Marie-esther,

This error is created because the conditions your cooling tower is experiencing are outside the psychrometric chart. In this case the air is supersaturated.

Use Type33 to correct any inconsistencies in the weather file before passing the data on to the cooling tower.

Type 33 is located under: Physical Phenomena/Thermodynamic Properties/Psychrometrics

Fred