Michael,
   There are two ways that you could specify the schedule.
1. if you are fairly certain that you will not want to come back and 
change the total number of people then you can enter the number of 
people in the zone as the "value" of the schedule for each time period.
2. if you may want to change the total number of people later on then 
you can enter the fraction of the maximum number of people in the zone 
as the value of the schedule (a value between 0 and 1) and then you can 
use the multiplier in order to set the maximum number of people. Your 
schedule would be:
00:00 - 06:00 - value 0.5
06:00 - 10:00 - value 0.3
10:00 - 14:00 - value 0.2
14:00 - 18:00 - value 1.0
18:00 - 24:00 - value 0.5
and the multiplier would of course be 10.
Kind regards,
  David
On 7/1/2011 07:11, Michael Tesfaye wrote:
> Dear All,
> I am trying to put in hourly values for occupation for Type 56 on 
> TRNSYS 16. I am using a new type of Schedule. the details are,
> 00:00 - 06:00 - 5 persons
> 06:00 - 10:00 - 3 persons
> 10:00 - 14:00 - 2 persons
> 14:00 - 18:00 - 10 persons
> 18:00 - 24:00 - 5 persons
> I am having trouble specifying this. after putting the values, is the 
> "Value" a 1 or a 0?? or is the "value" actually the number of persons 
> at that time interval?
> Also, how should i leave the Multiplication and Addition factors? 
> someone please explain the details ?
> thank you!!!
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110701/73308302/attachment-0005.htm>
    
    
More information about the TRNSYS-users
mailing list