[TRNSYS-users] TRNSYS-users Digest, Vol 67, Issue 61

王洋 wanghongyang1767 at gmail.com
Tue Jul 27 06:33:25 PDT 2010


Hi, Everyone!


Thanks a lot in advance!

I have some questions about TRNSYS:

1. About TRNSYS Building Description File: Where is it? How can i find it?

2.About TYPE's Output tab: Why some subjects have Value, some have Value 0?
Doesn't it have Value after running? Or basically it has Output Value?

3.Why Ambient Temperature isn't equal to Ventilation Air Temperature?

4. What's meaning of "Qequipment (Heat Transfer Rates of Zone
Equipment)=-2.00E+04" ?Can it be negative?

5. What's meaning of Heat Transfer Rates? What's the relationship between
Heat Transfer Rates and Energy Saving or Efficiency? Is it right that the
smaller(0 or Negative) the Value of Heat Transfer Rates is, the better the
Energy Saving or Efficiency is?

6. Which Type can calculate or compare the  energy consumption?

7. About the Equation: Whether is it similar to the Fortran Programming or
not? How to master the Equation Programming?

Br.

wang


2010/7/27 <trnsys-users-request at cae.wisc.edu>

> Send TRNSYS-users mailing list submissions to
>        trnsys-users at cae.wisc.edu
>
> To subscribe or unsubscribe via the World Wide Web, visit
>        https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
> or, via email, send a message with subject or body 'help' to
>        trnsys-users-request at cae.wisc.edu
>
> You can reach the person managing the list at
>        trnsys-users-owner at cae.wisc.edu
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of TRNSYS-users digest..."
>
> Today's Topics:
>
>   1. Re: TRNSYS-users Digest, Vol 67, Issue 59 (ghetu mariana)
>   2. trnsys 3d plugin error (Abdulhameed Mambo)
>
>
> ---------- 已转发邮件 ----------
> From: ghetu mariana <ghetu_mariana at yahoo.co.uk>
> To: trnsys-users at cae.wisc.edu
> Date: Tue, 27 Jul 2010 00:18:19 +0000 (GMT)
> Subject: Re: [TRNSYS-users] TRNSYS-users Digest, Vol 67, Issue 59
>  Pedro,
>
> You need to open TRNBuild first in order to open your  "project.bui".
> Otherwise you won't be able to do it.
>
> Best regards,
> Mariana
>
>  ------------------------------
> *From:* "trnsys-users-request at cae.wisc.edu" <
> trnsys-users-request at cae.wisc.edu>
> *To:* trnsys-users at cae.wisc.edu
> *Sent:* Mon, 26 July, 2010 11:10:57
> *Subject:* TRNSYS-users Digest, Vol 67, Issue 59
>
> Note: Forwarded message is attached.
>
> Send TRNSYS-users mailing list submissions to
>     trnsys-users at cae.wisc.edu
>
> To subscribe or unsubscribe via the World Wide Web, visit
>     https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
> or, via email, send a message with subject or body 'help' to
>     trnsys-users-request at cae.wisc.edu
>
> You can reach the person managing the list at
>     trnsys-users-owner at cae.wisc.edu
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of TRNSYS-users digest..."
> Today's Topics:
>
>   1. Re: Problem opennig "TRNSYS Building Description    File" out of
>       TRNBuild... (rgaray at labein.es)
>   2. Re: Problem opennig "TRNSYS Building Description File"    out of
>       TRNBuild... (Claros Marfil, Luis Jesus)
>   3. Re: Problem opennig "TRNSYS Building Description File"    out of
>       TRNBuild... (thiemann.stefan at vdi.de)
>   4. Dessicant Cooling (Julie Lestrade)
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
> Dear Pedro,
>
> I have also found that bug in trnbuild. This only happens when you try to
> open a file directly in the windows explorer.
> At least for me, the following sequence works properly:
> 1. open TRNBUILD
> 2. Open a file using the Open function/button in trnbuild
>
> Best regards,
>
> Roberto
>
> --------------------------------------------------------------------------
> Roberto Garay Martinez
> Labein-Tecnalia
> Unidad de Construcción y Desarrollo del Territorio
> c/Geldo. Parque Tecnológico de Bizkaia
> Edificio 700
> 48160 Derio (Bizkaia)
> Tel.: 34 94 607 33 00
> Fax: 34 94 607 33 49
> www.labein.es
> ---------------------------------------------------------------------------
> Visite nuestro blog:
> http://www.energiaenedificacion.com
> --------------------------------------------------------------------------
> ----- Mensaje de Pedro Gonçalves <pgoncalves.pt at gmail.com> en Fri, 23 Jul
> 2010 18:35:34 +0100 -----
> *Para:*
> <trnsys-users at cae.wisc.edu>
> *Asunto:*
> [TRNSYS-users] Problem opennig "TRNSYS Building Description File" out of
> TRNBuild...
> Dear All,
>
> When I´m trying to open "TRNSYS Building Description File" out of TRNBuild,
> appear a window with the following message: c:\program not found.
> I believe that is a problem of path definition in some place!!!
>
> Anyone knows how can I fix it?
>
> Thanks in advance.
> Regards,
> Pedro Gonçalves
>
> Hello Pedro,
>
>
>
> I think you should check the path of the “Building description file
> (*.bui)” in the “External Files” tab of the Type that you are using.
>
>
>
> Hope this help.
>
>
>
> Regards,
>
>
>
> Luis J. Claros
>  ------------------------------
>
> *De:* Pedro Gonçalves [mailto:pgoncalves.pt at gmail.com]
> *Enviado el:* viernes, 23 de julio de 2010 19:36
> *Para:* trnsys-users at cae.wisc.edu
> *Asunto:* [TRNSYS-users] Problem opennig "TRNSYS Building Description
> File" out of TRNBuild...
>
>
>
> Dear All,
>
>
>
> When I´m trying to open "TRNSYS Building Description File" out of TRNBuild,
> appear a window with the following message: c:\program not found.
>
> I believe that is a problem of path definition in some place!!!
>
>
>
> Anyone knows how can I fix it?
>
>
>
> Thanks in advance.
>
> Regards,
>
> Pedro Gonçalves
>
> Este mensaje se dirige exclusivamente a su destinatario, y puede contener información confidencial sometida a secreto profesional, o cuya divulgación esté legalmente prohibida. Cualquier opinión en él contenida es exclusiva de su autor y no representa necesariamente la opinión de la empresa. Si ha recibido este mensaje por error, le rogamos nos lo comunique de forma inmediata por esta misma vía y proceda a su eliminación, así como a la de cualquier documento adjunto al mismo. El correo electrónico vía Internet no es seguro y no se puede garantizar que no haya errores ya que puede ser interceptado, modificado, perdido o destruido, o contener virus. Cualquier persona que se ponga en contacto con nosotros por correo electrónico se considerará que asume estos riesgos.
>
> This e-mail is addressed exclusively to the recipient and may contain privileged information under a professional confidential agreement or it may be against the law to
>  disclose its contents. Any opinion contained in it belongs exclusively to his/her author and does not necessarily reflect the company’s view. If you receive this e-mail in error, please let us know immediately (by return e-mail) and proceed to its destruction, as well as any document attached to it. The sending of e-mails through the Internet is not safe and, therefore, error-free communications cannot be guaranteed, as they can be intercepted, changed, misled or destroyed or they might contain a virus. Any user contacting us through e-mails shall be understood to be assuming these risks.
>
> Hello,
>
> I think the problem is that Trnsys is based on Fortran and I
> discovered that it doesnt work properly if there is a space in the
> path. For example if your files are on the desktop you cant directly
> open the file.
>
> Best, Stefan
>
>
> -------------
> Hello Pedro,
>
> I think you should check the path of the "Building description file
> (*.bui)" in the "External Files" tab of the Type that you are using.
>
> Hope this help.
>
> Regards,
>
> Luis J. Claros
> ________________________________
> De: Pedro Gonçalves [mailto:pgoncalves.pt at gmail.com]
> Enviado el: viernes, 23 de julio de 2010 19:36
> Para: trnsys-users at cae.wisc.edu
> Asunto: [TRNSYS-users] Problem opennig "TRNSYS Building Description
> File" out of TRNBuild...
>
> Dear All,
>
> When I´m trying to open "TRNSYS Building Description File" out of
> TRNBuild, appear a window with the following message: c:\program not
> found.
> I believe that is a problem of path definition in some place!!!
>
> Anyone knows how can I fix it?
>
> Thanks in advance.
> Regards,
> Pedro Gonçalves
>
>
>
> Este mensaje se dirige exclusivamente a su destinatario, y puede
> contener información confidencial sometida a secreto profesional, o
> cuya divulgación esté legalmente prohibida. Cualquier opinión en
> él contenida es exclusiva de su autor y no representa necesariamente
> la opinión de la empresa. Si ha recibido este mensaje por error, le
> rogamos nos lo comunique de forma inmediata por esta misma vía y
> proceda a su eliminación, así como a la de cualquier documento
> adjunto al mismo. El correo electrónico vía Internet no es seguro y
> no se puede garantizar que no haya errores ya que puede ser
> interceptado, modificado, perdido o destruido, o contener virus.
> Cualquier persona que se ponga en contacto con nosotros por correo
> electrónico se considerará que asume estos riesgos.
>
> This e-mail is addressed exclusively to the recipient and may contain
> privileged information under a professional confidential agreement or
> it may be against the law to disclose its contents. Any opinion
> contained in it belongs exclusively to his/her author and does not
> necessarily reflect the company’s view. If you receive this e-mail
> in error, please let us know immediately (by return e-mail) and
> proceed to its destruction, as well as any document attached to it.
> The sending of e-mails through the Internet is not safe and,
> therefore, error-free communications cannot be guaranteed, as they
> can be intercepted, changed, misled or destroyed or they might
> contain a virus. Any user contacting us through e-mails shall be
> understood to be assuming these risks.
>
>
>
>
>
>
>
>
> Dear Trnsys Users,
>
> I was wondering if anyone has been trying to simulate a dessicant cooling
> installation ? Is there any tool very useful in the TESS library (I don't
> have access to a lot yet, since I could manage without them but who knows
> ...)
>
> thank you for any feedbacks on that subject,
>
> Best regards,
> Julie
>
> *Julie LESTRADE
> Ingénieur d'études
>
> CEDRE
> *Ophira 1, 1 Place Bermond
> 06560 SOPHIA-ANTIPOLIS
> Tel : 04 92 96 03 77
> Port : 06 45 68 07 53*
>
> *
>
>
>
>
> ---------- 已转发邮件 ----------
> From: Abdulhameed Mambo <A.D.Mambo at lboro.ac.uk>
> To: "trnsys-users at cae.wisc.edu" <trnsys-users at cae.wisc.edu>
> Date: Tue, 27 Jul 2010 12:23:33 +0100
> Subject: [TRNSYS-users] trnsys 3d plugin error
>
> I have been recieving this error messages whenever I attempted using
> trynsys 3d plugins. I wish to be helped.
>
>
>
>
>
> Sorry...the plugin has encountered an error.  This error may cause
> unpredictable behavior in the plugin--continue this session with caution!
> It would probably be a good idea to exit SketchUp and start again.
>
>
>
> For help, please contact hotline at transsolar.com, browse the list of known
> issues in the bug tracker, or post a new bug report.
>
>
>
> When reporting a bug, please include the error message and backtrace below
> (scroll down):
>
>
>
> ERROR:
>
> NoMethodError
>
> undefined method `reduce' for #<Array:0x11d0e148>
>
>
>
> BACKTRACE:
>
> C:/Program Files/Google/Google SketchUp
> 7/Plugins/Trnsys3d/lib/interfaces/DrawingUtils.rb:18:in `detect_base_face'
>
> C:/Program Files/Google/Google SketchUp
> 7/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:173:in `face_polygon'
>
> C:/Program Files/Google/Google SketchUp
> 7/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:172:in `each'
>
> C:/Program Files/Google/Google SketchUp
> 7/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:172:in `face_polygon'
>
> C:/Program Files/Google/Google SketchUp
> 7/Plugins/Trnsys3d/lib/interfaces/Surface.rb:107:in `update_input_object'
>
> C:/Program Files/Google/Google SketchUp
> 7/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:93:in `update_input_object'
>
> C:/Program Files/Google/Google SketchUp
> 7/Plugins/Trnsys3d/lib/interfaces/DrawingInterface.rb:219:in
> `create_from_entity'
>
> C:/Program Files/Google/Google SketchUp
> 7/Plugins/Trnsys3d/lib/interfaces/DrawingInterface.rb:206:in
> `new_from_entity'
>
> C:/Program Files/Google/Google SketchUp
> 7/Plugins/Trnsys3d/lib/observers/SurfaceGroupEntitiesObserver.rb:52:in
> `onElementAdded'
>
> C:/Program Files/Google/Google SketchUp
> 7/Plugins/Trnsys3d/lib/observers/SurfaceGroupEntitiesObserver.rb:23:in
> `initialize'
>
> C:/Program Files/Google/Google SketchUp
> 7/Plugins/Trnsys3d/lib/AsynchProc.rb:14:in `call'
>
> C:/Program Files/Google/Google SketchUp
> 7/Plugins/wxSU/lib/wxruby/lib/wx/classes/evthandler.rb:133:in
> `acquire_handler'
>
> C:/Program Files/Google/Google SketchUp
> 7/Plugins/wxSU/lib/wxruby/lib/wx/classes/evthandler.rb:133:in `call'
>
> (eval):960:in `notify'
>
> (eval):960
>
>
>
>
>
>
>
>
>
> Thank you.
>
> Mambo D A
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100727/db5b06cf/attachment-0005.htm>


More information about the TRNSYS-users mailing list