[TRNSYS-users] Unheated Space
David Bradley
bradley at tess-inc.com
Thu Jun 17 08:15:48 PDT 2010
Samar,
I am a bit unclear on what you are trying to do. Typically an unheated
space would not have any set point associated with it; the temperature
would simply float and there would be no heating load on that space. If
you are modeling such a space but there is a heated space next to it,
you can treat the wall in between as a BOUNDARY wall in TRNBuild and
specify the surface temperature of the back side (the side that is in
the conditioned space, not the side that is in the unheated space). Note
that what you are asked to specify is the surface temperature, not the
temperature of the air in the adjacent space but as a first guess, you
could probably assume that the surface is at the set point temperature.
Best,
David
On 6/17/2010 03:10, Samar-Jumah-Mustafa.Jaber at Tu-Ilmenau.De wrote:
>
> Dear All,
>
> I am trying to calculate the heating and cooling load by using TRNSbuild.
>
> The problem that I have an entrance in my model which considers as
> unheated spaces with set point temperature around 18 C as the same
> time it is adjacent with other volume's.
>
> Is there any ways to translate this adjacent wall with temperature
> condition into TRNSbuild?
>
> Thank you for your kind assisstance in advance.
>
> Samar
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100617/301713d1/attachment-0005.htm>
More information about the TRNSYS-users
mailing list