
>>
>> 290 Route des Lucioles BP 209 – F 06904 Sophia Antipolis Cedex
>>
>> Tél : +33-(0)4-93-95-67-21
>>
>> Fax : +33-(0)4-93-95-64-31
>>
>> *Évitez d’imprimer vos emails inutilement. Respectez l’environnement*
>>
>>
>> ------------------------------
>>
>> _______________________________________________
>> TRNSYS-users mailing listTRNSYS-users at cae.wisc.eduhttps://mailman.cae.wisc.edu/listinfo/trnsys-users
>>
>>
>>
>> ---------- 已转发邮件 ----------
>> From: 王洋 <wanghongyang1767 at gmail.com>
>> To: trnsys-users at cae.wisc.edu
>> Date: Thu, 10 Mar 2011 17:46:00 +0100
>> Subject: [TRNSYS-users] Wall heat transfer model in TRNSYS
>> Dear all,
>>
>> I have some questions about Wall heat transfer model in TRNSYS:
>>
>> 1. I only find some equations about wall in Manual( such as Radaitive heat
>> flows to the wall, external walls), but I only can understand a little.
>> Please tell me some reference books about Wall heat transfer model in
>> TRNSYS. Because I simulated an actual test room: the indoor and outdoor
>> temperature keep the same 20°C and 10°C, respectively, during one day 24
>> hours. As this situation, QHEAT muss be equal to Q heat loss by walls based
>> on energy balance. But the result of QHEAT in TRNSYS is 6632 kJ, but based
>> on heat transfer equations I got the heat loss energy is 24307 kJ. So I want
>> to know the Wall heat transfer model in TRNSYS.
>>
>> 2. To Wall heat transfer model in TRNSYS: Whether it will consider Solar
>> absorptance and Longwave Emission or not? But I didn't define these things.
>> But from NTYPE 906 Energy Balance for surfaces:
>> 1_B6_BAL = - 1_B6_DQWALLdt- 1_B6_QCOMI+ 1_B6_QCOMO+
>> 1_B6_QRADGI+ 1_B6_QRADGO- 1_B6_QALG
>> 5.839E-14 -2.217E+03 -1.093E-01 -2.217E+03 3.725E-03
>> 0.000E+00 0.000E+00
>>
>> But We can see B6_QRADGI still has value as 3.725E-03. I cann't
>> understand. Please explain possible reasons for it.
>>
>> B6_DQWALLdt in Manual is change of internal energy of surface, but it's a
>> little abstract. Here I only used the heatings in TRNBUILD, no other
>> internal gains. PLEASE give me some examples about change of internal energy
>> of surface. Is it energy Generation of Wall etc.? Why here is minus
>> (-2.217E+03)? What's difference between B6_DQWALLdt and B6_QCOMO? Why here
>> they are the same? Is there some reasons?
>>
>>
>>
>> 3. How to get or check the TRNSYS program's source code? And how to get
>> the TRNSYS program's setup files and look over the "compiled" files(fortran)
>> etc.? Because some simulation results I cann't understand such as the above
>> Wall heat transfer model in TRNSYS etc. I want to understand their model and
>> those simulation results and compare with the results by hand.
>>
>>
>> Many thanks!
>>
>> br.
>>
>> wang
>>
>> 2011/3/8 王洋 <wanghongyang1767 at gmail.com>
>>
>>>
>>>
>>> 2011/3/7 王洋 <wanghongyang1767 at gmail.com>
>>>
>>> Dear all,
>>>>
>>>> I have some questions about Wall heat transfer model in TRNSYS:
>>>>
>>>> 1. I only find some equations about wall in Manual( such as Radaitive
>>>> heat flows to the wall, external walls), but I only can understand a little.
>>>> Please tell me some reference books about Wall heat transfer model in
>>>> TRNSYS. Because I simulated an actual test room: the indoor and outdoor
>>>> temperature keep the same 20°C and 10°C, respectively, during one day 24
>>>> hours. As this situation, QHEAT muss be equal to Q heat loss by walls based
>>>> on energy balance. But the result of QHEAT in TRNSYS is 6632 kJ, but based
>>>> on heat transfer equations I got the heat loss energy is 24307 kJ. So I want
>>>> to know the Wall heat transfer model in TRNSYS.
>>>>
>>>> 2. To Wall heat transfer model in TRNSYS: Whether it will consider Solar
>>>> absorptance and Longwave Emission or not? But I didn't define these things.
>>>> But from NTYPE 906 Energy Balance for surfaces:
>>>> 1_B6_BAL = - 1_B6_DQWALLdt- 1_B6_QCOMI+ 1_B6_QCOMO+
>>>> 1_B6_QRADGI+ 1_B6_QRADGO- 1_B6_QALG
>>>> 5.839E-14 -2.217E+03 -1.093E-01 -2.217E+03
>>>> 3.725E-03 0.000E+00 0.000E+00
>>>>
>>>> But We can see B6_QRADGI still has value as 3.725E-03. I cann't
>>>> understand. Please explain possible reasons for it.
>>>>
>>>> B6_DQWALLdt in Manual is change of internal energy of surface, but it's
>>>> a little abstract. Here I only used the heatings in TRNBUILD, no other
>>>> internal gains. PLEASE give me some examples about change of internal energy
>>>> of surface. Is it energy Generation of Wall etc.? Why here is minus
>>>> (-2.217E+03)? What's difference between B6_DQWALLdt and B6_QCOMO? Why here
>>>> they are the same? Is there some reasons?
>>>>
>>>>
>>>>
>>>> 3. How to get or check the TRNSYS program's source code? And how to get
>>>> the TRNSYS program's setup files and look over the "compiled" files(fortran)
>>>> etc.? Because some simulation results I cann't understand such as the above
>>>> Wall heat transfer model in TRNSYS etc. I want to understand their model and
>>>> those simulation results and compare with the results by hand.
>>>>
>>>>
>>>> Many thanks!
>>>>
>>>> br.
>>>>
>>>> wang
>>>>
>>>> 2011/3/7 <trnsys-users-request at cae.wisc.edu>
>>>>
>>>>> Send TRNSYS-users mailing list submissions to
>>>>> trnsys-users at cae.wisc.edu
>>>>>
>>>>> To subscribe or unsubscribe via the World Wide Web, visit
>>>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>>> or, via email, send a message with subject or body 'help' to
>>>>> trnsys-users-request at cae.wisc.edu
>>>>>
>>>>> You can reach the person managing the list at
>>>>> trnsys-users-owner at cae.wisc.edu
>>>>>
>>>>> When replying, please edit your Subject line so it is more specific
>>>>> than "Re: Contents of TRNSYS-users digest..."
>>>>>
>>>>> Today's Topics:
>>>>>
>>>>> 1. Re: Questions...please reply (Matt Duffy)
>>>>> 2. Re: Stratified storage Tank (Matt Duffy)
>>>>> 3. Re: Strange error (Rambod Rayegan)
>>>>> 4. Re: Strange error (Matt Duffy)
>>>>>
>>>>>
>>>>> ---------- 已转发邮件 ----------
>>>>> From: "Matt Duffy" <duffy at tess-inc.com>
>>>>> To: juvenciotavares at hotmail.com, trnsys-users at engr.wisc.edu
>>>>> Date: Mon, 7 Mar 2011 09:34:17 -0600 (CST)
>>>>> Subject: Re: [TRNSYS-users] Questions...please reply
>>>>>
>>>>> Dear Juvencio,
>>>>>
>>>>> It appears that when you imported the file into TRNBuild, the
>>>>> application did not find the adjacent surface. This could be for a couple of
>>>>> reasons: the adjacency needs to be defined, or the surface in TRNSYS3D has a
>>>>> face that is reversed. Please refer to the TRNSYS3D tutorial PDF for more
>>>>> great information.
>>>>>
>>>>> Best regards,
>>>>>
>>>>> Matt Duffy
>>>>>
>>>>> *----- Original Message -----*
>>>>> *From:* "Juvêncio Correia Tavares" <juvenciotavares at hotmail.com>
>>>>> *Sent:* Fri, March 4, 2011 10:50
>>>>> *Subject:* Re: [TRNSYS-users] Questions...please reply
>>>>>
>>>>>
>>>>> I`m doing a dynamic simulation of buildings in TRNSYS, during the
>>>>> simulation gave the following error ... as you can see in the picture.
>>>>> how can I fix this error?
>>>>> < span title="Clique para obter tradu??es alternativas"
>>>>> class="ecxhps">And also, I would like to send me a PDF about
>>>>> connection.
>>>>>
>>>>> I await your response.
>>>>>
>>>>> thanks.
>>>>> ------------------------------
>>>>>
>>>>> _______________________________________________
>>>>> TRNSYS-users mailing listTRNSYS-users at cae.wisc.eduhttps://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>>>
>>>>>
>>>>>
>>>>> ---------- 已转发邮件 ----------
>>>>> From: "Matt Duffy" <duffy at tess-inc.com>
>>>>> To: "Lei Wang" <leiwang at tees.tamus.edu>, trnsys-users at cae.wisc.edu
>>>>> Date: Mon, 7 Mar 2011 09:41:06 -0600 (CST)
>>>>> Subject: Re: [TRNSYS-users] Stratified storage Tank
>>>>>
>>>>> Dear Lei Wang,
>>>>>
>>>>> I just tried this, and it simulated without problems in version 17, but
>>>>> when I tried in version 16, I also received the error. I can only
>>>>> speculate that this is due to the changes that we implemented for
>>>>> TrnsysConstants - we increased the number of parameters.
>>>>> Another option besides updating to version 17 is to use the Type534
>>>>> TESS
>>>>> Tank model as well. Please let me know if you have any more questions
>>>>> about this.
>>>>>
>>>>> Best regards,
>>>>>
>>>>> Matt Duffy
>>>>>
>>>>>
>>>>> ----- Original Message -----
>>>>> From: "Lei Wang" <leiwang at tees.tamus.edu>
>>>>> Sent: Fri, March 4, 2011 16:17
>>>>> Subject:[TRNSYS-users] Stratified storage Tank
>>>>>
>>>>>
>>>>> Hi, All
>>>>>
>>>>> I try to use the Type4a(stratified storage tank) to modeling the ChW
>>>>> thermal storage
>>>>> tank, which volume was 1 million gal and height was 100 feet.
>>>>>
>>>>>
>>>>> The description of the type is as following
>>>>> "The thermal performance of a fluid-filled sensible energy storage
>>>>> tank,
>>>>> subject to
>>>>> thermal stratification, can be modeled by assuming that the tank
>>>>> consists
>>>>> of N (N <=
>>>>> 100) fully-mixed equal volume segments"
>>>>>
>>>>> So I think the maximum nodes number can be 100.
>>>>>
>>>>> But when I input the number of nodes were 100, the TrnExe shows that
>>>>> there
>>>>> was a
>>>>> range check error. When I check the list file, there didn't show any
>>>>> error
>>>>> Information.
>>>>>
>>>>> When I input the number of nodes were 80, it works fine.
>>>>>
>>>>>
>>>>> Thanks
>>>>>
>>>>> Lei
>>>>>
>>>>>
>>>>> _______________________________________________
>>>>> TRNSYS-users mailing list
>>>>> TRNSYS-users at cae.wisc.edu
>>>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>>>
>>>>>
>>>>> ----- End of original message -----
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> ---------- 已转发邮件 ----------
>>>>> From: Rambod Rayegan <rraye001 at fiu.edu>
>>>>> To: hotline <hotline at transsolar.com>
>>>>> Date: Mon, 7 Mar 2011 10:49:42 -0500
>>>>> Subject: Re: [TRNSYS-users] Strange error
>>>>> Christian,
>>>>>
>>>>> Even when I change back the roof property to the previous one, the
>>>>> error exists. It seems, right now, it is independent of the roof property.
>>>>> This is the reason that I called it strange error.
>>>>>
>>>>> Rambod Rayegan
>>>>> Ph.D Candidate
>>>>> Mechanical Engineering Department
>>>>> Florida International University
>>>>> 10555 W Flagler St, EC3620
>>>>> Miami, FL, 33174
>>>>>
>>>>> 305-348-3558 (Office)
>>>>> 786-218-7375(Cell)
>>>>> 305-348-1932 (Fax)
>>>>> On Mon, Mar 7, 2011 at 7:33 AM, hotline <hotline at transsolar.com>wrote:
>>>>>
>>>>>> Hi,
>>>>>>
>>>>>> seems like you hit a limit for the generation of the transfer function
>>>>>> coefficients.
>>>>>> Please check if the roof is defined correctly.
>>>>>>
>>>>>> Regards
>>>>>> Christian
>>>>>>
>>>>>>
>>>>>> TRANSSOLAR Software Team
>>>>>>
>>>>>> hotline at transsolar.com
>>>>>>
>>>>>>
>>>>>>
>>>>>> www.trnsys.de
>>>>>>
>>>>>> Transsolar KlimaEngineering - Technologien für energieeffizientes
>>>>>> Bauen und Nutzerkomfort in Gebäuden
>>>>>>
>>>>>>
>>>>>> Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart /
>>>>>> Amtsgericht Stuttgart - HRB 23347 / UsSt.-Id: DE152272639
>>>>>>
>>>>>> Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
>>>>>> Dipl.Phys. Stefan Holst, Prof. Volkmar Bleicher
>>>>>>
>>>>>>
>>>>>> ------------------------------
>>>>>> *Von:* Rambod Rayegan [mailto:rraye001 at fiu.edu]
>>>>>> *Gesendet:* Samstag, 5. März 2011 06:08
>>>>>> *An:* trnsys-users at cae.wisc.edu
>>>>>> *Betreff:* [TRNSYS-users] Strange error
>>>>>>
>>>>>> Dear TRNSYS users:
>>>>>>
>>>>>> I am working on a model created buy TRNSYS 3d plugin in google
>>>>>> sketchup for couple of months. Everyday I add something to it or modify
>>>>>> some parameters in it. Today, I have just changed the roof type in the
>>>>>> building type 56 and tried to run it again but I have received the following
>>>>>> error:
>>>>>>
>>>>>>
>>>>>> Visual Fortran run-time error
>>>>>>
>>>>>> fortrtl:severe(64):input conversion error, unit 56, file
>>>>>> C:\.....building.trn
>>>>>> Image PC Routine Source DFORRT.DLL 02014C49 Unknown Unknown Unknown
>>>>>>
>>>>>>
>>>>>> Anybody has an idea to solve the issue?
>>>>>>
>>>>>> Thank you.
>>>>>>
>>>>>> Rambod Rayegan
>>>>>> Ph.D Candidate
>>>>>> Mechanical Engineering Department
>>>>>> Florida International University
>>>>>> 10555 W Flagler St, EC3620
>>>>>> Miami, FL, 33174
>>>>>>
>>>>>> 305-348-3558 (Office)
>>>>>> 786-218-7375(Cell)
>>>>>> 305-348-1932 (Fax)
>>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> ---------- 已转发邮件 ----------
>>>>> From: "Matt Duffy" <duffy at tess-inc.com>
>>>>> To: "Rambod Rayegan" <rraye001 at fiu.edu>, hotline at transsolar.com
>>>>> Date: Mon, 7 Mar 2011 09:57:02 -0600 (CST)
>>>>> Subject: Re: [TRNSYS-users] Strange error
>>>>> Dear Rambod,
>>>>>
>>>>> If you send me the IDF file, I might be able to shed some light on the
>>>>> error.
>>>>>
>>>>> Best regards,
>>>>>
>>>>> Matt Duffy
>>>>>
>>>>>
>>>>> *----- Original Message -----*
>>>>> *From:* "Rambod Rayegan" <rraye001 at fiu.edu>
>>>>> *Sent:* Mon, March 7, 2011 9:49
>>>>> *Subject:* Re: [TRNSYS-users] Strange error
>>>>>
>>>>> Christian,
>>>>>
>>>>> Even when I change back the roof property to the previous one, the
>>>>> error exists. It seems, right now, it is independent of the roof property.
>>>>> This is the reason that I called it strange error.
>>>>>
>>>>> Rambod Rayegan
>>>>> Ph.D Candidate
>>>>> Mechanical Engineering Department
>>>>> Florida International University
>>>>> 10555 W Flagler St, EC3620
>>>>> Miami, FL, 33174
>>>>>
>>>>> 305-348-3558 (Office)
>>>>> 786-218-7375(Cell)
>>>>> 305-348-1932 (Fax)
>>>>> On Mon, Mar 7, 2011 at 7:33 AM, hotline <hotline at transsolar.com>wrote:
>>>>>
>>>>>> Hi,
>>>>>>
>>>>>> seems like you hit a limit for the generation of the transfer function
>>>>>> coefficients.
>>>>>> Please check if the roof is defined correctly.
>>>>>>
>>>>>> Regards
>>>>>> Christian
>>>>>>
>>>>>>
>>>>>> TRANSSOLAR Software Team
>>>>>>
>>>>>> hotline at transsolar.com
>>>>>>
>>>>>>
>>>>>>
>>>>>> www.trnsys.de
>>>>>>
>>>>>> Transsolar KlimaEngineering - Technologien für energieeffizientes
>>>>>> Bauen und Nutzerkomfort in Gebäuden &n!
>>>>>> bsp;
>>>>>>
>>>>>> Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart /
>>>>>> Amtsgericht Stuttgart - HRB 23347 / UsSt.-Id: DE152272639
>>>>>>
>>>>>> Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
>>>>>> Dipl.Phys. Stefan Holst, Prof. Volkmar Bleicher
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>> ------------------------------
>>>>>> *Von:* Rambod Rayegan [mailto:rraye001 at fiu.edu]
>>>>>> *Gesendet:* Samstag, 5. Mä! ;rz 2011 06:08
>>>>>> *An:* trnsys-users at cae.wisc.edu
>>>>>> *Betreff:* [TRNSYS-users] Strange error
>>>>>>
>>>>>>
>>>>>>
>>>>>> Dear TRNSYS users:
>>>>>>
>>>>>> I am working on a model created buy TRNSYS 3d plugin in google
>>>>>> sketchup for couple of months. Everyday I add something to it or modify
>>>>>> some parameters in it. Today, I have just changed the roof type in the
>>>>>> building type 56 and tried to run it again but I have received the following
>>>>>> error:
>>>>>>
>>>>>>
>>>>>> Visual Fortran run-time error
>>>>>>
>>>>>> fortrtl:severe(64):input conversion error, unit 56, file
>>>>>> C:\.....building.trn
>>>>>> Image PC Routine Source DFORRT.DLL 02014C49 Unknown Unknown Unknown
>>>>>>
>>>>>>
>>>>>> Anybody has an idea to solve the issu! e?
>>>>>>
>>>>>> Thank you.
>>>>>>
>>>>>> Rambod Rayegan
>>>>>> Ph.D Candidate
>>>>>> Mechanical Engineering Department
>>>>>> Florida International University
>>>>>> 10555 W Flagler St, EC3620
>>>>>> Miami, FL, 33174
>>>>>>
>>>>>> 305-348-3558 (Office)
>>>>>> 786-218-7375(Cell)
>>>>>> 305-348-1932 (Fax)
>>>>>>
>>>>>>
>>>>>>
>>>>>
>>>>>
>>>>>
>>>>> ------------------------------
>>>>>
>>>>> _______________________________________________
>>>>> TRNSYS-users mailing listTRNSYS-users at cae.wisc.eduhttps://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>>>
>>>>>
>>>>> _______________________________________________
>>>>> TRNSYS-users mailing list
>>>>> TRNSYS-users at cae.wisc.edu
>>>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>>>
>>>>>
>>>>
>>>
>>
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at cae.wisc.edu
>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>
>>
>
> _______________________________________________
> TRNSYS-users mailing listTRNSYS-users at cae.wisc.eduhttps://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
> --
> ***************************
> David BRADLEY
> Principal
> Thermal Energy Systems Specialists, LLC
> 22 North Carroll Street - suite 370
> Madison, WI 53703 USA
>
> P:+1.608.274.2577
> F:+1.608.278.1475d.bradley at tess-inc.com
> http://www.tess-inc.comhttp://www.trnsys.com
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110313/e6572e9a/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: masseffectsmarthome.tpf
Type: application/octet-stream
Size: 108730 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110313/e6572e9a/attachment-0002.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: BuildingProject3.b17
Type: application/octet-stream
Size: 39762 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110313/e6572e9a/attachment-0003.obj>
More information about the TRNSYS-users
mailing list