[TRNSYS-users] weather simulators
David BRADLEY
d.bradley at tess-inc.com
Mon Jan 10 11:31:30 PST 2011
David
If you are using Trnsys17 and standard format weather files such as
*.tmy, *.tm2, *.epw, *.tm3 then I would recommend using Type15 for your
weather processing. If you are using Trnsys16 and a standard format
weather file then you need to use Type89 in combination with Type16.
Type9 is intended to read non-standard format data files and from your
description of the weather files that you have, it sounds as though you
will need to use Type9. If you have the *.xls version, I would recommend
that you save that file as a "comma separated value" file (*.csv) and
then read it with Type9. One of Type9's parameters asks you how many
header lines there are before the data begins. Another parameter asks
you how many values to read. This second parameter corresponds to the
number of columns that are in your *.xls file.
Kind regards,
David
On 1/8/2011 07:53, david irusta para wrote:
> Hi!!
>
> I´m trying to decide which weather simulator is better:
>
> - If I use 89e or 89f (.epw), trnsys only can resolve the first time.
> the next times appears "Visual Fortran run-time error" and I don´t
> know how to resolve it
>
> -Which combines of types 9 and 16 do you recommend??
>
> -I have archives with extensions .xls(excel) or .met(Spanish Ministery
> weather archives), where can I define the columns for type 9??
>
> I have done some examples, but I'd rather be sure before proceeding
>
> Thank you so much
>
> Best Regards!!
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110110/8bbee45a/attachment-0005.htm>
More information about the TRNSYS-users
mailing list