[TRNSYS-users] Type 334 Air handling Unit
Cramer Silkworth
silkworth at transsolar.com
Mon May 24 13:29:34 PDT 2010
Heike,
The frost protection functions as a bypass. The unit should be sending
air around the heat recovery core (directly to outside ) to maintain the
minimum outlet temperature. So you should end up with a lower
effectiveness compared to whatever you set.
-Cramer
--