[TRNSYS-users] Error in type 56, automatic heat transfer calculation for surface
LE XUAN, Tuan
tuan.lexuan at norpac.fr
Tue Jun 7 00:51:27 PDT 2011
Hello,
In my project TRNSYS version 17, when I run the calculation, I get an error that I cannot fix:
*** Fatal Error at time: 0.000000
Generated by Unit: 56
Generated by Type: 56
Message: Error in automatic calculation for heat transfer surface 5 or its adjacent surface!: Automatic heat transfer calculation Is Only Allowed on surfaces Within a zone. Please check building input file (. bui)!
I tried different things on my wall in question (external wall) without results:
1 - I put "the convective heat transfer coefficient of wall (front and back) on UserDefined
2 - I put "the convective heat transfer coefficient of wall (front and back) on internal calculation
3 - I deleted the wall
4 - I deleted the zone
5 - I removed the wall and I recreated
Each time, I have the same error message.
I do not know what to do and I need your help.
You will find attached the file. inf. with the number 5 test.
If you need further information I am at your disposal.
Thank you in advance.
Tuan LE XUAN Direction Technique Fluides
Tél : 03.57.63.45.89
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110607/d30456ff/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 756 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110607/d30456ff/attachment-0003.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.gif
Type: image/gif
Size: 138966 bytes
Desc: image002.gif
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110607/d30456ff/attachment-0005.gif>
-------------- next part --------------
*********************************************************************************************************************************************************************************************************
* TRNBuild 2.0.167
*********************************************************************************************************************************************************************************************************
* BUILDING DESCRIPTIONS FILE TRNSYS
* FOR BUILDING: D:\Data\Projets en cours\STD NSN\BUILD VIDE\Build.inf
* GET BY WORKING WITH TRNBuild 1.0 for Windows
*********************************************************************************************************************************************************************************************************
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* C o m m e n t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*#C ---------------------------------------------------- TYPES --------------------------------- *
*#C
*#C -----------------------------------------------------LAYERS --------------------------------- *
*#C
*#C -------------------------------------------------------- INPUTS ----------------------------- *
*#C
*#C ------------------------------------------------------SCHEDULES ----------------------------- *
*#C
*#C -------------------------------------------------------- WALLS ------------------------------ *
*#C
*#C ------------------------------------------------------ WINDOWS ------------------------------ *
*#C
*#C -------------------------------------------------------- GAINS ------------------------------ *
*#C
*#C -------------------------------------------------------- COMFORT----------------------------- *
*#C
*#C ---------------------------------------------------- INFILTRATION --------------------------- *
*#C
*#C ---------------------------------------------------- VENTILATION ---------------------------- *
*#C
*#C ------------------------------------------------------- HEATING ----------------------------- *
*#C
*#C -------------------------------------------------- ORIENTATIONS ----------------------------- *
*#C
*#C -------------------------------------------------------- ZONES ------------------------------ *
*#C
*#C ------------------------------------------------------- BUILDING ---------------------------- *
*#C
*#C ------------------------------- GEOSURF ----------------------------------------------------- *
*#C
*#C --------------------------------------------------- OUTPUTS --------------------------------- *
*#C
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* P r o j e c t
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*+++ PROJECT
*+++ TITLE=ERE PARK
*+++ DESCRIPTION=SIÈGE DE NORPAC
*+++ CREATED=T.LE XUAN
*+++ ADDRESS=1 AVENUE DE L'HORIZON
*+++ CITY=VILLENEUVE D'ASCQ
*+++ SWITCH=UNDEFINED
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* P r o p e r t i e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
PROPERTIES
DENSITY=1.204 : CAPACITY=1.012 : PRESSURE=101325.000 : HVAPOR=2454.0 : SIGMA=2.041e-007 : RTEMP=293.15
*--- alpha calculation -------------------
KFLOORUP=7.2 : EFLOORUP=0.31 : KFLOORDOWN=3.888 : EFLOORDOWN=0.31
KCEILUP=7.2 : ECEILUP=0.31 : KCEILDOWN=3.888 : ECEILDOWN=0.31
KVERTICAL=5.76 : EVERTICAL=0.3
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
TYPES
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* L a y e r s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
LAYER BETON
CONDUCTIVITY= 8.28 : CAPACITY= 1 : DENSITY= 2000
LAYER GRAVILLONS
CONDUCTIVITY= 6.84 : CAPACITY= 1 : DENSITY= 1600
LAYER PLATRE
CONDUCTIVITY= 0.9 : CAPACITY= 1 : DENSITY= 800
LAYER POLYURETHANE
CONDUCTIVITY= 0.086 : CAPACITY= 1.35 : DENSITY= 32
LAYER LM&FIXATIONS
CONDUCTIVITY= 0.158 : CAPACITY= 1.03 : DENSITY= 39
LAYER BARDAGE_BOIS
CONDUCTIVITY= 0.432 : CAPACITY= 2.45 : DENSITY= 440
LAYER TERRE_CUITE
CONDUCTIVITY= 3.024 : CAPACITY= 2 : DENSITY= 2285.7
LAYER UNIMAT_SOL
CONDUCTIVITY= 0.122 : CAPACITY= 1.45 : DENSITY= 88.5
LAYER ISOLANT_INT_PSE
CONDUCTIVITY= 0.119 : CAPACITY= 1.45 : DENSITY= 88.5
LAYER CBR_B11
RESISTANCE= 0.57
LAYER CBR_I21
RESISTANCE= 6.94
LAYER BAC_ACIER
CONDUCTIVITY= 93.6 : CAPACITY= 0.46 : DENSITY= 7500
LAYER CBR_MEN
RESISTANCE= 1.736
LAYER CBR_H11
RESISTANCE= 4.63
LAYER CBR_H31
RESISTANCE= 9.26
LAYER CBR_H11_TOITURE
RESISTANCE= 0.9
LAYER FIBRASTYRENE
CONDUCTIVITY= 0.14 : CAPACITY= 1.4 : DENSITY= 40
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* I n p u t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
INPUTS CNAT_1 T_COOL_ON MS_N_180_90 MS_S_0_90 MS_E_270_90 MS_W_90_90 BRIGHT INPUT001 TEMP_SOL SCEN_FROID_0.01 SCEN_CHAUD_0.01 TSOUFFLAGE_CTA HR_SOUFFLAGE 0.01_DEM_CHAUD 0.02_DEM_CHAUD
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* S c h e d u l e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
SCHEDULE CTA_LUNDI
HOURS =0.000 5.000 19.000 24.0
VALUES=0 1. 0 0
SCHEDULE CTA_SEMAINE
HOURS =0.000 6.000 19.000 24.0
VALUES=0 1. 0 0
SCHEDULE CTA_VENDREDI
HOURS =0.000 6.000 18.000 24.0
VALUES=0 1. 0 0
SCHEDULE CTA_WE
HOURS =0.000 24.0
VALUES=0 0
SCHEDULE OCCUP_SDR_SEM
HOURS =0.000 5.000 6.000 7.000 8.000 9.000 10.000 11.000 12.000 13.000 14.000 15.000 16.000 17.000 18.000 19.000 20.000 21.000 22.000 24.0
VALUES=0 0 0 0 0.25 0.5 0.5 0.5 0.25 0.25 0.5 0.5 0.5 0.5 0.25 0 0 0 0 0
SCHEDULE OCCUP_SDR_WE
HOURS =0.000 5.000 6.000 7.000 8.000 9.000 10.000 11.000 12.000 13.000 14.000 15.000 16.000 17.000 18.000 19.000 20.000 21.000 22.000 24.0
VALUES=0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0
SCHEDULE OCCUP_SDR_VENDREDI
HOURS =0.000 5.000 6.000 7.000 8.000 9.000 10.000 11.000 12.000 13.000 14.000 15.000 16.000 17.000 18.000 19.000 20.000 21.000 22.000 24.0
VALUES=0 0 0 0 0.25 0.5 0.5 0.5 0.25 0.25 0.5 0.5 0.25 0 0 0 0 0 0 0
SCHEDULE OCCUP_BUREAUX_DT_SEM
HOURS =0.000 5.000 6.000 7.000 8.000 9.000 10.000 11.000 12.000 13.000 14.000 15.000 16.000 17.000 18.000 19.000 20.000 21.000 22.000 24.0
VALUES=0 0 0 0.06 0.6 0.7 0.7 0.7 0.13 0.25 0.7 0.7 0.7 0.7 0.6 0.25 0.05 0 0 0
SCHEDULE OCCUP_BUREAUX_DT_VENDREDI
HOURS =0.000 5.000 6.000 7.000 8.000 9.000 10.000 11.000 12.000 13.000 14.000 15.000 16.000 17.000 18.000 19.000 20.000 21.000 22.000 24.0
VALUES=0 0 0 0.25 0.7 0.7 0.7 0.7 0.13 0.7 0.6 0.38 0.25 0.1 0.05 0 0 0 0 0
SCHEDULE OCCUP_BUREAUX_DT_WE
HOURS =0.000 5.000 6.000 7.000 8.000 9.000 10.000 11.000 12.000 13.000 14.000 15.000 16.000 17.000 18.000 19.000 20.000 21.000 22.000 24.0
VALUES=0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0
SCHEDULE OCCUP_BUREAUX_IND_SEM
HOURS =0.000 5.000 6.000 7.000 8.000 9.000 10.000 11.000 12.000 13.000 14.000 15.000 16.000 17.000 18.000 19.000 20.000 21.000 22.000 24.0
VALUES=0 0 0 0.25 1. 1. 1. 1. 0.5 0.5 1. 1. 1. 1. 1. 1. 0.5 0 0 0
SCHEDULE OCCUP_BUREAUX_COM_SEM
HOURS =0.000 5.000 6.000 7.000 8.000 9.000 10.000 11.000 12.000 13.000 14.000 15.000 16.000 17.000 18.000 19.000 20.000 21.000 22.000 24.0
VALUES=0 0 0 0 0.38 0.6 0.6 0.6 0.13 0.25 0.6 0.6 0.6 0.6 0.55 0.25 0.05 0 0 0
SCHEDULE OCCUP_BUREAUX_COM_VENDREDI
HOURS =0.000 5.000 6.000 7.000 8.000 9.000 10.000 11.000 12.000 13.000 14.000 15.000 16.000 17.000 18.000 19.000 20.000 21.000 22.000 24.0
VALUES=0 0 0 0.25 0.6 0.6 0.6 0.6 0.13 0.6 0.5 0.38 0.25 0.1 0.05 0 0 0 0 0
SCHEDULE OCCUP_CAFET_SEM
HOURS =0.000 5.000 6.000 7.000 8.000 9.000 10.000 11.000 12.000 13.000 14.000 15.000 16.000 17.000 18.000 19.000 20.000 21.000 22.000 24.0
VALUES=0 0 0 0 0 0 0 0 1. 0.5 0 0 0 0 0 0 0 0 0 0
SCHEDULE OCCUP_CAFET_WE
HOURS =0.000 5.000 6.000 7.000 8.000 9.000 10.000 11.000 12.000 13.000 14.000 15.000 16.000 17.000 18.000 19.000 20.000 21.000 22.000 24.0
VALUES=0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0
SCHEDULE OCCUP_COFFEE_SEM
HOURS =0.000 5.000 6.000 7.000 8.000 9.000 10.000 11.000 12.000 13.000 14.000 15.000 16.000 17.000 18.000 19.000 20.000 21.000 22.000 24.0
VALUES=0 0 0 0.06 0.5 0.25 0.25 0 0 0.5 0.25 0.25 0.06 0.06 0 0 0 0 0 0
SCHEDULE OCCUP_ACCUEIL_SEM
HOURS =0.000 5.000 6.000 7.000 8.000 9.000 10.000 11.000 12.000 13.000 14.000 15.000 16.000 17.000 18.000 19.000 20.000 21.000 22.000 24.0
VALUES=0 0 0 0.5 1. 0.2 0.2 0.2 1. 1. 0.2 0.2 0.2 0.2 0.5 0.5 0 0 0 0
SCHEDULE SERVEURS_CONTINUS_SEMAINE
HOURS =0.000 24.0
VALUES=1. 1.
SCHEDULE CTA
DAYS=1 2 3 4 5 6 7
HOURLY=CTA_LUNDI CTA_SEMAINE CTA_SEMAINE CTA_SEMAINE CTA_VENDREDI CTA_WE CTA_WE
SCHEDULE OCCUP_SDR
DAYS=1 2 3 4 5 6 7
HOURLY=OCCUP_SDR_SEM OCCUP_SDR_SEM OCCUP_SDR_SEM OCCUP_SDR_SEM OCCUP_SDR_VENDREDI OCCUP_SDR_WE OCCUP_SDR_WE
SCHEDULE OCCUP_BUREAUX_DT
DAYS=1 2 3 4 5 6 7
HOURLY=OCCUP_BUREAUX_DT_SEM OCCUP_BUREAUX_DT_SEM OCCUP_BUREAUX_DT_SEM OCCUP_BUREAUX_DT_SEM OCCUP_BUREAUX_DT_VENDREDI OCCUP_BUREAUX_DT_WE OCCUP_BUREAUX_DT_WE
SCHEDULE OCCUP_BUREAUX_IND
DAYS=1 2 3 4 5 6 7
HOURLY=OCCUP_BUREAUX_IND_SEM OCCUP_BUREAUX_IND_SEM OCCUP_BUREAUX_IND_SEM OCCUP_BUREAUX_IND_SEM OCCUP_BUREAUX_IND_SEM OCCUP_BUREAUX_DT_WE OCCUP_BUREAUX_DT_WE
SCHEDULE OCCUP_BUR_COMMERCES
DAYS=1 2 3 4 5 6 7
HOURLY=OCCUP_BUREAUX_COM_SEM OCCUP_BUREAUX_COM_SEM OCCUP_BUREAUX_COM_SEM OCCUP_BUREAUX_COM_SEM OCCUP_BUREAUX_COM_VENDREDI OCCUP_BUREAUX_DT_WE OCCUP_BUREAUX_DT_WE
SCHEDULE OCCUP_CAFETERIA
DAYS=1 2 3 4 5 6 7
HOURLY=OCCUP_CAFET_SEM OCCUP_SDR_SEM OCCUP_CAFET_SEM OCCUP_CAFET_SEM OCCUP_CAFET_SEM OCCUP_CAFET_WE OCCUP_CAFET_WE
SCHEDULE OCCUP_COFFEE_CORNER
DAYS=1 2 3 4 5 6 7
HOURLY=OCCUP_COFFEE_SEM OCCUP_COFFEE_SEM OCCUP_COFFEE_SEM OCCUP_COFFEE_SEM OCCUP_COFFEE_SEM OCCUP_CAFET_WE OCCUP_CAFET_WE
SCHEDULE OCCUP_ACCUEIL
DAYS=1 2 3 4 5 6 7
HOURLY=OCCUP_ACCUEIL_SEM OCCUP_ACCUEIL_SEM OCCUP_ACCUEIL_SEM OCCUP_ACCUEIL_SEM OCCUP_ACCUEIL_SEM OCCUP_CAFET_WE OCCUP_CAFET_WE
SCHEDULE SERVEURS_CONTINUS
DAYS=1 2 3 4 5 6 7
HOURLY=SERVEURS_CONTINUS_SEMAINE SERVEURS_CONTINUS_SEMAINE SERVEURS_CONTINUS_SEMAINE SERVEURS_CONTINUS_SEMAINE SERVEURS_CONTINUS_SEMAINE SERVEURS_CONTINUS_SEMAINE SERVEURS_CONTINUS_SEMAINE
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* W a l l s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
WALL PB_TP
LAYERS = BETON UNIMAT_SOL
THICKNESS= 0.2 0.1
ABS-FRONT= 0.8 : ABS-BACK= 0
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = FLOOR : HBACK= FLOOR
WALL MEXT_PEUPLIER
LAYERS = BETON LM&FIXATIONS BARDAGE_BOIS
THICKNESS= 0.25 0.12 0.02
ABS-FRONT= 0.4 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = VERTICAL : HBACK= 64
WALL MINT_LEGER
LAYERS = PLATRE
THICKNESS= 0.1
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = VERTICAL : HBACK= VERTICAL
WALL TOITURE
LAYERS = BETON POLYURETHANE GRAVILLONS
THICKNESS= 0.2 0.12 0.04
ABS-FRONT= 0.35 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = CEILING : HBACK= 64
WALL MEXT_TERRE_CUITE
LAYERS = BETON LM&FIXATIONS TERRE_CUITE
THICKNESS= 0.25 0.12 0.014
ABS-FRONT= 0.4 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 64
WALL MINT_LOURD
LAYERS = BETON
THICKNESS= 0.2
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = VERTICAL : HBACK= VERTICAL
WALL PLANCHER_INTERMEDIAIRE
LAYERS = BETON
THICKNESS= 0.2
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 11
WALL PLH_SDR
LAYERS = POLYURETHANE BAC_ACIER
THICKNESS= 0.1 0.001
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 11
WALL CBR_B11
LAYERS = CBR_B11
THICKNESS= 0
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 64
WALL CBR_I21
LAYERS = CBR_I21
THICKNESS= 0
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 64
WALL MINT_LNC
LAYERS = BETON ISOLANT_INT_PSE
THICKNESS= 0.2 0.1
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = VERTICAL : HBACK= VERTICAL
WALL CBR_MEN
LAYERS = CBR_MEN
THICKNESS= 0
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 64
WALL CBR_H11
LAYERS = CBR_H11
THICKNESS= 0
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 64
WALL CBR_H31
LAYERS = CBR_H31
THICKNESS= 0
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 64
WALL CBR_H11_TOITURE
LAYERS = CBR_H11_TOITURE
THICKNESS= 0
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 64
WALL PL_LNC
LAYERS = BETON FIBRASTYRENE
THICKNESS= 0.2 0.15
ABS-FRONT= 0.6 : ABS-BACK= 0
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = FLOOR : HBACK= CEILING
WALL CLOISON_VIDE_INT
LAYERS = PLATRE
THICKNESS= 0.05
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = VERTICAL : HBACK= VERTICAL
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* W i n d o w s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
WINDOW MEN_101
WINID=13010 : HINSIDE=VERTICAL : HOUTSIDE=VERTICAL : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.35 : UFRAME=11.16 : ABSFRAME=0.4 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
WINDOW MEN_113
WINID=13010 : HINSIDE=VERTICAL : HOUTSIDE=VERTICAL : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.35 : UFRAME=11.16 : ABSFRAME=0.4 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
WINDOW MEN_112
WINID=13010 : HINSIDE=VERTICAL : HOUTSIDE=VERTICAL : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.35 : UFRAME=11.16 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
WINDOW MEN_109
WINID=13010 : HINSIDE=VERTICAL : HOUTSIDE=VERTICAL : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.32 : UFRAME=11.88 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
WINDOW MEN_114
WINID=13010 : HINSIDE=VERTICAL : HOUTSIDE=VERTICAL : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.35 : UFRAME=11.16 : ABSFRAME=0.4 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
WINDOW MEN_111
WINID=13010 : HINSIDE=VERTICAL : HOUTSIDE=VERTICAL : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.35 : UFRAME=11.16 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
WINDOW MR1
WINID=13013 : HINSIDE=VERTICAL : HOUTSIDE=VERTICAL : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.18 : UFRAME=11.16 : ABSFRAME=0.4 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
WINDOW MR2
WINID=13013 : HINSIDE=VERTICAL : HOUTSIDE=VERTICAL : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.18 : UFRAME=11.16 : ABSFRAME=0.4 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
WINDOW RDC_NE
WINID=13010 : HINSIDE=VERTICAL : HOUTSIDE=VERTICAL : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.35 : UFRAME=11.16 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
WINDOW MR3
WINID=13013 : HINSIDE=VERTICAL : HOUTSIDE=VERTICAL : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.18 : UFRAME=11.16 : ABSFRAME=0.4 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
WINDOW RDC_NO
WINID=13010 : HINSIDE=VERTICAL : HOUTSIDE=VERTICAL : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.35 : UFRAME=11.16 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
WINDOW RDC_SE
WINID=13010 : HINSIDE=VERTICAL : HOUTSIDE=VERTICAL : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.3 : UFRAME=11.88 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
WINDOW CAFET_01
WINID=13010 : HINSIDE=VERTICAL : HOUTSIDE=VERTICAL : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.3 : UFRAME=11.88 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
WINDOW MEN_106
WINID=13010 : HINSIDE=VERTICAL : HOUTSIDE=VERTICAL : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.35 : UFRAME=11.16 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
WINDOW PORTE_INT
WINID=13013 : HINSIDE=VERTICAL : HOUTSIDE=VERTICAL : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.99 : UFRAME=10.8 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
WINDOW PORTE_SAS_VISITEURS
WINID=13013 : HINSIDE=VERTICAL : HOUTSIDE=VERTICAL : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.3 : UFRAME=12.6 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
WINDOW PORTE_SAS_NORPAC
WINID=13013 : HINSIDE=VERTICAL : HOUTSIDE=VERTICAL : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.3 : UFRAME=12.6 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* D e f a u l t G a i n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
GAIN PERS_ISO02
CONVECTIVE=156 : RADIATIVE=78 : HUMIDITY=0.081
GAIN PERS_ISO03
CONVECTIVE=180 : RADIATIVE=90 : HUMIDITY=0.139
GAIN PERS_ISO01
CONVECTIVE=144 : RADIATIVE=72 : HUMIDITY=0.059
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* O t h e r G a i n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
GAIN 0.06_SERVEURS
CONVECTIVE=5400 : RADIATIVE=5400 : HUMIDITY=0
GAIN BAIES_BRASSAGES
CONVECTIVE=1080 : RADIATIVE=1080 : HUMIDITY=0
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* C o m f o r t
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* I n f i l t r a t i o n
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
INFILTRATION I4_EGAL_1.5
AIRCHANGE=0.5
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* V e n t i l a t i o n
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
VENTILATION 0.01
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 3096*CTA
HUMIDITY=OUTSIDE
VENTILATION 0.02
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 960*CTA
HUMIDITY=OUTSIDE
VENTILATION 0.05
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 528*CTA
HUMIDITY=OUTSIDE
VENTILATION 0.07
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 576*CTA
HUMIDITY=OUTSIDE
VENTILATION 0.08
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 192*CTA
HUMIDITY=OUTSIDE
VENTILATION 0.09
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 360*CTA
HUMIDITY=OUTSIDE
VENTILATION 0.10
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 360*CTA
HUMIDITY=OUTSIDE
VENTILATION 0.11
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 360*CTA
HUMIDITY=OUTSIDE
VENTILATION 0.12
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 162*CTA
HUMIDITY=OUTSIDE
VENTILATION 0.13
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 540*CTA
HUMIDITY=OUTSIDE
VENTILATION 0.14
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 144*CTA
HUMIDITY=OUTSIDE
VENTILATION 0.15
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 72*CTA
HUMIDITY=OUTSIDE
VENTILATION 0.16
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 90*CTA
HUMIDITY=OUTSIDE
VENTILATION 0.17
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 36*CTA
HUMIDITY=OUTSIDE
VENTILATION 1.01
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 96*CTA
HUMIDITY=OUTSIDE
VENTILATION 1.02
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 144*CTA
HUMIDITY=OUTSIDE
VENTILATION 1.03
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 96*CTA
HUMIDITY=OUTSIDE
VENTILATION 1.04
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 96*CTA
HUMIDITY=OUTSIDE
VENTILATION 1.05
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 288*CTA
HUMIDITY=OUTSIDE
VENTILATION 1.07
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 96*CTA
HUMIDITY=OUTSIDE
VENTILATION 1.08
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 96*CTA
HUMIDITY=OUTSIDE
VENTILATION 1.09
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 576*CTA
HUMIDITY=OUTSIDE
VENTILATION 1.10
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 48*CTA
HUMIDITY=OUTSIDE
VENTILATION 1.11
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 96*CTA
HUMIDITY=OUTSIDE
VENTILATION 1.12
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 624*CTA
HUMIDITY=OUTSIDE
VENTILATION 1.13
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 1104*CTA
HUMIDITY=OUTSIDE
VENTILATION 1.14
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 48*CTA
HUMIDITY=OUTSIDE
VENTILATION 2.01
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 96*CTA
HUMIDITY=OUTSIDE
VENTILATION 2.02
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 960*CTA
HUMIDITY=OUTSIDE
VENTILATION 2.04
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 96*CTA
HUMIDITY=OUTSIDE
VENTILATION 2.05
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 816*CTA
HUMIDITY=OUTSIDE
VENTILATION 2.06
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 144*CTA
HUMIDITY=OUTSIDE
VENTILATION 2.07
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 432*CTA
HUMIDITY=OUTSIDE
VENTILATION 2.08
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 96*CTA
HUMIDITY=OUTSIDE
VENTILATION 2.09
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 48*CTA
HUMIDITY=OUTSIDE
VENTILATION 2.10
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 1104*CTA
HUMIDITY=OUTSIDE
VENTILATION 2.11
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 48*CTA
HUMIDITY=OUTSIDE
VENTILATION 2.13
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 48*CTA
HUMIDITY=OUTSIDE
VENTILATION 3.01
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 48*CTA
HUMIDITY=OUTSIDE
VENTILATION 3.02
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 960*CTA
HUMIDITY=OUTSIDE
VENTILATION 3.04
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 96*CTA
HUMIDITY=OUTSIDE
VENTILATION 3.05
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 816*CTA
HUMIDITY=OUTSIDE
VENTILATION 3.06
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 432*CTA
HUMIDITY=OUTSIDE
VENTILATION 3.07
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 96*CTA
HUMIDITY=OUTSIDE
VENTILATION 3.08
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 1104*CTA
HUMIDITY=OUTSIDE
VENTILATION 3.09
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 48*CTA
HUMIDITY=OUTSIDE
VENTILATION 3.11
TEMPERATURE=INPUT 1*TSOUFFLAGE_CTA
AIRFLOW=SCHEDULE 48*CTA
HUMIDITY=OUTSIDE
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* C o o l i n g
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
COOLING FROID_VC
ON=28
POWER=999999999
HUMIDITY=100
COOLING FROID_PR
ON=28
POWER=999999999
HUMIDITY=100
COOLING SERVEURS
ON=28
POWER=999999999
HUMIDITY=100
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* H e a t i n g
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
HEATING CHAUFFAGE_VC
ON=20
POWER=999999999
HUMIDITY=0
RRAD=0
HEATING CHAUFFAGE_PR
ON=20
POWER=999999999
HUMIDITY=0
RRAD=0.75
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONES 0.01_TDA01 0.02_ACCUEIL 0.03_SAS_01 0.04_SAS_02 0.05_TDA02 0.06_SALLE_SERVEURS 0.07_TDA03_ACHATS 0.08_ARCHIVES 0.09_ERE03 0.10_ERE02 0.11_ERE01 0.12_CIRCUL_RDC 0.13_CAFETERIA 0.14_BUR_IND ;
0.15_STOCKAGE01 0.16_STOCKAGE02 0.17_LT 1.01_BUREAU_PIR 1.02_BUREAUX 1.03_BUREAU_ALY 1.04_VISIO_DG 1.05_ACCUEIL_DG 1.06_PALIER_NE_E1 1.07_ERE14 1.08_ERE13 1.09_DRH 1.10_BAIES_BRASSAGE_E1 1.11_ERE12 ;
1.12_SECRETARIAT_GAL 1.14_ERE11 1.15_CIRCUL_SE_E1 2.01_ERE24 2.02_IND&ENVIR 2.03_PALIER_NE_E2 2.04_ERE23 2.05_DT_STRUCT&EDP 2.06_COFFEE_CORNER 2.07_DT 2.08_ERE22 2.09_TRACEURS 2.10_FLUIDES_METHODES ;
2.11_ERE21 2.12_CIRCUL_SE_E2 2.13_BAIES_BRASSAGE_E2 3.01_ERE34 3.02_CIRMAD_COMMERCES 3.03_PALIER_NE_E3 3.04_ERE33 3.05_COMMERCES_OF 3.06_TRAVAUX01 3.07_ERE32 3.08_TRAVAUX02 3.09_ERE31 ;
3.10_CIRCUL_SE_E3 3.11_BAIES_BRASSAGE_E3 1.13_BYTPRF ESC_SE ESC_CENTRAL ESC_SECONDAIRE ESC_NE WC_AILE_SUD WC_AILE_NORD
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* O r i e n t a t i o n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ORIENTATIONS H_0_0 SO SE NE NO M1_RDC M2_RDC M3_RDC M4_RDC M5_RDC M6_RDC M7_RDC M1_E1 M2_E1 M3_E1 M4_E1 M5_E1 M6_E1 M7_E1 M8_E1 M9_E1 M10_E1 M1_E2 M2_E2 M3_E2 M4_E2 M5_E2 M6_E2 M7_E2 M8_E2 M9_E2 ;
M1_E3 M2_E3 M3_E3 M4_E3 M5_E3 M6_E3 M7_E3 M8_E3 M9_E3
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
BUILDING
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 0.01_TDA01 / A i r n o d e TDA01
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 0.01_TDA01
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE TDA01
WINDOW=MR1 : SURF= 6 : AREA= 40.66 : EXTERNAL : ORI=SO : FSKY=0.5
WINDOW=MR2 : SURF= 8 : AREA= 14.69 : EXTERNAL : ORI=SE : FSKY=0.5
WINDOW=RDC_NE : SURF= 11 : AREA= 14.22 : EXTERNAL : ORI=M1_RDC : FSKY=0.5
WINDOW=RDC_NE : SURF= 12 : AREA= 14.22 : EXTERNAL : ORI=M2_RDC : FSKY=0.5
WALL =PB_TP : SURF= 1 : AREA= 205.3 : BOUNDARY=5 : GEOSURF=1
WALL =MEXT_PEUPLIER : SURF= 2 : AREA= 6 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =CBR_B11 : SURF= 3 : LENGTH= 35.8 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_I21 : SURF= 4 : LENGTH= 35.8 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_MEN : SURF= 7 : LENGTH= 12.51 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_MEN : SURF= 9 : LENGTH= 4.52 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_MEN : SURF= 10 : LENGTH= 9.8 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=308 : AREA= 19.7 : ADJACENT=1.01_BUREAU_PIR : ADJ_SURF=314 : FRONT
WALL =PLANCHER_INTERMEDIAIRE : SURF=315 : AREA= 23.9 : ADJACENT=1.02_BUREAUX : ADJ_SURF=316 : FRONT
WALL =PLANCHER_INTERMEDIAIRE : SURF=318 : AREA= 18.7 : ADJACENT=1.04_VISIO_DG : ADJ_SURF=319 : FRONT
WALL =PLANCHER_INTERMEDIAIRE : SURF=320 : AREA= 143 : ADJACENT=1.05_ACCUEIL_DG : ADJ_SURF=322 : FRONT
WALL =MINT_LOURD : SURF=482 : AREA= 31.6 : ADJACENT=ESC_SE : ADJ_SURF=483 : FRONT
WINDOW=PORTE_INT : SURF=727 : AREA= 2.1 : ADJACENT=ESC_SE : ADJ_SURF=728 : FRONT : ORI=SE
WALL =MINT_LEGER : SURF=484 : AREA= 48.66 : ADJACENT=0.02_ACCUEIL : ADJ_SURF=485 : FRONT
WINDOW=PORTE_INT : SURF=714 : AREA= 2.94 : ADJACENT=0.02_ACCUEIL : ADJ_SURF=719 : FRONT : ORI=NO
WALL =MEXT_TERRE_CUITE : SURF=851 : AREA= 16.9 : EXTERNAL : ORI=SE : FSKY=0.5
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 69*OCCUP_SDR : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 0.01
COOLING = FROID_VC
HEATING = CHAUFFAGE_VC
CAPACITANCE = 689.71 : VOLUME= 574.76 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 0.02_ACCUEIL / A i r n o d e 0.02_ACCUEIL
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 0.02_ACCUEIL
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 0.02_ACCUEIL
WINDOW=MR1 : SURF= 13 : AREA= 19.34 : EXTERNAL : ORI=SO : FSKY=0.5
WINDOW=MR1 : SURF= 14 : AREA= 17.55 : EXTERNAL : ORI=SO : FSKY=0.5
WINDOW=RDC_NE : SURF= 16 : AREA= 7.11 : EXTERNAL : ORI=M3_RDC : FSKY=0.5
WALL =PB_TP : SURF= 17 : AREA= 217.7 : EXTERNAL : ORI=H_0_0 : FSKY=0 : GEOSURF=1
WALL =CBR_B11 : SURF= 19 : LENGTH= 16.6 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF= 20 : AREA= 6.1 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =CBR_I21 : SURF= 21 : LENGTH= 16.6 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_MEN : SURF= 22 : LENGTH= 11.35 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_MEN : SURF= 24 : LENGTH= 2.45 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=323 : AREA= 31.5 : ADJACENT=1.05_ACCUEIL_DG : ADJ_SURF=324 : FRONT
WALL =PLANCHER_INTERMEDIAIRE : SURF=325 : AREA= 24.3 : ADJACENT=1.03_BUREAU_ALY : ADJ_SURF=326 : FRONT
WALL =PLANCHER_INTERMEDIAIRE : SURF=327 : AREA= 12.2 : ADJACENT=1.08_ERE13 : ADJ_SURF=328 : FRONT
WALL =PLANCHER_INTERMEDIAIRE : SURF=329 : AREA= 64.6 : ADJACENT=1.09_DRH : ADJ_SURF=330 : FRONT
WALL =PLANCHER_INTERMEDIAIRE : SURF=331 : AREA= 16.8 : ADJACENT=1.07_ERE14 : ADJ_SURF=332 : FRONT
WALL =PLANCHER_INTERMEDIAIRE : SURF=333 : AREA= 10.6 : ADJACENT=1.06_PALIER_NE_E1 : ADJ_SURF=334 : FRONT
WALL =PLANCHER_INTERMEDIAIRE : SURF=335 : AREA= 51.5 : ADJACENT=2.02_IND&ENVIR : ADJ_SURF=336 : FRONT
WALL =MINT_LEGER : SURF=485 : AREA= 48.66 : ADJACENT=TDA01 : ADJ_SURF=484 : BACK
WINDOW=PORTE_INT : SURF=719 : AREA= 2.94 : ADJACENT=TDA01 : ADJ_SURF=714 : BACK : ORI=NO
WALL =MINT_LOURD : SURF=486 : AREA= 11.8 : ADJACENT=0.04_SAS_02 : ADJ_SURF=487 : FRONT
WALL =MINT_LEGER : SURF=488 : AREA= 11.8 : ADJACENT=0.04_SAS_02 : ADJ_SURF=489 : FRONT
WALL =MINT_LEGER : SURF=490 : AREA= 24.05 : ADJACENT=0.03_SAS_01 : ADJ_SURF=491 : FRONT
WINDOW=PORTE_SAS_VISITEURS : SURF=729 : AREA= 4.05 : ADJACENT=0.03_SAS_01 : ADJ_SURF=730 : FRONT : ORI=SO
WALL =MINT_LEGER : SURF=492 : AREA= 24.96 : ADJACENT=0.05_TDA02 : ADJ_SURF=493 : FRONT
WINDOW=PORTE_INT : SURF=731 : AREA= 2.94 : ADJACENT=0.05_TDA02 : ADJ_SURF=732 : FRONT : ORI=NO
WALL =MINT_LEGER : SURF=494 : AREA= 31.56 : ADJACENT=WC_AILE_SUD : ADJ_SURF=495 : FRONT
WINDOW=PORTE_SAS_NORPAC : SURF=733 : AREA= 2.94 : ADJACENT=WC_AILE_SUD : ADJ_SURF=734 : FRONT : ORI=SE
WALL =MINT_LEGER : SURF=573 : AREA= 11.7 : ADJACENT=1.03_BUREAU_ALY : ADJ_SURF=572 : BACK
WALL =CLOISON_VIDE_INT : SURF=823 : AREA= 33.82 : ADJACENT=ESC_CENTRAL : ADJ_SURF=824 : FRONT
WALL =CLOISON_VIDE_INT : SURF=825 : AREA= 4.31 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=826 : FRONT
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 10*OCCUP_ACCUEIL : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 0.02
COOLING = FROID_VC
HEATING = CHAUFFAGE_VC
CAPACITANCE = 779.47 : VOLUME= 649.56 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 0.03_SAS_01 / A i r n o d e 0.03_SAS_01
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 0.03_SAS_01
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 0.03_SAS_01
WINDOW=MR1 : SURF= 15 : AREA= 9.44 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =PB_TP : SURF= 25 : AREA= 13.22 : EXTERNAL : ORI=H_0_0 : FSKY=0 : GEOSURF=1
WALL =CBR_B11 : SURF= 26 : LENGTH= 4.3 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_I21 : SURF= 28 : LENGTH= 4.3 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_MEN : SURF= 29 : LENGTH= 4.29 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=337 : AREA= 13.2 : ADJACENT=1.07_ERE14 : ADJ_SURF=338 : FRONT
WALL =MINT_LEGER : SURF=491 : AREA= 24.05 : ADJACENT=0.02_ACCUEIL : ADJ_SURF=490 : BACK
WINDOW=PORTE_SAS_VISITEURS : SURF=730 : AREA= 4.05 : ADJACENT=0.02_ACCUEIL : ADJ_SURF=729 : BACK : ORI=SO
REGIME
INFILTRATION= I4_EGAL_1.5
COOLING = FROID_VC
CAPACITANCE = 44.42 : VOLUME= 37.02 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 0.04_SAS_02 / A i r n o d e 0.04_SAS_02
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 0.04_SAS_02
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 0.04_SAS_02
WINDOW=MR1 : SURF= 18 : AREA= 9.44 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =PB_TP : SURF= 23 : AREA= 7.74 : EXTERNAL : ORI=H_0_0 : FSKY=0 : GEOSURF=1
WALL =CBR_B11 : SURF= 27 : LENGTH= 2 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_I21 : SURF= 30 : LENGTH= 2 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF= 31 : AREA= 5.7 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=339 : AREA= 7.7 : ADJACENT=1.06_PALIER_NE_E1 : ADJ_SURF=340 : FRONT
WALL =MINT_LOURD : SURF=487 : AREA= 11.8 : ADJACENT=0.02_ACCUEIL : ADJ_SURF=486 : BACK
WALL =MINT_LEGER : SURF=489 : AREA= 11.8 : ADJACENT=0.02_ACCUEIL : ADJ_SURF=488 : BACK
REGIME
INFILTRATION= I4_EGAL_1.5
COOLING = FROID_VC
CAPACITANCE = 26 : VOLUME= 21.67 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 0.05_TDA02 / A i r n o d e 0.05_TDA02
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 0.05_TDA02
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 0.05_TDA02
WINDOW=MR3 : SURF= 33 : AREA= 14.69 : EXTERNAL : ORI=NO : FSKY=0.5
WINDOW=MR1 : SURF= 32 : AREA= 40.66 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =PB_TP : SURF= 36 : AREA= 184.65 : EXTERNAL : ORI=H_0_0 : FSKY=0 : GEOSURF=1
WALL =CBR_B11 : SURF= 38 : LENGTH= 30.5 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF= 39 : AREA= 23.86 : EXTERNAL : ORI=NO : FSKY=0.5
WINDOW=RDC_NO : SURF= 34 : AREA= 13.94 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =CBR_I21 : SURF= 40 : LENGTH= 30.5 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_MEN : SURF= 41 : LENGTH= 12.51 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_MEN : SURF= 42 : LENGTH= 4.52 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =CBR_MEN : SURF= 43 : LENGTH= 6.9 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =MINT_LEGER : SURF= 51 : AREA= 33.26 : ADJACENT=0.06_SALLE_SERVEURS : ADJ_SURF=50 : BACK
WINDOW=PORTE_INT : SURF=735 : AREA= 2.94 : ADJACENT=0.06_SALLE_SERVEURS : ADJ_SURF=736 : BACK : ORI=NO
WALL =PLANCHER_INTERMEDIAIRE : SURF=341 : AREA= 184.65 : ADJACENT=1.09_DRH : ADJ_SURF=342 : FRONT
WALL =MINT_LEGER : SURF=493 : AREA= 24.96 : ADJACENT=0.02_ACCUEIL : ADJ_SURF=492 : BACK
WINDOW=PORTE_INT : SURF=732 : AREA= 2.94 : ADJACENT=0.02_ACCUEIL : ADJ_SURF=731 : BACK : ORI=NO
WALL =MINT_LEGER : SURF=496 : AREA= 37.5 : ADJACENT=0.06_SALLE_SERVEURS : ADJ_SURF=497 : FRONT
WALL =MINT_LEGER : SURF=498 : AREA= 16.26 : ADJACENT=0.07_TDA03_ACHATS : ADJ_SURF=499 : FRONT
WINDOW=PORTE_INT : SURF=737 : AREA= 2.94 : ADJACENT=0.07_TDA03_ACHATS : ADJ_SURF=738 : FRONT : ORI=NE
WALL =CLOISON_VIDE_INT : SURF=828 : AREA= 3.72 : ADJACENT=0.07_TDA03_ACHATS : ADJ_SURF=827 : BACK
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 19*OCCUP_BUREAUX_DT : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 0.05
COOLING = FROID_VC
HEATING = CHAUFFAGE_PR
CAPACITANCE = 620.42 : VOLUME= 517.02 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 0.06_SALLE_SERVEURS / A i r n o d e 0.06_SALLE_SERVEURS
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 0.06_SALLE_SERVEURS
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 0.06_SALLE_SERVEURS
WALL =PB_TP : SURF= 44 : AREA= 38.5 : EXTERNAL : ORI=H_0_0 : FSKY=0 : GEOSURF=1
WALL =MINT_LEGER : SURF= 50 : AREA= 33.26 : ADJACENT=0.05_TDA02 : ADJ_SURF=51 : FRONT
WINDOW=PORTE_INT : SURF=736 : AREA= 2.94 : ADJACENT=0.05_TDA02 : ADJ_SURF=735 : FRONT : ORI=NO
WALL =PLANCHER_INTERMEDIAIRE : SURF=343 : AREA= 28.8 : ADJACENT=1.09_DRH : ADJ_SURF=344 : FRONT
WALL =PLANCHER_INTERMEDIAIRE : SURF=345 : AREA= 9.7 : ADJACENT=1.10_BAIES_BRASSAGE_E1 : ADJ_SURF=346 : FRONT
WALL =MINT_LEGER : SURF=497 : AREA= 37.5 : ADJACENT=0.05_TDA02 : ADJ_SURF=496 : BACK
WALL =MINT_LEGER : SURF=500 : AREA= 32.7 : ADJACENT=0.07_TDA03_ACHATS : ADJ_SURF=501 : FRONT
WALL =MINT_LOURD : SURF=502 : AREA= 13.1 : ADJACENT=WC_AILE_SUD : ADJ_SURF=503 : FRONT
REGIME
GAIN = 0.06_SERVEURS : SCALE= SCHEDULE 1*SERVEURS_CONTINUS : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
COOLING = SERVEURS
CAPACITANCE = 129.32 : VOLUME= 107.77 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 0.07_TDA03_ACHATS / A i r n o d e 0.07_TDA03_ACHATS
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 0.07_TDA03_ACHATS
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 0.07_TDA03_ACHATS
WINDOW=MR3 : SURF= 35 : AREA= 14.69 : EXTERNAL : ORI=NO : FSKY=0.5
WINDOW=MR1 : SURF= 37 : AREA= 40.66 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =PB_TP : SURF= 45 : AREA= 143.86 : EXTERNAL : ORI=H_0_0 : FSKY=0 : GEOSURF=1
WALL =CBR_B11 : SURF= 46 : LENGTH= 14.9 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF= 47 : AREA= 13.72 : EXTERNAL : ORI=NO : FSKY=0.5
WINDOW=RDC_NO : SURF= 48 : AREA= 27.88 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =CBR_I21 : SURF= 49 : LENGTH= 14.9 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =CBR_MEN : SURF= 52 : LENGTH= 13.8 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =MINT_LEGER : SURF= 55 : AREA= 31.7 : ADJACENT=0.08_ARCHIVES : ADJ_SURF=54 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=347 : AREA= 143.9 : ADJACENT=1.12_SECRETARIAT_GAL : ADJ_SURF=348 : FRONT
WALL =MINT_LEGER : SURF=499 : AREA= 16.26 : ADJACENT=0.05_TDA02 : ADJ_SURF=498 : BACK
WINDOW=PORTE_INT : SURF=738 : AREA= 2.94 : ADJACENT=0.05_TDA02 : ADJ_SURF=737 : BACK : ORI=NE
WALL =MINT_LEGER : SURF=501 : AREA= 32.7 : ADJACENT=0.06_SALLE_SERVEURS : ADJ_SURF=500 : BACK
WALL =MINT_LOURD : SURF=504 : AREA= 9 : ADJACENT=WC_AILE_SUD : ADJ_SURF=505 : FRONT
WALL =MINT_LEGER : SURF=506 : AREA= 12 : ADJACENT=WC_AILE_SUD : ADJ_SURF=507 : FRONT
WALL =MINT_LEGER : SURF=508 : AREA= 32.9 : ADJACENT=0.08_ARCHIVES : ADJ_SURF=509 : FRONT
WALL =MINT_LEGER : SURF=510 : AREA= 12.2 : ADJACENT=WC_AILE_NORD : ADJ_SURF=511 : FRONT
WALL =CLOISON_VIDE_INT : SURF=827 : AREA= 3.72 : ADJACENT=0.05_TDA02 : ADJ_SURF=828 : FRONT
WALL =CLOISON_VIDE_INT : SURF=829 : AREA= 15.9 : ADJACENT=0.14_BUR_IND : ADJ_SURF=830 : FRONT
WALL =CLOISON_VIDE_INT : SURF=831 : AREA= 24.22 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=832 : FRONT
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 18*OCCUP_BUREAUX_DT : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 0.07
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 483.37 : VOLUME= 402.81 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 0.08_ARCHIVES / A i r n o d e 0.08_ARCHIVES
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 0.08_ARCHIVES
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 0.08_ARCHIVES
WALL =PB_TP : SURF= 53 : AREA= 49.7 : EXTERNAL : ORI=H_0_0 : FSKY=0 : GEOSURF=1
WALL =MINT_LEGER : SURF= 54 : AREA= 31.7 : ADJACENT=0.07_TDA03_ACHATS : ADJ_SURF=55 : FRONT
WALL =PLANCHER_INTERMEDIAIRE : SURF=349 : AREA= 18.5 : ADJACENT=1.11_ERE12(NON_TERMINE) : ADJ_SURF=350 : FRONT
WALL =PLANCHER_INTERMEDIAIRE : SURF=351 : AREA= 19 : ADJACENT=1.12_SECRETARIAT_GAL : ADJ_SURF=352 : FRONT
WALL =PLANCHER_INTERMEDIAIRE : SURF=353 : AREA= 12.2 : ADJACENT=1.13_BYTPRF : ADJ_SURF=370 : FRONT
WALL =MINT_LEGER : SURF=509 : AREA= 32.9 : ADJACENT=0.07_TDA03_ACHATS : ADJ_SURF=508 : BACK
WALL =MINT_LOURD : SURF=512 : AREA= 7.1 : ADJACENT=WC_AILE_NORD : ADJ_SURF=513 : FRONT
WALL =MINT_LEGER : SURF=514 : AREA= 33.76 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=515 : FRONT
WINDOW=PORTE_INT : SURF=739 : AREA= 2.94 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=740 : FRONT : ORI=NE
WALL =MINT_LEGER : SURF=516 : AREA= 11.2 : ADJACENT=0.14_BUR_IND : ADJ_SURF=517 : FRONT
REGIME
INFILTRATION= I4_EGAL_1.5
VENTILATION = 0.08
CAPACITANCE = 167.06 : VOLUME= 139.22 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 0.09_ERE03 / A i r n o d e 0.09_ERE03
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 0.09_ERE03
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 0.09_ERE03
WINDOW=RDC_SE : SURF= 59 : AREA= 6.46 : EXTERNAL : ORI=M4_RDC : FSKY=0.5
WALL =PB_TP : SURF= 60 : AREA= 20.1 : EXTERNAL : ORI=H_0_0 : FSKY=0 : GEOSURF=1
WALL =CBR_B11 : SURF= 62 : LENGTH= 6.6 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_H11 : SURF= 64 : LENGTH= 6.6 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_MEN : SURF= 66 : LENGTH= 4.25 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_H31 : SURF= 67 : LENGTH= 5.2 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF= 61 : AREA= 1.9 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF= 63 : AREA= 1.9 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF= 65 : AREA= 8.1 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =PLH_SDR : SURF=378 : AREA= 20.1 : EXTERNAL : ORI=H_0_0 : FSKY=1
WALL =MINT_LOURD : SURF=518 : AREA= 17.3 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=519 : FRONT
WALL =MINT_LEGER : SURF=520 : AREA= 12.5 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=521 : FRONT
WINDOW=PORTE_INT : SURF=741 : AREA= 2.1 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=742 : FRONT : ORI=NO
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 8*OCCUP_SDR : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 0.09
COOLING = FROID_VC
HEATING = CHAUFFAGE_VC
CAPACITANCE = 67.46 : VOLUME= 56.22 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 0.10_ERE02 / A i r n o d e 0.10_ERE02
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 0.10_ERE02
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 0.10_ERE02
WINDOW=RDC_SE : SURF= 56 : AREA= 6.46 : EXTERNAL : ORI=M5_RDC : FSKY=0.5
WALL =PB_TP : SURF= 57 : AREA= 20.02 : EXTERNAL : ORI=H_0_0 : FSKY=0 : GEOSURF=1
WALL =CBR_B11 : SURF= 58 : LENGTH= 6.6 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_H11 : SURF= 68 : LENGTH= 6.6 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_MEN : SURF= 69 : LENGTH= 4.25 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_H31 : SURF= 70 : LENGTH= 5.2 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF= 71 : AREA= 1.9 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF= 72 : AREA= 1.9 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF= 73 : AREA= 8.1 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =PLH_SDR : SURF=379 : AREA= 20 : EXTERNAL : ORI=H_0_0 : FSKY=1
WALL =MINT_LOURD : SURF=522 : AREA= 17.3 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=523 : FRONT
WALL =MINT_LEGER : SURF=524 : AREA= 12.5 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=525 : FRONT
WINDOW=PORTE_INT : SURF=743 : AREA= 2.1 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=744 : FRONT : ORI=SE
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 8*OCCUP_SDR : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 0.10
COOLING = FROID_VC
HEATING = CHAUFFAGE_VC
CAPACITANCE = 67.32 : VOLUME= 56.1 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 0.11_ERE01 / A i r n o d e 0.11_ERE01
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 0.11_ERE01
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 0.11_ERE01
WINDOW=RDC_SE : SURF= 74 : AREA= 6.48 : EXTERNAL : ORI=M6_RDC : FSKY=0.5
WALL =PB_TP : SURF= 75 : AREA= 19.19 : EXTERNAL : ORI=H_0_0 : FSKY=0 : GEOSURF=1
WALL =CBR_B11 : SURF= 76 : LENGTH= 6.6 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_H11 : SURF= 77 : LENGTH= 6.6 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_MEN : SURF= 78 : LENGTH= 4.25 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_H31 : SURF= 79 : LENGTH= 5.2 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF= 80 : AREA= 1.9 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF= 81 : AREA= 1.9 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF= 82 : AREA= 8.1 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =PLH_SDR : SURF=380 : AREA= 19.2 : EXTERNAL : ORI=H_0_0 : FSKY=1
WALL =MINT_LOURD : SURF=526 : AREA= 11.6 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=527 : FRONT
WINDOW=PORTE_INT : SURF=745 : AREA= 2.1 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=746 : FRONT : ORI=SO
WALL =MINT_LOURD : SURF=528 : AREA= 9.4 : ADJACENT=ESC_SECONDAIRE : ADJ_SURF=529 : FRONT
WALL =MINT_LOURD : SURF=530 : AREA= 8.3 : ADJACENT=0.13_CAFETERIA : ADJ_SURF=531 : FRONT
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 8*OCCUP_SDR : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 0.11
COOLING = FROID_VC
HEATING = CHAUFFAGE_VC
CAPACITANCE = 64.48 : VOLUME= 53.73 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 0.12_CIRCUL_RDC / A i r n o d e 0.12_CIRCUL_RDC
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 0.12_CIRCUL_RDC
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 0.12_CIRCUL_RDC
WALL =PB_TP : SURF= 84 : AREA= 172.28 : EXTERNAL : ORI=H_0_0 : FSKY=0 : GEOSURF=1
WALL =CBR_B11 : SURF= 85 : LENGTH= 8.2 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_H11 : SURF= 86 : LENGTH= 6.5 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_H31 : SURF= 88 : LENGTH= 9.5 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF= 90 : AREA= 4.8 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF= 91 : AREA= 5.6 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_I21 : SURF= 92 : LENGTH= 1.7 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =PLH_SDR : SURF=371 : AREA= 17.9 : EXTERNAL : ORI=H_0_0 : FSKY=1
WALL =PLANCHER_INTERMEDIAIRE : SURF=372 : AREA= 31.5 : ADJACENT=1.12_SECRETARIAT_GAL : ADJ_SURF=373 : FRONT
WALL =PLANCHER_INTERMEDIAIRE : SURF=374 : AREA= 25.1 : ADJACENT=1.15_CIRCUL_SE_E1 : ADJ_SURF=375 : FRONT
WALL =PLANCHER_INTERMEDIAIRE : SURF=376 : AREA= 91.3 : ADJACENT=1.13_BYTPRF : ADJ_SURF=377 : FRONT
WALL =MINT_LEGER : SURF=515 : AREA= 33.76 : ADJACENT=0.08_ARCHIVES : ADJ_SURF=514 : BACK
WINDOW=PORTE_INT : SURF=740 : AREA= 2.94 : ADJACENT=0.08_ARCHIVES : ADJ_SURF=739 : BACK : ORI=NE
WALL =MINT_LOURD : SURF=519 : AREA= 17.3 : ADJACENT=0.09_ERE03 : ADJ_SURF=518 : BACK
WALL =MINT_LEGER : SURF=521 : AREA= 12.5 : ADJACENT=0.09_ERE03 : ADJ_SURF=520 : BACK
WINDOW=PORTE_INT : SURF=742 : AREA= 2.1 : ADJACENT=0.09_ERE03 : ADJ_SURF=741 : BACK : ORI=NO
WALL =MINT_LOURD : SURF=523 : AREA= 17.3 : ADJACENT=0.10_ERE02 : ADJ_SURF=522 : BACK
WALL =MINT_LEGER : SURF=525 : AREA= 12.5 : ADJACENT=0.10_ERE02 : ADJ_SURF=524 : BACK
WINDOW=PORTE_INT : SURF=744 : AREA= 2.1 : ADJACENT=0.10_ERE02 : ADJ_SURF=743 : BACK : ORI=SE
WALL =MINT_LOURD : SURF=527 : AREA= 11.6 : ADJACENT=0.11_ERE01 : ADJ_SURF=526 : BACK
WINDOW=PORTE_INT : SURF=746 : AREA= 2.1 : ADJACENT=0.11_ERE01 : ADJ_SURF=745 : BACK : ORI=SO
WALL =MINT_LEGER : SURF=532 : AREA= 40.4 : ADJACENT=WC_AILE_NORD : ADJ_SURF=533 : FRONT
WINDOW=PORTE_INT : SURF=747 : AREA= 4.2 : ADJACENT=WC_AILE_NORD : ADJ_SURF=748 : FRONT : ORI=NO
WALL =MINT_LOURD : SURF=534 : AREA= 18.7 : ADJACENT=ESC_SECONDAIRE : ADJ_SURF=535 : FRONT
WINDOW=PORTE_INT : SURF=749 : AREA= 2.1 : ADJACENT=ESC_SECONDAIRE : ADJ_SURF=750 : FRONT : ORI=NE
WALL =MINT_LEGER : SURF=536 : AREA= 4.16 : ADJACENT=0.13_CAFETERIA : ADJ_SURF=537 : FRONT
WINDOW=PORTE_INT : SURF=751 : AREA= 2.94 : ADJACENT=0.13_CAFETERIA : ADJ_SURF=752 : FRONT : ORI=NO
WALL =MINT_LEGER : SURF=538 : AREA= 18 : ADJACENT=0.14_BUR_IND : ADJ_SURF=539 : FRONT
WINDOW=PORTE_INT : SURF=753 : AREA= 8.4 : ADJACENT=0.14_BUR_IND : ADJ_SURF=754 : FRONT : ORI=NO
WALL =MINT_LEGER : SURF=540 : AREA= 23.86 : ADJACENT=0.15_STOCKAGE01 : ADJ_SURF=541 : FRONT
WINDOW=PORTE_INT : SURF=755 : AREA= 2.94 : ADJACENT=0.15_STOCKAGE01 : ADJ_SURF=756 : FRONT : ORI=NO
WALL =MINT_LEGER : SURF=542 : AREA= 20.66 : ADJACENT=0.16_STOCKAGE02 : ADJ_SURF=543 : FRONT
WINDOW=PORTE_INT : SURF=757 : AREA= 2.1 : ADJACENT=0.16_STOCKAGE02 : ADJ_SURF=758 : FRONT : ORI=NO
WINDOW=PORTE_INT : SURF=759 : AREA= 2.94 : ADJACENT=0.16_STOCKAGE02 : ADJ_SURF=760 : FRONT : ORI=NE
WALL =MINT_LNC : SURF=544 : AREA= 6.26 : ADJACENT=0.16_STOCKAGE02 : ADJ_SURF=545 : FRONT
WINDOW=PORTE_INT : SURF=761 : AREA= 2.94 : ADJACENT=0.16_STOCKAGE02 : ADJ_SURF=762 : FRONT : ORI=NE
WALL =MINT_LNC : SURF=546 : AREA= 4.3 : ADJACENT=0.17_LT : ADJ_SURF=547 : FRONT
WINDOW=PORTE_INT : SURF=763 : AREA= 4.2 : ADJACENT=0.17_LT : ADJ_SURF=764 : FRONT : ORI=NO
WALL =MINT_LOURD : SURF=548 : AREA= 5.9 : ADJACENT=ESC_NE : ADJ_SURF=549 : FRONT
WINDOW=PORTE_INT : SURF=765 : AREA= 2.1 : ADJACENT=ESC_NE : ADJ_SURF=766 : FRONT : ORI=SE
WALL =CLOISON_VIDE_INT : SURF=826 : AREA= 4.31 : ADJACENT=0.02_ACCUEIL : ADJ_SURF=825 : BACK
WALL =CLOISON_VIDE_INT : SURF=832 : AREA= 24.22 : ADJACENT=0.07_TDA03_ACHATS : ADJ_SURF=831 : BACK
REGIME
INFILTRATION= I4_EGAL_1.5
VENTILATION = 0.12
COOLING = FROID_VC
HEATING = CHAUFFAGE_VC
CAPACITANCE = 578.86 : VOLUME= 482.38 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 0.13_CAFETERIA / A i r n o d e 0.13_CAFETERIA
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 0.13_CAFETERIA
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 0.13_CAFETERIA
WINDOW=CAFET_01 : SURF= 87 : AREA= 6.95 : EXTERNAL : ORI=M7_RDC : FSKY=0.5
WALL =PB_TP : SURF= 89 : AREA= 62.47 : EXTERNAL : ORI=H_0_0 : FSKY=0 : GEOSURF=1
WALL =CBR_B11 : SURF= 93 : LENGTH= 10.6 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_H11 : SURF= 94 : LENGTH= 2.9 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_H31 : SURF= 95 : LENGTH= 3 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF= 96 : AREA= 1.9 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF= 97 : AREA= 20.7 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_I21 : SURF= 98 : LENGTH= 10.6 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_MEN : SURF= 83 : LENGTH= 4.58 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=381 : AREA= 62.47 : ADJACENT=1.13_BYTPRF : ADJ_SURF=382 : FRONT
WALL =MINT_LOURD : SURF=531 : AREA= 8.3 : ADJACENT=0.11_ERE01 : ADJ_SURF=530 : BACK
WALL =MINT_LEGER : SURF=537 : AREA= 4.16 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=536 : BACK
WINDOW=PORTE_INT : SURF=752 : AREA= 2.94 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=751 : BACK : ORI=NO
WALL =MINT_LOURD : SURF=550 : AREA= 12.7 : ADJACENT=ESC_SECONDAIRE : ADJ_SURF=551 : FRONT
WALL =MINT_LEGER : SURF=552 : AREA= 31.2 : ADJACENT=0.16_STOCKAGE02 : ADJ_SURF=553 : FRONT
WALL =MINT_LNC : SURF=554 : AREA= 15.2 : ADJACENT=0.16_STOCKAGE02 : ADJ_SURF=555 : FRONT
REGIME
GAIN = PERS_ISO03 : SCALE= SCHEDULE 10*OCCUP_CAFETERIA : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 0.13
COOLING = FROID_VC
HEATING = CHAUFFAGE_VC
CAPACITANCE = 209.9 : VOLUME= 174.92 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 0.14_BUR_IND / A i r n o d e 0.14_BUR_IND
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 0.14_BUR_IND
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 0.14_BUR_IND
WALL =PB_TP : SURF=101 : AREA= 51.2 : EXTERNAL : ORI=H_0_0 : FSKY=0 : GEOSURF=1
WALL =CBR_B11 : SURF=102 : LENGTH= 12.2 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=103 : AREA= 15.42 : EXTERNAL : ORI=NO : FSKY=0.5
WINDOW=RDC_NO : SURF=104 : AREA= 18.58 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =CBR_I21 : SURF=105 : LENGTH= 12.2 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =CBR_MEN : SURF=106 : LENGTH= 9.2 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=383 : AREA= 51.2 : ADJACENT=1.13_BYTPRF : ADJ_SURF=384 : FRONT
WALL =MINT_LEGER : SURF=517 : AREA= 11.2 : ADJACENT=0.08_ARCHIVES : ADJ_SURF=516 : BACK
WALL =MINT_LEGER : SURF=539 : AREA= 18 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=538 : BACK
WINDOW=PORTE_INT : SURF=754 : AREA= 8.4 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=753 : BACK : ORI=NO
WALL =MINT_LEGER : SURF=556 : AREA= 11.7 : ADJACENT=0.15_STOCKAGE01 : ADJ_SURF=557 : FRONT
WALL =MINT_LNC : SURF=558 : AREA= 29.3 : ADJACENT=0.17_LT : ADJ_SURF=559 : FRONT
WALL =CLOISON_VIDE_INT : SURF=830 : AREA= 15.9 : ADJACENT=0.07_TDA03_ACHATS : ADJ_SURF=829 : BACK
REGIME
INFILTRATION= I4_EGAL_1.5
VENTILATION = 0.14
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 172.03 : VOLUME= 143.36 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 0.15_STOCKAGE01 / A i r n o d e 0.15_STOCKAGE01
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 0.15_STOCKAGE01
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 0.15_STOCKAGE01
WALL =PB_TP : SURF=109 : AREA= 53.62 : EXTERNAL : ORI=H_0_0 : FSKY=0 : GEOSURF=1
WALL =CBR_B11 : SURF=110 : LENGTH= 5.3 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=111 : AREA= 14.8 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =CBR_I21 : SURF=113 : LENGTH= 5.3 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=385 : AREA= 53.6 : ADJACENT=1.13_BYTPRF : ADJ_SURF=386 : FRONT
WALL =MINT_LEGER : SURF=541 : AREA= 23.86 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=540 : BACK
WINDOW=PORTE_INT : SURF=756 : AREA= 2.94 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=755 : BACK : ORI=NO
WALL =MINT_LEGER : SURF=557 : AREA= 11.7 : ADJACENT=0.14_BUR_IND : ADJ_SURF=556 : BACK
REGIME
INFILTRATION= I4_EGAL_1.5
VENTILATION = 0.15
CAPACITANCE = 180.17 : VOLUME= 150.14 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 0.16_STOCKAGE02 / A i r n o d e 0.16_STOCKAGE02
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 0.16_STOCKAGE02
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 0.16_STOCKAGE02
WALL =PB_TP : SURF= 99 : AREA= 61.38 : EXTERNAL : ORI=H_0_0 : FSKY=0 : GEOSURF=1
WALL =CBR_B11 : SURF=100 : LENGTH= 11.3 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=107 : AREA= 22.3 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =CBR_I21 : SURF=108 : LENGTH= 11.3 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF=112 : AREA= 9.2 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=387 : AREA= 61.4 : ADJACENT=1.13_BYTPRF : ADJ_SURF=388 : FRONT
WALL =MINT_LEGER : SURF=543 : AREA= 20.66 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=542 : BACK
WINDOW=PORTE_INT : SURF=758 : AREA= 2.1 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=757 : BACK : ORI=NO
WINDOW=PORTE_INT : SURF=760 : AREA= 2.94 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=759 : BACK : ORI=NE
WALL =MINT_LNC : SURF=545 : AREA= 6.26 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=544 : BACK
WINDOW=PORTE_INT : SURF=762 : AREA= 2.94 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=761 : BACK : ORI=NE
WALL =MINT_LEGER : SURF=553 : AREA= 31.2 : ADJACENT=0.13_CAFETERIA : ADJ_SURF=552 : BACK
WALL =MINT_LNC : SURF=555 : AREA= 15.2 : ADJACENT=0.13_CAFETERIA : ADJ_SURF=554 : BACK
REGIME
INFILTRATION= I4_EGAL_1.5
VENTILATION = 0.16
CAPACITANCE = 206.23 : VOLUME= 171.86 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 0.17_LT / A i r n o d e 0.17_LT
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 0.17_LT
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 0.17_LT
WALL =PB_TP : SURF=114 : AREA= 49.24 : EXTERNAL : ORI=H_0_0 : FSKY=0 : GEOSURF=1
WALL =CBR_B11 : SURF=115 : LENGTH= 12.6 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=116 : AREA= 16 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =CBR_I21 : SURF=117 : LENGTH= 12.6 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=118 : AREA= 19.2 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =PL_LNC : SURF=389 : AREA= 49.2 : ADJACENT=1.13_BYTPRF : ADJ_SURF=390 : FRONT
WALL =MINT_LNC : SURF=547 : AREA= 4.3 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=546 : BACK
WINDOW=PORTE_INT : SURF=764 : AREA= 4.2 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=763 : BACK : ORI=NO
WALL =MINT_LNC : SURF=559 : AREA= 29.3 : ADJACENT=0.14_BUR_IND : ADJ_SURF=558 : BACK
WALL =MINT_LOURD : SURF=560 : AREA= 16 : ADJACENT=ESC_NE : ADJ_SURF=561 : FRONT
WALL =MINT_LOURD : SURF=633 : AREA= 26.04 : INTERNAL
REGIME
INFILTRATION= I4_EGAL_1.5
VENTILATION = 0.17
CAPACITANCE = 165.44 : VOLUME= 137.87 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 1.01_BUREAU_PIR / A i r n o d e 1.01_BUREAU_PIR
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 1.01_BUREAU_PIR
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 1.01_BUREAU_PIR
WALL =CBR_I21 : SURF=120 : LENGTH= 9.1 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=121 : AREA= 5.41 : EXTERNAL : ORI=SO : FSKY=0.5
WINDOW=MEN_113 : SURF=119 : AREA= 1.98 : EXTERNAL : ORI=SO : FSKY=0.5
WINDOW=MEN_101 : SURF=124 : AREA= 4.41 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_I21 : SURF=122 : LENGTH= 9.1 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=123 : AREA= 13.6 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_MEN : SURF=125 : LENGTH= 3.56 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=314 : AREA= 19.7 : ADJACENT=TDA01 : ADJ_SURF=308 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=391 : AREA= 19.7 : ADJACENT=2.02_IND&ENVIR : ADJ_SURF=392 : FRONT
WALL =MINT_LEGER : SURF=562 : AREA= 11.2 : ADJACENT=1.05_ACCUEIL_DG : ADJ_SURF=563 : FRONT
WINDOW=PORTE_INT : SURF=767 : AREA= 2.1 : ADJACENT=1.05_ACCUEIL_DG : ADJ_SURF=768 : FRONT : ORI=NO
WALL =MINT_LEGER : SURF=564 : AREA= 4.1 : ADJACENT=1.04_VISIO_DG : ADJ_SURF=565 : FRONT
WALL =MINT_LOURD : SURF=566 : AREA= 7 : ADJACENT=ESC_SE : ADJ_SURF=567 : FRONT
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 1*OCCUP_BUREAUX_IND : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 1.01
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 66.26 : VOLUME= 55.22 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 1.02_BUREAUX / A i r n o d e 1.02_BUREAUX
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 1.02_BUREAUX
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 1.02_BUREAUX
WINDOW=MEN_112 : SURF=146 : AREA= 13.23 : EXTERNAL : ORI=M1_E1 : FSKY=0.5
WALL =CBR_I21 : SURF=126 : LENGTH= 13.5 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=127 : AREA= 14.9 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_I21 : SURF=130 : LENGTH= 13.5 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF=131 : AREA= 9.8 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =CBR_MEN : SURF=132 : LENGTH= 7.35 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=316 : AREA= 23.9 : ADJACENT=TDA01 : ADJ_SURF=315 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=393 : AREA= 49.3 : ADJACENT=2.02_IND&ENVIR : ADJ_SURF=394 : FRONT
WALL =MINT_LEGER : SURF=568 : AREA= 35.7 : ADJACENT=1.05_ACCUEIL_DG : ADJ_SURF=569 : FRONT
WINDOW=PORTE_INT : SURF=769 : AREA= 4.2 : ADJACENT=1.05_ACCUEIL_DG : ADJ_SURF=770 : FRONT : ORI=SO
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 2*OCCUP_BUREAUX_IND : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 1.02
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 165.78 : VOLUME= 138.15 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 1.03_BUREAU_ALY / A i r n o d e 1.03_BUREAU_ALY
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 1.03_BUREAU_ALY
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 1.03_BUREAU_ALY
WALL =CBR_I21 : SURF=128 : LENGTH= 5.4 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=133 : AREA= 6.28 : EXTERNAL : ORI=SO : FSKY=0.5
WINDOW=MEN_101 : SURF=134 : AREA= 8.82 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_I21 : SURF=135 : LENGTH= 5.4 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_MEN : SURF=137 : LENGTH= 4.9 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=326 : AREA= 24.3 : ADJACENT=0.02_ACCUEIL : ADJ_SURF=325 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=395 : AREA= 24.28 : ADJACENT=2.02_IND&ENVIR : ADJ_SURF=396 : FRONT
WALL =MINT_LEGER : SURF=570 : AREA= 10.8 : ADJACENT=1.05_ACCUEIL_DG : ADJ_SURF=571 : FRONT
WINDOW=PORTE_INT : SURF=771 : AREA= 2.1 : ADJACENT=1.05_ACCUEIL_DG : ADJ_SURF=772 : FRONT : ORI=NE
WALL =MINT_LEGER : SURF=572 : AREA= 11.7 : ADJACENT=0.02_ACCUEIL : ADJ_SURF=573 : FRONT
WALL =MINT_LEGER : SURF=574 : AREA= 18.9 : ADJACENT=1.07_ERE14 : ADJ_SURF=575 : FRONT
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 1*OCCUP_BUREAUX_IND : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 1.03
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 81.58 : VOLUME= 67.98 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 1.04_VISIO_DG / A i r n o d e 1.04_VISIO_DG
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 1.04_VISIO_DG
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 1.04_VISIO_DG
WALL =PLANCHER_INTERMEDIAIRE : SURF=319 : AREA= 18.7 : ADJACENT=TDA01 : ADJ_SURF=318 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=397 : AREA= 9 : ADJACENT=2.02_IND&ENVIR : ADJ_SURF=398 : FRONT
WALL =PLANCHER_INTERMEDIAIRE : SURF=399 : AREA= 9.7 : ADJACENT=2.01_ERE24 : ADJ_SURF=400 : FRONT
WALL =MINT_LEGER : SURF=565 : AREA= 4.1 : ADJACENT=1.01_BUREAU_PIR : ADJ_SURF=564 : BACK
WALL =MINT_LOURD : SURF=576 : AREA= 14.3 : ADJACENT=ESC_SE : ADJ_SURF=577 : FRONT
WALL =MINT_LEGER : SURF=578 : AREA= 32.2 : ADJACENT=1.05_ACCUEIL_DG : ADJ_SURF=579 : FRONT
WINDOW=PORTE_INT : SURF=773 : AREA= 2.1 : ADJACENT=1.05_ACCUEIL_DG : ADJ_SURF=774 : FRONT : ORI=NO
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 6*OCCUP_SDR : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 1.04
COOLING = FROID_VC
HEATING = CHAUFFAGE_VC
CAPACITANCE = 62.83 : VOLUME= 52.36 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 1.05_ACCUEIL_DG / A i r n o d e 1.05_ACCUEIL_DG
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 1.05_ACCUEIL_DG
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 1.05_ACCUEIL_DG
WINDOW=MEN_112 : SURF=145 : AREA= 8.82 : EXTERNAL : ORI=M2_E1 : FSKY=0.5
WALL =CBR_I21 : SURF=138 : LENGTH= 17.2 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_I21 : SURF=139 : LENGTH= 17.2 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=141 : AREA= 9.47 : EXTERNAL : ORI=SO : FSKY=0.5
WINDOW=MEN_101 : SURF=144 : AREA= 13.23 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=142 : AREA= 6.6 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF=143 : AREA= 9.9 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =CBR_MEN : SURF=129 : LENGTH= 12.25 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=322 : AREA= 143 : ADJACENT=TDA01 : ADJ_SURF=320 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=324 : AREA= 31.5 : ADJACENT=0.02_ACCUEIL : ADJ_SURF=323 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=401 : AREA= 139.8 : ADJACENT=2.02_IND&ENVIR : ADJ_SURF=402 : FRONT
WALL =MINT_LEGER : SURF=563 : AREA= 11.2 : ADJACENT=1.01_BUREAU_PIR : ADJ_SURF=562 : BACK
WINDOW=PORTE_INT : SURF=768 : AREA= 2.1 : ADJACENT=1.01_BUREAU_PIR : ADJ_SURF=767 : BACK : ORI=NO
WALL =MINT_LEGER : SURF=569 : AREA= 35.7 : ADJACENT=1.02_BUREAUX : ADJ_SURF=568 : BACK
WINDOW=PORTE_INT : SURF=770 : AREA= 4.2 : ADJACENT=1.02_BUREAUX : ADJ_SURF=769 : BACK : ORI=SO
WALL =MINT_LEGER : SURF=571 : AREA= 10.8 : ADJACENT=1.03_BUREAU_ALY : ADJ_SURF=570 : BACK
WINDOW=PORTE_INT : SURF=772 : AREA= 2.1 : ADJACENT=1.03_BUREAU_ALY : ADJ_SURF=771 : BACK : ORI=NE
WALL =MINT_LEGER : SURF=579 : AREA= 32.2 : ADJACENT=1.04_VISIO_DG : ADJ_SURF=578 : BACK
WINDOW=PORTE_INT : SURF=774 : AREA= 2.1 : ADJACENT=1.04_VISIO_DG : ADJ_SURF=773 : BACK : ORI=NO
WALL =MINT_LOURD : SURF=580 : AREA= 7 : ADJACENT=ESC_SE : ADJ_SURF=581 : FRONT
WALL =MINT_LOURD : SURF=582 : AREA= 23 : ADJACENT=1.06_PALIER_NE_E1 : ADJ_SURF=583 : FRONT
WINDOW=PORTE_INT : SURF=775 : AREA= 4.2 : ADJACENT=1.06_PALIER_NE_E1 : ADJ_SURF=776 : FRONT : ORI=SE
WALL =CLOISON_VIDE_INT : SURF=833 : AREA= 5.07 : ADJACENT=1.09_DRH : ADJ_SURF=834 : FRONT
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 7*OCCUP_BUR_COMMERCES : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 1.05
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 469.63 : VOLUME= 391.36 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 1.06_PALIER_NE_E1 / A i r n o d e 1.06_PALIER_NE_E1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 1.06_PALIER_NE_E1
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 1.06_PALIER_NE_E1
WINDOW=MEN_112 : SURF=147 : AREA= 4.41 : EXTERNAL : ORI=M3_E1 : FSKY=0.5
WINDOW=MEN_109 : SURF=155 : AREA= 1.863 : EXTERNAL : ORI=M4_E1 : FSKY=0.5
WALL =CBR_I21 : SURF=148 : LENGTH= 4 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =CBR_I21 : SURF=149 : LENGTH= 4 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF=153 : AREA= 4.9 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =CBR_MEN : SURF=154 : LENGTH= 3.485 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=334 : AREA= 10.6 : ADJACENT=0.02_ACCUEIL : ADJ_SURF=333 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=340 : AREA= 7.7 : ADJACENT=0.04_SAS_02 : ADJ_SURF=339 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=403 : AREA= 14.2 : ADJACENT=2.03_PALIER_NE_E1 : ADJ_SURF=404 : FRONT
WALL =MINT_LOURD : SURF=583 : AREA= 23 : ADJACENT=1.05_ACCUEIL_DG : ADJ_SURF=582 : BACK
WINDOW=PORTE_INT : SURF=776 : AREA= 4.2 : ADJACENT=1.05_ACCUEIL_DG : ADJ_SURF=775 : BACK : ORI=SE
WALL =MINT_LEGER : SURF=584 : AREA= 16.83 : ADJACENT=ESC_CENTRAL : ADJ_SURF=585 : FRONT
REGIME
INFILTRATION= I4_EGAL_1.5
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 47.75 : VOLUME= 39.79 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 1.07_ERE14 / A i r n o d e 1.07_ERE14
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 1.07_ERE14
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 1.07_ERE14
WALL =CBR_I21 : SURF=152 : LENGTH= 6.8 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_I21 : SURF=156 : LENGTH= 6.8 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=157 : AREA= 7.875 : EXTERNAL : ORI=SO : FSKY=0.5
WINDOW=MEN_101 : SURF=150 : AREA= 8.82 : EXTERNAL : ORI=SO : FSKY=0.5
WINDOW=MEN_101 : SURF=151 : AREA= 2.205 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_MEN : SURF=158 : LENGTH= 6.125 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=332 : AREA= 16.8 : ADJACENT=0.02_ACCUEIL : ADJ_SURF=331 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=338 : AREA= 13.2 : ADJACENT=0.03_SAS_01 : ADJ_SURF=337 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=405 : AREA= 11.3 : ADJACENT=2.02_IND&ENVIR : ADJ_SURF=406 : FRONT
WALL =PLANCHER_INTERMEDIAIRE : SURF=407 : AREA= 18.7 : ADJACENT=2.05_DT_STRUCT&EDP : ADJ_SURF=409 : FRONT
WALL =MINT_LEGER : SURF=575 : AREA= 18.9 : ADJACENT=1.03_BUREAU_ALY : ADJ_SURF=574 : BACK
WALL =MINT_LEGER : SURF=586 : AREA= 10.8 : ADJACENT=1.09_DRH : ADJ_SURF=587 : FRONT
WINDOW=PORTE_INT : SURF=777 : AREA= 2.1 : ADJACENT=1.09_DRH : ADJ_SURF=778 : FRONT : ORI=SE
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 12*OCCUP_SDR : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 1.07
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 100.93 : VOLUME= 84.11 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 1.08_ERE13 / A i r n o d e 1.08_ERE13
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 1.08_ERE13
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 1.08_ERE13
WALL =PLANCHER_INTERMEDIAIRE : SURF=328 : AREA= 12.2 : ADJACENT=0.02_ACCUEIL : ADJ_SURF=327 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=410 : AREA= 12.2 : ADJACENT=2.04_ERE23(NON_TERMINE) : ADJ_SURF=412 : FRONT
WALL =MINT_LEGER : SURF=588 : AREA= 37.3 : ADJACENT=1.09_DRH : ADJ_SURF=589 : FRONT
WINDOW=PORTE_INT : SURF=159 : AREA= 2.1 : ADJACENT=1.09_DRH : ADJ_SURF=160 : FRONT : ORI=NE
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 4*OCCUP_SDR : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 1.08
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 40.92 : VOLUME= 34.1 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 1.09_DRH / A i r n o d e 1.09_DRH
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 1.09_DRH
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 1.09_DRH
WALL =CBR_I21 : SURF=161 : LENGTH= 34.1 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_I21 : SURF=162 : LENGTH= 34.1 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=163 : AREA= 19.465 : EXTERNAL : ORI=SO : FSKY=0.5
WINDOW=MEN_101 : SURF=165 : AREA= 2.205 : EXTERNAL : ORI=SO : FSKY=0.5
WINDOW=MEN_101 : SURF=167 : AREA= 22.05 : EXTERNAL : ORI=SO : FSKY=0.5
WINDOW=MEN_114 : SURF=168 : AREA= 1.98 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_MEN : SURF=166 : LENGTH= 26.825 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=164 : AREA= 27.75 : EXTERNAL : ORI=NO : FSKY=0.5
WINDOW=MEN_101 : SURF=169 : AREA= 22.05 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=330 : AREA= 64.6 : ADJACENT=0.02_ACCUEIL : ADJ_SURF=329 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=342 : AREA= 184.65 : ADJACENT=0.05_TDA02 : ADJ_SURF=341 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=344 : AREA= 28.8 : ADJACENT=0.06_SALLE_SERVEURS : ADJ_SURF=343 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=413 : AREA= 254.9 : ADJACENT=2.05_DT_STRUCT&EDP : ADJ_SURF=414 : FRONT
WALL =PLANCHER_INTERMEDIAIRE : SURF=415 : AREA= 5.9 : ADJACENT=2.04_ERE23(NON_TERMINE) : ADJ_SURF=416 : FRONT
WALL =MINT_LEGER : SURF=587 : AREA= 10.8 : ADJACENT=1.07_ERE14 : ADJ_SURF=586 : BACK
WINDOW=PORTE_INT : SURF=778 : AREA= 2.1 : ADJACENT=1.07_ERE14 : ADJ_SURF=777 : BACK : ORI=SE
WALL =MINT_LEGER : SURF=589 : AREA= 37.3 : ADJACENT=1.08_ERE13 : ADJ_SURF=588 : BACK
WINDOW=PORTE_INT : SURF=160 : AREA= 2.1 : ADJACENT=1.08_ERE13 : ADJ_SURF=159 : BACK : ORI=NE
WALL =MINT_LEGER : SURF=590 : AREA= 16.6 : ADJACENT=1.12_SECRETARIAT_GAL : ADJ_SURF=591 : FRONT
WINDOW=PORTE_INT : SURF=783 : AREA= 2.1 : ADJACENT=1.12_SECRETARIAT_GAL : ADJ_SURF=784 : FRONT : ORI=NE
WALL =MINT_LOURD : SURF=592 : AREA= 28.9 : ADJACENT=WC_AILE_SUD : ADJ_SURF=593 : FRONT
WALL =MINT_LEGER : SURF=594 : AREA= 12.6 : ADJACENT=WC_AILE_SUD : ADJ_SURF=595 : FRONT
WINDOW=PORTE_INT : SURF=785 : AREA= 4.2 : ADJACENT=WC_AILE_SUD : ADJ_SURF=786 : FRONT : ORI=NO
WALL =MINT_LEGER : SURF=597 : AREA= 23 : ADJACENT=1.10_BAIES_BRASSAGE_E1 : ADJ_SURF=596 : BACK
WINDOW=PORTE_INT : SURF=779 : AREA= 2.1 : ADJACENT=1.10_BAIES_BRASSAGE_E1 : ADJ_SURF=780 : BACK : ORI=NO
WALL =MINT_LEGER : SURF=605 : AREA= 1.56 : ADJACENT=1.12_SECRETARIAT_GAL : ADJ_SURF=604 : BACK
WINDOW=PORTE_INT : SURF=781 : AREA= 2.94 : ADJACENT=1.12_SECRETARIAT_GAL : ADJ_SURF=782 : BACK : ORI=NE
WALL =CLOISON_VIDE_INT : SURF=834 : AREA= 5.07 : ADJACENT=1.05_ACCUEIL_DG : ADJ_SURF=833 : BACK
WALL =CLOISON_VIDE_INT : SURF=835 : AREA= 26.49 : ADJACENT=ESC_CENTRAL : ADJ_SURF=836 : FRONT
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 26*OCCUP_BUREAUX_DT : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 1.09
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 876.29 : VOLUME= 730.24 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 1.10_BAIES_BRASSAGE_E1 / A i r n o d e 1.10_BAIES_BRASSAGE_E1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 1.10_BAIES_BRASSAGE_E1
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 1.10_BAIES_BRASSAGE_E1
WALL =PLANCHER_INTERMEDIAIRE : SURF=346 : AREA= 9.7 : ADJACENT=0.06_SALLE_SERVEURS : ADJ_SURF=345 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=417 : AREA= 9.7 : ADJACENT=2.13_BAIES_BRASSAGE(NON_TERMINE) : ADJ_SURF=170 : FRONT
WALL =MINT_LEGER : SURF=596 : AREA= 23 : ADJACENT=1.09_DRH : ADJ_SURF=597 : FRONT
WINDOW=PORTE_INT : SURF=780 : AREA= 2.1 : ADJACENT=1.09_DRH : ADJ_SURF=779 : FRONT : ORI=NO
WALL =MINT_LEGER : SURF=598 : AREA= 10 : ADJACENT=1.12_SECRETARIAT_GAL : ADJ_SURF=599 : FRONT
REGIME
GAIN = BAIES_BRASSAGES : SCALE= SCHEDULE 1*SERVEURS_CONTINUS : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 1.10
CAPACITANCE = 32.5 : VOLUME= 27.08 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 1.11_ERE12 / A i r n o d e 1.11_ERE12(NON_TERMINE)
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 1.11_ERE12
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 1.11_ERE12(NON_TERMINE)
WALL =PLANCHER_INTERMEDIAIRE : SURF=350 : AREA= 18.5 : ADJACENT=0.08_ARCHIVES : ADJ_SURF=349 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=419 : AREA= 18.5 : ADJACENT=2.08_ERE22(NON_TERMINE) : ADJ_SURF=420 : FRONT
WALL =MINT_LEGER : SURF=600 : AREA= 47.2 : ADJACENT=1.12_SECRETARIAT_GAL : ADJ_SURF=601 : FRONT
WINDOW=PORTE_INT : SURF=172 : AREA= 2.1 : ADJACENT=1.12_SECRETARIAT_GAL : ADJ_SURF=173 : FRONT : ORI=SE
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 8*OCCUP_SDR : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 1.11
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 62.12 : VOLUME= 51.77 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 1.12_SECRETARIAT_GAL / A i r n o d e 1.12_SECRETARIAT_GAL
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 1.12_SECRETARIAT_GAL
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 1.12_SECRETARIAT_GAL
WINDOW=MEN_112 : SURF=178 : AREA= 13.23 : EXTERNAL : ORI=M6_E1 : FSKY=0.5
WINDOW=MEN_106 : SURF=179 : AREA= 1.98 : EXTERNAL : ORI=M5_E1 : FSKY=0.5
WALL =CBR_I21 : SURF=174 : LENGTH= 10.3 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_I21 : SURF=175 : LENGTH= 16.2 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=176 : AREA= 18.94 : EXTERNAL : ORI=NO : FSKY=0.5
WINDOW=MEN_101 : SURF=177 : AREA= 26.46 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =CBR_MEN : SURF=180 : LENGTH= 23.15 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF=181 : AREA= 13.6 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_I21 : SURF=183 : LENGTH= 16.2 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=348 : AREA= 143.9 : ADJACENT=0.07_TDA03_ACHATS : ADJ_SURF=347 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=352 : AREA= 19 : ADJACENT=0.08_ARCHIVES : ADJ_SURF=351 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=373 : AREA= 31.5 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=372 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=421 : AREA= 159.8 : ADJACENT=2.07_DT : ADJ_SURF=422 : FRONT
WALL =PLANCHER_INTERMEDIAIRE : SURF=423 : AREA= 18.4 : ADJACENT=2.09_TRACEURS(NON_TERMINE) : ADJ_SURF=424 : FRONT
WALL =PLANCHER_INTERMEDIAIRE : SURF=425 : AREA= 56 : ADJACENT=2.06_COFFEE_CORNER : ADJ_SURF=427 : FRONT
WALL =MINT_LEGER : SURF=591 : AREA= 16.6 : ADJACENT=1.09_DRH : ADJ_SURF=590 : BACK
WINDOW=PORTE_INT : SURF=784 : AREA= 2.1 : ADJACENT=1.09_DRH : ADJ_SURF=783 : BACK : ORI=NE
WALL =MINT_LEGER : SURF=599 : AREA= 10 : ADJACENT=1.10_BAIES_BRASSAGE_E1 : ADJ_SURF=598 : BACK
WALL =MINT_LEGER : SURF=601 : AREA= 47.2 : ADJACENT=1.11_ERE12(NON_TERMINE) : ADJ_SURF=600 : BACK
WINDOW=PORTE_INT : SURF=173 : AREA= 2.1 : ADJACENT=1.11_ERE12(NON_TERMINE) : ADJ_SURF=172 : BACK : ORI=SE
WALL =MINT_LEGER : SURF=602 : AREA= 12 : ADJACENT=WC_AILE_SUD : ADJ_SURF=603 : FRONT
WALL =MINT_LEGER : SURF=604 : AREA= 1.56 : ADJACENT=1.09_DRH : ADJ_SURF=605 : FRONT
WINDOW=PORTE_INT : SURF=782 : AREA= 2.94 : ADJACENT=1.09_DRH : ADJ_SURF=781 : FRONT : ORI=NE
WALL =MINT_LOURD : SURF=606 : AREA= 19.8 : ADJACENT=WC_AILE_NORD : ADJ_SURF=607 : FRONT
WALL =MINT_LEGER : SURF=608 : AREA= 12.1 : ADJACENT=WC_AILE_NORD : ADJ_SURF=609 : FRONT
WALL =MINT_LEGER : SURF=795 : AREA= 3.5 : ADJACENT=1.15_CIRCUL_SE_E1 : ADJ_SURF=793 : BACK
WINDOW=PORTE_INT : SURF=797 : AREA= 2.1 : ADJACENT=1.15_CIRCUL_SE_E1 : ADJ_SURF=796 : BACK : ORI=SO
WALL =CLOISON_VIDE_INT : SURF=837 : AREA= 33.88 : ADJACENT=1.13_BYTPRF : ADJ_SURF=838 : FRONT
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 26*OCCUP_BUREAUX_DT : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 1.12
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 786.48 : VOLUME= 655.4 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 1.14_ERE11 / A i r n o d e 1.14_ERE11
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 1.14_ERE11
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 1.14_ERE11
WALL =PLANCHER_INTERMEDIAIRE : SURF=428 : AREA= 10.7 : ADJACENT=2.11_ERE21(NON_TERMINE) : ADJ_SURF=429 : FRONT
WALL =MINT_LEGER : SURF=611 : AREA= 29.4 : ADJACENT=1.13_BYTPRF : ADJ_SURF=610 : BACK
WINDOW=PORTE_INT : SURF=787 : AREA= 2.1 : ADJACENT=1.13_BYTPRF : ADJ_SURF=788 : BACK : ORI=SE
WALL =MINT_LOURD : SURF=616 : AREA= 9.7 : ADJACENT=ESC_NE : ADJ_SURF=200 : FRONT
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 1*OCCUP_SDR : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 1.14
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 35.95 : VOLUME= 29.96 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 1.15_CIRCUL_SE_E1 / A i r n o d e 1.15_CIRCUL_SE_E1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 1.15_CIRCUL_SE_E1
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 1.15_CIRCUL_SE_E1
WINDOW=MEN_111 : SURF=199 : AREA= 13.23 : EXTERNAL : ORI=M7_E1 : FSKY=0.5
WALL =CBR_I21 : SURF=198 : LENGTH= 8.1 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF=202 : AREA= 9.5 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_MEN : SURF=203 : LENGTH= 7.35 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=375 : AREA= 25.1 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=374 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=432 : AREA= 23.2 : ADJACENT=2.12_CIRCUL_SE_E2 : ADJ_SURF=433 : FRONT
WALL =MINT_LEGER : SURF=201 : AREA= 27.7 : ADJACENT=WC_AILE_NORD : ADJ_SURF=617 : FRONT
WINDOW=PORTE_INT : SURF=791 : AREA= 4.2 : ADJACENT=WC_AILE_NORD : ADJ_SURF=792 : FRONT : ORI=SO
WALL =MINT_LEGER : SURF=618 : AREA= 2.2 : ADJACENT=ESC_SECONDAIRE : ADJ_SURF=619 : FRONT
WINDOW=PORTE_INT : SURF=789 : AREA= 2.1 : ADJACENT=ESC_SECONDAIRE : ADJ_SURF=790 : FRONT : ORI=NE
WALL =MINT_LEGER : SURF=793 : AREA= 3.5 : ADJACENT=1.12_SECRETARIAT_GAL : ADJ_SURF=795 : FRONT
WINDOW=PORTE_INT : SURF=796 : AREA= 2.1 : ADJACENT=1.12_SECRETARIAT_GAL : ADJ_SURF=797 : FRONT : ORI=SO
REGIME
INFILTRATION= I4_EGAL_1.5
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 78.08 : VOLUME= 65.07 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 2.01_ERE24 / A i r n o d e 2.01_ERE24
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 2.01_ERE24
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 2.01_ERE24
WALL =PLANCHER_INTERMEDIAIRE : SURF=400 : AREA= 9.7 : ADJACENT=1.04_VISIO_DG : ADJ_SURF=399 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=434 : AREA= 9.7 : ADJACENT=3.01_ERE34 : ADJ_SURF=435 : FRONT
WALL =MINT_LOURD : SURF=620 : AREA= 9.7 : ADJACENT=ESC_SE : ADJ_SURF=621 : FRONT
WALL =MINT_LEGER : SURF=622 : AREA= 23.3 : ADJACENT=2.02_IND&ENVIR : ADJ_SURF=623 : FRONT
WINDOW=PORTE_INT : SURF=171 : AREA= 2.1 : ADJACENT=2.02_IND&ENVIR : ADJ_SURF=197 : FRONT : ORI=NE
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 4*OCCUP_SDR : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 2.01
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 32.66 : VOLUME= 27.22 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 2.02_IND&ENVIR / A i r n o d e 2.02_IND&ENVIR
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 2.02_IND&ENVIR
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 2.02_IND&ENVIR
WINDOW=MEN_112 : SURF=188 : AREA= 22.05 : EXTERNAL : ORI=M1_E2 : FSKY=0.5
WALL =CBR_I21 : SURF=182 : LENGTH= 47.7 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_I21 : SURF=184 : LENGTH= 47.7 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF=185 : AREA= 19.7 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=186 : AREA= 34.8 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=187 : AREA= 24.15 : EXTERNAL : ORI=SO : FSKY=0.5
WINDOW=MEN_113 : SURF=189 : AREA= 1.98 : EXTERNAL : ORI=SO : FSKY=0.5
WINDOW=MEN_101 : SURF=190 : AREA= 30.87 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_MEN : SURF=191 : LENGTH= 30.5 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=336 : AREA= 51.5 : ADJACENT=0.02_ACCUEIL : ADJ_SURF=335 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=392 : AREA= 19.7 : ADJACENT=1.01_BUREAU_PIR : ADJ_SURF=391 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=394 : AREA= 49.3 : ADJACENT=1.02_BUREAUX : ADJ_SURF=393 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=396 : AREA= 24.28 : ADJACENT=1.03_BUREAU_ALY : ADJ_SURF=395 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=398 : AREA= 9 : ADJACENT=1.04_VISIO_DG : ADJ_SURF=397 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=402 : AREA= 139.8 : ADJACENT=1.05_ACCUEIL_DG : ADJ_SURF=401 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=406 : AREA= 11.3 : ADJACENT=1.07_ERE14 : ADJ_SURF=405 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=436 : AREA= 306.68 : ADJACENT=3.02_CIRMAD_COMMERCES : ADJ_SURF=437 : FRONT
WALL =MINT_LEGER : SURF=623 : AREA= 23.3 : ADJACENT=2.01_ERE24 : ADJ_SURF=622 : BACK
WINDOW=PORTE_INT : SURF=197 : AREA= 2.1 : ADJACENT=2.01_ERE24 : ADJ_SURF=171 : BACK : ORI=NE
WALL =MINT_LOURD : SURF=624 : AREA= 16.8 : ADJACENT=ESC_SE : ADJ_SURF=625 : FRONT
WINDOW=PORTE_INT : SURF=206 : AREA= 2.1 : ADJACENT=ESC_SE : ADJ_SURF=220 : FRONT : ORI=SO
WALL =MINT_LOURD : SURF=626 : AREA= 16.5 : ADJACENT=2.03_PALIER_NE_E1 : ADJ_SURF=627 : FRONT
WINDOW=PORTE_INT : SURF=204 : AREA= 2.1 : ADJACENT=2.03_PALIER_NE_E1 : ADJ_SURF=205 : FRONT : ORI=NO
WALL =CLOISON_VIDE_INT : SURF=839 : AREA= 41.41 : ADJACENT=2.05_DT_STRUCT&EDP : ADJ_SURF=840 : FRONT
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 29*OCCUP_BUR_COMMERCES : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 2.02
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 1030.44 : VOLUME= 858.7 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 2.03_PALIER_NE_E2 / A i r n o d e 2.03_PALIER_NE_E1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 2.03_PALIER_NE_E2
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 2.03_PALIER_NE_E1
WINDOW=MEN_112 : SURF=192 : AREA= 4.41 : EXTERNAL : ORI=M2_E2 : FSKY=0.5
WINDOW=MEN_109 : SURF=196 : AREA= 1.863 : EXTERNAL : ORI=M3_E2 : FSKY=0.5
WALL =CBR_I21 : SURF=193 : LENGTH= 3.8 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =CBR_I21 : SURF=194 : LENGTH= 3.8 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF=195 : AREA= 4.4 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =CBR_MEN : SURF=208 : LENGTH= 3.485 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=404 : AREA= 14.2 : ADJACENT=1.06_PALIER_NE_E1 : ADJ_SURF=403 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=438 : AREA= 14 : ADJACENT=3.03_PALIER_NE_E3 : ADJ_SURF=439 : FRONT
WALL =MINT_LOURD : SURF=627 : AREA= 16.5 : ADJACENT=2.02_IND&ENVIR : ADJ_SURF=626 : BACK
WINDOW=PORTE_INT : SURF=205 : AREA= 2.1 : ADJACENT=2.02_IND&ENVIR : ADJ_SURF=204 : BACK : ORI=NO
WALL =MINT_LEGER : SURF=628 : AREA= 2.8 : ADJACENT=2.05_DT_STRUCT&EDP : ADJ_SURF=629 : FRONT
WINDOW=PORTE_INT : SURF=222 : AREA= 2.1 : ADJACENT=2.05_DT_STRUCT&EDP : ADJ_SURF=229 : FRONT : ORI=SO
WALL =MINT_LEGER : SURF=630 : AREA= 17 : ADJACENT=ESC_CENTRAL : ADJ_SURF=631 : FRONT
REGIME
INFILTRATION= I4_EGAL_1.5
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 47.08 : VOLUME= 39.23 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 2.04_ERE23 / A i r n o d e 2.04_ERE23(NON_TERMINE)
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 2.04_ERE23
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 2.04_ERE23(NON_TERMINE)
WALL =PLANCHER_INTERMEDIAIRE : SURF=412 : AREA= 12.2 : ADJACENT=1.08_ERE13 : ADJ_SURF=410 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=416 : AREA= 5.9 : ADJACENT=1.09_DRH : ADJ_SURF=415 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=440 : AREA= 18.1 : ADJACENT=3.04_ERE33(NON_TERMINE) : ADJ_SURF=441 : FRONT
WALL =MINT_LEGER : SURF=632 : AREA= 46.8 : ADJACENT=2.05_DT_STRUCT&EDP : ADJ_SURF=634 : FRONT
WINDOW=PORTE_INT : SURF=245 : AREA= 2.1 : ADJACENT=2.05_DT_STRUCT&EDP : ADJ_SURF=230 : FRONT : ORI=SO
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 8*OCCUP_SDR : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 2.04
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 60.65 : VOLUME= 50.54 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 2.05_DT_STRUCT&EDP / A i r n o d e 2.05_DT_STRUCT&EDP
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 2.05_DT_STRUCT&EDP
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 2.05_DT_STRUCT&EDP
WALL =CBR_I21 : SURF=207 : LENGTH= 38.1 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_I21 : SURF=209 : LENGTH= 38.1 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=210 : AREA= 24.25 : EXTERNAL : ORI=SO : FSKY=0.5
WINDOW=MEN_101 : SURF=212 : AREA= 30.87 : EXTERNAL : ORI=SO : FSKY=0.5
WINDOW=MEN_114 : SURF=213 : AREA= 1.98 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=211 : AREA= 27.55 : EXTERNAL : ORI=NO : FSKY=0.5
WINDOW=MEN_101 : SURF=214 : AREA= 22.05 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =CBR_MEN : SURF=215 : LENGTH= 30.5 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=409 : AREA= 18.7 : ADJACENT=1.07_ERE14 : ADJ_SURF=407 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=414 : AREA= 254.9 : ADJACENT=1.09_DRH : ADJ_SURF=413 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=442 : AREA= 295.1 : ADJACENT=3.05_COMMERCES_OF : ADJ_SURF=443 : FRONT
WALL =MINT_LEGER : SURF=629 : AREA= 2.8 : ADJACENT=2.03_PALIER_NE_E1 : ADJ_SURF=628 : BACK
WINDOW=PORTE_INT : SURF=229 : AREA= 2.1 : ADJACENT=2.03_PALIER_NE_E1 : ADJ_SURF=222 : BACK : ORI=SO
WALL =MINT_LEGER : SURF=634 : AREA= 46.8 : ADJACENT=2.04_ERE23(NON_TERMINE) : ADJ_SURF=632 : BACK
WINDOW=PORTE_INT : SURF=230 : AREA= 2.1 : ADJACENT=2.04_ERE23(NON_TERMINE) : ADJ_SURF=245 : BACK : ORI=SO
WALL =MINT_LOURD : SURF=635 : AREA= 29.1 : ADJACENT=WC_AILE_SUD : ADJ_SURF=636 : FRONT
WALL =MINT_LEGER : SURF=637 : AREA= 12.8 : ADJACENT=WC_AILE_SUD : ADJ_SURF=638 : FRONT
WINDOW=PORTE_INT : SURF=253 : AREA= 4.2 : ADJACENT=WC_AILE_SUD : ADJ_SURF=254 : FRONT : ORI=NO
WALL =MINT_LEGER : SURF=639 : AREA= 2.4 : ADJACENT=2.06_COFFEE_CORNER : ADJ_SURF=640 : FRONT
WINDOW=PORTE_INT : SURF=268 : AREA= 2.1 : ADJACENT=2.06_COFFEE_CORNER : ADJ_SURF=269 : FRONT : ORI=NE
WALL =MINT_LEGER : SURF=641 : AREA= 23 : ADJACENT=2.13_BAIES_BRASSAGE(NON_TERMINE) : ADJ_SURF=642 : FRONT
WINDOW=PORTE_INT : SURF=246 : AREA= 2.1 : ADJACENT=2.13_BAIES_BRASSAGE(NON_TERMINE) : ADJ_SURF=252 : FRONT : ORI=NO
WALL =MINT_LEGER : SURF=643 : AREA= 8.2 : ADJACENT=2.09_TRACEURS(NON_TERMINE) : ADJ_SURF=644 : FRONT
WALL =MINT_LEGER : SURF=645 : AREA= 10.2 : ADJACENT=2.07_DT : ADJ_SURF=646 : FRONT
WALL =CLOISON_VIDE_INT : SURF=840 : AREA= 41.41 : ADJACENT=2.02_IND&ENVIR : ADJ_SURF=839 : BACK
WALL =CLOISON_VIDE_INT : SURF=841 : AREA= 26.49 : ADJACENT=ESC_CENTRAL : ADJ_SURF=842 : FRONT
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 33*OCCUP_BUREAUX_DT : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 2.05
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 991.4 : VOLUME= 826.17 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 2.06_COFFEE_CORNER / A i r n o d e 2.06_COFFEE_CORNER
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 2.06_COFFEE_CORNER
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 2.06_COFFEE_CORNER
WINDOW=MEN_111 : SURF=219 : AREA= 13.23 : EXTERNAL : ORI=M5_E2 : FSKY=0.5
WINDOW=MEN_106 : SURF=218 : AREA= 1.98 : EXTERNAL : ORI=M4_E2 : FSKY=0.5
WALL =CBR_I21 : SURF=216 : LENGTH= 10.3 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_I21 : SURF=217 : LENGTH= 10.3 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF=221 : AREA= 13.6 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_MEN : SURF=223 : LENGTH= 8.45 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=427 : AREA= 56 : ADJACENT=1.12_SECRETARIAT_GAL : ADJ_SURF=425 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=444 : AREA= 56 : ADJACENT=3.06_TRAVAUX01 : ADJ_SURF=445 : FRONT
WALL =MINT_LEGER : SURF=640 : AREA= 2.4 : ADJACENT=2.05_DT_STRUCT&EDP : ADJ_SURF=639 : BACK
WINDOW=PORTE_INT : SURF=269 : AREA= 2.1 : ADJACENT=2.05_DT_STRUCT&EDP : ADJ_SURF=268 : BACK : ORI=NE
WALL =MINT_LEGER : SURF=647 : AREA= 24.2 : ADJACENT=2.07_DT : ADJ_SURF=648 : FRONT
WALL =MINT_LEGER : SURF=649 : AREA= 12 : ADJACENT=WC_AILE_SUD : ADJ_SURF=650 : FRONT
WALL =MINT_LEGER : SURF=651 : AREA= 12.2 : ADJACENT=WC_AILE_NORD : ADJ_SURF=652 : FRONT
WALL =MINT_LEGER : SURF=674 : AREA= 4.5 : ADJACENT=2.12_CIRCUL_SE_E2 : ADJ_SURF=673 : BACK
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 20*OCCUP_COFFEE_CORNER : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 2.06
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 188.03 : VOLUME= 156.69 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 2.07_DT / A i r n o d e 2.07_DT
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 2.07_DT
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 2.07_DT
WALL =CBR_I21 : SURF=224 : LENGTH= 21.7 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =CBR_I21 : SURF=225 : LENGTH= 21.7 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=226 : AREA= 34.14 : EXTERNAL : ORI=NO : FSKY=0.5
WINDOW=MEN_101 : SURF=228 : AREA= 26.46 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =CBR_MEN : SURF=227 : LENGTH= 14.7 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=422 : AREA= 159.8 : ADJACENT=1.12_SECRETARIAT_GAL : ADJ_SURF=421 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=446 : AREA= 159.42 : ADJACENT=3.06_TRAVAUX01 : ADJ_SURF=447 : FRONT
WALL =MINT_LEGER : SURF=646 : AREA= 10.2 : ADJACENT=2.05_DT_STRUCT&EDP : ADJ_SURF=645 : BACK
WALL =MINT_LEGER : SURF=648 : AREA= 24.2 : ADJACENT=2.06_COFFEE_CORNER : ADJ_SURF=647 : BACK
WALL =MINT_LEGER : SURF=653 : AREA= 33 : ADJACENT=2.09_TRACEURS(NON_TERMINE) : ADJ_SURF=654 : FRONT
WALL =MINT_LEGER : SURF=655 : AREA= 47.2 : ADJACENT=2.08_ERE22(NON_TERMINE) : ADJ_SURF=656 : FRONT
WINDOW=PORTE_INT : SURF=292 : AREA= 2.1 : ADJACENT=2.08_ERE22(NON_TERMINE) : ADJ_SURF=273 : FRONT : ORI=SE
WALL =MINT_LOURD : SURF=657 : AREA= 19.8 : ADJACENT=WC_AILE_NORD : ADJ_SURF=658 : FRONT
WALL =CLOISON_VIDE_INT : SURF=843 : AREA= 34.05 : ADJACENT=2.10_FLUIDES_METHODES : ADJ_SURF=844 : FRONT
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 8*OCCUP_BUREAUX_DT : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 2.07
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 535.66 : VOLUME= 446.38 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 2.08_ERE22 / A i r n o d e 2.08_ERE22(NON_TERMINE)
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 2.08_ERE22
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 2.08_ERE22(NON_TERMINE)
WALL =PLANCHER_INTERMEDIAIRE : SURF=420 : AREA= 18.5 : ADJACENT=1.11_ERE12(NON_TERMINE) : ADJ_SURF=419 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=448 : AREA= 18.5 : ADJACENT=3.07_ERE32 : ADJ_SURF=449 : FRONT
WALL =MINT_LEGER : SURF=656 : AREA= 47.2 : ADJACENT=2.07_DT : ADJ_SURF=655 : BACK
WINDOW=PORTE_INT : SURF=273 : AREA= 2.1 : ADJACENT=2.07_DT : ADJ_SURF=292 : BACK : ORI=SE
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 8*OCCUP_SDR : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 2.08
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 62.12 : VOLUME= 51.77 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 2.09_TRACEURS / A i r n o d e 2.09_TRACEURS(NON_TERMINE)
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 2.09_TRACEURS
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 2.09_TRACEURS(NON_TERMINE)
WALL =PLANCHER_INTERMEDIAIRE : SURF=424 : AREA= 18.4 : ADJACENT=1.12_SECRETARIAT_GAL : ADJ_SURF=423 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=450 : AREA= 18.4 : ADJACENT=3.06_TRAVAUX01 : ADJ_SURF=451 : FRONT
WALL =MINT_LEGER : SURF=644 : AREA= 8.2 : ADJACENT=2.05_DT_STRUCT&EDP : ADJ_SURF=643 : BACK
WALL =MINT_LEGER : SURF=654 : AREA= 33 : ADJACENT=2.07_DT : ADJ_SURF=653 : BACK
WALL =MINT_LNC : SURF=659 : AREA= 10 : ADJACENT=2.13_BAIES_BRASSAGE(NON_TERMINE) : ADJ_SURF=660 : FRONT
REGIME
INFILTRATION= I4_EGAL_1.5
VENTILATION = 2.09
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 61.66 : VOLUME= 51.38 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 2.10_FLUIDES_METHODES / A i r n o d e 2.10_FLUIDES_METHODES
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 2.10_FLUIDES_METHODES
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 2.10_FLUIDES_METHODES
WINDOW=MEN_106 : SURF=242 : AREA= 1.98 : EXTERNAL : ORI=M8_E2 : FSKY=0.5
WINDOW=MEN_111 : SURF=243 : AREA= 4.41 : EXTERNAL : ORI=M9_E2 : FSKY=0.5
WALL =CBR_I21 : SURF=231 : LENGTH= 55.9 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =CBR_I21 : SURF=232 : LENGTH= 55.9 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=233 : AREA= 26.42 : EXTERNAL : ORI=NO : FSKY=0.5
WINDOW=MEN_101 : SURF=237 : AREA= 35.28 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=234 : AREA= 31.69 : EXTERNAL : ORI=NE : FSKY=0.5
WINDOW=MEN_101 : SURF=238 : AREA= 13.23 : EXTERNAL : ORI=NE : FSKY=0.5
WINDOW=MEN_113 : SURF=239 : AREA= 1.98 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF=235 : AREA= 23.12 : EXTERNAL : ORI=SE : FSKY=0.5
WINDOW=MEN_111 : SURF=240 : AREA= 8.82 : EXTERNAL : ORI=SE : FSKY=0.5
WINDOW=MEN_106 : SURF=241 : AREA= 3.96 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF=236 : AREA= 5.8 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_MEN : SURF=244 : LENGTH= 38.7 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=431 : AREA= 370.9 : ADJACENT=1.13_BYTPRF : ADJ_SURF=430 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=452 : AREA= 370.8 : ADJACENT=3.08_TRAVAUX02 : ADJ_SURF=453 : FRONT
WALL =MINT_LEGER : SURF=661 : AREA= 24.9 : ADJACENT=2.11_ERE21(NON_TERMINE) : ADJ_SURF=662 : FRONT
WINDOW=PORTE_INT : SURF=418 : AREA= 2.1 : ADJACENT=2.11_ERE21(NON_TERMINE) : ADJ_SURF=313 : FRONT : ORI=SE
WALL =MINT_LOURD : SURF=663 : AREA= 16.7 : ADJACENT=ESC_NE : ADJ_SURF=664 : FRONT
WINDOW=PORTE_INT : SURF=458 : AREA= 2.1 : ADJACENT=ESC_NE : ADJ_SURF=794 : FRONT : ORI=NE
WALL =MINT_LOURD : SURF=665 : AREA= 26 : ADJACENT=ESC_SECONDAIRE : ADJ_SURF=666 : FRONT
WALL =CLOISON_VIDE_INT : SURF=844 : AREA= 34.05 : ADJACENT=2.07_DT : ADJ_SURF=843 : BACK
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 43*OCCUP_BUREAUX_DT : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 2.10
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 1245.89 : VOLUME= 1038.24 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 2.11_ERE21 / A i r n o d e 2.11_ERE21(NON_TERMINE)
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 2.11_ERE21
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 2.11_ERE21(NON_TERMINE)
WALL =PLANCHER_INTERMEDIAIRE : SURF=429 : AREA= 10.7 : ADJACENT=1.14_ERE11 : ADJ_SURF=428 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=454 : AREA= 10.7 : ADJACENT=3.09_ERE31(NON_TERMINE) : ADJ_SURF=455 : FRONT
WALL =MINT_LEGER : SURF=662 : AREA= 24.9 : ADJACENT=2.10_FLUIDES_METHODES : ADJ_SURF=661 : BACK
WINDOW=PORTE_INT : SURF=313 : AREA= 2.1 : ADJACENT=2.10_FLUIDES_METHODES : ADJ_SURF=418 : BACK : ORI=SE
WALL =MINT_LOURD : SURF=667 : AREA= 9.7 : ADJACENT=ESC_NE : ADJ_SURF=668 : FRONT
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 4*OCCUP_SDR : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 2.11
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 35.92 : VOLUME= 29.93 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 2.12_CIRCUL_SE_E2 / A i r n o d e 2.12_CIRCUL_SE_E2
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 2.12_CIRCUL_SE_E2
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 2.12_CIRCUL_SE_E2
WINDOW=MEN_111 : SURF=250 : AREA= 13.23 : EXTERNAL : ORI=M6_E2 : FSKY=0.5
WALL =CBR_I21 : SURF=247 : LENGTH= 8.2 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_I21 : SURF=248 : LENGTH= 8.2 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF=249 : AREA= 9.7 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_MEN : SURF=251 : LENGTH= 7.35 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=433 : AREA= 23.2 : ADJACENT=1.15_CIRCUL_SE_E1 : ADJ_SURF=432 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=456 : AREA= 22.8 : ADJACENT=3.10_CIRCUL_SE_E3 : ADJ_SURF=457 : FRONT
WALL =MINT_LEGER : SURF=669 : AREA= 27.7 : ADJACENT=WC_AILE_NORD : ADJ_SURF=670 : FRONT
WINDOW=PORTE_INT : SURF=293 : AREA= 4.2 : ADJACENT=WC_AILE_NORD : ADJ_SURF=306 : FRONT : ORI=NO
WALL =MINT_LEGER : SURF=671 : AREA= 2.2 : ADJACENT=ESC_SECONDAIRE : ADJ_SURF=672 : FRONT
WINDOW=PORTE_INT : SURF=307 : AREA= 2.1 : ADJACENT=ESC_SECONDAIRE : ADJ_SURF=312 : FRONT : ORI=NE
WALL =MINT_LEGER : SURF=673 : AREA= 4.5 : ADJACENT=2.06_COFFEE_CORNER : ADJ_SURF=674 : FRONT
REGIME
INFILTRATION= I4_EGAL_1.5
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 76.44 : VOLUME= 63.7 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 2.13_BAIES_BRASSAGE_E2 / A i r n o d e 2.13_BAIES_BRASSAGE(NON_TERMINE)
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 2.13_BAIES_BRASSAGE_E2
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 2.13_BAIES_BRASSAGE(NON_TERMINE)
WALL =MINT_LEGER : SURF=642 : AREA= 23 : ADJACENT=2.05_DT_STRUCT&EDP : ADJ_SURF=641 : BACK
WINDOW=PORTE_INT : SURF=252 : AREA= 2.1 : ADJACENT=2.05_DT_STRUCT&EDP : ADJ_SURF=246 : BACK : ORI=NO
WALL =MINT_LNC : SURF=660 : AREA= 10 : ADJACENT=2.09_TRACEURS(NON_TERMINE) : ADJ_SURF=659 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=136 : AREA= 9.66 : ADJACENT=3.11_BAIES_BRASSAGE_E3(NON_TERMINE) : ADJ_SURF=140 : FRONT
WALL =PLANCHER_INTERMEDIAIRE : SURF=170 : AREA= 9.7 : ADJACENT=1.10_BAIES_BRASSAGE_E1 : ADJ_SURF=417 : BACK
REGIME
GAIN = BAIES_BRASSAGES : SCALE= SCHEDULE 1*SERVEURS_CONTINUS : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 2.13
CAPACITANCE = 32.46 : VOLUME= 27.05 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 3.01_ERE34 / A i r n o d e 3.01_ERE34
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 3.01_ERE34
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 3.01_ERE34
WALL =PLANCHER_INTERMEDIAIRE : SURF=435 : AREA= 9.7 : ADJACENT=2.01_ERE24 : ADJ_SURF=434 : BACK
WALL =TOITURE : SURF=408 : AREA= 9.7 : EXTERNAL : ORI=H_0_0 : FSKY=1
WALL =MINT_LEGER : SURF=675 : AREA= 23.3 : ADJACENT=3.02_CIRMAD_COMMERCES : ADJ_SURF=676 : FRONT
WINDOW=PORTE_INT : SURF=459 : AREA= 2.1 : ADJACENT=3.02_CIRMAD_COMMERCES : ADJ_SURF=798 : FRONT : ORI=SE
WALL =MINT_LOURD : SURF=677 : AREA= 9.7 : ADJACENT=ESC_SE : ADJ_SURF=678 : FRONT
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 4*OCCUP_SDR : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 3.01
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 32.66 : VOLUME= 27.22 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 3.02_CIRMAD_COMMERCES / A i r n o d e 3.02_CIRMAD_COMMERCES
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 3.02_CIRMAD_COMMERCES
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 3.02_CIRMAD_COMMERCES
WINDOW=MEN_111 : SURF=260 : AREA= 22.05 : EXTERNAL : ORI=M1_E3 : FSKY=0.5
WALL =CBR_H11_TOITURE : SURF=256 : LENGTH= 47.7 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_I21 : SURF=255 : LENGTH= 47.7 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=257 : AREA= 24.25 : EXTERNAL : ORI=SO : FSKY=0.5
WINDOW=MEN_101 : SURF=261 : AREA= 30.87 : EXTERNAL : ORI=SO : FSKY=0.5
WINDOW=MEN_113 : SURF=262 : AREA= 1.98 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=258 : AREA= 34.8 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF=259 : AREA= 19.6 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =CBR_MEN : SURF=263 : LENGTH= 30.5 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=437 : AREA= 306.68 : ADJACENT=2.02_IND&ENVIR : ADJ_SURF=436 : BACK
WALL =TOITURE : SURF=411 : AREA= 299.2 : EXTERNAL : ORI=H_0_0 : FSKY=1
WALL =MINT_LEGER : SURF=676 : AREA= 23.3 : ADJACENT=3.01_ERE34 : ADJ_SURF=675 : BACK
WINDOW=PORTE_INT : SURF=798 : AREA= 2.1 : ADJACENT=3.01_ERE34 : ADJ_SURF=459 : BACK : ORI=SE
WALL =MINT_LOURD : SURF=679 : AREA= 16.8 : ADJACENT=ESC_SE : ADJ_SURF=680 : FRONT
WINDOW=PORTE_INT : SURF=799 : AREA= 2.1 : ADJACENT=ESC_SE : ADJ_SURF=800 : FRONT : ORI=SE
WALL =MINT_LEGER : SURF=681 : AREA= 2.9 : ADJACENT=3.03_PALIER_NE_E3 : ADJ_SURF=682 : FRONT
WINDOW=PORTE_INT : SURF=803 : AREA= 2.1 : ADJACENT=3.03_PALIER_NE_E3 : ADJ_SURF=804 : FRONT : ORI=SE
WALL =MINT_LOURD : SURF=683 : AREA= 1.1 : ADJACENT=3.03_PALIER_NE_E3 : ADJ_SURF=684 : FRONT
WINDOW=PORTE_INT : SURF=801 : AREA= 2.1 : ADJACENT=3.03_PALIER_NE_E3 : ADJ_SURF=802 : FRONT : ORI=NE
WALL =CLOISON_VIDE_INT : SURF=845 : AREA= 33.6 : ADJACENT=3.05_COMMERCES_OF : ADJ_SURF=846 : FRONT
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 35*OCCUP_BUR_COMMERCES : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 3.02
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 1005.14 : VOLUME= 837.62 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 3.03_PALIER_NE_E3 / A i r n o d e 3.03_PALIER_NE_E3
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 3.03_PALIER_NE_E3
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 3.03_PALIER_NE_E3
WINDOW=MEN_111 : SURF=264 : AREA= 4.41 : EXTERNAL : ORI=M2_E3 : FSKY=0.5
WINDOW=MEN_109 : SURF=267 : AREA= 1.863 : EXTERNAL : ORI=M3_E3 : FSKY=0.5
WALL =CBR_H11_TOITURE : SURF=265 : LENGTH= 3.9 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_I21 : SURF=266 : LENGTH= 3.9 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF=271 : AREA= 4.6 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =CBR_MEN : SURF=272 : LENGTH= 3.49 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=439 : AREA= 14 : ADJACENT=2.03_PALIER_NE_E1 : ADJ_SURF=438 : BACK
WALL =TOITURE : SURF=426 : AREA= 13.7 : EXTERNAL : ORI=H_0_0 : FSKY=1
WALL =MINT_LEGER : SURF=682 : AREA= 2.9 : ADJACENT=3.02_CIRMAD_COMMERCES : ADJ_SURF=681 : BACK
WINDOW=PORTE_INT : SURF=804 : AREA= 2.1 : ADJACENT=3.02_CIRMAD_COMMERCES : ADJ_SURF=803 : BACK : ORI=SE
WALL =MINT_LOURD : SURF=684 : AREA= 1.1 : ADJACENT=3.02_CIRMAD_COMMERCES : ADJ_SURF=683 : BACK
WINDOW=PORTE_INT : SURF=802 : AREA= 2.1 : ADJACENT=3.02_CIRMAD_COMMERCES : ADJ_SURF=801 : BACK : ORI=NE
WALL =MINT_LEGER : SURF=685 : AREA= 16.7 : ADJACENT=ESC_CENTRAL : ADJ_SURF=686 : FRONT
REGIME
INFILTRATION= I4_EGAL_1.5
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 46.03 : VOLUME= 38.36 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 3.04_ERE33 / A i r n o d e 3.04_ERE33(NON_TERMINE)
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 3.04_ERE33
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 3.04_ERE33(NON_TERMINE)
WALL =PLANCHER_INTERMEDIAIRE : SURF=441 : AREA= 18.1 : ADJACENT=2.04_ERE23(NON_TERMINE) : ADJ_SURF=440 : BACK
WALL =TOITURE : SURF=460 : AREA= 18.2 : EXTERNAL : ORI=H_0_0 : FSKY=1
WALL =MINT_LEGER : SURF=687 : AREA= 46.6 : ADJACENT=3.05_COMMERCES_OF : ADJ_SURF=688 : FRONT
WINDOW=PORTE_INT : SURF=810 : AREA= 2.1 : ADJACENT=3.05_COMMERCES_OF : ADJ_SURF=809 : FRONT : ORI=SO
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 8*OCCUP_SDR : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 3.04
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 61.15 : VOLUME= 50.96 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 3.05_COMMERCES_OF / A i r n o d e 3.05_COMMERCES_OF
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 3.05_COMMERCES_OF
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 3.05_COMMERCES_OF
WALL =CBR_I21 : SURF=270 : LENGTH= 38.2 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_H11_TOITURE : SURF=274 : LENGTH= 38.2 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=275 : AREA= 24.25 : EXTERNAL : ORI=SO : FSKY=0.5
WINDOW=MEN_101 : SURF=278 : AREA= 30.87 : EXTERNAL : ORI=SO : FSKY=0.5
WINDOW=MEN_113 : SURF=279 : AREA= 1.98 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=276 : AREA= 27.75 : EXTERNAL : ORI=NO : FSKY=0.5
WINDOW=MEN_101 : SURF=280 : AREA= 22.05 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =CBR_MEN : SURF=277 : LENGTH= 30.5 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=443 : AREA= 295.1 : ADJACENT=2.05_DT_STRUCT&EDP : ADJ_SURF=442 : BACK
WALL =TOITURE : SURF=461 : AREA= 294.2 : EXTERNAL : ORI=H_0_0 : FSKY=1
WALL =MINT_LEGER : SURF=688 : AREA= 46.6 : ADJACENT=3.04_ERE33(NON_TERMINE) : ADJ_SURF=687 : BACK
WINDOW=PORTE_INT : SURF=809 : AREA= 2.1 : ADJACENT=3.04_ERE33(NON_TERMINE) : ADJ_SURF=810 : BACK : ORI=SO
WALL =MINT_LOURD : SURF=689 : AREA= 28.8 : ADJACENT=WC_AILE_SUD : ADJ_SURF=690 : FRONT
WALL =MINT_LEGER : SURF=691 : AREA= 12.6 : ADJACENT=WC_AILE_SUD : ADJ_SURF=692 : FRONT
WINDOW=PORTE_INT : SURF=807 : AREA= 4.2 : ADJACENT=WC_AILE_SUD : ADJ_SURF=808 : FRONT : ORI=NO
WALL =MINT_LEGER : SURF=693 : AREA= 16.7 : ADJACENT=ESC_CENTRAL : ADJ_SURF=694 : FRONT
WALL =MINT_LEGER : SURF=695 : AREA= 4.1 : ADJACENT=3.06_TRAVAUX01 : ADJ_SURF=696 : FRONT
WALL =MINT_LEGER : SURF=697 : AREA= 23 : ADJACENT=3.11_BAIES_BRASSAGE_E3(NON_TERMINE) : ADJ_SURF=698 : FRONT
WINDOW=PORTE_INT : SURF=805 : AREA= 2.1 : ADJACENT=3.11_BAIES_BRASSAGE_E3(NON_TERMINE) : ADJ_SURF=806 : FRONT : ORI=NO
WALL =MINT_LEGER : SURF=699 : AREA= 16.5 : ADJACENT=3.06_TRAVAUX01 : ADJ_SURF=700 : FRONT
WINDOW=PORTE_INT : SURF=811 : AREA= 2.1 : ADJACENT=3.06_TRAVAUX01 : ADJ_SURF=812 : FRONT : ORI=NE
WALL =CLOISON_VIDE_INT : SURF=846 : AREA= 33.6 : ADJACENT=3.02_CIRMAD_COMMERCES : ADJ_SURF=845 : BACK
WALL =CLOISON_VIDE_INT : SURF=847 : AREA= 26.49 : ADJACENT=ESC_CENTRAL : ADJ_SURF=848 : FRONT
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 24*OCCUP_BUR_COMMERCES : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 3.05
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 988.51 : VOLUME= 823.76 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 3.06_TRAVAUX01 / A i r n o d e 3.06_TRAVAUX01
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 3.06_TRAVAUX01
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 3.06_TRAVAUX01
WINDOW=MEN_106 : SURF=287 : AREA= 1.98 : EXTERNAL : ORI=M4_E3 : FSKY=0.5
WINDOW=MEN_111 : SURF=289 : AREA= 13.23 : EXTERNAL : ORI=M5_E3 : FSKY=0.5
WALL =CBR_I21 : SURF=281 : LENGTH= 26.3 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =CBR_H11_TOITURE : SURF=282 : LENGTH= 26.3 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=283 : AREA= 16.96 : EXTERNAL : ORI=NO : FSKY=0.5
WINDOW=MEN_101 : SURF=284 : AREA= 26.46 : EXTERNAL : ORI=NO : FSKY=0.5
WINDOW=MEN_113 : SURF=285 : AREA= 1.98 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =CBR_MEN : SURF=288 : LENGTH= 23.15 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF=286 : AREA= 13.1 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=445 : AREA= 56 : ADJACENT=2.06_COFFEE_CORNER : ADJ_SURF=444 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=447 : AREA= 159.42 : ADJACENT=2.07_DT : ADJ_SURF=446 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=451 : AREA= 18.4 : ADJACENT=2.09_TRACEURS(NON_TERMINE) : ADJ_SURF=450 : BACK
WALL =TOITURE : SURF=462 : AREA= 232.3 : EXTERNAL : ORI=H_0_0 : FSKY=1
WALL =MINT_LEGER : SURF=696 : AREA= 4.1 : ADJACENT=3.05_COMMERCES_OF : ADJ_SURF=695 : BACK
WALL =MINT_LEGER : SURF=700 : AREA= 16.5 : ADJACENT=3.05_COMMERCES_OF : ADJ_SURF=699 : BACK
WINDOW=PORTE_INT : SURF=812 : AREA= 2.1 : ADJACENT=3.05_COMMERCES_OF : ADJ_SURF=811 : BACK : ORI=NE
WALL =MINT_LEGER : SURF=701 : AREA= 10 : ADJACENT=3.11_BAIES_BRASSAGE_E3(NON_TERMINE) : ADJ_SURF=702 : FRONT
WALL =MINT_LEGER : SURF=703 : AREA= 12 : ADJACENT=WC_AILE_SUD : ADJ_SURF=704 : FRONT
WALL =MINT_LEGER : SURF=705 : AREA= 47.2 : ADJACENT=3.07_ERE32 : ADJ_SURF=706 : FRONT
WINDOW=PORTE_INT : SURF=813 : AREA= 2.1 : ADJACENT=3.07_ERE32 : ADJ_SURF=814 : FRONT : ORI=NO
WALL =MINT_LEGER : SURF=707 : AREA= 16.5 : ADJACENT=WC_AILE_NORD : ADJ_SURF=708 : FRONT
WALL =MINT_LEGER : SURF=709 : AREA= 2.2 : ADJACENT=3.10_CIRCUL_SE_E3 : ADJ_SURF=710 : FRONT
WINDOW=PORTE_INT : SURF=815 : AREA= 2.1 : ADJACENT=3.10_CIRCUL_SE_E3 : ADJ_SURF=816 : FRONT : ORI=NE
WALL =MINT_LOURD : SURF=711 : AREA= 20 : ADJACENT=WC_AILE_NORD : ADJ_SURF=712 : FRONT
WALL =CLOISON_VIDE_INT : SURF=849 : AREA= 34.05 : ADJACENT=3.08_TRAVAUX02 : ADJ_SURF=850 : FRONT
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 15*OCCUP_BUR_COMMERCES : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 3.06
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 780.53 : VOLUME= 650.44 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 3.07_ERE32 / A i r n o d e 3.07_ERE32
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 3.07_ERE32
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 3.07_ERE32
WALL =PLANCHER_INTERMEDIAIRE : SURF=449 : AREA= 18.5 : ADJACENT=2.08_ERE22(NON_TERMINE) : ADJ_SURF=448 : BACK
WALL =TOITURE : SURF=463 : AREA= 18.5 : EXTERNAL : ORI=H_0_0 : FSKY=1
WALL =MINT_LEGER : SURF=706 : AREA= 47.2 : ADJACENT=3.06_TRAVAUX01 : ADJ_SURF=705 : BACK
WINDOW=PORTE_INT : SURF=814 : AREA= 2.1 : ADJACENT=3.06_TRAVAUX01 : ADJ_SURF=813 : BACK : ORI=NO
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 8*OCCUP_SDR : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 3.07
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 62.29 : VOLUME= 51.91 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 3.08_TRAVAUX02 / A i r n o d e 3.08_TRAVAUX02
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 3.08_TRAVAUX02
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 3.08_TRAVAUX02
WINDOW=MEN_106 : SURF=303 : AREA= 1.98 : EXTERNAL : ORI=M8_E3 : FSKY=0.5
WINDOW=MEN_111 : SURF=304 : AREA= 4.41 : EXTERNAL : ORI=M9_E3 : FSKY=0.5
WALL =CBR_I21 : SURF=290 : LENGTH= 56 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =CBR_H11_TOITURE : SURF=291 : LENGTH= 56 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=294 : AREA= 26.32 : EXTERNAL : ORI=NO : FSKY=0.5
WINDOW=MEN_101 : SURF=295 : AREA= 35.28 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=296 : AREA= 29.71 : EXTERNAL : ORI=NE : FSKY=0.5
WINDOW=MEN_101 : SURF=297 : AREA= 13.23 : EXTERNAL : ORI=NE : FSKY=0.5
WINDOW=MEN_113 : SURF=298 : AREA= 3.96 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF=299 : AREA= 23.22 : EXTERNAL : ORI=SE : FSKY=0.5
WINDOW=MEN_106 : SURF=300 : AREA= 3.96 : EXTERNAL : ORI=SE : FSKY=0.5
WINDOW=MEN_111 : SURF=301 : AREA= 8.82 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF=302 : AREA= 5.8 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_MEN : SURF=305 : LENGTH= 39.8 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=453 : AREA= 370.8 : ADJACENT=2.10_FLUIDES_METHODES : ADJ_SURF=452 : BACK
WALL =MINT_LOURD : SURF=713 : AREA= 26 : ADJACENT=ESC_SECONDAIRE : ADJ_SURF=715 : FRONT
WALL =MINT_LEGER : SURF=716 : AREA= 24.9 : ADJACENT=3.09_ERE31(NON_TERMINE) : ADJ_SURF=717 : FRONT
WINDOW=PORTE_INT : SURF=817 : AREA= 2.1 : ADJACENT=3.09_ERE31(NON_TERMINE) : ADJ_SURF=818 : FRONT : ORI=NO
WALL =MINT_LOURD : SURF=718 : AREA= 16.8 : ADJACENT=ESC_NE : ADJ_SURF=720 : FRONT
WINDOW=PORTE_INT : SURF=819 : AREA= 2.1 : ADJACENT=ESC_NE : ADJ_SURF=820 : FRONT : ORI=NE
WALL =CLOISON_VIDE_INT : SURF=850 : AREA= 34.05 : ADJACENT=3.06_TRAVAUX01 : ADJ_SURF=849 : BACK
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 46*OCCUP_BUR_COMMERCES : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 3.08
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 1210.18 : VOLUME= 1008.48 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 3.09_ERE31 / A i r n o d e 3.09_ERE31(NON_TERMINE)
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 3.09_ERE31
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 3.09_ERE31(NON_TERMINE)
WALL =PLANCHER_INTERMEDIAIRE : SURF=455 : AREA= 10.7 : ADJACENT=2.11_ERE21(NON_TERMINE) : ADJ_SURF=454 : BACK
WALL =TOITURE : SURF=464 : AREA= 10.66 : EXTERNAL : ORI=H_0_0 : FSKY=1
WALL =MINT_LEGER : SURF=717 : AREA= 24.9 : ADJACENT=3.08_TRAVAUX02 : ADJ_SURF=716 : BACK
WINDOW=PORTE_INT : SURF=818 : AREA= 2.1 : ADJACENT=3.08_TRAVAUX02 : ADJ_SURF=817 : BACK : ORI=NO
WALL =MINT_LOURD : SURF=721 : AREA= 9.7 : ADJACENT=ESC_NE : ADJ_SURF=722 : FRONT
REGIME
GAIN = PERS_ISO01 : SCALE= SCHEDULE 4*OCCUP_SDR : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 3.09
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 35.82 : VOLUME= 29.85 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 3.10_CIRCUL_SE_E3 / A i r n o d e 3.10_CIRCUL_SE_E3
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 3.10_CIRCUL_SE_E3
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 3.10_CIRCUL_SE_E3
WINDOW=MEN_111 : SURF=309 : AREA= 13.23 : EXTERNAL : ORI=M6_E3 : FSKY=0.5
WALL =CBR_I21 : SURF=310 : LENGTH= 7.9 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_H11_TOITURE : SURF=311 : LENGTH= 7.9 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF=317 : AREA= 8.8 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_MEN : SURF=321 : LENGTH= 7.35 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=457 : AREA= 22.8 : ADJACENT=2.12_CIRCUL_SE_E2 : ADJ_SURF=456 : BACK
WALL =TOITURE : SURF=465 : AREA= 22.61 : EXTERNAL : ORI=H_0_0 : FSKY=1
WALL =MINT_LEGER : SURF=710 : AREA= 2.2 : ADJACENT=3.06_TRAVAUX01 : ADJ_SURF=709 : BACK
WINDOW=PORTE_INT : SURF=816 : AREA= 2.1 : ADJACENT=3.06_TRAVAUX01 : ADJ_SURF=815 : BACK : ORI=NE
WALL =MINT_LEGER : SURF=723 : AREA= 27.8 : ADJACENT=WC_AILE_NORD : ADJ_SURF=724 : FRONT
WALL =MINT_LOURD : SURF=725 : AREA= 2.2 : ADJACENT=ESC_SECONDAIRE : ADJ_SURF=726 : FRONT
WINDOW=PORTE_INT : SURF=821 : AREA= 2.1 : ADJACENT=ESC_SECONDAIRE : ADJ_SURF=822 : FRONT : ORI=NE
REGIME
INFILTRATION= I4_EGAL_1.5
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 75.97 : VOLUME= 63.31 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 3.11_BAIES_BRASSAGE_E3 / A i r n o d e 3.11_BAIES_BRASSAGE_E3(NON_TERMINE)
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 3.11_BAIES_BRASSAGE_E3
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 3.11_BAIES_BRASSAGE_E3(NON_TERMINE)
WALL =TOITURE : SURF=466 : AREA= 9.7 : EXTERNAL : ORI=H_0_0 : FSKY=1
WALL =MINT_LEGER : SURF=698 : AREA= 23 : ADJACENT=3.05_COMMERCES_OF : ADJ_SURF=697 : BACK
WINDOW=PORTE_INT : SURF=806 : AREA= 2.1 : ADJACENT=3.05_COMMERCES_OF : ADJ_SURF=805 : BACK : ORI=NO
WALL =MINT_LEGER : SURF=702 : AREA= 10 : ADJACENT=3.06_TRAVAUX01 : ADJ_SURF=701 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=140 : AREA= 9.66 : ADJACENT=2.13_BAIES_BRASSAGE(NON_TERMINE) : ADJ_SURF=136 : BACK
REGIME
GAIN = BAIES_BRASSAGES : SCALE= SCHEDULE 1*SERVEURS_CONTINUS : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 3.11
CAPACITANCE = 32.46 : VOLUME= 27.05 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e 1.13_BYTPRF / A i r n o d e 1.13_BYTPRF
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE 1.13_BYTPRF
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE 1.13_BYTPRF
WINDOW=MEN_106 : SURF=368 : AREA= 1.98 : EXTERNAL : ORI=M9_E1 : FSKY=0.5
WINDOW=MEN_111 : SURF=369 : AREA= 4.41 : EXTERNAL : ORI=M10_E1 : FSKY=0.5
WALL =CBR_I21 : SURF=356 : LENGTH= 6.1 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =CBR_I21 : SURF=357 : LENGTH= 49.9 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=358 : AREA= 26.42 : EXTERNAL : ORI=NO : FSKY=0.5
WINDOW=MEN_101 : SURF=359 : AREA= 35.28 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =CBR_MEN : SURF=360 : LENGTH= 23.15 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF=361 : AREA= 13.6 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =CBR_I21 : SURF=362 : LENGTH= 49.9 : EXTERNAL : ORI=NO : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=363 : AREA= 31.69 : EXTERNAL : ORI=NE : FSKY=0.5
WINDOW=MEN_114 : SURF=354 : AREA= 1.98 : EXTERNAL : ORI=NE : FSKY=0.5
WINDOW=MEN_101 : SURF=355 : AREA= 13.23 : EXTERNAL : ORI=NE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF=364 : AREA= 20.82 : EXTERNAL : ORI=SE : FSKY=0.5
WINDOW=MEN_111 : SURF=366 : AREA= 8.82 : EXTERNAL : ORI=SE : FSKY=0.5
WINDOW=MEN_106 : SURF=367 : AREA= 3.96 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =MEXT_PEUPLIER : SURF=365 : AREA= 5.8 : EXTERNAL : ORI=SO : FSKY=0.5
WALL =PLANCHER_INTERMEDIAIRE : SURF=370 : AREA= 12.2 : ADJACENT=0.08_ARCHIVES : ADJ_SURF=353 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=377 : AREA= 91.3 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=376 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=382 : AREA= 62.47 : ADJACENT=0.13_CAFETERIA : ADJ_SURF=381 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=384 : AREA= 51.2 : ADJACENT=0.14_BUR_IND : ADJ_SURF=383 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=386 : AREA= 53.6 : ADJACENT=0.15_STOCKAGE01 : ADJ_SURF=385 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=388 : AREA= 61.4 : ADJACENT=0.16_STOCKAGE02 : ADJ_SURF=387 : BACK
WALL =PL_LNC : SURF=390 : AREA= 49.2 : ADJACENT=0.17_LT : ADJ_SURF=389 : BACK
WALL =PLANCHER_INTERMEDIAIRE : SURF=430 : AREA= 370.9 : ADJACENT=2.10_FLUIDES_METHODES : ADJ_SURF=431 : FRONT
WALL =MINT_LEGER : SURF=610 : AREA= 29.4 : ADJACENT=1.14_ERE11 : ADJ_SURF=611 : FRONT
WINDOW=PORTE_INT : SURF=788 : AREA= 2.1 : ADJACENT=1.14_ERE11 : ADJ_SURF=787 : FRONT : ORI=SE
WALL =MINT_LOURD : SURF=612 : AREA= 18.8 : ADJACENT=ESC_NE : ADJ_SURF=613 : FRONT
WALL =MINT_LOURD : SURF=614 : AREA= 26.7 : ADJACENT=ESC_SECONDAIRE : ADJ_SURF=615 : FRONT
WALL =CLOISON_VIDE_INT : SURF=838 : AREA= 33.88 : ADJACENT=1.12_SECRETARIAT_GAL : ADJ_SURF=837 : BACK
REGIME
GAIN = PERS_ISO02 : SCALE= SCHEDULE 39*OCCUP_BUREAUX_DT : GEOPOS= 0
INFILTRATION= I4_EGAL_1.5
VENTILATION = 1.13
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 1246.32 : VOLUME= 1038.6 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ESC_SE / A i r n o d e ESC_SE
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ESC_SE
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE ESC_SE
WALL =CBR_B11 : SURF=469 : LENGTH= 6.8 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =PB_TP : SURF=475 : AREA= 16.88 : EXTERNAL : ORI=H_0_0 : FSKY=0
WALL =TOITURE : SURF=476 : AREA= 16.88 : EXTERNAL : ORI=H_0_0 : FSKY=1
WALL =CBR_H11 : SURF=470 : LENGTH= 6.8 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =MEXT_TERRE_CUITE : SURF=477 : AREA= 76.16 : EXTERNAL : ORI=SE : FSKY=0.5
WALL =MINT_LOURD : SURF=483 : AREA= 31.6 : ADJACENT=TDA01 : ADJ_SURF=482 : BACK
WINDOW=PORTE_INT : SURF=728 : AREA= 2.1 : ADJACENT=TDA01 : ADJ_SURF=727 : BACK : ORI=SE
WALL =MINT_LOURD : SURF=567 : AREA= 7 : ADJACENT=1.01_BUREAU_PIR : ADJ_SURF=566 : BACK
WALL =MINT_LOURD : SURF=577 : AREA= 14.3 : ADJACENT=1.04_VISIO_DG : ADJ_SURF=576 : BACK
WALL =MINT_LOURD : SURF=581 : AREA= 7 : ADJACENT=1.05_ACCUEIL_DG : ADJ_SURF=580 : BACK
WALL =MINT_LOURD : SURF=621 : AREA= 9.7 : ADJACENT=2.01_ERE24 : ADJ_SURF=620 : BACK
WALL =MINT_LOURD : SURF=625 : AREA= 16.8 : ADJACENT=2.02_IND&ENVIR : ADJ_SURF=624 : BACK
WINDOW=PORTE_INT : SURF=220 : AREA= 2.1 : ADJACENT=2.02_IND&ENVIR : ADJ_SURF=206 : BACK : ORI=SO
WALL =MINT_LOURD : SURF=678 : AREA= 9.7 : ADJACENT=3.01_ERE34 : ADJ_SURF=677 : BACK
WALL =MINT_LOURD : SURF=680 : AREA= 16.8 : ADJACENT=3.02_CIRMAD_COMMERCES : ADJ_SURF=679 : BACK
WINDOW=PORTE_INT : SURF=800 : AREA= 2.1 : ADJACENT=3.02_CIRMAD_COMMERCES : ADJ_SURF=799 : BACK : ORI=SE
REGIME
INFILTRATION= I4_EGAL_1.5
CAPACITANCE = 226.87 : VOLUME= 189.06 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ESC_CENTRAL / A i r n o d e ESC_CENTRAL
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ESC_CENTRAL
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE ESC_CENTRAL
WALL =PB_TP : SURF=478 : AREA= 14.92 : EXTERNAL : ORI=H_0_0 : FSKY=0
WALL =TOITURE : SURF=479 : AREA= 14.92 : EXTERNAL : ORI=H_0_0 : FSKY=1
WALL =MINT_LEGER : SURF=585 : AREA= 16.83 : ADJACENT=1.06_PALIER_NE_E1 : ADJ_SURF=584 : BACK
WALL =MINT_LEGER : SURF=631 : AREA= 17 : ADJACENT=2.03_PALIER_NE_E1 : ADJ_SURF=630 : BACK
WALL =MINT_LEGER : SURF=686 : AREA= 16.7 : ADJACENT=3.03_PALIER_NE_E3 : ADJ_SURF=685 : BACK
WALL =MINT_LEGER : SURF=694 : AREA= 16.7 : ADJACENT=3.05_COMMERCES_OF : ADJ_SURF=693 : BACK
WALL =CLOISON_VIDE_INT : SURF=824 : AREA= 33.82 : ADJACENT=0.02_ACCUEIL : ADJ_SURF=823 : BACK
WALL =CLOISON_VIDE_INT : SURF=836 : AREA= 26.49 : ADJACENT=1.09_DRH : ADJ_SURF=835 : BACK
WALL =CLOISON_VIDE_INT : SURF=842 : AREA= 26.49 : ADJACENT=2.05_DT_STRUCT&EDP : ADJ_SURF=841 : BACK
WALL =CLOISON_VIDE_INT : SURF=848 : AREA= 26.49 : ADJACENT=3.05_COMMERCES_OF : ADJ_SURF=847 : BACK
REGIME
INFILTRATION= I4_EGAL_1.5
CAPACITANCE = 200.52 : VOLUME= 167.1 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ESC_SECONDAIRE / A i r n o d e ESC_SECONDAIRE
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ESC_SECONDAIRE
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE ESC_SECONDAIRE
WALL =PB_TP : SURF=467 : AREA= 9.43 : EXTERNAL : ORI=H_0_0 : FSKY=0
WALL =TOITURE : SURF=468 : AREA= 9.43 : EXTERNAL : ORI=H_0_0 : FSKY=1
WALL =MINT_LOURD : SURF=529 : AREA= 9.4 : ADJACENT=0.11_ERE01 : ADJ_SURF=528 : BACK
WALL =MINT_LOURD : SURF=535 : AREA= 18.7 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=534 : BACK
WINDOW=PORTE_INT : SURF=750 : AREA= 2.1 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=749 : BACK : ORI=NE
WALL =MINT_LOURD : SURF=551 : AREA= 12.7 : ADJACENT=0.13_CAFETERIA : ADJ_SURF=550 : BACK
WALL =MINT_LOURD : SURF=615 : AREA= 26.7 : ADJACENT=1.13_BYTPRF : ADJ_SURF=614 : BACK
WALL =MINT_LEGER : SURF=619 : AREA= 2.2 : ADJACENT=1.15_CIRCUL_SE_E1 : ADJ_SURF=618 : BACK
WINDOW=PORTE_INT : SURF=790 : AREA= 2.1 : ADJACENT=1.15_CIRCUL_SE_E1 : ADJ_SURF=789 : BACK : ORI=NE
WALL =MINT_LOURD : SURF=666 : AREA= 26 : ADJACENT=2.10_FLUIDES_METHODES : ADJ_SURF=665 : BACK
WALL =MINT_LEGER : SURF=672 : AREA= 2.2 : ADJACENT=2.12_CIRCUL_SE_E2 : ADJ_SURF=671 : BACK
WINDOW=PORTE_INT : SURF=312 : AREA= 2.1 : ADJACENT=2.12_CIRCUL_SE_E2 : ADJ_SURF=307 : BACK : ORI=NE
WALL =MINT_LOURD : SURF=715 : AREA= 26 : ADJACENT=3.08_TRAVAUX02 : ADJ_SURF=713 : BACK
WALL =MINT_LOURD : SURF=726 : AREA= 2.2 : ADJACENT=3.10_CIRCUL_SE_E3 : ADJ_SURF=725 : BACK
WINDOW=PORTE_INT : SURF=822 : AREA= 2.1 : ADJACENT=3.10_CIRCUL_SE_E3 : ADJ_SURF=821 : BACK : ORI=NE
REGIME
INFILTRATION= I4_EGAL_1.5
COOLING = FROID_PR
HEATING = CHAUFFAGE_PR
CAPACITANCE = 126.74 : VOLUME= 105.62 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ESC_NE / A i r n o d e ESC_NE
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ESC_NE
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE ESC_NE
WALL =PB_TP : SURF=471 : AREA= 10.19 : EXTERNAL : ORI=H_0_0 : FSKY=0
WALL =TOITURE : SURF=472 : AREA= 10.19 : EXTERNAL : ORI=H_0_0 : FSKY=1
WALL =MINT_LOURD : SURF=549 : AREA= 5.9 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=548 : BACK
WINDOW=PORTE_INT : SURF=766 : AREA= 2.1 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=765 : BACK : ORI=SE
WALL =MINT_LOURD : SURF=561 : AREA= 16 : ADJACENT=0.17_LT : ADJ_SURF=560 : BACK
WALL =MINT_LOURD : SURF=613 : AREA= 18.8 : ADJACENT=1.13_BYTPRF : ADJ_SURF=612 : BACK
WALL =MINT_LOURD : SURF=200 : AREA= 9.7 : ADJACENT=1.14_ERE11 : ADJ_SURF=616 : BACK
WALL =MINT_LOURD : SURF=664 : AREA= 16.7 : ADJACENT=2.10_FLUIDES_METHODES : ADJ_SURF=663 : BACK
WINDOW=PORTE_INT : SURF=794 : AREA= 2.1 : ADJACENT=2.10_FLUIDES_METHODES : ADJ_SURF=458 : BACK : ORI=NE
WALL =MINT_LOURD : SURF=668 : AREA= 9.7 : ADJACENT=2.11_ERE21(NON_TERMINE) : ADJ_SURF=667 : BACK
WALL =MINT_LOURD : SURF=720 : AREA= 16.8 : ADJACENT=3.08_TRAVAUX02 : ADJ_SURF=718 : BACK
WINDOW=PORTE_INT : SURF=820 : AREA= 2.1 : ADJACENT=3.08_TRAVAUX02 : ADJ_SURF=819 : BACK : ORI=NE
WALL =MINT_LOURD : SURF=722 : AREA= 9.7 : ADJACENT=3.09_ERE31(NON_TERMINE) : ADJ_SURF=721 : BACK
REGIME
INFILTRATION= I4_EGAL_1.5
CAPACITANCE = 136.96 : VOLUME= 114.13 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e WC_AILE_SUD / A i r n o d e WC_AILE_SUD
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE WC_AILE_SUD
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE WC_AILE_SUD
WALL =PB_TP : SURF=473 : AREA= 30.64 : EXTERNAL : ORI=H_0_0 : FSKY=0
WALL =TOITURE : SURF=474 : AREA= 30.64 : EXTERNAL : ORI=H_0_0 : FSKY=1
WALL =MINT_LEGER : SURF=495 : AREA= 31.56 : ADJACENT=0.02_ACCUEIL : ADJ_SURF=494 : BACK
WINDOW=PORTE_SAS_NORPAC : SURF=734 : AREA= 2.94 : ADJACENT=0.02_ACCUEIL : ADJ_SURF=733 : BACK : ORI=SE
WALL =MINT_LOURD : SURF=503 : AREA= 13.1 : ADJACENT=0.06_SALLE_SERVEURS : ADJ_SURF=502 : BACK
WALL =MINT_LOURD : SURF=505 : AREA= 9 : ADJACENT=0.07_TDA03_ACHATS : ADJ_SURF=504 : BACK
WALL =MINT_LEGER : SURF=507 : AREA= 12 : ADJACENT=0.07_TDA03_ACHATS : ADJ_SURF=506 : BACK
WALL =MINT_LOURD : SURF=593 : AREA= 28.9 : ADJACENT=1.09_DRH : ADJ_SURF=592 : BACK
WALL =MINT_LEGER : SURF=595 : AREA= 12.6 : ADJACENT=1.09_DRH : ADJ_SURF=594 : BACK
WINDOW=PORTE_INT : SURF=786 : AREA= 4.2 : ADJACENT=1.09_DRH : ADJ_SURF=785 : BACK : ORI=NO
WALL =MINT_LEGER : SURF=603 : AREA= 12 : ADJACENT=1.12_SECRETARIAT_GAL : ADJ_SURF=602 : BACK
WALL =MINT_LOURD : SURF=636 : AREA= 29.1 : ADJACENT=2.05_DT_STRUCT&EDP : ADJ_SURF=635 : BACK
WALL =MINT_LEGER : SURF=638 : AREA= 12.8 : ADJACENT=2.05_DT_STRUCT&EDP : ADJ_SURF=637 : BACK
WINDOW=PORTE_INT : SURF=254 : AREA= 4.2 : ADJACENT=2.05_DT_STRUCT&EDP : ADJ_SURF=253 : BACK : ORI=NO
WALL =MINT_LEGER : SURF=650 : AREA= 12 : ADJACENT=2.06_COFFEE_CORNER : ADJ_SURF=649 : BACK
WALL =MINT_LOURD : SURF=690 : AREA= 28.8 : ADJACENT=3.05_COMMERCES_OF : ADJ_SURF=689 : BACK
WALL =MINT_LEGER : SURF=692 : AREA= 12.6 : ADJACENT=3.05_COMMERCES_OF : ADJ_SURF=691 : BACK
WINDOW=PORTE_INT : SURF=808 : AREA= 4.2 : ADJACENT=3.05_COMMERCES_OF : ADJ_SURF=807 : BACK : ORI=NO
WALL =MINT_LEGER : SURF=704 : AREA= 12 : ADJACENT=3.06_TRAVAUX01 : ADJ_SURF=703 : BACK
REGIME
INFILTRATION= I4_EGAL_1.5
CAPACITANCE = 411.8 : VOLUME= 343.17 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e WC_AILE_NORD / A i r n o d e WC_AILE_NORD
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE WC_AILE_NORD
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE WC_AILE_NORD
WALL =PB_TP : SURF=480 : AREA= 34.45 : EXTERNAL : ORI=H_0_0 : FSKY=0
WALL =TOITURE : SURF=481 : AREA= 34.45 : EXTERNAL : ORI=H_0_0 : FSKY=1
WALL =MINT_LEGER : SURF=511 : AREA= 12.2 : ADJACENT=0.07_TDA03_ACHATS : ADJ_SURF=510 : BACK
WALL =MINT_LOURD : SURF=513 : AREA= 7.1 : ADJACENT=0.08_ARCHIVES : ADJ_SURF=512 : BACK
WALL =MINT_LEGER : SURF=533 : AREA= 40.4 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=532 : BACK
WINDOW=PORTE_INT : SURF=748 : AREA= 4.2 : ADJACENT=0.12_CIRCUL_RDC : ADJ_SURF=747 : BACK : ORI=NO
WALL =MINT_LOURD : SURF=607 : AREA= 19.8 : ADJACENT=1.12_SECRETARIAT_GAL : ADJ_SURF=606 : BACK
WALL =MINT_LEGER : SURF=609 : AREA= 12.1 : ADJACENT=1.12_SECRETARIAT_GAL : ADJ_SURF=608 : BACK
WALL =MINT_LEGER : SURF=617 : AREA= 27.7 : ADJACENT=1.15_CIRCUL_SE_E1 : ADJ_SURF=201 : BACK
WINDOW=PORTE_INT : SURF=792 : AREA= 4.2 : ADJACENT=1.15_CIRCUL_SE_E1 : ADJ_SURF=791 : BACK : ORI=SO
WALL =MINT_LEGER : SURF=652 : AREA= 12.2 : ADJACENT=2.06_COFFEE_CORNER : ADJ_SURF=651 : BACK
WALL =MINT_LOURD : SURF=658 : AREA= 19.8 : ADJACENT=2.07_DT : ADJ_SURF=657 : BACK
WALL =MINT_LEGER : SURF=670 : AREA= 27.7 : ADJACENT=2.12_CIRCUL_SE_E2 : ADJ_SURF=669 : BACK
WINDOW=PORTE_INT : SURF=306 : AREA= 4.2 : ADJACENT=2.12_CIRCUL_SE_E2 : ADJ_SURF=293 : BACK : ORI=NO
WALL =MINT_LEGER : SURF=708 : AREA= 16.5 : ADJACENT=3.06_TRAVAUX01 : ADJ_SURF=707 : BACK
WALL =MINT_LOURD : SURF=712 : AREA= 20 : ADJACENT=3.06_TRAVAUX01 : ADJ_SURF=711 : BACK
WALL =MINT_LEGER : SURF=724 : AREA= 27.8 : ADJACENT=3.10_CIRCUL_SE_E3 : ADJ_SURF=723 : BACK
REGIME
INFILTRATION= I4_EGAL_1.5
CAPACITANCE = 463.01 : VOLUME= 385.84 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* O u t p u t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
OUTPUTS
TRANSFER : TIMEBASE=1.000
AIRNODES = TDA01 0.02_ACCUEIL 0.03_SAS_01 0.04_SAS_02 0.05_TDA02 0.06_SALLE_SERVEURS 0.07_TDA03_ACHATS 0.08_ARCHIVES 0.09_ERE03 0.10_ERE02 0.11_ERE01 0.12_CIRCUL_RDC 0.13_CAFETERIA 0.14_BUR_IND ;
0.15_STOCKAGE01 0.16_STOCKAGE02 0.17_LT 1.01_BUREAU_PIR 1.02_BUREAUX 1.03_BUREAU_ALY 1.04_VISIO_DG 1.05_ACCUEIL_DG 1.06_PALIER_NE_E1 1.07_ERE14 1.08_ERE13 1.09_DRH 1.10_BAIES_BRASSAGE_E1 ;
1.11_ERE12(NON_TERMINE) 1.12_SECRETARIAT_GAL 1.14_ERE11 1.15_CIRCUL_SE_E1 2.01_ERE24 2.02_IND&ENVIR 2.03_PALIER_NE_E1 2.04_ERE23(NON_TERMINE) 2.05_DT_STRUCT&EDP 2.06_COFFEE_CORNER 2.07_DT ;
2.08_ERE22(NON_TERMINE) 2.09_TRACEURS(NON_TERMINE) 2.10_FLUIDES_METHODES 2.11_ERE21(NON_TERMINE) 2.12_CIRCUL_SE_E2 2.13_BAIES_BRASSAGE(NON_TERMINE) 3.01_ERE34 3.02_CIRMAD_COMMERCES 3.03_PALIER_NE_E3 ;
3.04_ERE33(NON_TERMINE) 3.05_COMMERCES_OF 3.06_TRAVAUX01 3.07_ERE32 3.08_TRAVAUX02 3.09_ERE31(NON_TERMINE) 3.10_CIRCUL_SE_E3 3.11_BAIES_BRASSAGE_E3(NON_TERMINE) 1.13_BYTPRF ESC_SE ESC_CENTRAL ;
ESC_SECONDAIRE ESC_NE WC_AILE_SUD WC_AILE_NORD
NTYPES = 1 : TAIR - air temperature of airnode
AIRNODES = TDA01 0.02_ACCUEIL 0.03_SAS_01 0.04_SAS_02 0.05_TDA02 0.06_SALLE_SERVEURS 0.07_TDA03_ACHATS 0.08_ARCHIVES 0.09_ERE03 0.10_ERE02 0.11_ERE01 0.12_CIRCUL_RDC 0.13_CAFETERIA 0.14_BUR_IND ;
0.15_STOCKAGE01 0.16_STOCKAGE02 0.17_LT 1.01_BUREAU_PIR 1.02_BUREAUX 1.03_BUREAU_ALY 1.04_VISIO_DG 1.05_ACCUEIL_DG 1.06_PALIER_NE_E1 1.07_ERE14 1.08_ERE13 1.09_DRH 1.10_BAIES_BRASSAGE_E1 ;
1.11_ERE12(NON_TERMINE) 1.12_SECRETARIAT_GAL 1.14_ERE11 1.15_CIRCUL_SE_E1 2.01_ERE24 2.02_IND&ENVIR 2.03_PALIER_NE_E1 2.04_ERE23(NON_TERMINE) 2.05_DT_STRUCT&EDP 2.06_COFFEE_CORNER 2.07_DT ;
2.08_ERE22(NON_TERMINE) 2.09_TRACEURS(NON_TERMINE) 2.10_FLUIDES_METHODES 2.11_ERE21(NON_TERMINE) 2.12_CIRCUL_SE_E2 2.13_BAIES_BRASSAGE(NON_TERMINE) 3.01_ERE34 3.02_CIRMAD_COMMERCES 3.03_PALIER_NE_E3 ;
3.04_ERE33(NON_TERMINE) 3.05_COMMERCES_OF 3.06_TRAVAUX01 3.07_ERE32 3.08_TRAVAUX02 3.09_ERE31(NON_TERMINE) 3.10_CIRCUL_SE_E3 3.11_BAIES_BRASSAGE_E3(NON_TERMINE) 1.13_BYTPRF ESC_SE ESC_CENTRAL ;
ESC_SECONDAIRE ESC_NE WC_AILE_SUD WC_AILE_NORD
NTYPES = 90 : THEAT - Set temperature heating
AIRNODES = TDA01 0.02_ACCUEIL 0.03_SAS_01 0.04_SAS_02 0.05_TDA02 0.06_SALLE_SERVEURS 0.07_TDA03_ACHATS 0.08_ARCHIVES 0.09_ERE03 0.10_ERE02 0.11_ERE01 0.12_CIRCUL_RDC 0.13_CAFETERIA 0.14_BUR_IND ;
0.15_STOCKAGE01 0.16_STOCKAGE02 0.17_LT 1.01_BUREAU_PIR 1.02_BUREAUX 1.03_BUREAU_ALY 1.04_VISIO_DG 1.05_ACCUEIL_DG 1.06_PALIER_NE_E1 1.07_ERE14 1.08_ERE13 1.09_DRH 1.10_BAIES_BRASSAGE_E1 ;
1.11_ERE12(NON_TERMINE) 1.12_SECRETARIAT_GAL 1.14_ERE11 1.15_CIRCUL_SE_E1 2.01_ERE24 2.02_IND&ENVIR 2.03_PALIER_NE_E1 2.04_ERE23(NON_TERMINE) 2.05_DT_STRUCT&EDP 2.06_COFFEE_CORNER 2.07_DT ;
2.08_ERE22(NON_TERMINE) 2.09_TRACEURS(NON_TERMINE) 2.10_FLUIDES_METHODES 2.11_ERE21(NON_TERMINE) 2.12_CIRCUL_SE_E2 2.13_BAIES_BRASSAGE(NON_TERMINE) 3.01_ERE34 3.02_CIRMAD_COMMERCES 3.03_PALIER_NE_E3 ;
3.04_ERE33(NON_TERMINE) 3.05_COMMERCES_OF 3.06_TRAVAUX01 3.07_ERE32 3.08_TRAVAUX02 3.09_ERE31(NON_TERMINE) 3.10_CIRCUL_SE_E3 3.11_BAIES_BRASSAGE_E3(NON_TERMINE) 1.13_BYTPRF ESC_SE ESC_CENTRAL ;
ESC_SECONDAIRE ESC_NE WC_AILE_SUD WC_AILE_NORD
NTYPES = 9 : RELHUM - relativ humidity of airnode air
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* E n d
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
END
_EXTENSION_WINPOOL_START_
WINDOW 4.1 DOE-2 Data File : Multi Band Calculation
Unit System : SI
Name : TRNSYS 15 WINDOW LIB
Desc : Einfachglas, 5.8
Window ID : 1001
Tilt : 90.0
Glazings : 1
Frame : 11 2.270
Spacer : 5 Class5 0.000 1.000 0.000
Total Height: 1219.2 mm
Total Width : 914.4 mm
Glass Height: 1079.5 mm
Glass Width : 774.7 mm
Mullion : None
Gap Thick Cond dCond Vis dVis Dens dDens Pr dPr
1 0 0 0 0 0 0 0 0 0
2 0 0 0 0 0 0 0 0 0
3 0 0 0 0 0 0 0 0 0
4 0 0 0 0 0 0 0 0 0
5 0 0 0 0 0 0 0 0 0
Angle 0 10 20 30 40 50 60 70 80 90 Hemis
Tsol 0.830 0.829 0.827 0.823 0.813 0.792 0.744 0.632 0.384 0.000 0.749
Abs1 0.095 0.096 0.098 0.101 0.105 0.109 0.114 0.117 0.114 0.000 0.106
Abs2 0 0 0 0 0 0 0 0 0 0 0
Abs3 0 0 0 0 0 0 0 0 0 0 0
Abs4 0 0 0 0 0 0 0 0 0 0 0
Abs5 0 0 0 0 0 0 0 0 0 0 0
Abs6 0 0 0 0 0 0 0 0 0 0 0
Rfsol 0.075 0.074 0.075 0.076 0.082 0.099 0.142 0.251 0.502 1.000 0.135
Rbsol 0.075 0.074 0.075 0.076 0.082 0.099 0.142 0.251 0.502 1.000 0.135
Tvis 0.901 0.901 0.900 0.897 0.890 0.871 0.824 0.706 0.441 0.000 0.823
Rfvis 0.081 0.081 0.082 0.083 0.090 0.108 0.155 0.271 0.536 1.000 0.146
Rbvis 0.081 0.081 0.082 0.083 0.090 0.108 0.155 0.271 0.536 1.000 0.146
SHGC 0.855 0.855 0.853 0.849 0.841 0.821 0.774 0.663 0.414 0.000 0.777
SC: 0.78
Layer ID# 9052 0 0 0 0 0
Tir 0.000 0 0 0 0 0
Emis F 0.840 0 0 0 0 0
Emis B 0.840 0 0 0 0 0
Thickness(mm) 4.0 0 0 0 0 0
Cond(W/m2-C ) 225.0 0 0 0 0 0
Spectral File None None None None None None
Overall and Center of Glass Ig U-values (W/m2-C)
Outdoor Temperature -17.8 C 15.6 C 26.7 C 37.8 C
Solar WdSpd hcout hrout hin
(W/m2) (m/s) (W/m2-C)
0 0.00 12.25 3.42 8.23 5.27 5.27 4.95 4.95 4.94 4.94 5.53 5.53
0 6.71 25.47 3.33 8.29 6.26 6.26 5.73 5.73 5.68 5.68 6.46 6.46
783 0.00 12.25 3.49 8.17 5.25 5.25 4.58 4.58 5.24 5.24 5.66 5.66
783 6.71 25.47 3.37 8.27 6.25 6.25 5.53 5.53 5.95 5.95 6.57 6.57
WINDOW 4.1 DOE-2 Data File : Multi Band Calculation
Unit System : SI
Name : TRNSYS 15 WINDOW LIB
Desc : Waermeschutzglas,Ar, 1.4 71/59
Window ID : 2001
Tilt : 90.0
Glazings : 2
Frame : 11 2.270
Spacer : 1 Class1 2.330 -0.010 0.138
Total Height: 1219.2 mm
Total Width : 914.4 mm
Glass Height: 1079.5 mm
Glass Width : 774.7 mm
Mullion : None
Gap Thick Cond dCond Vis dVis Dens dDens Pr dPr
1 Argon 16.0 0.01620 5.000 2.110 6.300 1.780 -0.0060 0.680 0.00066
2 0 0 0 0 0 0 0 0 0
3 0 0 0 0 0 0 0 0 0
4 0 0 0 0 0 0 0 0 0
5 0 0 0 0 0 0 0 0 0
Angle 0 10 20 30 40 50 60 70 80 90 Hemis
Tsol 0.426 0.428 0.422 0.413 0.402 0.380 0.333 0.244 0.113 0.000 0.354
Abs1 0.118 0.118 0.120 0.123 0.129 0.135 0.142 0.149 0.149 0.000 0.132
Abs2 0.190 0.192 0.198 0.201 0.200 0.199 0.199 0.185 0.117 0.000 0.191
Abs3 0 0 0 0 0 0 0 0 0 0 0
Abs4 0 0 0 0 0 0 0 0 0 0 0
Abs5 0 0 0 0 0 0 0 0 0 0 0
Abs6 0 0 0 0 0 0 0 0 0 0 0
Rfsol 0.266 0.262 0.260 0.262 0.269 0.286 0.326 0.422 0.621 1.000 0.314
Rbsol 0.215 0.209 0.207 0.210 0.219 0.237 0.272 0.356 0.560 0.999 0.260
Tvis 0.706 0.710 0.701 0.688 0.670 0.635 0.556 0.403 0.188 0.000 0.590
Rfvis 0.121 0.115 0.114 0.118 0.132 0.163 0.228 0.376 0.649 1.000 0.203
Rbvis 0.103 0.096 0.093 0.096 0.108 0.132 0.179 0.286 0.520 0.999 0.162
SHGC 0.589 0.593 0.591 0.586 0.574 0.551 0.505 0.405 0.218 0.000 0.518
SC: 0.55
Layer ID# 9052 9065 0 0 0 0
Tir 0.000 0.000 0 0 0 0
Emis F 0.840 0.140 0 0 0 0
Emis B 0.840 0.840 0 0 0 0
Thickness(mm) 4.0 4.0 0 0 0 0
Cond(W/m2-C ) 225.0 225.0 0 0 0 0
Spectral File None None None None None None
Overall and Center of Glass Ig U-values (W/m2-C)
Outdoor Temperature -17.8 C 15.6 C 26.7 C 37.8 C
Solar WdSpd hcout hrout hin
(W/m2) (m/s) (W/m2-C)
0 0.00 12.25 3.25 7.62 1.54 1.54 1.31 1.31 1.35 1.35 1.47 1.47
0 6.71 25.47 3.21 7.64 1.62 1.62 1.36 1.36 1.40 1.40 1.53 1.53
783 0.00 12.25 3.39 7.99 1.69 1.69 1.54 1.54 1.51 1.51 1.54 1.54
783 6.71 25.47 3.30 7.81 1.79 1.79 1.63 1.63 1.58 1.58 1.59 1.59
WINDOW 4.1 DOE-2 Data File : Multi Band Calculation
Unit System : SI
Name : TRNSYS15 WINDOW LIB
Desc : Saint Gobain CLIMAPLUS FUTUR AR 1.1 4/15/4
Window ID : 13002
Tilt : 90.0
Glazings : 2
Frame : 11 TRNSYS WIN - 1 2.270
Spacer : 1 Class1 2.330 -0.010 0.138
Total Height: 1600.0 mm
Total Width : 1250.0 mm
Glass Height: 1460.3 mm
Glass Width : 1110.3 mm
Mullion : None
Gap Thick Cond dCond Vis dVis Dens dDens Pr dPr
1 Argon 15.0 0.01620 5.000 2.110 6.300 1.780 -0.0060 0.680 0.00066
2 0 0 0 0 0 0 0 0 0
3 0 0 0 0 0 0 0 0 0
4 0 0 0 0 0 0 0 0 0
5 0 0 0 0 0 0 0 0 0
Angle 0 10 20 30 40 50 60 70 80 90 Hemis
Tsol 0.521 0.524 0.517 0.508 0.495 0.472 0.418 0.312 0.153 0.000 0.439
Abs1 0.022 0.022 0.023 0.023 0.025 0.026 0.027 0.029 0.031 0.000 0.025
Abs2 0.102 0.104 0.112 0.117 0.119 0.123 0.135 0.142 0.105 0.000 0.121
Abs3 0 0 0 0 0 0 0 0 0 0 0
Abs4 0 0 0 0 0 0 0 0 0 0 0
Abs5 0 0 0 0 0 0 0 0 0 0 0
Abs6 0 0 0 0 0 0 0 0 0 0 0
Rfsol 0.355 0.350 0.349 0.352 0.361 0.379 0.420 0.517 0.711 1.000 0.404
Rbsol 0.295 0.289 0.287 0.290 0.299 0.316 0.350 0.430 0.616 0.999 0.337
Tvis 0.782 0.787 0.776 0.763 0.744 0.705 0.618 0.450 0.212 0.000 0.655
Rfvis 0.131 0.124 0.123 0.127 0.142 0.173 0.239 0.388 0.664 1.000 0.214
Rbvis 0.138 0.131 0.128 0.131 0.144 0.169 0.218 0.325 0.551 0.999 0.198
SHGC 0.609 0.613 0.613 0.609 0.598 0.578 0.534 0.435 0.244 0.000 0.544
SC: 0.60
Layer ID# 4054 7202 0 0 0 0
Tir 0.000 0.000 0 0 0 0
Emis F 0.840 0.040 0 0 0 0
Emis B 0.840 0.840 0 0 0 0
Thickness(mm) 4.0 4.0 0 0 0 0
Cond(W/m2-C ) 225.0 225.0 0 0 0 0
Spectral File None None None None None None
Overall and Center of Glass Ig U-values (W/m2-C)
Outdoor Temperature -17.8 C 15.6 C 26.7 C 37.8 C
Solar WdSpd hcout hrout hin
(W/m2) (m/s) (W/m2-C)
0 0.00 12.25 3.23 7.55 1.32 1.32 1.05 1.05 1.07 1.07 1.16 1.16
0 6.71 25.47 3.21 7.57 1.39 1.39 1.08 1.08 1.10 1.10 1.20 1.20
783 0.00 12.25 3.28 6.91 1.38 1.38 1.15 1.15 1.13 1.13 1.16 1.16
783 6.71 25.47 3.23 6.66 1.45 1.45 1.20 1.20 1.16 1.16 1.19 1.19
WINDOW 4.1 DOE-2 Data File : Multi Band Calculation
Unit System : SI
Name : TRNSYS15 WINDOW LIB
Desc : Saint Gobain PLANISOL Neutral 6242 6/16/6
Window ID : 13010
Tilt : 90.0
Glazings : 2
Frame : 11 TRNSYS WIN - 1 2.270
Spacer : 1 Class1 2.330 -0.010 0.138
Total Height: 1600.0 mm
Total Width : 1250.0 mm
Glass Height: 1460.3 mm
Glass Width : 1110.3 mm
Mullion : None
Gap Thick Cond dCond Vis dVis Dens dDens Pr dPr
1 Argon 16.0 0.01620 5.000 2.110 6.300 1.780 -0.0060 0.680 0.00066
2 0 0 0 0 0 0 0 0 0
3 0 0 0 0 0 0 0 0 0
4 0 0 0 0 0 0 0 0 0
5 0 0 0 0 0 0 0 0 0
Angle 0 10 20 30 40 50 60 70 80 90 Hemis
Tsol 0.355 0.357 0.351 0.344 0.333 0.314 0.274 0.200 0.091 0.000 0.293
Abs1 0.298 0.301 0.308 0.313 0.313 0.316 0.327 0.333 0.272 0.001 0.311
Abs2 0.063 0.064 0.064 0.065 0.066 0.067 0.065 0.057 0.041 0.000 0.062
Abs3 0 0 0 0 0 0 0 0 0 0 0
Abs4 0 0 0 0 0 0 0 0 0 0 0
Abs5 0 0 0 0 0 0 0 0 0 0 0
Abs6 0 0 0 0 0 0 0 0 0 0 0
Rfsol 0.284 0.278 0.276 0.279 0.288 0.303 0.334 0.410 0.596 0.999 0.323
Rbsol 0.268 0.264 0.262 0.262 0.267 0.281 0.315 0.402 0.591 1.000 0.307
Tvis 0.613 0.617 0.608 0.597 0.581 0.550 0.480 0.348 0.161 0.000 0.511
Rfvis 0.178 0.172 0.169 0.172 0.183 0.204 0.245 0.340 0.553 0.999 0.230
Rbvis 0.119 0.113 0.112 0.116 0.130 0.159 0.223 0.367 0.634 1.000 0.199
SHGC 0.424 0.427 0.421 0.415 0.405 0.387 0.346 0.266 0.140 0.000 0.362
SC: 0.43
Layer ID# 7209 4048 0 0 0 0
Tir 0.000 0.000 0 0 0 0
Emis F 0.840 0.840 0 0 0 0
Emis B 0.040 0.840 0 0 0 0
Thickness(mm) 6.0 6.0 0 0 0 0
Cond(W/m2-C ) 150.0 150.0 0 0 0 0
Spectral File None None None None None None
Overall and Center of Glass Ig U-values (W/m2-C)
Outdoor Temperature -17.8 C 15.6 C 26.7 C 37.8 C
Solar WdSpd hcout hrout hin
(W/m2) (m/s) (W/m2-C)
0 0.00 12.25 3.24 7.55 1.32 1.32 1.00 1.00 1.02 1.02 1.14 1.14
0 6.71 25.47 3.21 7.57 1.39 1.39 1.03 1.03 1.05 1.05 1.18 1.18
783 0.00 12.25 3.51 6.87 1.26 1.26 1.06 1.06 1.13 1.13 1.31 1.31
783 6.71 25.47 3.36 6.13 1.33 1.33 1.08 1.08 1.12 1.12 1.26 1.26
WINDOW 4.1 DOE-2 Data File : Multi Band Calculation
Unit System : SI
Name : TRNSYS15 WINDOW LIB
Desc : Saint Gobain PLANISOL Gruen 4024 6/16/6
Window ID : 13013
Tilt : 90.0
Glazings : 2
Frame : 11 TRNSYS WIN - 1 2.270
Spacer : 1 Class1 2.330 -0.010 0.138
Total Height: 1600.0 mm
Total Width : 1250.0 mm
Glass Height: 1460.3 mm
Glass Width : 1110.3 mm
Mullion : None
Gap Thick Cond dCond Vis dVis Dens dDens Pr dPr
1 Argon 16.0 0.01620 5.000 2.110 6.300 1.780 -0.0060 0.680 0.00066
2 0 0 0 0 0 0 0 0 0
3 0 0 0 0 0 0 0 0 0
4 0 0 0 0 0 0 0 0 0
5 0 0 0 0 0 0 0 0 0
Angle 0 10 20 30 40 50 60 70 80 90 Hemis
Tsol 0.193 0.194 0.191 0.187 0.181 0.170 0.148 0.108 0.049 0.000 0.159
Abs1 0.669 0.675 0.679 0.680 0.675 0.667 0.656 0.613 0.450 0.001 0.645
Abs2 0.034 0.035 0.035 0.035 0.036 0.036 0.035 0.031 0.022 0.000 0.034
Abs3 0 0 0 0 0 0 0 0 0 0 0
Abs4 0 0 0 0 0 0 0 0 0 0 0
Abs5 0 0 0 0 0 0 0 0 0 0 0
Abs6 0 0 0 0 0 0 0 0 0 0 0
Rfsol 0.104 0.097 0.095 0.098 0.108 0.126 0.160 0.249 0.480 0.999 0.152
Rbsol 0.229 0.224 0.223 0.224 0.230 0.246 0.285 0.381 0.582 1.000 0.275
Tvis 0.399 0.401 0.396 0.388 0.378 0.357 0.312 0.225 0.103 0.000 0.332
Rfvis 0.126 0.119 0.117 0.120 0.131 0.150 0.186 0.277 0.503 0.999 0.176
Rbvis 0.096 0.089 0.088 0.093 0.107 0.138 0.204 0.354 0.629 1.000 0.179
SHGC 0.265 0.267 0.264 0.261 0.255 0.244 0.221 0.173 0.095 0.000 0.229
SC: 0.28
Layer ID# 7212 4048 0 0 0 0
Tir 0.000 0.000 0 0 0 0
Emis F 0.840 0.840 0 0 0 0
Emis B 0.070 0.840 0 0 0 0
Thickness(mm) 6.0 6.0 0 0 0 0
Cond(W/m2-C ) 150.0 150.0 0 0 0 0
Spectral File None None None None None None
Overall and Center of Glass Ig U-values (W/m2-C)
Outdoor Temperature -17.8 C 15.6 C 26.7 C 37.8 C
Solar WdSpd hcout hrout hin
(W/m2) (m/s) (W/m2-C)
0 0.00 12.25 3.24 7.57 1.38 1.38 1.10 1.10 1.13 1.13 1.24 1.24
0 6.71 25.47 3.21 7.60 1.46 1.46 1.13 1.13 1.16 1.16 1.28 1.28
783 0.00 12.25 3.85 7.12 1.13 1.13 1.39 1.39 1.52 1.52 1.64 1.64
783 6.71 25.47 3.55 6.36 1.29 1.29 1.24 1.24 1.39 1.39 1.57 1.57
*** END OF LIBRARY ***
***************************************************************************************************
*WinID Description Design U-Value g-value T-sol Rf-sol T-vis
***************************************************************************************************
1001 Einfachglas, 5.8 4 5.68 0.855 0.83 0.075 0.901
2001 Waermeschutzglas,Ar, 1.4 71/59 4/16/4 1.4 0.589 0.426 0.266 0.706
13002 Saint Gobain CLIMAPLUS FUTUR AR 1.1 4/15/4 4/15/4 1.1 0.609 0.521 0.355 0.782
13010 Saint Gobain PLANISOL Neutral 6242 6/16/6 6/16/6 1.05 0.424 0.355 0.284 0.613
13013 Saint Gobain PLANISOL Gruen 4024 6/16/6 6/16/6 1.16 0.265 0.193 0.104 0.399
_EXTENSION_WINPOOL_END_
_EXTENSION_BuildingGeometry_START_
_EXTENSION_BuildingGeometry_END_
_EXTENSION_ExternalShadingGeometry_START_
_EXTENSION_ExternalShadingGeometry_END_
_EXTENSION_GeoPositionGeometry_START_
_EXTENSION_GeoPositionGeometry_END_
***** WALL TRANSFERFUNCTION CALCULATIONS *****
---------- WALL TYPE PB_TP ----------
THERMAL CONDUCTANCE, U= 1.18508 kJ/h m2K; U-Wert= 0.31174 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 4.4646923E+00 3.1470048E-05 1.4520543E+02 1.0000000E+00
1 -8.3776512E+00 1.2340246E-02 -2.7286890E+02 -1.2916847E+00
2 4.9973492E+00 7.1756150E-02 1.6025554E+02 4.5223703E-01
3 -1.0080896E+00 5.2003885E-02 -3.4407364E+01 -4.1198618E-02
4 6.6928323E-02 6.1392934E-03 1.9885724E+00 7.8784962E-04
5 -8.5511362E-04 1.0417530E-04 -3.0942482E-02 -1.3856503E-06
6 1.3765606E-06 1.8221895E-07 3.9419178E-05
SUM 1.4237540E-01 1.4237540E-01 1.4237541E-01 1.2014017E-01
---------- WALL TYPE MEXT_PEUPLIER ----------
THERMAL CONDUCTANCE, U= 1.19620 kJ/h m2K; U-Wert= 0.31451 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 2.0962769E+01 7.4076232E-06 1.4520622E+02 1.0000000E+00
1 -4.4819089E+01 6.0736590E-03 -2.7108639E+02 -1.2810393E+00
2 3.0369757E+01 4.9099691E-02 1.5620739E+02 4.2317184E-01
3 -6.8995564E+00 4.9328161E-02 -3.2876517E+01 -4.8654925E-02
4 5.1094971E-01 9.0287328E-03 2.7397117E+00 1.7056964E-03
5 -1.1065554E-02 2.9864935E-04 -7.7147787E-02 -1.6944348E-05
6 7.3230548E-05 1.3715518E-06 5.6949813E-04
7 -2.5175449E-08 5.2227686E-10 -1.5378786E-07
SUM 1.1383767E-01 1.1383767E-01 1.1383767E-01 9.5166382E-02
---------- WALL TYPE MINT_LEGER ----------
THERMAL CONDUCTANCE, U= 9.00000 kJ/h m2K; U-Wert= 1.75439 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 3.0277997E+01 9.5984825E-01 3.0277997E+01 1.0000000E+00
1 -2.7982590E+01 4.1783755E+00 -2.7982590E+01 -3.4127616E-01
2 3.6931626E+00 8.2086579E-01 3.6931626E+00 3.8966463E-03
3 -2.4988201E-02 4.4931281E-03 -2.4988201E-02 -1.7751618E-07
4 8.1684104E-07 1.1099971E-07 8.1684104E-07
SUM 5.9635828E+00 5.9635828E+00 5.9635828E+00 6.6262031E-01
---------- WALL TYPE TOITURE ----------
THERMAL CONDUCTANCE, U= 0.70158 kJ/h m2K; U-Wert= 0.18863 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 6.5592801E+01 2.4757424E-05 1.4520541E+02 1.0000000E+00
1 -1.3934643E+02 9.9198904E-03 -2.5115176E+02 -1.1420683E+00
2 9.3817565E+01 5.4591464E-02 1.2734657E+02 3.1379294E-01
3 -2.1363036E+01 3.6339264E-02 -2.2253553E+01 -2.2538061E-02
4 1.4125088E+00 3.8481604E-03 9.6439992E-01 1.6710523E-04
5 -8.6372939E-03 5.9858934E-05 -6.2911889E-03 -3.3771482E-07
6 1.2003638E-05 1.2055536E-07 1.0685143E-05
SUM 1.0478352E-01 1.0478352E-01 1.0478352E-01 1.4935333E-01
---------- WALL TYPE MEXT_TERRE_CUITE ----------
THERMAL CONDUCTANCE, U= 1.25894 kJ/h m2K; U-Wert= 0.33008 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 6.6322019E+01 4.0146547E-05 1.4520622E+02 1.0000000E+00
1 -1.4217032E+02 1.4150431E-02 -2.5437110E+02 -1.1659251E+00
2 9.4823976E+01 7.2728469E-02 1.2742617E+02 2.9240415E-01
3 -2.0008994E+01 4.4874818E-02 -1.9020422E+01 -1.8571430E-02
4 1.1843188E+00 4.3016132E-03 9.0346153E-01 2.4075775E-04
5 -1.4856103E-02 5.6946127E-05 -8.1894038E-03 -1.5214406E-07
6 6.2596307E-06 7.8511951E-08 4.4665400E-06
SUM 1.3615250E-01 1.3615250E-01 1.3615250E-01 1.0814818E-01
---------- WALL TYPE MINT_LOURD ----------
THERMAL CONDUCTANCE, U= 41.40000 kJ/h m2K; U-Wert= 3.89171 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 1.4520706E+02 3.5784834E+00 1.4520706E+02 1.0000000E+00
1 -1.3953195E+02 1.8129768E+01 -1.3953195E+02 -3.7696082E-01
2 2.0566222E+01 4.3028953E+00 2.0566222E+01 6.0894239E-03
3 -1.9544317E-01 3.4749679E-02 -1.9544317E-01 -6.1584681E-07
4 1.4170016E-05 1.9223051E-06 1.4170016E-05
SUM 2.6045899E+01 2.6045899E+01 2.6045899E+01 6.2912799E-01
---------- WALL TYPE PLANCHER_INTERMEDIAI----------
THERMAL CONDUCTANCE, U= 41.40000 kJ/h m2K; U-Wert= 3.89171 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 1.4520706E+02 3.5784834E+00 1.4520706E+02 1.0000000E+00
1 -1.3953195E+02 1.8129768E+01 -1.3953195E+02 -3.7696082E-01
2 2.0566222E+01 4.3028953E+00 2.0566222E+01 6.0894239E-03
3 -1.9544317E-01 3.4749679E-02 -1.9544317E-01 -6.1584681E-07
4 1.4170016E-05 1.9223051E-06 1.4170016E-05
SUM 2.6045899E+01 2.6045899E+01 2.6045899E+01 6.2912799E-01
---------- WALL TYPE PLH_SDR ----------
THERMAL CONDUCTANCE, U= 0.85999 kJ/h m2K; U-Wert= 0.22956 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 5.6271137E+00 2.6261637E-01 2.1771940E+00 1.0000000E+00
1 -5.4525547E+00 4.5501683E-01 -1.5176608E+00 -1.4057774E-01
2 5.6478955E-01 2.1506293E-02 7.9628472E-02 5.4154096E-05
3 -2.0554420E-04 3.4354343E-06 -1.8723296E-05
SUM 7.3914292E-01 7.3914292E-01 7.3914292E-01 8.5947641E-01
---------- WALL TYPE CBR_B11 ----------
THERMAL CONDUCTANCE, U= 1.75439 kJ/h m2K; U-Wert= 0.45005 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 1.7543860E+00 1.7543860E+00 1.7543860E+00 1.0000000E+00
SUM 1.7543860E+00 1.7543860E+00 1.7543860E+00 1.0000000E+00
---------- WALL TYPE CBR_I21 ----------
THERMAL CONDUCTANCE, U= 0.14409 kJ/h m2K; U-Wert= 0.03976 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 1.4409222E-01 1.4409222E-01 1.4409222E-01 1.0000000E+00
SUM 1.4409222E-01 1.4409222E-01 1.4409222E-01 1.0000000E+00
---------- WALL TYPE MINT_LNC ----------
THERMAL CONDUCTANCE, U= 1.15675 kJ/h m2K; U-Wert= 0.30468 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 4.4094546E+00 2.7010018E-05 1.4520543E+02 1.0000000E+00
1 -8.3251415E+00 1.1315779E-02 -2.7453170E+02 -1.3031348E+00
2 5.0118488E+00 6.7951864E-02 1.6285228E+02 4.6340000E-01
3 -1.0284477E+00 5.0857231E-02 -3.5461470E+01 -4.3126006E-02
4 6.9752753E-02 6.2524028E-03 2.1065817E+00 8.7987252E-04
5 -9.5179098E-04 1.1229462E-04 -3.4651706E-02 -1.6008440E-06
6 1.5804999E-06 2.1295301E-07 4.6019109E-05
SUM 1.3651679E-01 1.3651679E-01 1.3651680E-01 1.1801750E-01
---------- WALL TYPE CBR_MEN ----------
THERMAL CONDUCTANCE, U= 0.57604 kJ/h m2K; U-Wert= 0.15577 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 5.7603689E-01 5.7603689E-01 5.7603689E-01 1.0000000E+00
SUM 5.7603689E-01 5.7603689E-01 5.7603689E-01 1.0000000E+00
---------- WALL TYPE CBR_H11 ----------
THERMAL CONDUCTANCE, U= 0.21598 kJ/h m2K; U-Wert= 0.05939 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 2.1598272E-01 2.1598272E-01 2.1598272E-01 1.0000000E+00
SUM 2.1598272E-01 2.1598272E-01 2.1598272E-01 1.0000000E+00
---------- WALL TYPE CBR_H31 ----------
THERMAL CONDUCTANCE, U= 0.10799 kJ/h m2K; U-Wert= 0.02985 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 1.0799136E-01 1.0799136E-01 1.0799136E-01 1.0000000E+00
SUM 1.0799136E-01 1.0799136E-01 1.0799136E-01 1.0000000E+00
---------- WALL TYPE CBR_H11_TOITURE ----------
THERMAL CONDUCTANCE, U= 1.11111 kJ/h m2K; U-Wert= 0.29326 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 1.1111111E+00 1.1111111E+00 1.1111111E+00 1.0000000E+00
SUM 1.1111111E+00 1.1111111E+00 1.1111111E+00 1.0000000E+00
---------- WALL TYPE PL_LNC ----------
THERMAL CONDUCTANCE, U= 0.91276 kJ/h m2K; U-Wert= 0.24307 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 3.1594976E+00 5.1345858E-05 1.4520542E+02 1.0000000E+00
1 -5.7074277E+00 1.3654213E-02 -2.6293293E+02 -1.2232266E+00
2 3.2182692E+00 6.5388335E-02 1.4496165E+02 3.8729393E-01
3 -5.8246761E-01 3.8894356E-02 -2.8503512E+01 -3.1227836E-02
4 3.3998756E-02 3.5637496E-03 1.4054852E+00 3.7768032E-04
5 -2.7639413E-04 4.2180675E-05 -1.4537573E-02 -5.6405917E-07
6 3.7590737E-07 4.4311288E-08 1.5379833E-05
SUM 1.2159422E-01 1.2159422E-01 1.2159423E-01 1.3321658E-01
---------- WALL TYPE CLOISON_VIDE_INT ----------
THERMAL CONDUCTANCE, U= 18.00000 kJ/h m2K; U-Wert= 2.70270 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 3.1237845E+01 1.1428821E+01 3.1237845E+01 1.0000000E+00
1 -1.3511476E+01 6.3421799E+00 -1.3511476E+01 -1.1780374E-02
2 6.1583658E-02 1.6952099E-02 6.1583658E-02
SUM 1.7787953E+01 1.7787953E+01 1.7787953E+01 9.8821963E-01
************* REQUIRED INPUTS *************
*:InpNR | Label | UNIT | INPUT DESCRIPTION | Old label
* | 1 | TAMB | C | AMBIENT TEMPERATURE | TAMB
* | 2 | RELHUMAMB | % | RELATIVE AMBIENT HUMIDITY | ARELHUM
* | 3 | TSKY | C | FIKTIVE SKY TEMPERATURE | TSKY
* | 4 | TSGRD | C | GROUND TEMPERATURE | TGRD
* | 5 | AZEN | degrees | SOLAR ZENITH ANGLE | AZEN
* | 6 | AAZM | degrees | SOLAR AZIMUTH ANGLE | AAZM
* | 7 | IT_H_0_0 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION H_0_0 | ITH_0_0
* | 8 | IT_SO | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION SO | ITSO
* | 9 | IT_SE | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION SE | ITSE
* | 10 | IT_NE | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION NE | ITNE
* | 11 | IT_NO | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION NO | ITNO
* | 12 | IT_M1_RDC | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M1_RDC | ITM1_RDC
* | 13 | IT_M2_RDC | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M2_RDC | ITM2_RDC
* | 14 | IT_M3_RDC | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M3_RDC | ITM3_RDC
* | 15 | IT_M4_RDC | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M4_RDC | ITM4_RDC
* | 16 | IT_M5_RDC | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M5_RDC | ITM5_RDC
* | 17 | IT_M6_RDC | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M6_RDC | ITM6_RDC
* | 18 | IT_M7_RDC | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M7_RDC | ITM7_RDC
* | 19 | IT_M1_E1 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M1_E1 | ITM1_E1
* | 20 | IT_M2_E1 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M2_E1 | ITM2_E1
* | 21 | IT_M3_E1 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M3_E1 | ITM3_E1
* | 22 | IT_M4_E1 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M4_E1 | ITM4_E1
* | 23 | IT_M5_E1 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M5_E1 | ITM5_E1
* | 24 | IT_M6_E1 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M6_E1 | ITM6_E1
* | 25 | IT_M7_E1 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M7_E1 | ITM7_E1
* | 26 | IT_M8_E1 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M8_E1 | ITM8_E1
* | 27 | IT_M9_E1 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M9_E1 | ITM9_E1
* | 28 | IT_M10_E1 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M10_E1 | ITM10_E1
* | 29 | IT_M1_E2 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M1_E2 | ITM1_E2
* | 30 | IT_M2_E2 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M2_E2 | ITM2_E2
* | 31 | IT_M3_E2 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M3_E2 | ITM3_E2
* | 32 | IT_M4_E2 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M4_E2 | ITM4_E2
* | 33 | IT_M5_E2 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M5_E2 | ITM5_E2
* | 34 | IT_M6_E2 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M6_E2 | ITM6_E2
* | 35 | IT_M7_E2 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M7_E2 | ITM7_E2
* | 36 | IT_M8_E2 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M8_E2 | ITM8_E2
* | 37 | IT_M9_E2 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M9_E2 | ITM9_E2
* | 38 | IT_M1_E3 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M1_E3 | ITM1_E3
* | 39 | IT_M2_E3 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M2_E3 | ITM2_E3
* | 40 | IT_M3_E3 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M3_E3 | ITM3_E3
* | 41 | IT_M4_E3 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M4_E3 | ITM4_E3
* | 42 | IT_M5_E3 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M5_E3 | ITM5_E3
* | 43 | IT_M6_E3 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M6_E3 | ITM6_E3
* | 44 | IT_M7_E3 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M7_E3 | ITM7_E3
* | 45 | IT_M8_E3 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M8_E3 | ITM8_E3
* | 46 | IT_M9_E3 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION M9_E3 | ITM9_E3
* | 47 | IB_H_0_0 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION H_0_0 | IBH_0_0
* | 48 | IB_SO | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION SO | IBSO
* | 49 | IB_SE | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION SE | IBSE
* | 50 | IB_NE | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION NE | IBNE
* | 51 | IB_NO | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION NO | IBNO
* | 52 | IB_M1_RDC | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M1_RDC | IBM1_RDC
* | 53 | IB_M2_RDC | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M2_RDC | IBM2_RDC
* | 54 | IB_M3_RDC | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M3_RDC | IBM3_RDC
* | 55 | IB_M4_RDC | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M4_RDC | IBM4_RDC
* | 56 | IB_M5_RDC | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M5_RDC | IBM5_RDC
* | 57 | IB_M6_RDC | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M6_RDC | IBM6_RDC
* | 58 | IB_M7_RDC | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M7_RDC | IBM7_RDC
* | 59 | IB_M1_E1 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M1_E1 | IBM1_E1
* | 60 | IB_M2_E1 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M2_E1 | IBM2_E1
* | 61 | IB_M3_E1 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M3_E1 | IBM3_E1
* | 62 | IB_M4_E1 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M4_E1 | IBM4_E1
* | 63 | IB_M5_E1 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M5_E1 | IBM5_E1
* | 64 | IB_M6_E1 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M6_E1 | IBM6_E1
* | 65 | IB_M7_E1 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M7_E1 | IBM7_E1
* | 66 | IB_M8_E1 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M8_E1 | IBM8_E1
* | 67 | IB_M9_E1 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M9_E1 | IBM9_E1
* | 68 | IB_M10_E1 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M10_E1 | IBM10_E1
* | 69 | IB_M1_E2 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M1_E2 | IBM1_E2
* | 70 | IB_M2_E2 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M2_E2 | IBM2_E2
* | 71 | IB_M3_E2 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M3_E2 | IBM3_E2
* | 72 | IB_M4_E2 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M4_E2 | IBM4_E2
* | 73 | IB_M5_E2 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M5_E2 | IBM5_E2
* | 74 | IB_M6_E2 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M6_E2 | IBM6_E2
* | 75 | IB_M7_E2 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M7_E2 | IBM7_E2
* | 76 | IB_M8_E2 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M8_E2 | IBM8_E2
* | 77 | IB_M9_E2 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M9_E2 | IBM9_E2
* | 78 | IB_M1_E3 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M1_E3 | IBM1_E3
* | 79 | IB_M2_E3 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M2_E3 | IBM2_E3
* | 80 | IB_M3_E3 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M3_E3 | IBM3_E3
* | 81 | IB_M4_E3 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M4_E3 | IBM4_E3
* | 82 | IB_M5_E3 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M5_E3 | IBM5_E3
* | 83 | IB_M6_E3 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M6_E3 | IBM6_E3
* | 84 | IB_M7_E3 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M7_E3 | IBM7_E3
* | 85 | IB_M8_E3 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M8_E3 | IBM8_E3
* | 86 | IB_M9_E3 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION M9_E3 | IBM9_E3
* | 87 | AI_H_0_0 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION H_0_0 | AIH_0_0
* | 88 | AI_SO | degrees | ANGLE OF INCIDENCE FOR ORIENTATION SO | AISO
* | 89 | AI_SE | degrees | ANGLE OF INCIDENCE FOR ORIENTATION SE | AISE
* | 90 | AI_NE | degrees | ANGLE OF INCIDENCE FOR ORIENTATION NE | AINE
* | 91 | AI_NO | degrees | ANGLE OF INCIDENCE FOR ORIENTATION NO | AINO
* | 92 | AI_M1_RDC | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M1_RDC | AIM1_RDC
* | 93 | AI_M2_RDC | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M2_RDC | AIM2_RDC
* | 94 | AI_M3_RDC | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M3_RDC | AIM3_RDC
* | 95 | AI_M4_RDC | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M4_RDC | AIM4_RDC
* | 96 | AI_M5_RDC | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M5_RDC | AIM5_RDC
* | 97 | AI_M6_RDC | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M6_RDC | AIM6_RDC
* | 98 | AI_M7_RDC | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M7_RDC | AIM7_RDC
* | 99 | AI_M1_E1 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M1_E1 | AIM1_E1
* | 100 | AI_M2_E1 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M2_E1 | AIM2_E1
* | 101 | AI_M3_E1 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M3_E1 | AIM3_E1
* | 102 | AI_M4_E1 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M4_E1 | AIM4_E1
* | 103 | AI_M5_E1 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M5_E1 | AIM5_E1
* | 104 | AI_M6_E1 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M6_E1 | AIM6_E1
* | 105 | AI_M7_E1 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M7_E1 | AIM7_E1
* | 106 | AI_M8_E1 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M8_E1 | AIM8_E1
* | 107 | AI_M9_E1 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M9_E1 | AIM9_E1
* | 108 | AI_M10_E1 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M10_E1 | AIM10_E1
* | 109 | AI_M1_E2 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M1_E2 | AIM1_E2
* | 110 | AI_M2_E2 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M2_E2 | AIM2_E2
* | 111 | AI_M3_E2 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M3_E2 | AIM3_E2
* | 112 | AI_M4_E2 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M4_E2 | AIM4_E2
* | 113 | AI_M5_E2 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M5_E2 | AIM5_E2
* | 114 | AI_M6_E2 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M6_E2 | AIM6_E2
* | 115 | AI_M7_E2 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M7_E2 | AIM7_E2
* | 116 | AI_M8_E2 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M8_E2 | AIM8_E2
* | 117 | AI_M9_E2 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M9_E2 | AIM9_E2
* | 118 | AI_M1_E3 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M1_E3 | AIM1_E3
* | 119 | AI_M2_E3 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M2_E3 | AIM2_E3
* | 120 | AI_M3_E3 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M3_E3 | AIM3_E3
* | 121 | AI_M4_E3 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M4_E3 | AIM4_E3
* | 122 | AI_M5_E3 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M5_E3 | AIM5_E3
* | 123 | AI_M6_E3 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M6_E3 | AIM6_E3
* | 124 | AI_M7_E3 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M7_E3 | AIM7_E3
* | 125 | AI_M8_E3 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M8_E3 | AIM8_E3
* | 126 | AI_M9_E3 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION M9_E3 | AIM9_E3
* | 127 | GRDREF | - | GROUND REFLECTION FOR SKY DIFFUSE RADIATION SHADING | GRDREF
* | 128 | CNAT_1 | any | INPUT | CNAT_1
* | 129 | T_COOL_ON | any | INPUT | T_COOL_ON
* | 130 | MS_N_180_90 | any | INPUT | MS_N_180_9
* | 131 | MS_S_0_90 | any | INPUT | MS_S_0_90
* | 132 | MS_E_270_90 | any | INPUT | MS_E_270_9
* | 133 | MS_W_90_90 | any | INPUT | MS_W_90_90
* | 134 | BRIGHT | any | INPUT | BRIGHT
* | 135 | INPUT001 | any | INPUT | INPUT001
* | 136 | TEMP_SOL | any | INPUT | TEMP_SOL
* | 137 | SCEN_FROID_0.01 | any | INPUT | SCEN_FROID
* | 138 | SCEN_CHAUD_0.01 | any | INPUT | SCEN_CHAUD
* | 139 | TSOUFFLAGE_CTA | any | INPUT | TSOUFFLAGE
* | 140 | HR_SOUFFLAGE | any | INPUT | HR_SOUFFLA
* | 141 | 0.01_DEM_CHAUD | any | INPUT | 0.01_DEM_C
* | 142 | 0.02_DEM_CHAUD | any | INPUT | 0.02_DEM_C
************* DESIRED OUTPUTS *************
*:OutNr | Label | Unit | ZNr | Airnode | SurfNr| OUTPUT DESCRIPTION | old label
* | 1 | TAIR_TDA01 | C | 1 | TDA01 | | air temperature of airnode | TAIR 1
* | 2 | TAIR_0.02_ACCUEIL | C | 2 | 0.02_ACCUEIL | | air temperature of airnode | TAIR 2
* | 3 | TAIR_0.03_SAS_01 | C | 3 | 0.03_SAS_01 | | air temperature of airnode | TAIR 3
* | 4 | TAIR_0.04_SAS_02 | C | 4 | 0.04_SAS_02 | | air temperature of airnode | TAIR 4
* | 5 | TAIR_0.05_TDA02 | C | 5 | 0.05_TDA02 | | air temperature of airnode | TAIR 5
* | 6 | TAIR_0.06_SALLE_SERVEURS | C | 6 | 0.06_SALLE_SERVEURS | | air temperature of airnode | TAIR 6
* | 7 | TAIR_0.07_TDA03_ACHATS | C | 7 | 0.07_TDA03_ACHATS | | air temperature of airnode | TAIR 7
* | 8 | TAIR_0.08_ARCHIVES | C | 8 | 0.08_ARCHIVES | | air temperature of airnode | TAIR 8
* | 9 | TAIR_0.09_ERE03 | C | 9 | 0.09_ERE03 | | air temperature of airnode | TAIR 9
* | 10 | TAIR_0.10_ERE02 | C | 10 | 0.10_ERE02 | | air temperature of airnode | TAIR 10
* | 11 | TAIR_0.11_ERE01 | C | 11 | 0.11_ERE01 | | air temperature of airnode | TAIR 11
* | 12 | TAIR_0.12_CIRCUL_RDC | C | 12 | 0.12_CIRCUL_RDC | | air temperature of airnode | TAIR 12
* | 13 | TAIR_0.13_CAFETERIA | C | 13 | 0.13_CAFETERIA | | air temperature of airnode | TAIR 13
* | 14 | TAIR_0.14_BUR_IND | C | 14 | 0.14_BUR_IND | | air temperature of airnode | TAIR 14
* | 15 | TAIR_0.15_STOCKAGE01 | C | 15 | 0.15_STOCKAGE01 | | air temperature of airnode | TAIR 15
* | 16 | TAIR_0.16_STOCKAGE02 | C | 16 | 0.16_STOCKAGE02 | | air temperature of airnode | TAIR 16
* | 17 | TAIR_0.17_LT | C | 17 | 0.17_LT | | air temperature of airnode | TAIR 17
* | 18 | TAIR_1.01_BUREAU_PIR | C | 18 | 1.01_BUREAU_PIR | | air temperature of airnode | TAIR 18
* | 19 | TAIR_1.02_BUREAUX | C | 19 | 1.02_BUREAUX | | air temperature of airnode | TAIR 19
* | 20 | TAIR_1.03_BUREAU_ALY | C | 20 | 1.03_BUREAU_ALY | | air temperature of airnode | TAIR 20
* | 21 | TAIR_1.04_VISIO_DG | C | 21 | 1.04_VISIO_DG | | air temperature of airnode | TAIR 21
* | 22 | TAIR_1.05_ACCUEIL_DG | C | 22 | 1.05_ACCUEIL_DG | | air temperature of airnode | TAIR 22
* | 23 | TAIR_1.06_PALIER_NE_E1 | C | 23 | 1.06_PALIER_NE_E1 | | air temperature of airnode | TAIR 23
* | 24 | TAIR_1.07_ERE14 | C | 24 | 1.07_ERE14 | | air temperature of airnode | TAIR 24
* | 25 | TAIR_1.08_ERE13 | C | 25 | 1.08_ERE13 | | air temperature of airnode | TAIR 25
* | 26 | TAIR_1.09_DRH | C | 26 | 1.09_DRH | | air temperature of airnode | TAIR 26
* | 27 | TAIR_1.10_BAIES_BRASSAGE_ | C | 27 | 1.10_BAIES_BRASSAGE_ | | air temperature of airnode | TAIR 27
* | 28 | TAIR_1.11_ERE12(NON_TERMI | C | 28 | 1.11_ERE12(NON_TERMI | | air temperature of airnode | TAIR 28
* | 29 | TAIR_1.12_SECRETARIAT_GAL | C | 29 | 1.12_SECRETARIAT_GAL | | air temperature of airnode | TAIR 29
* | 30 | TAIR_1.14_ERE11 | C | 30 | 1.14_ERE11 | | air temperature of airnode | TAIR 30
* | 31 | TAIR_1.15_CIRCUL_SE_E1 | C | 31 | 1.15_CIRCUL_SE_E1 | | air temperature of airnode | TAIR 31
* | 32 | TAIR_2.01_ERE24 | C | 32 | 2.01_ERE24 | | air temperature of airnode | TAIR 32
* | 33 | TAIR_2.02_IND&ENVIR | C | 33 | 2.02_IND&ENVIR | | air temperature of airnode | TAIR 33
* | 34 | TAIR_2.03_PALIER_NE_E1 | C | 34 | 2.03_PALIER_NE_E1 | | air temperature of airnode | TAIR 34
* | 35 | TAIR_2.04_ERE23(NON_TERMI | C | 35 | 2.04_ERE23(NON_TERMI | | air temperature of airnode | TAIR 35
* | 36 | TAIR_2.05_DT_STRUCT&EDP | C | 36 | 2.05_DT_STRUCT&EDP | | air temperature of airnode | TAIR 36
* | 37 | TAIR_2.06_COFFEE_CORNER | C | 37 | 2.06_COFFEE_CORNER | | air temperature of airnode | TAIR 37
* | 38 | TAIR_2.07_DT | C | 38 | 2.07_DT | | air temperature of airnode | TAIR 38
* | 39 | TAIR_2.08_ERE22(NON_TERMI | C | 39 | 2.08_ERE22(NON_TERMI | | air temperature of airnode | TAIR 39
* | 40 | TAIR_2.09_TRACEURS(NON_TE | C | 40 | 2.09_TRACEURS(NON_TE | | air temperature of airnode | TAIR 40
* | 41 | TAIR_2.10_FLUIDES_METHODE | C | 41 | 2.10_FLUIDES_METHODE | | air temperature of airnode | TAIR 41
* | 42 | TAIR_2.11_ERE21(NON_TERMI | C | 42 | 2.11_ERE21(NON_TERMI | | air temperature of airnode | TAIR 42
* | 43 | TAIR_2.12_CIRCUL_SE_E2 | C | 43 | 2.12_CIRCUL_SE_E2 | | air temperature of airnode | TAIR 43
* | 44 | TAIR_2.13_BAIES_BRASSAGE( | C | 44 | 2.13_BAIES_BRASSAGE( | | air temperature of airnode | TAIR 44
* | 45 | TAIR_3.01_ERE34 | C | 45 | 3.01_ERE34 | | air temperature of airnode | TAIR 45
* | 46 | TAIR_3.02_CIRMAD_COMMERCE | C | 46 | 3.02_CIRMAD_COMMERCE | | air temperature of airnode | TAIR 46
* | 47 | TAIR_3.03_PALIER_NE_E3 | C | 47 | 3.03_PALIER_NE_E3 | | air temperature of airnode | TAIR 47
* | 48 | TAIR_3.04_ERE33(NON_TERMI | C | 48 | 3.04_ERE33(NON_TERMI | | air temperature of airnode | TAIR 48
* | 49 | TAIR_3.05_COMMERCES_OF | C | 49 | 3.05_COMMERCES_OF | | air temperature of airnode | TAIR 49
* | 50 | TAIR_3.06_TRAVAUX01 | C | 50 | 3.06_TRAVAUX01 | | air temperature of airnode | TAIR 50
* | 51 | TAIR_3.07_ERE32 | C | 51 | 3.07_ERE32 | | air temperature of airnode | TAIR 51
* | 52 | TAIR_3.08_TRAVAUX02 | C | 52 | 3.08_TRAVAUX02 | | air temperature of airnode | TAIR 52
* | 53 | TAIR_3.09_ERE31(NON_TERMI | C | 53 | 3.09_ERE31(NON_TERMI | | air temperature of airnode | TAIR 53
* | 54 | TAIR_3.10_CIRCUL_SE_E3 | C | 54 | 3.10_CIRCUL_SE_E3 | | air temperature of airnode | TAIR 54
* | 55 | TAIR_3.11_BAIES_BRASSAGE_ | C | 55 | 3.11_BAIES_BRASSAGE_ | | air temperature of airnode | TAIR 55
* | 56 | TAIR_1.13_BYTPRF | C | 56 | 1.13_BYTPRF | | air temperature of airnode | TAIR 56
* | 57 | TAIR_ESC_SE | C | 57 | ESC_SE | | air temperature of airnode | TAIR 57
* | 58 | TAIR_ESC_CENTRAL | C | 58 | ESC_CENTRAL | | air temperature of airnode | TAIR 58
* | 59 | TAIR_ESC_SECONDAIRE | C | 59 | ESC_SECONDAIRE | | air temperature of airnode | TAIR 59
* | 60 | TAIR_ESC_NE | C | 60 | ESC_NE | | air temperature of airnode | TAIR 60
* | 61 | TAIR_WC_AILE_SUD | C | 61 | WC_AILE_SUD | | air temperature of airnode | TAIR 61
* | 62 | TAIR_WC_AILE_NORD | C | 62 | WC_AILE_NORD | | air temperature of airnode | TAIR 62
* | 63 | THEAT_TDA01 | C | 1 | TDA01 | | set temperature heating of airnode | THEAT 1
* | 64 | THEAT_0.02_ACCUEIL | C | 2 | 0.02_ACCUEIL | | set temperature heating of airnode | THEAT 2
* | 65 | THEAT_0.03_SAS_01 | C | 3 | 0.03_SAS_01 | | set temperature heating of airnode | THEAT 3
* | 66 | THEAT_0.04_SAS_02 | C | 4 | 0.04_SAS_02 | | set temperature heating of airnode | THEAT 4
* | 67 | THEAT_0.05_TDA02 | C | 5 | 0.05_TDA02 | | set temperature heating of airnode | THEAT 5
* | 68 | THEAT_0.06_SALLE_SERVEURS | C | 6 | 0.06_SALLE_SERVEURS | | set temperature heating of airnode | THEAT 6
* | 69 | THEAT_0.07_TDA03_ACHATS | C | 7 | 0.07_TDA03_ACHATS | | set temperature heating of airnode | THEAT 7
* | 70 | THEAT_0.08_ARCHIVES | C | 8 | 0.08_ARCHIVES | | set temperature heating of airnode | THEAT 8
* | 71 | THEAT_0.09_ERE03 | C | 9 | 0.09_ERE03 | | set temperature heating of airnode | THEAT 9
* | 72 | THEAT_0.10_ERE02 | C | 10 | 0.10_ERE02 | | set temperature heating of airnode | THEAT 10
* | 73 | THEAT_0.11_ERE01 | C | 11 | 0.11_ERE01 | | set temperature heating of airnode | THEAT 11
* | 74 | THEAT_0.12_CIRCUL_RDC | C | 12 | 0.12_CIRCUL_RDC | | set temperature heating of airnode | THEAT 12
* | 75 | THEAT_0.13_CAFETERIA | C | 13 | 0.13_CAFETERIA | | set temperature heating of airnode | THEAT 13
* | 76 | THEAT_0.14_BUR_IND | C | 14 | 0.14_BUR_IND | | set temperature heating of airnode | THEAT 14
* | 77 | THEAT_0.15_STOCKAGE01 | C | 15 | 0.15_STOCKAGE01 | | set temperature heating of airnode | THEAT 15
* | 78 | THEAT_0.16_STOCKAGE02 | C | 16 | 0.16_STOCKAGE02 | | set temperature heating of airnode | THEAT 16
* | 79 | THEAT_0.17_LT | C | 17 | 0.17_LT | | set temperature heating of airnode | THEAT 17
* | 80 | THEAT_1.01_BUREAU_PIR | C | 18 | 1.01_BUREAU_PIR | | set temperature heating of airnode | THEAT 18
* | 81 | THEAT_1.02_BUREAUX | C | 19 | 1.02_BUREAUX | | set temperature heating of airnode | THEAT 19
* | 82 | THEAT_1.03_BUREAU_ALY | C | 20 | 1.03_BUREAU_ALY | | set temperature heating of airnode | THEAT 20
* | 83 | THEAT_1.04_VISIO_DG | C | 21 | 1.04_VISIO_DG | | set temperature heating of airnode | THEAT 21
* | 84 | THEAT_1.05_ACCUEIL_DG | C | 22 | 1.05_ACCUEIL_DG | | set temperature heating of airnode | THEAT 22
* | 85 | THEAT_1.06_PALIER_NE_E1 | C | 23 | 1.06_PALIER_NE_E1 | | set temperature heating of airnode | THEAT 23
* | 86 | THEAT_1.07_ERE14 | C | 24 | 1.07_ERE14 | | set temperature heating of airnode | THEAT 24
* | 87 | THEAT_1.08_ERE13 | C | 25 | 1.08_ERE13 | | set temperature heating of airnode | THEAT 25
* | 88 | THEAT_1.09_DRH | C | 26 | 1.09_DRH | | set temperature heating of airnode | THEAT 26
* | 89 | THEAT_1.10_BAIES_BRASSAGE | C | 27 | 1.10_BAIES_BRASSAGE_ | | set temperature heating of airnode | THEAT 27
* | 90 | THEAT_1.11_ERE12(NON_TERM | C | 28 | 1.11_ERE12(NON_TERMI | | set temperature heating of airnode | THEAT 28
* | 91 | THEAT_1.12_SECRETARIAT_GA | C | 29 | 1.12_SECRETARIAT_GAL | | set temperature heating of airnode | THEAT 29
* | 92 | THEAT_1.14_ERE11 | C | 30 | 1.14_ERE11 | | set temperature heating of airnode | THEAT 30
* | 93 | THEAT_1.15_CIRCUL_SE_E1 | C | 31 | 1.15_CIRCUL_SE_E1 | | set temperature heating of airnode | THEAT 31
* | 94 | THEAT_2.01_ERE24 | C | 32 | 2.01_ERE24 | | set temperature heating of airnode | THEAT 32
* | 95 | THEAT_2.02_IND&ENVIR | C | 33 | 2.02_IND&ENVIR | | set temperature heating of airnode | THEAT 33
* | 96 | THEAT_2.03_PALIER_NE_E1 | C | 34 | 2.03_PALIER_NE_E1 | | set temperature heating of airnode | THEAT 34
* | 97 | THEAT_2.04_ERE23(NON_TERM | C | 35 | 2.04_ERE23(NON_TERMI | | set temperature heating of airnode | THEAT 35
* | 98 | THEAT_2.05_DT_STRUCT&EDP | C | 36 | 2.05_DT_STRUCT&EDP | | set temperature heating of airnode | THEAT 36
* | 99 | THEAT_2.06_COFFEE_CORNER | C | 37 | 2.06_COFFEE_CORNER | | set temperature heating of airnode | THEAT 37
* | 100 | THEAT_2.07_DT | C | 38 | 2.07_DT | | set temperature heating of airnode | THEAT 38
* | 101 | THEAT_2.08_ERE22(NON_TERM | C | 39 | 2.08_ERE22(NON_TERMI | | set temperature heating of airnode | THEAT 39
* | 102 | THEAT_2.09_TRACEURS(NON_T | C | 40 | 2.09_TRACEURS(NON_TE | | set temperature heating of airnode | THEAT 40
* | 103 | THEAT_2.10_FLUIDES_METHOD | C | 41 | 2.10_FLUIDES_METHODE | | set temperature heating of airnode | THEAT 41
* | 104 | THEAT_2.11_ERE21(NON_TERM | C | 42 | 2.11_ERE21(NON_TERMI | | set temperature heating of airnode | THEAT 42
* | 105 | THEAT_2.12_CIRCUL_SE_E2 | C | 43 | 2.12_CIRCUL_SE_E2 | | set temperature heating of airnode | THEAT 43
* | 106 | THEAT_2.13_BAIES_BRASSAGE | C | 44 | 2.13_BAIES_BRASSAGE( | | set temperature heating of airnode | THEAT 44
* | 107 | THEAT_3.01_ERE34 | C | 45 | 3.01_ERE34 | | set temperature heating of airnode | THEAT 45
* | 108 | THEAT_3.02_CIRMAD_COMMERC | C | 46 | 3.02_CIRMAD_COMMERCE | | set temperature heating of airnode | THEAT 46
* | 109 | THEAT_3.03_PALIER_NE_E3 | C | 47 | 3.03_PALIER_NE_E3 | | set temperature heating of airnode | THEAT 47
* | 110 | THEAT_3.04_ERE33(NON_TERM | C | 48 | 3.04_ERE33(NON_TERMI | | set temperature heating of airnode | THEAT 48
* | 111 | THEAT_3.05_COMMERCES_OF | C | 49 | 3.05_COMMERCES_OF | | set temperature heating of airnode | THEAT 49
* | 112 | THEAT_3.06_TRAVAUX01 | C | 50 | 3.06_TRAVAUX01 | | set temperature heating of airnode | THEAT 50
* | 113 | THEAT_3.07_ERE32 | C | 51 | 3.07_ERE32 | | set temperature heating of airnode | THEAT 51
* | 114 | THEAT_3.08_TRAVAUX02 | C | 52 | 3.08_TRAVAUX02 | | set temperature heating of airnode | THEAT 52
* | 115 | THEAT_3.09_ERE31(NON_TERM | C | 53 | 3.09_ERE31(NON_TERMI | | set temperature heating of airnode | THEAT 53
* | 116 | THEAT_3.10_CIRCUL_SE_E3 | C | 54 | 3.10_CIRCUL_SE_E3 | | set temperature heating of airnode | THEAT 54
* | 117 | THEAT_3.11_BAIES_BRASSAGE | C | 55 | 3.11_BAIES_BRASSAGE_ | | set temperature heating of airnode | THEAT 55
* | 118 | THEAT_1.13_BYTPRF | C | 56 | 1.13_BYTPRF | | set temperature heating of airnode | THEAT 56
* | 119 | THEAT_ESC_SE | C | 57 | ESC_SE | | set temperature heating of airnode | THEAT 57
* | 120 | THEAT_ESC_CENTRAL | C | 58 | ESC_CENTRAL | | set temperature heating of airnode | THEAT 58
* | 121 | THEAT_ESC_SECONDAIRE | C | 59 | ESC_SECONDAIRE | | set temperature heating of airnode | THEAT 59
* | 122 | THEAT_ESC_NE | C | 60 | ESC_NE | | set temperature heating of airnode | THEAT 60
* | 123 | THEAT_WC_AILE_SUD | C | 61 | WC_AILE_SUD | | set temperature heating of airnode | THEAT 61
* | 124 | THEAT_WC_AILE_NORD | C | 62 | WC_AILE_NORD | | set temperature heating of airnode | THEAT 62
* | 125 | RELHUM_TDA01 | % | 1 | TDA01 | | relativ humidity of airnode air | RELHUM 1
* | 126 | RELHUM_0.02_ACCUEIL | % | 2 | 0.02_ACCUEIL | | relativ humidity of airnode air | RELHUM 2
* | 127 | RELHUM_0.03_SAS_01 | % | 3 | 0.03_SAS_01 | | relativ humidity of airnode air | RELHUM 3
* | 128 | RELHUM_0.04_SAS_02 | % | 4 | 0.04_SAS_02 | | relativ humidity of airnode air | RELHUM 4
* | 129 | RELHUM_0.05_TDA02 | % | 5 | 0.05_TDA02 | | relativ humidity of airnode air | RELHUM 5
* | 130 | RELHUM_0.06_SALLE_SERVEUR | % | 6 | 0.06_SALLE_SERVEURS | | relativ humidity of airnode air | RELHUM 6
* | 131 | RELHUM_0.07_TDA03_ACHATS | % | 7 | 0.07_TDA03_ACHATS | | relativ humidity of airnode air | RELHUM 7
* | 132 | RELHUM_0.08_ARCHIVES | % | 8 | 0.08_ARCHIVES | | relativ humidity of airnode air | RELHUM 8
* | 133 | RELHUM_0.09_ERE03 | % | 9 | 0.09_ERE03 | | relativ humidity of airnode air | RELHUM 9
* | 134 | RELHUM_0.10_ERE02 | % | 10 | 0.10_ERE02 | | relativ humidity of airnode air | RELHUM10
* | 135 | RELHUM_0.11_ERE01 | % | 11 | 0.11_ERE01 | | relativ humidity of airnode air | RELHUM11
* | 136 | RELHUM_0.12_CIRCUL_RDC | % | 12 | 0.12_CIRCUL_RDC | | relativ humidity of airnode air | RELHUM12
* | 137 | RELHUM_0.13_CAFETERIA | % | 13 | 0.13_CAFETERIA | | relativ humidity of airnode air | RELHUM13
* | 138 | RELHUM_0.14_BUR_IND | % | 14 | 0.14_BUR_IND | | relativ humidity of airnode air | RELHUM14
* | 139 | RELHUM_0.15_STOCKAGE01 | % | 15 | 0.15_STOCKAGE01 | | relativ humidity of airnode air | RELHUM15
* | 140 | RELHUM_0.16_STOCKAGE02 | % | 16 | 0.16_STOCKAGE02 | | relativ humidity of airnode air | RELHUM16
* | 141 | RELHUM_0.17_LT | % | 17 | 0.17_LT | | relativ humidity of airnode air | RELHUM17
* | 142 | RELHUM_1.01_BUREAU_PIR | % | 18 | 1.01_BUREAU_PIR | | relativ humidity of airnode air | RELHUM18
* | 143 | RELHUM_1.02_BUREAUX | % | 19 | 1.02_BUREAUX | | relativ humidity of airnode air | RELHUM19
* | 144 | RELHUM_1.03_BUREAU_ALY | % | 20 | 1.03_BUREAU_ALY | | relativ humidity of airnode air | RELHUM20
* | 145 | RELHUM_1.04_VISIO_DG | % | 21 | 1.04_VISIO_DG | | relativ humidity of airnode air | RELHUM21
* | 146 | RELHUM_1.05_ACCUEIL_DG | % | 22 | 1.05_ACCUEIL_DG | | relativ humidity of airnode air | RELHUM22
* | 147 | RELHUM_1.06_PALIER_NE_E1 | % | 23 | 1.06_PALIER_NE_E1 | | relativ humidity of airnode air | RELHUM23
* | 148 | RELHUM_1.07_ERE14 | % | 24 | 1.07_ERE14 | | relativ humidity of airnode air | RELHUM24
* | 149 | RELHUM_1.08_ERE13 | % | 25 | 1.08_ERE13 | | relativ humidity of airnode air | RELHUM25
* | 150 | RELHUM_1.09_DRH | % | 26 | 1.09_DRH | | relativ humidity of airnode air | RELHUM26
* | 151 | RELHUM_1.10_BAIES_BRASSAG | % | 27 | 1.10_BAIES_BRASSAGE_ | | relativ humidity of airnode air | RELHUM27
* | 152 | RELHUM_1.11_ERE12(NON_TER | % | 28 | 1.11_ERE12(NON_TERMI | | relativ humidity of airnode air | RELHUM28
* | 153 | RELHUM_1.12_SECRETARIAT_G | % | 29 | 1.12_SECRETARIAT_GAL | | relativ humidity of airnode air | RELHUM29
* | 154 | RELHUM_1.14_ERE11 | % | 30 | 1.14_ERE11 | | relativ humidity of airnode air | RELHUM30
* | 155 | RELHUM_1.15_CIRCUL_SE_E1 | % | 31 | 1.15_CIRCUL_SE_E1 | | relativ humidity of airnode air | RELHUM31
* | 156 | RELHUM_2.01_ERE24 | % | 32 | 2.01_ERE24 | | relativ humidity of airnode air | RELHUM32
* | 157 | RELHUM_2.02_IND&ENVIR | % | 33 | 2.02_IND&ENVIR | | relativ humidity of airnode air | RELHUM33
* | 158 | RELHUM_2.03_PALIER_NE_E1 | % | 34 | 2.03_PALIER_NE_E1 | | relativ humidity of airnode air | RELHUM34
* | 159 | RELHUM_2.04_ERE23(NON_TER | % | 35 | 2.04_ERE23(NON_TERMI | | relativ humidity of airnode air | RELHUM35
* | 160 | RELHUM_2.05_DT_STRUCT&EDP | % | 36 | 2.05_DT_STRUCT&EDP | | relativ humidity of airnode air | RELHUM36
* | 161 | RELHUM_2.06_COFFEE_CORNER | % | 37 | 2.06_COFFEE_CORNER | | relativ humidity of airnode air | RELHUM37
* | 162 | RELHUM_2.07_DT | % | 38 | 2.07_DT | | relativ humidity of airnode air | RELHUM38
* | 163 | RELHUM_2.08_ERE22(NON_TER | % | 39 | 2.08_ERE22(NON_TERMI | | relativ humidity of airnode air | RELHUM39
* | 164 | RELHUM_2.09_TRACEURS(NON_ | % | 40 | 2.09_TRACEURS(NON_TE | | relativ humidity of airnode air | RELHUM40
* | 165 | RELHUM_2.10_FLUIDES_METHO | % | 41 | 2.10_FLUIDES_METHODE | | relativ humidity of airnode air | RELHUM41
* | 166 | RELHUM_2.11_ERE21(NON_TER | % | 42 | 2.11_ERE21(NON_TERMI | | relativ humidity of airnode air | RELHUM42
* | 167 | RELHUM_2.12_CIRCUL_SE_E2 | % | 43 | 2.12_CIRCUL_SE_E2 | | relativ humidity of airnode air | RELHUM43
* | 168 | RELHUM_2.13_BAIES_BRASSAG | % | 44 | 2.13_BAIES_BRASSAGE( | | relativ humidity of airnode air | RELHUM44
* | 169 | RELHUM_3.01_ERE34 | % | 45 | 3.01_ERE34 | | relativ humidity of airnode air | RELHUM45
* | 170 | RELHUM_3.02_CIRMAD_COMMER | % | 46 | 3.02_CIRMAD_COMMERCE | | relativ humidity of airnode air | RELHUM46
* | 171 | RELHUM_3.03_PALIER_NE_E3 | % | 47 | 3.03_PALIER_NE_E3 | | relativ humidity of airnode air | RELHUM47
* | 172 | RELHUM_3.04_ERE33(NON_TER | % | 48 | 3.04_ERE33(NON_TERMI | | relativ humidity of airnode air | RELHUM48
* | 173 | RELHUM_3.05_COMMERCES_OF | % | 49 | 3.05_COMMERCES_OF | | relativ humidity of airnode air | RELHUM49
* | 174 | RELHUM_3.06_TRAVAUX01 | % | 50 | 3.06_TRAVAUX01 | | relativ humidity of airnode air | RELHUM50
* | 175 | RELHUM_3.07_ERE32 | % | 51 | 3.07_ERE32 | | relativ humidity of airnode air | RELHUM51
* | 176 | RELHUM_3.08_TRAVAUX02 | % | 52 | 3.08_TRAVAUX02 | | relativ humidity of airnode air | RELHUM52
* | 177 | RELHUM_3.09_ERE31(NON_TER | % | 53 | 3.09_ERE31(NON_TERMI | | relativ humidity of airnode air | RELHUM53
* | 178 | RELHUM_3.10_CIRCUL_SE_E3 | % | 54 | 3.10_CIRCUL_SE_E3 | | relativ humidity of airnode air | RELHUM54
* | 179 | RELHUM_3.11_BAIES_BRASSAG | % | 55 | 3.11_BAIES_BRASSAGE_ | | relativ humidity of airnode air | RELHUM55
* | 180 | RELHUM_1.13_BYTPRF | % | 56 | 1.13_BYTPRF | | relativ humidity of airnode air | RELHUM56
* | 181 | RELHUM_ESC_SE | % | 57 | ESC_SE | | relativ humidity of airnode air | RELHUM57
* | 182 | RELHUM_ESC_CENTRAL | % | 58 | ESC_CENTRAL | | relativ humidity of airnode air | RELHUM58
* | 183 | RELHUM_ESC_SECONDAIRE | % | 59 | ESC_SECONDAIRE | | relativ humidity of airnode air | RELHUM59
* | 184 | RELHUM_ESC_NE | % | 60 | ESC_NE | | relativ humidity of airnode air | RELHUM60
* | 185 | RELHUM_WC_AILE_SUD | % | 61 | WC_AILE_SUD | | relativ humidity of airnode air | RELHUM61
* | 186 | RELHUM_WC_AILE_NORD | % | 62 | WC_AILE_NORD | | relativ humidity of airnode air | RELHUM62
*** THERMAL CONDUCTANCE OF USED WALL TYPES ***
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
WALL PB_TP U= 0.312 W/m2K
WALL MEXT_PEUPLIER U= 0.315 W/m2K
WALL MINT_LEGER U= 1.754 W/m2K
WALL TOITURE U= 0.189 W/m2K
WALL MEXT_TERRE_CUITE U= 0.330 W/m2K
WALL MINT_LOURD U= 3.892 W/m2K
WALL PLANCHER_INTERMEDIAI U= 3.892 W/m2K
WALL PLH_SDR U= 0.230 W/m2K
WALL CBR_B11 U= 0.450 W/m2K
WALL CBR_I21 U= 0.040 W/m2K
WALL MINT_LNC U= 0.305 W/m2K
WALL CBR_MEN U= 0.156 W/m2K
WALL CBR_H11 U= 0.059 W/m2K
WALL CBR_H31 U= 0.030 W/m2K
WALL CBR_H11_TOITURE U= 0.293 W/m2K
WALL PL_LNC U= 0.243 W/m2K
WALL CLOISON_VIDE_INT U= 2.703 W/m2K
--
Les donnees et renseignements contenus dans ce message sont personnels, confidentiels et secrets. Toute publication, utilisation ou diffusion, meme partielle, doit etre autorisee. Si vous n'etes pas le bon destinataire, nous vous demandons de ne pas lire, copier, utiliser ou divulguer cette communication. Nous vous prions de notifier cette erreur a l'expediteur et d'effacer immediatement cette communication de votre systeme.
Any data and information contained in this electronic mail is personal, confidential and secret. Any total or partial publication, use or distribution must be authorized. If you are not the right addressee, we ask you not to read, copy, use or disclose this communication. Please notify this error to the sender and erase at once this communication from your system.
More information about the TRNSYS-users
mailing list