Nils,
I think that if you use the combination of QCOMO and QCOMI, you can get 
at the energy transfer through the wall. QCOMO is the energy from 
outside the wall into the wall surface. QCOMI is the same for the inner 
surface. The difference between the two should be the amount of energy 
either stored by or given up by the wall.
Best,
David
On 12/16/2011 07:29, Nils Nikolai wrote:
> Dear TrnSYS users,
>
> i have the same question as Pablo. I am not sure how i can actually 
> get the heat flux through a wall. Is there an answer to this question?
>
> Thanks in Advance,
> Nils
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
-- 
***************************