Chun Kwong,
Internally, TRNSYS replaces functions like MAX(), GT(), LE() with a
single letter character. The internal representation of either the GT()
function or the MAX() function is probably "j" - thus the strange
representation of your equation in the list file. Looking through your
equations, I see
M_ChWS_PSA = gt(N_ahu_PSA1,0.1) ...
but I don't see an equation that sets the value of N_ahu_PSA1. If that variable is an input to your Trnsys Studio equation block then make sure that you have the output of an equation connected up to it. If N_ahu_PSA1 is the result of another equation, open up your *.dck file and search through it to make sure that the equation is correctly defined elsewhere in the input file.
Kind regards,
David
On 2/14/2011 08:34, Matt Duffy wrote:
> Dear Chun Kwong LEE,
>
> This is very strange. I wonder if it is similar to what David Bradley
> wrote to the group last week about special characters? What TRNSYS version
> are you using?
>
> Best regards,
>
> Matt Duffy
>
>
> ----- Original Message -----
> From: ""<a8304506 at graduate.hku.hk>
> Sent: Mon, February 14, 2011 3:01
> Subject:[TRNSYS-users] Strange error when using the equation proforma
>
>
> Dear Trnsys users.
>
> When I try to simulate a HVAC system, I got the following error message
> copied
> from the .lst file related to an equation proforma:
>
>
> * EQUATIONS "ChWSH_P"
>
>
> EQUATIONS 12
> M_ChWS_PO_max = 85323
> M_ChWS_PSA_max = 104280
> S_SAV_PO1 = gt([71,1],0.1)*gt([86,1],0.01)*Max(Min([86,1],1.0),0.3)
> S_SAV_PSA1 = gt([71,5],0.01)*gt([110,1],0.01)*Max(Min([110,1],1.0),0.3)
> tMP = M_ChWS_PO_max*S_SAV_PO1+M_ChWS_PSA_max*S_SAV_PSA1
> xPO = gt(tMP,0.01)*M_ChWS_PO_max*S_SAV_PO1/Max(tMP,0.01)
> xPSA = 1-xPO
> M_ChWS_PO =
> gt(N_ahu_PO,0.1)*Min([43,2]*N_chwsp_P*S_SAV_PO1,M_ChWS_PO_max)/Max(N_ahu_PO,0.01)
> M_ChWS_PSA =
> gt(N_ahu_PSA1,0.1)*Min([43,2]*N_chwsp_P*S_SAV_PSA1,M_ChWS_PSA_max)/Max(N_ahu_PSA1,0.01)
>
> *** Fatal Error at time : 0.000000
> Generated by Unit : Not applicable or not available
> Generated by Type : Not applicable or not available
> TRNSYS Message 20 : The referenced variable used in this equation has
> not been defined in the TRNSYS input file. The equation begins with the
> string
> in "reported information"
> Reported information : M_CHWS_PSA = j(N_AH
>
>
> *** Fatal Error at time : 0.000000
> Generated by Unit : Not applicable or not available
> Generated by Type : Not applicable or not available
> TRNSYS Message 20 : The referenced variable used in this equation has
> not been defined in the TRNSYS input file. The equation begins with the
> string
> in "reported information"
> Reported information : M_CHWS_PSA = j(N_AH
>
> Does anyone konw what's going wrong? Another strange matter is that when I
> input the formula for M_ChWS_PO, I use N_ahu_PO1 (see attached screenshot).
> However, in the input and listing files, it becomes N_ahu_PO. How can I
> rectify
> the problem? Thank you!
>
> Best Regards
> LEE, Chun Kwong
> City University of Hong Kong
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
> ----- End of original message -----
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
More information about the TRNSYS-users
mailing list