[TRNSYS-users] TRNBLD - active layer - Thickness of adjacent	layers
    Schrade, Johannes 
    Johannes.Schrade at ibp.fraunhofer.de
       
    Fri Dec 16 04:12:40 PST 2011
    
    
  
Dear Marion,
 
Thanks for your reply.
If I draw the right conclusion from your explanation, this warning I mentioned in my first email, was not correct.
Is there a possibility to avoid this control and the following resetting of the input data within TRNBLD?
 
Kind regards,
Johannes Schrade
 
Johannes Schrade
Abteilung Wärmetechnik
Fraunhofer-Institut für Bauphysik
Nobelstr. 12
70569 Stuttgart
johannes.schrade at ibp.fraunhofer.de <mailto:johannes.schrade at ibp.fraunhofer.de> 
Telefon 0711 / 970-3416
Telefax 0711 / 970-3399
www.ibp.fraunhofer.de/wt/ <http://www.ibp.fraunhofer.de/wt/> 
Johannes Schrade
Department Heat Technology 
Fraunhofer Institute for Building Physics
Nobelstr. 12
70569 Stuttgart, Germany
johannes.schrade at ibp.fraunhofer.de <mailto:johannes.schrade at ibp.fraunhofer.de> 
Phone +49 711 / 970-3416
Fax +49 711 / 970-3399
www.ibp.fraunhofer.de/wt/ <http://www.ibp.fraunhofer.de/wt/> 
 
Von: Marion Hiller [mailto:hiller at transsolar.com] 
Gesendet: Freitag, 16. Dezember 2011 12:58
An: Schrade, Johannes; l.f.r.peeters
Cc: trnsys-users
Betreff: AW: Re: [TRNSYS-users] TRNBLD - active layer - Thickness of adjacent layers
 
Johannes and Leen, 
 
thanks for pointing out the confusion about the active layer boundary conditions due to mistakes in the manual documentation. 
 
I checked the equations with the original literature and the code. 
 
The base equation is for all three systems is Eq. 5.4.4.-15: 
 
 
 
For the following boundary conditions 
 
 
the summation can be neglected and yield to Eq. 5.4.4. -16 (which is wrong in the manual!) 
 
 
 
For the capillary tube system the “ln” can be replaced by 1/3 if 
 is less than  1.85718. 
 
 
Thus, for both capillary tube system and ordinary TAB the above mentioned conditions have to be valid! 
For the floor heating the conditions are the same for layer 1 with d1, For layer 2 with d2 different condition apply. 
(On page 5-187 of the manual there is a mistake: the “lower then” has to be “greater then” for the condition of d1!) 
 
 
 
 
The conditions are checked by entering the layers in TRNbuild. 
 
Further details about the model can be found in the following book (it is written in German): 
 
„Thermoaktive Systeme tabs“ von Markus Koschenz und Beat Lehmann, 2000 
If you are interessted I can double check if you can buy the book at Transsolar. 
 
Best regards, 
 
Marion 
 
P.S.: We will upate the documentation for the next release. 
 
Dipl.-Ing. Marion Hiller 
TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes Bauen und Nutzerkomfort in Gebäude 
Munich - New York - Stuttgart + 49.711.67976.0 
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart 
Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.: DE152272639 
Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer, Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher  
  
 
________________________________
   
Von: leen peeters [mailto:l.f.r.peeters at gmail.com] 
Gesendet: Dienstag, 13. Dezember 2011 20:08
An: Schrade, Johannes
Cc: trnsys-users at cae.wisc.edu
Betreff: Re: [TRNSYS-users] TRNBLD - active layer - Thickness of adjacent layers 
 
Johannes, 
  
I know they violate one another. As I cannot access the code of type 56, I cannot check the implementation. We are currently working on finding out where the limits of the model are ... 
The model is based on an EMPA model, but there are no international publications I found that really discuss the implementation of the active layer model. 
  
It is a numerical derivation, so emperics are not the cause. I will get back to you once I figured out more. 
  
Leen 
On Tue, Dec 13, 2011 at 1:29 PM, Schrade, Johannes <Johannes.Schrade at ibp.fraunhofer.de <mailto:Johannes.Schrade at ibp.fraunhofer.de> > wrote: 
Dear Leen, dear TRNSYS users, 
  
Thanks for your quick reply. 
However, I’m not really satisfied with your suggestion, as I want to understand the reason behind it. 
If you are right, I violated the requirement “outside diameter over pipe distance < 0.2”. But, this requirement is completely independent from the layer thickness of the adjacent layer, isn’t it? 
On the other side, if both adjacent layers must be conform to the minimum thickness of 0.3 times pipe spacing, I would have caused a violation of this requirement by setting the pipe spacing to 24 cm and the layer thickness to 8mm. But for this, I didn’t receive any warning. 
Last but not least, there are oppositional specifications for the required ratio between thickness of adjacent layer(s) and pipe spacing in the TRNBLD user manual. On page 5-186 the ratio should be greater than 0.3, on page 5-187 the ratio should be equal or smaller than 0.3 and on page 5-59 the ratio should be equal or greater than 0.3. So, nearly all possibilities are mentioned. I’m a bit confused. 
  
Looking forward to some light into the dark, 
  
Kind regards, 
Johannes Schrade 
  
  
  
Johannes Schrade
Abteilung Wärmetechnik 
Fraunhofer-Institut für Bauphysik
Nobelstr. 12
70569 Stuttgart 
johannes.schrade at ibp.fraunhofer.de
Telefon 0711 / 970-3416
Telefax 0711 / 970-3399
www.ibp.fraunhofer.de/wt/ 
Johannes Schrade
Department Heat Technology 
Fraunhofer Institute for Building Physics
Nobelstr. 12
70569 Stuttgart, Germany 
johannes.schrade at ibp.fraunhofer.de
Phone +49 711 / 970-3416 <tel:%2B49%20711%20%2F%20970-3416> 
Fax +49 711 / 970-3399 <tel:%2B49%20711%20%2F%20970-3399> 
www.ibp.fraunhofer.de/wt/ 
  
Von: leen peeters [mailto:l.f.r.peeters at gmail.com] 
Gesendet: Montag, 12. Dezember 2011 22:09
An: Schrade, Johannes
Cc: trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu> 
Betreff: Re: [TRNSYS-users] TRNBLD - active layer - Thickness of adjacent layers 
  
Johannes, 
  
as soon as you decrease the distance between the pipes, you come closer to the limits set regarding the modeling of the heat transfer in the direction of the water flow (direction z in the mathematical model). The stability of that model requires that you achieve a certain boundary condition, which is a.o. function of the thermal resistance of the water-pipe-inter pipe distance. In order to ensure these boundary conditions are satisfied the ratio of pipe outside diameter over pipe distance < 0.2 AND the ratios of layer thickness over pipe distance > 0.3. The 0.024-value you received for the minimum layer thickness comes from this limitation. I assume the extra measure is invoked once you come close to the 0.2-limit. 
As soon as you take 0.1 for the pipe distance, you can again select 0.008 m for layer thickness ... 
Playing around with conductivity or capacity does not help, as the measure seems to be implemented through the above limits only .... 
  
Leen 
On Mon, Dec 12, 2011 at 1:48 PM, Schrade, Johannes <Johannes.Schrade at ibp.fraunhofer.de> wrote: 
Dear TRNSYS users, 
  
I have some problems with the active layer module of TRNBLD, which I used for modeling a floor heating system. 
The active layers, which should be displayed in the model, are defined as following: 
  
Layer 1: 
·         Pipe spacing: 24 cm 
·         Pipe outside diameter: 16 mm 
·         Pipe wall thickness: 2 mm 
  
Layer 2: 
·         Pipe spacing: 8 cm 
·         Pipe outside diameter: 16 mm 
·         Pipe wall thickness: 2 mm 
  
By specifying the thicknesses of the layers adjacent to the active layers, the following curiosity appeared. 
  
For case 1, I set the thickness of the layer above the active layer to 73 mm, which is greater than 0.3 times the pipe spacing, and I set the layer below to 0.5 times the pipe outside diameter (requirements taken from manual TRNSYS 17, 5-187, table). This step had worked pretty good and the simulation was running without any problems. 
In a second step, I revised the model and included the second active layer into the TRNBLD model. As the floor screed should be identical for both cases, I tried to define the thicknesses of the adjacent layers the same way as I did it in case 1. But when I tried to reduce the thickness of the adjacent layer below, the following warning appeared: “thickness must be in the range of 0.024 to 1.0”. 
In order to understand this warning I had a closer look to the manual of TRNBLD. On page 5-58 (TRNSYS 17) I found a remark that both layers adjacent to the active layer must be greater than 0.3 times pipe spacing. This would explain, why the warning appears, but I do not understand, why the first case should be unproblematic, as the required minimum thickness in this case should be 72mm and why this is not mentioned in the mathematical description. 
Does anyone has an idea, what could be the reason behind that, or might this be a known or unknown bug? If this requirement dependent on the pipe spacing should be really used for both layers, this would mean that extremely thick floor screeds of +15cm are necessary to model a floor heating system with a pipe spacing of 24 cm. This sounds absolutely unrealistic. 
  
Hoping for some help, 
Kind regards, 
  
Johannes Schrade 
  
Johannes Schrade
Abteilung Wärmetechnik 
Fraunhofer-Institut für Bauphysik
Nobelstr. 12
70569 Stuttgart 
johannes.schrade at ibp.fraunhofer.de
Telefon 0711 / 970-3416
Telefax 0711 / 970-3399
www.ibp.fraunhofer.de/wt/ 
Johannes Schrade
Department Heat Technology 
Fraunhofer Institute for Building Physics
Nobelstr. 12
70569 Stuttgart, Germany 
johannes.schrade at ibp.fraunhofer.de
Phone +49 711 / 970-3416 <tel:%2B49%20711%20%2F%20970-3416> 
Fax +49 711 / 970-3399 <tel:%2B49%20711%20%2F%20970-3399> 
www.ibp.fraunhofer.de/wt/ 
  
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu
https://mailman.cae.wisc.edu/listinfo/trnsys-users 
  
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111216/5b65011a/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 4021 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111216/5b65011a/attachment-0015.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1858 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111216/5b65011a/attachment-0016.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 2137 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111216/5b65011a/attachment-0017.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 1006 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111216/5b65011a/attachment-0018.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 21290 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111216/5b65011a/attachment-0019.jpg>
    
    
More information about the TRNSYS-users
mailing list