Heat pumps can't really do that - they are either on and operating at
whatever capacity they have available given the entering water
conditions or they are off. Unless they are multistage heat pumps, they
can't load follow and provide a constant outlet temperature regardless
of the inlet temperature. In reality and in simulation, you would have
to look for a method of actually doing that. One thing you could try is
to have a bypass valve upstream of the heat pump, oversize the heat pump
so that it can always heat or cool the liquid enough and then divert
some of the upstream liquid around the heat pump and mix it back in
downstream like a tempering valve.
Best,
David
Mavi Cambronero Vázquez wrote:
> Hi everybody!!
>
> I´d like to get a fixed outlet temperature from a water-water heat
> pump. Do you know how to do it???
>
> Thank you!!!
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100325/842d1f48/attachment-0001.htm>
More information about the TRNSYS-users
mailing list