[TRNSYS-users] Optimisation.

gossard at cict.fr gossard at cict.fr
Wed Jul 7 04:39:34 PDT 2010


Hi all,

I want to find the optimal characteristics (minimising the annual  
energy-consumption) of the massive part of the external wall and study  
the influence of the insulation layer (position or/and nature) on the  
optimal characteristics of the massive part. My variables are the  
conductivity, the capacity and the density of the massive part. I'm  
using GenOpt2 and TRNSYS 16 for that.
If I understood correctly, the calculations of heat transfer through  
the wall depend on the nature of the wall (if it is heavy or light)  
and so, they depend on the wall time base. But how to adapt this wall  
time base to the nature of each wall ? Is it possible to do it with  
GenOpt commands ?

Please, find enclosed my BUI-file. The external wall I want to  
optimize is called "MUREXT34" (external wall) and I search the optimal  
characteristics of "PARPAING" (massive part).

Best regards,
Didier Gossard.

----------------------------------------------------------------
This message was sent using IMP, the Internet Messaging Program.

-------------- next part --------------
*********************************************************************************************************************************************************************************************************
*  TRNBuild   1.0.94
*********************************************************************************************************************************************************************************************************
*   BUILDING DESCRIPTIONS FILE TRNSYS
*   FOR BUILDING:   C:\Documents and Settings\gossard\Mes documents\M1_opt\Building.bui
*   GET BY WORKING WITH TRNBuild 1.0 for Windows
*********************************************************************************************************************************************************************************************************
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  C o m m e n t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  P r o j e c t
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*+++ PROJECT
*+++ TITLE=BUI FOR TRNSYS 15.0
*+++ DESCRIPTION=GENERATED BY SIMCAD
*+++ CREATED=IISIBAT at CSTB.FR
*+++ ADDRESS=CSTB
*+++ CITY=F-06904 SOPHIA ANTIPOLIS
*+++ SWITCH=UNDEFINED
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  P r o p e r t i e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
PROPERTIES
 DENSITY=1.204 : CAPACITY=1.012 : HVAPOR=2454.0 : SIGMA=2.041e-007 : RTEMP=293.15
*--- alpha calculation -------------------
 KFLOORUP=7.2 : EFLOORUP=0.31 : KFLOORDOWN=3.888 : EFLOORDOWN=0.31
 KCEILUP=7.2 : ECEILUP=0.31 : KCEILDOWN=3.888 : ECEILDOWN=0.31
 KVERTICAL=5.76 : EVERTICAL=0.3
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
TYPES
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  L a y e r s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
LAYER PLATRBA13
 CONDUCTIVITY=  1.227 : CAPACITY=    0.8 : DENSITY=    790
LAYER LAMEAIRCL
 CONDUCTIVITY=  0.217 : CAPACITY=  1.227 : DENSITY=      1
LAYER LAINEROCHE
 CONDUCTIVITY=  0.216 : CAPACITY=   1.03 : DENSITY=   8.83
LAYER ENDUITEXT
 CONDUCTIVITY=   4.68 : CAPACITY=      1 : DENSITY=   1900
LAYER PARPAING
 CONDUCTIVITY=  1.434 : CAPACITY=  2.843 : DENSITY=    874
LAYER POLYEXP
 CONDUCTIVITY= 0.1368 : CAPACITY=   1.45 : DENSITY=     13
LAYER PLATRE
 CONDUCTIVITY=    0.9 : CAPACITY=      1 : DENSITY=    750
LAYER BETON
 CONDUCTIVITY=    7.2 : CAPACITY=      1 : DENSITY=   2400
LAYER HOURDISO
 CONDUCTIVITY=  0.255 : CAPACITY=    1.3 : DENSITY=    368
LAYER BOIS
 CONDUCTIVITY=   0.93 : CAPACITY=    2.4 : DENSITY=    650
LAYER ALUMINIUM
 RESISTANCE=    0.001
LAYER TUILBETON
 CONDUCTIVITY=    7.2 : CAPACITY=      1 : DENSITY=   2400
LAYER CBRFACPLB
 RESISTANCE=     0.93
LAYER FICTIF
 RESISTANCE=    0.001
LAYER CBRFACPLH
 RESISTANCE=     5.55
LAYER CBRPOUPLB
 RESISTANCE=     0.37
LAYER CBRFACFAC
 RESISTANCE=    13.88
LAYER LAYER001
 RESISTANCE=   1.4731
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  I n p u t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
INPUTS TTERRE VOLETS NUIT TVENT VNUIT
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  S c h e d u l e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
SCHEDULE PERSSEM
 HOURS =0.000 7.000 16.000 24.0
 VALUES=1. 0 1. 1. 
SCHEDULE PERSWE
 HOURS =0.000 24.0
 VALUES=1. 1. 
SCHEDULE ECLAIRE
 HOURS =0.000 6.000 21.000 24.0
 VALUES=0 1. 0 0 
SCHEDULE ELECTROMEN
 HOURS =0.000 17.000 21.000 24.0
 VALUES=0 1. 0 0 
SCHEDULE LAVAGE
 HOURS =0.000 20.000 21.000 24.0
 VALUES=0 1. 0 0 
SCHEDULE CUISISEM
 HOURS =0.000 18.000 19.000 24.0
 VALUES=0 1. 0 0 
SCHEDULE CUISIWE
 HOURS =0.000 10.000 11.000 18.000 19.000 24.0
 VALUES=0 1. 0 1. 0 0 
SCHEDULE RALENTCH
 HOURS =0.000 6.000 7.000 22.000 24.0
 VALUES=17. 18. 19. 17. 17. 
SCHEDULE SCHED001
 HOURS =0.000 16.000 22.000 24.0
 VALUES=0 1. 0 0 
SCHEDULE PERSONNE
 DAYS=1 2 3 4 5 6 7
 HOURLY=PERSSEM PERSSEM PERSSEM PERSSEM PERSSEM PERSWE PERSWE
SCHEDULE CUISINE
 DAYS=1 2 3 4 5 6 7
 HOURLY=CUISISEM CUISISEM CUISISEM CUISISEM CUISISEM CUISIWE CUISIWE
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  W a l l s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
WALL DALBASSE
 LAYERS   = BETON POLYEXP 
 THICKNESS= 0.2   0.1     
 ABS-FRONT= 0.6   : ABS-BACK= 0.6  
 HFRONT   = 21.2 : HBACK= 72
WALL DALINTER
 LAYERS   = PLATRE LAINEROCHE 
 THICKNESS= 0.01   0.3        
 ABS-FRONT= 0.1   : ABS-BACK= 0.3  
 HFRONT   = 36 : HBACK= 90
WALL CLOISON05
 LAYERS   = PLATRBA13 LAMEAIRCL PLATRBA13 
 THICKNESS= 0.013     0.05      0.013     
 ABS-FRONT= 0.3   : ABS-BACK= 0.3  
 HFRONT   = 27.69 : HBACK= 27.69
WALL MUREXT34
 LAYERS   = PLATRE POLYEXP PARPAING ENDUITEXT 
 THICKNESS= 0.01   0.2     0.2      0.015     
 ABS-FRONT= 0.3   : ABS-BACK= 0.25 
 HFRONT   = 27.69 : HBACK= 90
WALL PORTGARA
 LAYERS   = ALUMINIUM 
 THICKNESS= 0         
 ABS-FRONT= 0.6   : ABS-BACK= 0.6  
 HFRONT   = 27.69 : HBACK= 90
WALL MURGAR22
 LAYERS   = PLATRE PARPAING ENDUITEXT 
 THICKNESS= 0.01   0.2      0.015     
 ABS-FRONT= 0.3   : ABS-BACK= 0.25 
 HFRONT   = 27.69 : HBACK= 90
WALL TOITURE
 LAYERS   = TUILBETON 
 THICKNESS= 0.025     
 ABS-FRONT= 0.6   : ABS-BACK= 0.6  
 HFRONT   = 36 : HBACK= 90
WALL PORTEBOIS
 LAYERS   = BOIS  POLYEXP BOIS  
 THICKNESS= 0.016 0.008   0.016 
 ABS-FRONT= 0.6   : ABS-BACK= 0.6  
 HFRONT   = 27.69 : HBACK= 90
WALL CBRFACPLB
 LAYERS   = CBRFACPLB 
 THICKNESS= 0         
 ABS-FRONT= 0.6   : ABS-BACK= 0.6  
 HFRONT   = 11 : HBACK= 64
WALL CBRFACPLH
 LAYERS   = CBRFACPLH 
 THICKNESS= 0         
 ABS-FRONT= 0.6   : ABS-BACK= 0.6  
 HFRONT   = 11 : HBACK= 64
WALL CBRPOUPLB
 LAYERS   = CBRPOUPLB 
 THICKNESS= 0         
 ABS-FRONT= 0.6   : ABS-BACK= 0.6  
 HFRONT   = 11 : HBACK= 64
WALL CBRFACFAC
 LAYERS   = CBRFACFAC 
 THICKNESS= 0         
 ABS-FRONT= 0.6   : ABS-BACK= 0.6  
 HFRONT   = 11 : HBACK= 64
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  W i n d o w s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
WINDOW DOUBLE
 WINID=5001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.15 : UFRAME=1.8 : ABSFRAME=0.15 : RISHADE=0 : RESHADE=INPUT 0.053*VOLETS : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
 CCISHADE=0.5
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  D e f a u l t  G a i n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
GAIN PERS_ISO04
 CONVECTIVE=180 : RADIATIVE=90 : HUMIDITY=0.11
GAIN LIGHT01_01
 CONVECTIVE=INPUT 432*NUIT : RADIATIVE=INPUT 648*NUIT : HUMIDITY=0
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  O t h e r  G a i n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
GAIN CUISSON
 CONVECTIVE=86 : RADIATIVE=774 : HUMIDITY=0
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  C o m f o r t
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  I n f i l t r a t i o n
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
INFILTRATION INFIL001
 AIRCHANGE=INPUT 3*VNUIT+0.2
INFILTRATION INFILGAR
 AIRCHANGE=1
INFILTRATION INFILCOMB
 AIRCHANGE=0.8
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  V e n t i l a t i o n
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
VENTILATION VENT001
 TEMPERATURE=OUTSIDE
 AIRCHANGE=0.66
 HUMIDITY=OUTSIDE
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  C o o l i n g
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
COOLING COOL001
 ON=26
 POWER=999999999
 HUMIDITY=100
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  H e a t i n g
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
HEATING HEAT001
 ON=SCHEDULE 1*RALENTCH
 POWER=999999999
 HUMIDITY=0
 RRAD=0.7
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONES ZON01 ZON02 ZON03 ZON04 ZON05
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  O r i e n t a t i o n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ORIENTATIONS NORD SUD EST OUEST TOITNORD TOITSUD
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
BUILDING
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZON01  /  A i r n o d e  ZON01
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZON01
AIRNODE ZON01
WALL  =DALBASSE   : SURF=  1 : AREA=     49.91 : BOUNDARY=INPUT 1*TTERRE
WALL  =DALINTER   : SURF=  2 : AREA=     49.91 : ADJACENT=ZON05 : FRONT
WALL  =MUREXT34   : SURF=  3 : AREA=     14.43 : EXTERNAL : ORI=SUD : FSKY=0.5
WINDOW=DOUBLE     : SURF=  4 : AREA=       1.5 : EXTERNAL : ORI=SUD : FSKY=0.5 : ESHADE=INPUT 1*VOLETS
WINDOW=DOUBLE     : SURF=  5 : AREA=      1.26 : EXTERNAL : ORI=SUD : FSKY=0.5 : ESHADE=INPUT 1*VOLETS
WALL  =MUREXT34   : SURF=  6 : AREA=     11.86 : EXTERNAL : ORI=NORD : FSKY=0.5
WINDOW=DOUBLE     : SURF=  7 : AREA=      2.58 : EXTERNAL : ORI=NORD : FSKY=0.5 : ESHADE=INPUT 1*VOLETS
WALL  =MUREXT34   : SURF=  9 : AREA=      5.92 : EXTERNAL : ORI=OUEST : FSKY=0.5
WALL  =MUREXT34   : SURF= 10 : AREA=      2.15 : EXTERNAL : ORI=EST : FSKY=0.5
WALL  =CLOISON05  : SURF= 11 : AREA=       4.3 : INTERNAL
WALL  =CLOISON05  : SURF= 12 : AREA=     19.59 : ADJACENT=ZON03 : BACK
WALL  =CLOISON05  : SURF= 13 : AREA=     23.72 : ADJACENT=ZON02 : BACK
WALL  =MUREXT34   : SURF= 14 : AREA=      12.7 : ADJACENT=ZON04 : FRONT
WALL  =PORTEBOIS  : SURF=  8 : AREA=      1.94 : EXTERNAL : ORI=NORD : FSKY=0.5
WALL  =PORTEBOIS  : SURF= 44 : AREA=      1.68 : ADJACENT=ZON04 : BACK
WALL  =CBRFACPLH  : SURF= 39 : LENGTH=     13.75 : EXTERNAL : ORI=NORD : FSKY=0.5
WALL  =CBRFACPLB  : SURF= 48 : LENGTH=     13.75 : EXTERNAL : ORI=NORD : FSKY=0.5
WALL  =CBRPOUPLB  : SURF= 52 : LENGTH=      10.3 : EXTERNAL : ORI=NORD : FSKY=0.5
WALL  =CBRFACFAC  : SURF= 53 : LENGTH=       2.5 : EXTERNAL : ORI=NORD : FSKY=0.5
 REGIME
 GAIN        = PERS_ISO04 : SCALE= SCHEDULE 1.5*SCHED001
 GAIN        = LIGHT01_01 : SCALE= SCHEDULE 1*ECLAIRE
 GAIN        = CUISSON    : SCALE= SCHEDULE 1*CUISINE
 INFILTRATION= INFIL001
 VENTILATION = VENT001
 COOLING     = COOL001
 HEATING     = HEAT001
 CAPACITANCE = 393.924 : VOLUME= 128.27  : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZON02  /  A i r n o d e  ZON02
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZON02
AIRNODE ZON02
WALL  =DALBASSE   : SURF= 15 : AREA=     19.87 : BOUNDARY=INPUT 1*TTERRE
WALL  =DALINTER   : SURF= 16 : AREA=     19.87 : ADJACENT=ZON05 : FRONT
WALL  =MUREXT34   : SURF= 17 : AREA=     12.86 : EXTERNAL : ORI=NORD : FSKY=0.5
WINDOW=DOUBLE     : SURF= 18 : AREA=      2.07 : EXTERNAL : ORI=NORD : FSKY=0.5 : ESHADE=INPUT 1*VOLETS
WALL  =MUREXT34   : SURF= 19 : AREA=      8.79 : EXTERNAL : ORI=EST : FSKY=0.5
WALL  =CLOISON05  : SURF= 20 : AREA=     17.58 : INTERNAL
WALL  =CLOISON05  : SURF= 21 : AREA=     23.72 : ADJACENT=ZON01 : FRONT
WALL  =CBRFACPLB  : SURF= 41 : LENGTH=      7.25 : EXTERNAL : ORI=NORD : FSKY=0.5
WALL  =CBRFACPLH  : SURF= 49 : LENGTH=      7.25 : EXTERNAL : ORI=NORD : FSKY=0.5
WALL  =CBRFACFAC  : SURF= 54 : LENGTH=       2.5 : EXTERNAL : ORI=NORD : FSKY=0.5
 REGIME
 INFILTRATION= INFIL001
 VENTILATION = VENT001
 COOLING     = COOL001
 HEATING     = HEAT001
 CAPACITANCE = 181.272 : VOLUME= 51.06   : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZON03  /  A i r n o d e  ZON03
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZON03
AIRNODE ZON03
WALL  =DALBASSE   : SURF= 22 : AREA=     14.49 : BOUNDARY=INPUT 1*TTERRE
WALL  =DALINTER   : SURF= 23 : AREA=     14.49 : ADJACENT=ZON05 : FRONT
WALL  =CLOISON05  : SURF= 24 : AREA=     19.59 : ADJACENT=ZON01 : FRONT
WALL  =MUREXT34   : SURF= 25 : AREA=      8.72 : EXTERNAL : ORI=SUD : FSKY=0.5
WINDOW=DOUBLE     : SURF= 26 : AREA=       1.5 : EXTERNAL : ORI=SUD : FSKY=0.5 : ESHADE=INPUT 1*VOLETS
WALL  =MUREXT34   : SURF= 27 : AREA=      9.36 : EXTERNAL : ORI=EST : FSKY=0.5
WALL  =CBRFACPLB  : SURF= 47 : LENGTH=       9.3 : EXTERNAL : ORI=NORD : FSKY=0.5
WALL  =CBRFACPLH  : SURF= 50 : LENGTH=       9.3 : EXTERNAL : ORI=NORD : FSKY=0.5
WALL  =CBRFACFAC  : SURF= 55 : LENGTH=       2.5 : EXTERNAL : ORI=NORD : FSKY=0.5
 REGIME
 INFILTRATION= INFIL001
 VENTILATION = VENT001
 COOLING     = COOL001
 HEATING     = HEAT001
 CAPACITANCE = 164.688 : VOLUME= 37.24   : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZON04  /  A i r n o d e  ZON04
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZON04
AIRNODE ZON04
WALL  =DALBASSE   : SURF= 28 : AREA=     18.59 : BOUNDARY=INPUT 1*TTERRE
WALL  =TOITURE    : SURF= 29 : AREA=     21.26 : EXTERNAL : ORI=TOITNORD : FSKY=1
WALL  =MURGAR22   : SURF= 30 : AREA=      8.45 : EXTERNAL : ORI=SUD : FSKY=0.5
WALL  =PORTGARA   : SURF= 31 : AREA=      6.18 : EXTERNAL : ORI=NORD : FSKY=0.5
WALL  =MURGAR22   : SURF= 32 : AREA=      2.26 : EXTERNAL : ORI=NORD : FSKY=0.5
WALL  =MURGAR22   : SURF= 33 : AREA=     14.54 : EXTERNAL : ORI=OUEST : FSKY=0.5
WALL  =MUREXT34   : SURF= 34 : AREA=      12.7 : ADJACENT=ZON01 : BACK
WALL  =PORTEBOIS  : SURF= 43 : AREA=      1.68 : ADJACENT=ZON01 : FRONT
 REGIME
 INFILTRATION= INFILGAR
 CAPACITANCE = 57.324  : VOLUME= 47.77   : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZON05  /  A i r n o d e  ZON05
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZON05
AIRNODE ZON05
WALL  =DALINTER   : SURF= 35 : AREA=     49.91 : ADJACENT=ZON01 : BACK
WALL  =DALINTER   : SURF= 36 : AREA=     19.87 : ADJACENT=ZON02 : BACK
WALL  =DALINTER   : SURF= 37 : AREA=     14.49 : ADJACENT=ZON03 : BACK
WALL  =TOITURE    : SURF= 38 : AREA=        48 : EXTERNAL : ORI=TOITNORD : FSKY=1
WALL  =MURGAR22   : SURF= 40 : AREA=      8.26 : EXTERNAL : ORI=OUEST : FSKY=0.5
WALL  =MURGAR22   : SURF= 42 : AREA=      8.26 : EXTERNAL : ORI=EST : FSKY=0.5
WALL  =TOITURE    : SURF= 59 : AREA=        48 : EXTERNAL : ORI=TOITSUD : FSKY=0.5
 REGIME
 INFILTRATION= INFILCOMB
 CAPACITANCE = 560.148 : VOLUME= 66.79   : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  O u t p u t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
OUTPUTS
 TRANSFER : TIMEBASE=1.000
 AIRNODES = ZON01 ZON02 ZON03 ZON04 ZON05 
 NTYPES =   1 : TAIR - air temperature of zone
        =  30 : QHEAT - sensible heating demand of zone (positive values)
        =  31 : QCOOL - sensible cooling demand of zone (positive values)
        =  32 : SQHEAT - sum of sensible heating demand for group of zones (positive values)
        =  33 : SQCOOL - sum of sensible cooling demand for group of zones (positive values)
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  E n d
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
END

_EXTENSION_WINPOOL_START_
WINDOW 4.1  DOE-2 Data File : Multi Band Calculation
Unit System : SI
Name        : TRNSYS 15 WINDOW LIB
Desc        : Isolierglas, 2.8
Window ID   : 1002
Tilt        : 90.0
Glazings    : 2
Frame       : 11                       2.270
Spacer      :  1 Class1                2.330  -0.010   0.138
Total Height: 1219.2 mm
Total Width :  914.4 mm
Glass Height: 1079.5 mm
Glass Width :  774.7 mm
Mullion     : None
Gap        Thick   Cond  dCond    Vis   dVis   Dens   dDens     Pr     dPr
1 Air       16.0 0.02410  7.600  1.730 10.000  1.290 -0.0044  0.720 0.00180
2              0       0      0      0      0      0       0      0       0
3              0       0      0      0      0      0       0      0       0
4              0       0      0      0      0      0       0      0       0
5              0       0      0      0      0      0       0      0       0
Angle     0    10    20    30    40    50    60    70    80    90 Hemis
Tsol  0.693 0.692 0.688 0.681 0.666 0.633 0.565 0.426 0.197 0.000 0.590
Abs1  0.101 0.102 0.104 0.107 0.112 0.118 0.126 0.137 0.143 0.000 0.116
Abs2  0.080 0.080 0.081 0.083 0.086 0.087 0.087 0.079 0.058 0.000 0.082
Abs3      0     0     0     0     0     0     0     0     0     0     0
Abs4      0     0     0     0     0     0     0     0     0     0     0
Abs5      0     0     0     0     0     0     0     0     0     0     0
Abs6      0     0     0     0     0     0     0     0     0     0     0
Rfsol 0.126 0.126 0.126 0.128 0.137 0.161 0.223 0.358 0.601 1.000 0.202
Rbsol 0.126 0.126 0.126 0.128 0.137 0.161 0.223 0.358 0.601 1.000 0.202
Tvis  0.817 0.816 0.815 0.811 0.799 0.768 0.695 0.538 0.273 0.000 0.714
Rfvis 0.148 0.148 0.148 0.151 0.162 0.191 0.262 0.417 0.682 1.000 0.236
Rbvis 0.148 0.148 0.148 0.151 0.162 0.191 0.262 0.417 0.682 1.000 0.236
SHGC  0.755 0.754 0.752 0.746 0.733 0.703 0.635 0.493 0.252 0.000 0.655
SC: 0.69
Layer ID#         9052     9052        0        0        0        0
Tir              0.000    0.000        0        0        0        0
Emis F           0.840    0.840        0        0        0        0
Emis B           0.840    0.840        0        0        0        0
Thickness(mm)      4.0      4.0        0        0        0        0
Cond(W/m2-C     ) 225.0    225.0        0        0        0        0
Spectral File     None     None     None     None     None     None
Overall and Center of Glass Ig U-values (W/m2-C)
Outdoor Temperature                 -17.8 C      15.6 C      26.7 C      37.8 C
Solar      WdSpd  hcout hrout  hin
(W/m2)     (m/s)     (W/m2-C)
0        0.00  12.25  3.29  7.89  2.56 2.56  2.56 2.56  2.64 2.64  2.85 2.85
0        6.71  25.47  3.24  7.93  2.77 2.77  2.75 2.75  2.83 2.83  3.07 3.07
783        0.00  12.25  3.40  7.49  2.58 2.58  2.72 2.72  2.87 2.87  3.01 3.01
783        6.71  25.47  3.31  7.64  2.80 2.80  2.88 2.88  3.07 3.07  3.22 3.22
WINDOW 4.1  TRNSYS 15 Data File : Multi Band Calculation
Unit System : SI
Name        : TRNSYS 15 WINDOW LIB
Desc        : Dble,Low-e,Ar
Window ID   : 5001
Tilt        : 90.0
Glazings    : 2
Frame       :  1 Al no break          10.790
Spacer      :  1 Class1                2.330  -0.010   0.138
Total Height: 1219.2 mm
Total Width :  914.4 mm
Glass Height: 1104.9 mm
Glass Width :  800.1 mm
Mullion     : None
Gap        Thick   Cond  dCond    Vis   dVis   Dens   dDens     Pr     dPr
1 Argon     12.7 0.01620  5.000  2.110  6.300  1.780 -0.0060  0.680 0.00066
2              0       0      0      0      0      0       0      0       0
3              0       0      0      0      0      0       0      0       0
4              0       0      0      0      0      0       0      0       0
5              0       0      0      0      0      0       0      0       0
Angle     0    10    20    30    40    50    60    70    80    90 Hemis
Tsol  0.544 0.548 0.539 0.529 0.514 0.486 0.426 0.312 0.145 0.000 0.453
Abs1  0.187 0.190 0.200 0.207 0.210 0.218 0.242 0.273 0.248 0.001 0.221
Abs2  0.048 0.049 0.049 0.050 0.051 0.052 0.050 0.045 0.033 0.000 0.048
Abs3      0     0     0     0     0     0     0     0     0     0     0
Abs4      0     0     0     0     0     0     0     0     0     0     0
Abs5      0     0     0     0     0     0     0     0     0     0     0
Abs6      0     0     0     0     0     0     0     0     0     0     0
Rfsol 0.220 0.214 0.212 0.214 0.224 0.244 0.282 0.371 0.574 0.999 0.268
Rbsol 0.236 0.231 0.230 0.232 0.241 0.261 0.307 0.414 0.629 1.000 0.291
Tvis  0.769 0.774 0.763 0.749 0.730 0.692 0.605 0.440 0.205 0.000 0.642
Rfvis 0.138 0.131 0.128 0.131 0.143 0.168 0.217 0.323 0.549 0.999 0.197
Rbvis 0.127 0.120 0.119 0.124 0.138 0.168 0.233 0.379 0.650 1.000 0.208
SHGC  0.596 0.600 0.592 0.583 0.569 0.543 0.483 0.366 0.188 0.000 0.507
SC: 0.69
Layer ID#          400        1        0        0        0        0
Tir              0.000    0.000        0        0        0        0
Emis F           0.840    0.840        0        0        0        0
Emis B           0.100    0.840        0        0        0        0
Thickness(mm)      3.0      2.5        0        0        0        0
Cond(W/m2-C     ) 300.0    360.0        0        0        0        0
Spectral File     None     None     None     None     None     None
Overall and Center of Glass Ig U-values (W/m2-C)
Outdoor Temperature                 -17.8 C      15.6 C      26.7 C      37.8 C
Solar      WdSpd  hcout hrout  hin
(W/m2)     (m/s)     (W/m2-C)
0        0.00  12.25  3.24  7.59  1.44 1.44  1.35 1.35  1.38 1.38  1.45 1.45
0        6.71  25.47  3.21  7.62  1.51 1.51  1.39 1.39  1.43 1.43  1.51 1.51
783        0.00  12.25  3.41  6.82  1.41 1.41  1.42 1.42  1.47 1.47  1.53 1.53
783        6.71  25.47  3.31  7.10  1.51 1.51  1.45 1.45  1.51 1.51  1.56 1.56
*** END OF LIBRARY ***
***************************************************************************************************
*WinID   Description                              Design         U-Value g-value T-sol Rf-sol T-vis
***************************************************************************************************
  1002   Isolierglas, 2.8                         4/16/4           2.83  0.755  0.693  0.126  0.817
  5001   Dble,Low-e,Ar                            3/12.7/2.5       1.43  0.596  0.544  0.22  0.769
_EXTENSION_WINPOOL_END_




More information about the TRNSYS-users mailing list