Dear all

 

Just for information I finally get quite good results by adjusting the
thermal characteristic of the concrete slab above the active layer. I
previously used standard values from BESTEST (
<http://www.nrel.gov/docs/legosti/old/6231.pdf>
http://www.nrel.gov/docs/legosti/old/6231.pdf) which are quite extreme. When
using more conventional values for reinforced concrete I get emitted power
to the zone really close from manufacturer calculations (gap < 2%).

 

--

Antoine Gautier