<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.01 Transitional//EN">
<html>
<head>
  <meta content="text/html; charset=ISO-8859-1"
 http-equiv="Content-Type">
</head>
<body bgcolor="#ffffff" text="#000000">
Samar,<br>
 I am a bit unclear on what you are trying to do. Typically an unheated
space would not have any set point associated with it; the temperature
would simply float and there would be no heating load on that space. If
you are modeling such a space but there is a heated space next to it,
you can treat the wall in between as a BOUNDARY wall in TRNBuild and
specify the surface temperature of the back side (the side that is in
the conditioned space, not the side that is in the unheated space).
Note that what you are asked to specify is the surface temperature, not
the temperature of the air in the adjacent space but as a first guess,
you could probably assume that the surface is at the set point
temperature.<br>
Best,<br>
 David<br>
<br>
<br>
On 6/17/2010 03:10, <a class="moz-txt-link-abbreviated" href="mailto:Samar-Jumah-Mustafa.Jaber@Tu-Ilmenau.De">Samar-Jumah-Mustafa.Jaber@Tu-Ilmenau.De</a> wrote:
<blockquote
 cite="mid:249f4fce3e646fe3a770a88e1e10ceb5@merkur.rz.tu-ilmenau.de"
 type="cite">
  <p>Dear All,</p>
  <p>I am trying to calculate the heating and cooling load by using
TRNSbuild. </p>
  <p>The problem that I have an entrance in my model which considers as
unheated spaces with set point temperature around 18 C as the same time
it is adjacent with other volume's.</p>
  <p>Is there any ways to translate this adjacent wall with temperature
condition into TRNSbuild?</p>
  <p>Thank you for your kind assisstance in advance.</p>
  <p>Samar </p>
  <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
  </pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:bradley@tess-inc.com">bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>