[TRNSYS-users] PID Controller
LE GALL, Jace
jace.legall at bouygues-construction.com
Tue May 4 22:36:20 PDT 2010
David,
I had thought of this problem so I tried using a 'parameters' to create
a second signal opp = 1 - control_signal that I've set as an input on
the other port but it was still useless. Fortunately, it worked when I
changed to a Type11-f. So your advice would be to use the standard types
as often as possible (I am an new TRNSys user)?
Thank you for your helpful response,
Best regards,
Jace LE GALL
BYME Engineering Hub
From: David Bradley [mailto:bradley at tess-inc.com]
Sent: Wednesday, May 05, 2010 5:45 AM
To: LE GALL, Jace
Cc: trnsys-users at cae.wisc.edu
Subject: Re: [TRNSYS-users] PID Controller
Jace,
There is no fundamental incompatibility. Type647 expects a value
between 0 and 1 and the way you have your PID set up, it sounds like it
is outputting a value between 0 and 1. Bear in mind that Type647 does
not automatically divert the remainder of the flow to the other port. If
you have two outlets and all the flow that does not go one direction
automatically goes the other way, you might consider using Type11-f. And
no, this is not the first time I have ever recommended using a standard
Type in place of a TESS Type... :-)
Best,
David
--
Les donnees et renseignements contenus dans ce message sont personnels, confidentiels et secrets. Toute publication, utilisation ou diffusion, meme partielle, doit etre autorisee. Si vous n'etes pas le bon destinataire, nous vous demandons de ne pas lire, copier, utiliser ou divulguer cette communication. Nous vous prions de notifier cette erreur a l'expediteur et d'effacer immediatement cette communication de votre systeme.
Any data and information contained in this electronic mail is personal, confidential and secret. Any total or partial publication, use or distribution must be authorized. If you are not the right addressee, we ask you not to read, copy, use or disclose this communication. Please notify this error to the sender and erase at once this communication from your system.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100505/31bdbd72/attachment-0001.htm>
More information about the TRNSYS-users
mailing list