[TRNSYS-users] heating floor modeling with type 56 integrated component

Antoine Gautier antoine.gautier at solamen.fr
Fri Jun 3 05:26:04 PDT 2011


Dear all

 

Just for information I finally get quite good results by adjusting the
thermal characteristic of the concrete slab above the active layer. I
previously used standard values from BESTEST (
<http://www.nrel.gov/docs/legosti/old/6231.pdf>
http://www.nrel.gov/docs/legosti/old/6231.pdf) which are quite extreme. When
using more conventional values for reinforced concrete I get emitted power
to the zone really close from manufacturer calculations (gap < 2%).

 

--

Antoine Gautier
Solamen
+33 6 98 78 56 46

antoine.gautier at solamen.fr

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110603/d9c746c0/attachment-0005.htm>


More information about the TRNSYS-users mailing list