[TRNSYS-users] Optimisation.
gossard at cict.fr
gossard at cict.fr
Wed Jul 7 04:39:34 PDT 2010
Hi all,
I want to find the optimal characteristics (minimising the annual
energy-consumption) of the massive part of the external wall and study
the influence of the insulation layer (position or/and nature) on the
optimal characteristics of the massive part. My variables are the
conductivity, the capacity and the density of the massive part. I'm
using GenOpt2 and TRNSYS 16 for that.
If I understood correctly, the calculations of heat transfer through
the wall depend on the nature of the wall (if it is heavy or light)
and so, they depend on the wall time base. But how to adapt this wall
time base to the nature of each wall ? Is it possible to do it with
GenOpt commands ?
Please, find enclosed my BUI-file. The external wall I want to
optimize is called "MUREXT34" (external wall) and I search the optimal
characteristics of "PARPAING" (massive part).
Best regards,
Didier Gossard.
----------------------------------------------------------------
This message was sent using IMP, the Internet Messaging Program.
-------------- next part --------------
*********************************************************************************************************************************************************************************************************
* TRNBuild 1.0.94
*********************************************************************************************************************************************************************************************************
* BUILDING DESCRIPTIONS FILE TRNSYS
* FOR BUILDING: C:\Documents and Settings\gossard\Mes documents\M1_opt\Building.bui
* GET BY WORKING WITH TRNBuild 1.0 for Windows
*********************************************************************************************************************************************************************************************************
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* C o m m e n t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* P r o j e c t
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*+++ PROJECT
*+++ TITLE=BUI FOR TRNSYS 15.0
*+++ DESCRIPTION=GENERATED BY SIMCAD
*+++ CREATED=IISIBAT at CSTB.FR
*+++ ADDRESS=CSTB
*+++ CITY=F-06904 SOPHIA ANTIPOLIS
*+++ SWITCH=UNDEFINED
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* P r o p e r t i e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
PROPERTIES
DENSITY=1.204 : CAPACITY=1.012 : HVAPOR=2454.0 : SIGMA=2.041e-007 : RTEMP=293.15
*--- alpha calculation -------------------
KFLOORUP=7.2 : EFLOORUP=0.31 : KFLOORDOWN=3.888 : EFLOORDOWN=0.31
KCEILUP=7.2 : ECEILUP=0.31 : KCEILDOWN=3.888 : ECEILDOWN=0.31
KVERTICAL=5.76 : EVERTICAL=0.3
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
TYPES
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* L a y e r s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
LAYER PLATRBA13
CONDUCTIVITY= 1.227 : CAPACITY= 0.8 : DENSITY= 790
LAYER LAMEAIRCL
CONDUCTIVITY= 0.217 : CAPACITY= 1.227 : DENSITY= 1
LAYER LAINEROCHE
CONDUCTIVITY= 0.216 : CAPACITY= 1.03 : DENSITY= 8.83
LAYER ENDUITEXT
CONDUCTIVITY= 4.68 : CAPACITY= 1 : DENSITY= 1900
LAYER PARPAING
CONDUCTIVITY= 1.434 : CAPACITY= 2.843 : DENSITY= 874
LAYER POLYEXP
CONDUCTIVITY= 0.1368 : CAPACITY= 1.45 : DENSITY= 13
LAYER PLATRE
CONDUCTIVITY= 0.9 : CAPACITY= 1 : DENSITY= 750
LAYER BETON
CONDUCTIVITY= 7.2 : CAPACITY= 1 : DENSITY= 2400
LAYER HOURDISO
CONDUCTIVITY= 0.255 : CAPACITY= 1.3 : DENSITY= 368
LAYER BOIS
CONDUCTIVITY= 0.93 : CAPACITY= 2.4 : DENSITY= 650
LAYER ALUMINIUM
RESISTANCE= 0.001
LAYER TUILBETON
CONDUCTIVITY= 7.2 : CAPACITY= 1 : DENSITY= 2400
LAYER CBRFACPLB
RESISTANCE= 0.93
LAYER FICTIF
RESISTANCE= 0.001
LAYER CBRFACPLH
RESISTANCE= 5.55
LAYER CBRPOUPLB
RESISTANCE= 0.37
LAYER CBRFACFAC
RESISTANCE= 13.88
LAYER LAYER001
RESISTANCE= 1.4731
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* I n p u t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
INPUTS TTERRE VOLETS NUIT TVENT VNUIT
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* S c h e d u l e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
SCHEDULE PERSSEM
HOURS =0.000 7.000 16.000 24.0
VALUES=1. 0 1. 1.
SCHEDULE PERSWE
HOURS =0.000 24.0
VALUES=1. 1.
SCHEDULE ECLAIRE
HOURS =0.000 6.000 21.000 24.0
VALUES=0 1. 0 0
SCHEDULE ELECTROMEN
HOURS =0.000 17.000 21.000 24.0
VALUES=0 1. 0 0
SCHEDULE LAVAGE
HOURS =0.000 20.000 21.000 24.0
VALUES=0 1. 0 0
SCHEDULE CUISISEM
HOURS =0.000 18.000 19.000 24.0
VALUES=0 1. 0 0
SCHEDULE CUISIWE
HOURS =0.000 10.000 11.000 18.000 19.000 24.0
VALUES=0 1. 0 1. 0 0
SCHEDULE RALENTCH
HOURS =0.000 6.000 7.000 22.000 24.0
VALUES=17. 18. 19. 17. 17.
SCHEDULE SCHED001
HOURS =0.000 16.000 22.000 24.0
VALUES=0 1. 0 0
SCHEDULE PERSONNE
DAYS=1 2 3 4 5 6 7
HOURLY=PERSSEM PERSSEM PERSSEM PERSSEM PERSSEM PERSWE PERSWE
SCHEDULE CUISINE
DAYS=1 2 3 4 5 6 7
HOURLY=CUISISEM CUISISEM CUISISEM CUISISEM CUISISEM CUISIWE CUISIWE
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* W a l l s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
WALL DALBASSE
LAYERS = BETON POLYEXP
THICKNESS= 0.2 0.1
ABS-FRONT= 0.6 : ABS-BACK= 0.6
HFRONT = 21.2 : HBACK= 72
WALL DALINTER
LAYERS = PLATRE LAINEROCHE
THICKNESS= 0.01 0.3
ABS-FRONT= 0.1 : ABS-BACK= 0.3
HFRONT = 36 : HBACK= 90
WALL CLOISON05
LAYERS = PLATRBA13 LAMEAIRCL PLATRBA13
THICKNESS= 0.013 0.05 0.013
ABS-FRONT= 0.3 : ABS-BACK= 0.3
HFRONT = 27.69 : HBACK= 27.69
WALL MUREXT34
LAYERS = PLATRE POLYEXP PARPAING ENDUITEXT
THICKNESS= 0.01 0.2 0.2 0.015
ABS-FRONT= 0.3 : ABS-BACK= 0.25
HFRONT = 27.69 : HBACK= 90
WALL PORTGARA
LAYERS = ALUMINIUM
THICKNESS= 0
ABS-FRONT= 0.6 : ABS-BACK= 0.6
HFRONT = 27.69 : HBACK= 90
WALL MURGAR22
LAYERS = PLATRE PARPAING ENDUITEXT
THICKNESS= 0.01 0.2 0.015
ABS-FRONT= 0.3 : ABS-BACK= 0.25
HFRONT = 27.69 : HBACK= 90
WALL TOITURE
LAYERS = TUILBETON
THICKNESS= 0.025
ABS-FRONT= 0.6 : ABS-BACK= 0.6
HFRONT = 36 : HBACK= 90
WALL PORTEBOIS
LAYERS = BOIS POLYEXP BOIS
THICKNESS= 0.016 0.008 0.016
ABS-FRONT= 0.6 : ABS-BACK= 0.6
HFRONT = 27.69 : HBACK= 90
WALL CBRFACPLB
LAYERS = CBRFACPLB
THICKNESS= 0
ABS-FRONT= 0.6 : ABS-BACK= 0.6
HFRONT = 11 : HBACK= 64
WALL CBRFACPLH
LAYERS = CBRFACPLH
THICKNESS= 0
ABS-FRONT= 0.6 : ABS-BACK= 0.6
HFRONT = 11 : HBACK= 64
WALL CBRPOUPLB
LAYERS = CBRPOUPLB
THICKNESS= 0
ABS-FRONT= 0.6 : ABS-BACK= 0.6
HFRONT = 11 : HBACK= 64
WALL CBRFACFAC
LAYERS = CBRFACFAC
THICKNESS= 0
ABS-FRONT= 0.6 : ABS-BACK= 0.6
HFRONT = 11 : HBACK= 64
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* W i n d o w s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
WINDOW DOUBLE
WINID=5001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.15 : UFRAME=1.8 : ABSFRAME=0.15 : RISHADE=0 : RESHADE=INPUT 0.053*VOLETS : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* D e f a u l t G a i n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
GAIN PERS_ISO04
CONVECTIVE=180 : RADIATIVE=90 : HUMIDITY=0.11
GAIN LIGHT01_01
CONVECTIVE=INPUT 432*NUIT : RADIATIVE=INPUT 648*NUIT : HUMIDITY=0
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* O t h e r G a i n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
GAIN CUISSON
CONVECTIVE=86 : RADIATIVE=774 : HUMIDITY=0
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* C o m f o r t
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* I n f i l t r a t i o n
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
INFILTRATION INFIL001
AIRCHANGE=INPUT 3*VNUIT+0.2
INFILTRATION INFILGAR
AIRCHANGE=1
INFILTRATION INFILCOMB
AIRCHANGE=0.8
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* V e n t i l a t i o n
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
VENTILATION VENT001
TEMPERATURE=OUTSIDE
AIRCHANGE=0.66
HUMIDITY=OUTSIDE
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* C o o l i n g
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
COOLING COOL001
ON=26
POWER=999999999
HUMIDITY=100
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* H e a t i n g
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
HEATING HEAT001
ON=SCHEDULE 1*RALENTCH
POWER=999999999
HUMIDITY=0
RRAD=0.7
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONES ZON01 ZON02 ZON03 ZON04 ZON05
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* O r i e n t a t i o n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ORIENTATIONS NORD SUD EST OUEST TOITNORD TOITSUD
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
BUILDING
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZON01 / A i r n o d e ZON01
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZON01
AIRNODE ZON01
WALL =DALBASSE : SURF= 1 : AREA= 49.91 : BOUNDARY=INPUT 1*TTERRE
WALL =DALINTER : SURF= 2 : AREA= 49.91 : ADJACENT=ZON05 : FRONT
WALL =MUREXT34 : SURF= 3 : AREA= 14.43 : EXTERNAL : ORI=SUD : FSKY=0.5
WINDOW=DOUBLE : SURF= 4 : AREA= 1.5 : EXTERNAL : ORI=SUD : FSKY=0.5 : ESHADE=INPUT 1*VOLETS
WINDOW=DOUBLE : SURF= 5 : AREA= 1.26 : EXTERNAL : ORI=SUD : FSKY=0.5 : ESHADE=INPUT 1*VOLETS
WALL =MUREXT34 : SURF= 6 : AREA= 11.86 : EXTERNAL : ORI=NORD : FSKY=0.5
WINDOW=DOUBLE : SURF= 7 : AREA= 2.58 : EXTERNAL : ORI=NORD : FSKY=0.5 : ESHADE=INPUT 1*VOLETS
WALL =MUREXT34 : SURF= 9 : AREA= 5.92 : EXTERNAL : ORI=OUEST : FSKY=0.5
WALL =MUREXT34 : SURF= 10 : AREA= 2.15 : EXTERNAL : ORI=EST : FSKY=0.5
WALL =CLOISON05 : SURF= 11 : AREA= 4.3 : INTERNAL
WALL =CLOISON05 : SURF= 12 : AREA= 19.59 : ADJACENT=ZON03 : BACK
WALL =CLOISON05 : SURF= 13 : AREA= 23.72 : ADJACENT=ZON02 : BACK
WALL =MUREXT34 : SURF= 14 : AREA= 12.7 : ADJACENT=ZON04 : FRONT
WALL =PORTEBOIS : SURF= 8 : AREA= 1.94 : EXTERNAL : ORI=NORD : FSKY=0.5
WALL =PORTEBOIS : SURF= 44 : AREA= 1.68 : ADJACENT=ZON04 : BACK
WALL =CBRFACPLH : SURF= 39 : LENGTH= 13.75 : EXTERNAL : ORI=NORD : FSKY=0.5
WALL =CBRFACPLB : SURF= 48 : LENGTH= 13.75 : EXTERNAL : ORI=NORD : FSKY=0.5
WALL =CBRPOUPLB : SURF= 52 : LENGTH= 10.3 : EXTERNAL : ORI=NORD : FSKY=0.5
WALL =CBRFACFAC : SURF= 53 : LENGTH= 2.5 : EXTERNAL : ORI=NORD : FSKY=0.5
REGIME
GAIN = PERS_ISO04 : SCALE= SCHEDULE 1.5*SCHED001
GAIN = LIGHT01_01 : SCALE= SCHEDULE 1*ECLAIRE
GAIN = CUISSON : SCALE= SCHEDULE 1*CUISINE
INFILTRATION= INFIL001
VENTILATION = VENT001
COOLING = COOL001
HEATING = HEAT001
CAPACITANCE = 393.924 : VOLUME= 128.27 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZON02 / A i r n o d e ZON02
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZON02
AIRNODE ZON02
WALL =DALBASSE : SURF= 15 : AREA= 19.87 : BOUNDARY=INPUT 1*TTERRE
WALL =DALINTER : SURF= 16 : AREA= 19.87 : ADJACENT=ZON05 : FRONT
WALL =MUREXT34 : SURF= 17 : AREA= 12.86 : EXTERNAL : ORI=NORD : FSKY=0.5
WINDOW=DOUBLE : SURF= 18 : AREA= 2.07 : EXTERNAL : ORI=NORD : FSKY=0.5 : ESHADE=INPUT 1*VOLETS
WALL =MUREXT34 : SURF= 19 : AREA= 8.79 : EXTERNAL : ORI=EST : FSKY=0.5
WALL =CLOISON05 : SURF= 20 : AREA= 17.58 : INTERNAL
WALL =CLOISON05 : SURF= 21 : AREA= 23.72 : ADJACENT=ZON01 : FRONT
WALL =CBRFACPLB : SURF= 41 : LENGTH= 7.25 : EXTERNAL : ORI=NORD : FSKY=0.5
WALL =CBRFACPLH : SURF= 49 : LENGTH= 7.25 : EXTERNAL : ORI=NORD : FSKY=0.5
WALL =CBRFACFAC : SURF= 54 : LENGTH= 2.5 : EXTERNAL : ORI=NORD : FSKY=0.5
REGIME
INFILTRATION= INFIL001
VENTILATION = VENT001
COOLING = COOL001
HEATING = HEAT001
CAPACITANCE = 181.272 : VOLUME= 51.06 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZON03 / A i r n o d e ZON03
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZON03
AIRNODE ZON03
WALL =DALBASSE : SURF= 22 : AREA= 14.49 : BOUNDARY=INPUT 1*TTERRE
WALL =DALINTER : SURF= 23 : AREA= 14.49 : ADJACENT=ZON05 : FRONT
WALL =CLOISON05 : SURF= 24 : AREA= 19.59 : ADJACENT=ZON01 : FRONT
WALL =MUREXT34 : SURF= 25 : AREA= 8.72 : EXTERNAL : ORI=SUD : FSKY=0.5
WINDOW=DOUBLE : SURF= 26 : AREA= 1.5 : EXTERNAL : ORI=SUD : FSKY=0.5 : ESHADE=INPUT 1*VOLETS
WALL =MUREXT34 : SURF= 27 : AREA= 9.36 : EXTERNAL : ORI=EST : FSKY=0.5
WALL =CBRFACPLB : SURF= 47 : LENGTH= 9.3 : EXTERNAL : ORI=NORD : FSKY=0.5
WALL =CBRFACPLH : SURF= 50 : LENGTH= 9.3 : EXTERNAL : ORI=NORD : FSKY=0.5
WALL =CBRFACFAC : SURF= 55 : LENGTH= 2.5 : EXTERNAL : ORI=NORD : FSKY=0.5
REGIME
INFILTRATION= INFIL001
VENTILATION = VENT001
COOLING = COOL001
HEATING = HEAT001
CAPACITANCE = 164.688 : VOLUME= 37.24 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZON04 / A i r n o d e ZON04
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZON04
AIRNODE ZON04
WALL =DALBASSE : SURF= 28 : AREA= 18.59 : BOUNDARY=INPUT 1*TTERRE
WALL =TOITURE : SURF= 29 : AREA= 21.26 : EXTERNAL : ORI=TOITNORD : FSKY=1
WALL =MURGAR22 : SURF= 30 : AREA= 8.45 : EXTERNAL : ORI=SUD : FSKY=0.5
WALL =PORTGARA : SURF= 31 : AREA= 6.18 : EXTERNAL : ORI=NORD : FSKY=0.5
WALL =MURGAR22 : SURF= 32 : AREA= 2.26 : EXTERNAL : ORI=NORD : FSKY=0.5
WALL =MURGAR22 : SURF= 33 : AREA= 14.54 : EXTERNAL : ORI=OUEST : FSKY=0.5
WALL =MUREXT34 : SURF= 34 : AREA= 12.7 : ADJACENT=ZON01 : BACK
WALL =PORTEBOIS : SURF= 43 : AREA= 1.68 : ADJACENT=ZON01 : FRONT
REGIME
INFILTRATION= INFILGAR
CAPACITANCE = 57.324 : VOLUME= 47.77 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZON05 / A i r n o d e ZON05
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZON05
AIRNODE ZON05
WALL =DALINTER : SURF= 35 : AREA= 49.91 : ADJACENT=ZON01 : BACK
WALL =DALINTER : SURF= 36 : AREA= 19.87 : ADJACENT=ZON02 : BACK
WALL =DALINTER : SURF= 37 : AREA= 14.49 : ADJACENT=ZON03 : BACK
WALL =TOITURE : SURF= 38 : AREA= 48 : EXTERNAL : ORI=TOITNORD : FSKY=1
WALL =MURGAR22 : SURF= 40 : AREA= 8.26 : EXTERNAL : ORI=OUEST : FSKY=0.5
WALL =MURGAR22 : SURF= 42 : AREA= 8.26 : EXTERNAL : ORI=EST : FSKY=0.5
WALL =TOITURE : SURF= 59 : AREA= 48 : EXTERNAL : ORI=TOITSUD : FSKY=0.5
REGIME
INFILTRATION= INFILCOMB
CAPACITANCE = 560.148 : VOLUME= 66.79 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* O u t p u t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
OUTPUTS
TRANSFER : TIMEBASE=1.000
AIRNODES = ZON01 ZON02 ZON03 ZON04 ZON05
NTYPES = 1 : TAIR - air temperature of zone
= 30 : QHEAT - sensible heating demand of zone (positive values)
= 31 : QCOOL - sensible cooling demand of zone (positive values)
= 32 : SQHEAT - sum of sensible heating demand for group of zones (positive values)
= 33 : SQCOOL - sum of sensible cooling demand for group of zones (positive values)
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* E n d
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
END
_EXTENSION_WINPOOL_START_
WINDOW 4.1 DOE-2 Data File : Multi Band Calculation
Unit System : SI
Name : TRNSYS 15 WINDOW LIB
Desc : Isolierglas, 2.8
Window ID : 1002
Tilt : 90.0
Glazings : 2
Frame : 11 2.270
Spacer : 1 Class1 2.330 -0.010 0.138
Total Height: 1219.2 mm
Total Width : 914.4 mm
Glass Height: 1079.5 mm
Glass Width : 774.7 mm
Mullion : None
Gap Thick Cond dCond Vis dVis Dens dDens Pr dPr
1 Air 16.0 0.02410 7.600 1.730 10.000 1.290 -0.0044 0.720 0.00180
2 0 0 0 0 0 0 0 0 0
3 0 0 0 0 0 0 0 0 0
4 0 0 0 0 0 0 0 0 0
5 0 0 0 0 0 0 0 0 0
Angle 0 10 20 30 40 50 60 70 80 90 Hemis
Tsol 0.693 0.692 0.688 0.681 0.666 0.633 0.565 0.426 0.197 0.000 0.590
Abs1 0.101 0.102 0.104 0.107 0.112 0.118 0.126 0.137 0.143 0.000 0.116
Abs2 0.080 0.080 0.081 0.083 0.086 0.087 0.087 0.079 0.058 0.000 0.082
Abs3 0 0 0 0 0 0 0 0 0 0 0
Abs4 0 0 0 0 0 0 0 0 0 0 0
Abs5 0 0 0 0 0 0 0 0 0 0 0
Abs6 0 0 0 0 0 0 0 0 0 0 0
Rfsol 0.126 0.126 0.126 0.128 0.137 0.161 0.223 0.358 0.601 1.000 0.202
Rbsol 0.126 0.126 0.126 0.128 0.137 0.161 0.223 0.358 0.601 1.000 0.202
Tvis 0.817 0.816 0.815 0.811 0.799 0.768 0.695 0.538 0.273 0.000 0.714
Rfvis 0.148 0.148 0.148 0.151 0.162 0.191 0.262 0.417 0.682 1.000 0.236
Rbvis 0.148 0.148 0.148 0.151 0.162 0.191 0.262 0.417 0.682 1.000 0.236
SHGC 0.755 0.754 0.752 0.746 0.733 0.703 0.635 0.493 0.252 0.000 0.655
SC: 0.69
Layer ID# 9052 9052 0 0 0 0
Tir 0.000 0.000 0 0 0 0
Emis F 0.840 0.840 0 0 0 0
Emis B 0.840 0.840 0 0 0 0
Thickness(mm) 4.0 4.0 0 0 0 0
Cond(W/m2-C ) 225.0 225.0 0 0 0 0
Spectral File None None None None None None
Overall and Center of Glass Ig U-values (W/m2-C)
Outdoor Temperature -17.8 C 15.6 C 26.7 C 37.8 C
Solar WdSpd hcout hrout hin
(W/m2) (m/s) (W/m2-C)
0 0.00 12.25 3.29 7.89 2.56 2.56 2.56 2.56 2.64 2.64 2.85 2.85
0 6.71 25.47 3.24 7.93 2.77 2.77 2.75 2.75 2.83 2.83 3.07 3.07
783 0.00 12.25 3.40 7.49 2.58 2.58 2.72 2.72 2.87 2.87 3.01 3.01
783 6.71 25.47 3.31 7.64 2.80 2.80 2.88 2.88 3.07 3.07 3.22 3.22
WINDOW 4.1 TRNSYS 15 Data File : Multi Band Calculation
Unit System : SI
Name : TRNSYS 15 WINDOW LIB
Desc : Dble,Low-e,Ar
Window ID : 5001
Tilt : 90.0
Glazings : 2
Frame : 1 Al no break 10.790
Spacer : 1 Class1 2.330 -0.010 0.138
Total Height: 1219.2 mm
Total Width : 914.4 mm
Glass Height: 1104.9 mm
Glass Width : 800.1 mm
Mullion : None
Gap Thick Cond dCond Vis dVis Dens dDens Pr dPr
1 Argon 12.7 0.01620 5.000 2.110 6.300 1.780 -0.0060 0.680 0.00066
2 0 0 0 0 0 0 0 0 0
3 0 0 0 0 0 0 0 0 0
4 0 0 0 0 0 0 0 0 0
5 0 0 0 0 0 0 0 0 0
Angle 0 10 20 30 40 50 60 70 80 90 Hemis
Tsol 0.544 0.548 0.539 0.529 0.514 0.486 0.426 0.312 0.145 0.000 0.453
Abs1 0.187 0.190 0.200 0.207 0.210 0.218 0.242 0.273 0.248 0.001 0.221
Abs2 0.048 0.049 0.049 0.050 0.051 0.052 0.050 0.045 0.033 0.000 0.048
Abs3 0 0 0 0 0 0 0 0 0 0 0
Abs4 0 0 0 0 0 0 0 0 0 0 0
Abs5 0 0 0 0 0 0 0 0 0 0 0
Abs6 0 0 0 0 0 0 0 0 0 0 0
Rfsol 0.220 0.214 0.212 0.214 0.224 0.244 0.282 0.371 0.574 0.999 0.268
Rbsol 0.236 0.231 0.230 0.232 0.241 0.261 0.307 0.414 0.629 1.000 0.291
Tvis 0.769 0.774 0.763 0.749 0.730 0.692 0.605 0.440 0.205 0.000 0.642
Rfvis 0.138 0.131 0.128 0.131 0.143 0.168 0.217 0.323 0.549 0.999 0.197
Rbvis 0.127 0.120 0.119 0.124 0.138 0.168 0.233 0.379 0.650 1.000 0.208
SHGC 0.596 0.600 0.592 0.583 0.569 0.543 0.483 0.366 0.188 0.000 0.507
SC: 0.69
Layer ID# 400 1 0 0 0 0
Tir 0.000 0.000 0 0 0 0
Emis F 0.840 0.840 0 0 0 0
Emis B 0.100 0.840 0 0 0 0
Thickness(mm) 3.0 2.5 0 0 0 0
Cond(W/m2-C ) 300.0 360.0 0 0 0 0
Spectral File None None None None None None
Overall and Center of Glass Ig U-values (W/m2-C)
Outdoor Temperature -17.8 C 15.6 C 26.7 C 37.8 C
Solar WdSpd hcout hrout hin
(W/m2) (m/s) (W/m2-C)
0 0.00 12.25 3.24 7.59 1.44 1.44 1.35 1.35 1.38 1.38 1.45 1.45
0 6.71 25.47 3.21 7.62 1.51 1.51 1.39 1.39 1.43 1.43 1.51 1.51
783 0.00 12.25 3.41 6.82 1.41 1.41 1.42 1.42 1.47 1.47 1.53 1.53
783 6.71 25.47 3.31 7.10 1.51 1.51 1.45 1.45 1.51 1.51 1.56 1.56
*** END OF LIBRARY ***
***************************************************************************************************
*WinID Description Design U-Value g-value T-sol Rf-sol T-vis
***************************************************************************************************
1002 Isolierglas, 2.8 4/16/4 2.83 0.755 0.693 0.126 0.817
5001 Dble,Low-e,Ar 3/12.7/2.5 1.43 0.596 0.544 0.22 0.769
_EXTENSION_WINPOOL_END_
More information about the TRNSYS-users
mailing list