[TRNSYS-users] (no subject)
David Bradley
bradley at tess-inc.com
Fri Jan 15 10:08:34 PST 2010
Sek,
I am not sure that approximating an active chilled beam using the
cooled ceiling model is correct. In my understanding, the cooled ceiling
models a purely radiative device whereas an active chilled beam supplies
a small amount of cooled, dehumidified air to the space through some
induction nozzles that draw room air over a series of cool water pipes,
cooling it and supplying it right back to the room. I would think that
the more correct methodology would be to write a model of an active
chilled beam itself.
Best regards,
David
#SEK JUN-YANG# wrote:
> Dear Trnsys users,
>
> I am trying to create an active chilled beam for a typical office
> space and I would like to clarify the steps that I have tried.
> Firstly, I created a new layer, which is the cooled ceiling, under
> wall type manager. After which, I added this new layer to the wall
> type( Roof). Lastly, I defined the cooled ceiling under each zone. If
> there is any errors or if I have missed out on any steps I would
> greatly appreciate any remedies provided. I would also like to find
> out if I were to model a passive beam, what are the different
> procedures in modeling. Thank you.
>
> Best Regards,
> Sek Jun-Yang
>
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100115/ca3b3dc9/attachment-0005.htm>
More information about the TRNSYS-users
mailing list