Dear all
I am trying to compare the results provided by the active layer model
integrated in Type 56 with manufacturer data.
Test case is simple.
· Adiabatic walls without windows
· No internal gains
· No air flow rate (nor ventilation nor infiltration)
· Infinite cooling power to maintain the ambient temperature at the
value used in manufacturer calculations (14°C)
· Heating floor precisely parameterized according to manufacturer
specifications (loops number, water flow rate, conductivity of insulation,
etc.)
· QALFL gives me the total emitted power and QCOOL the power emitted
to the zone
Below is the result of the comparison at stationary conditions (plus a
sensitivity perform in TRNSYS on pipe wall conductivity and loops number).
Manufacturer
TRNSYS
Conductivity W/m.K
-
0.35
0.45
0.35
Loops number
3
3
3
1
Total emitted power W
9564
7776
7850
7819
Zone emitted power W
8980
7185
7254
7225
Water outlet temperature °C
23.8
27.7
-
-
Ratio zone/total emitted power
94%
92%
92%
92%
Gap on zone emitted power / Man.
-
-20%
-19%
-20%
Does the gap between TRNSYS and manufacturer data fall within the model
uncertainty or does it seem too high to you ? (~20% on power emitted to the
zone)
Perhaps I missed something in my test case
Or would you have any other advice to reduce the discrepancy ? (giving the
fact that input data uncertainties are very small in my case since I have
the detailed manufacturer specifications)
Thanks a lot.
Regards
--
Antoine Gautier
Solamen
+33 6 98 78 56 46
antoine.gautier at solamen.fr