Thank you very much for all your answers, being :

- Werner Keilholz and Vincent Coste : connect type 56 to a type 23 which sets a target temperature for automatic cooling and heating in type 56, giving the desired operative temperature ;

- David Bradley : set up a HVAC system to pay attention to including operative temperature ;

- Maarten Sourbron: compute T_corrected = 2*Tset-Tmsurf, with Tset = desired operative temperature and Tmsurf the mean surface temp which type56 gives as an output and set T_corrected as the target temperature for automatic cooling and heating in type 56.

 

Until now, I have only tried the first solution and I still have got some problems to give type 23 correct parameters but I am investigating.

 

Thanks for your help !

 

Héloïse Pelen

ETAMINE

 

heloise.pelen at etamine.coop <mailto:heloise.pelen at etamine.coop> 

75 rue de la Villette - 69003 Lyon

Std : 04 37 45 34 20 / Fax : 04 37 45 41 38

Ld : 04 37 45 34 13 / Port : 06 65 07 41 77

	
	

Visitez notre site web : www.etamine.coop !

 

De : Maarten Sourbron [mailto:Maarten.Sourbron at mech.kuleuven.be] 
Envoyé : vendredi 12 novembre 2010 09:44
À : David BRADLEY; Heloise PELEN
Cc : trnsys-users at engr.wisc.edu
Objet : RE: [TRNSYS-users] Top control in the Type 56

 

Dear Héloïse, 

 

If you want to use the ideal heating and cooling option of type56, you can change the set point at wich you want to heat or cool.

e.g. if you want to start heating at T_op=T_set=20°C, determine an input to type56 being T_corrected = 2*Tset-Tmsurf, with Tset = 20 and Tmsurf the mean surface temp which type56 gives as an output.

It comes from T_operative = (T_air+T_mean_surf)/2, or with the symbols of above T_set = (T_corrected+Tmsurf)/2.

So, instead of supplying the required operative temperature T_set as input, you supply the equivalent air temperature, so with T_corrected as air temp and Tmsurf as surface temp you end up with an operative temp = T_set.

 

Works fine, with no numerical issues, only a small oscillation around T_set, but with a small enough time step, this is neglectable.

 

Good luck,

 

Maarten

 

-- 


Departement Werktuigkunde-Department of Mechanical Engineering 


Katholieke Universiteit Leuven


Celestijnenlaan 300A bus 2421


3001 Heverlee (Leuven)


T : 0032 (0)16 32 28 73


F : 0032 (0)16 32 29 85


E : Maarten.Sourbron at mech.kuleuven.be
________________________________


From: David BRADLEY [mailto:d.bradley at tess-inc.com] 
Sent: maandag 8 november 2010 20:48
To: Heloise PELEN
Cc: trnsys-users at engr.wisc.edu
Subject: Re: [TRNSYS-users] Top control in the Type 56

 

Heloise,
  If you are using the automatic heating and cooling types that are built into Type56/TRNBuild then these only pay attention to the zone air temperature in order to compute the sensible load on the space. The control of those components is assumed to be instantaneous and ideal. If you are simulating a building and an actual HVAC system then you can set up the HVAC system to pay attention to whatever Type56 output variables that you want (including operative temperature). PID control is possible using Type22 but in my experience a lot of portions of the HVAC system are based on ON/OFF control (Type108). When implementing controls of any kind you need to make sure that your timesteps are small (1 to 5 minutes); recall that TRNSYS can make one control decision per timestep and then it must stick with that decision until the next timestep.
Regards,
 David


On 11/8/2010 10:25, Heloise PELEN wrote: 

Dear TRNSYS users,

 

The Type 56 uses a control on the air temperature « TAIR » to compute the sensible heat demand of each thermal zones.

This temperature does not include the surface temperature and doesn't fully describe the temperature actually felt by the human, body.

 

Is there a way to control the operative temperature, rather than on the air temperature, in type 56 ?

I thought about using Type 22 but the simulation seems rather unstable with more than on Type 22, and I would like to be able to control the operative temperature in each thermal zones.

 

Thanks for your help !

 

Best regards,

Héloïse Pelen

ETAMINE

 

heloise.pelen at etamine.coop <mailto:heloise.pelen at etamine.coop> 

75 rue de la Villette - 69003 Lyon

Std : 04 37 45 34 20 / Fax : 04 37 45 41 38

Ld : 04 37 45 34 13 / Port : 06 65 07 41 77

 

 

Visitez notre site web : www.etamine.coop !

 

 
 
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu
https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users

 

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
 
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
 
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20101116/94349fd2/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 5948 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20101116/94349fd2/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 2166 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20101116/94349fd2/attachment-0003.jpg>


More information about the TRNSYS-users mailing list