[TRNSYS-users] questions about shading matrix file
Marion Hiller
hiller at transsolar.com
Fri Apr 8 00:14:08 PDT 2011
Dear Pauline,
In Trnsys3D you can define shader surfaces and heat transfer surfaces
like walls windows etc.
After finishing the drawing there are two ways to continue:
- Import the IDf file directly into Studio by the 3D building
wizard.
This creates you a B17 file as well as studio project. A shading matix
can be created by TRNbuild only.
There you have make a right mouse click on Type 56 -> edit building.
- You start TRNbuild and use the Import function. This creates
you a B17 file only
Shading matrices are created by TRNbuild only. For creating a shading
matrix you may check documentation
05-MultizoneBuilding.pdf section 5.2.7, 5.2.7.2 and 5.5.1
The matrix files don’t exist in the studio. They are assumed to be in
the same directory as B17 file and have a fixed name.
Type 56 uses the shading matrix automatically when it is there. Check
for a notice in the list file.
Concerning the capacity, do you use the latest TRNSYS 17.00.0019? This
should work fine.
V1….Vx means 1st, 2nd, ….Vertex ID
Regards,
Marion
Dipl.-Ing. Marion Hiller
TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes Bauen
und Nutzerkomfort in Gebäude
Munich - New York - Stuttgart + 49.711.67976.0
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart
Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.:
DE152272639
Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher
_____
Von: Pauline GELIN [mailto:p.gelin at katene.fr]
Gesendet: Donnerstag, 7. April 2011 09:22
An: trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] questions about shading matrix file
Dear all,
I would like to know when and where the new shading matrix file is used
in TRNSYS simulation studio.
I drew a building with a shading object thanks to the Sketchup plugin
TRnSYS3D. I imported it in TRNBuild and I could read information about
this shading object in the window “Geo-Info”.
But I don’t know what these parameters (from V1 to V4)mean and above all
where they are use.
I read on the MultizoneBuilding manual that a .shm file was also
created. So I thought it was like a .dat file and should be linked in
the simulation studio but I didn’t find where.
Is there anyone who knows when and where the shading datas are used
during the simulation?
I have also another little question, always about the IDF file import in
TRNBuild: volumes of zones are well imported but the linked capacitance
calculations are not done. Is there a problem from my file or is it
always like this? Do I have to multiply by 1.2 myself manually?
Thanks a lot in advance.
Pauline Gelin