Sek,<br>
  I am not sure that approximating an active chilled beam using the
cooled ceiling model is correct. In my understanding, the cooled
ceiling models a purely radiative device whereas an active chilled beam
supplies a small amount of cooled, dehumidified air to the space
through some induction nozzles that draw room air over a series of cool
water pipes, cooling it and supplying it right back to the room. I
would think that the more correct methodology would be to write a model
of an active chilled beam itself. <br>
Best regards,<br>
 David<br>
<br>
<br>
#SEK JUN-YANG# wrote:
<blockquote
 cite="mid:316ED1F87911FC479407CAB86CD9842437B010@MAIL24.student.main.ntu.edu.sg"
 type="cite">
  <meta content="text/html; charset=unicode" http-equiv="Content-Type">
  <meta name="GENERATOR" content="MSHTML 8.00.6001.18854">
  <div><font color="#000000" face="Arial" size="2">Dear Trnsys users,</font></div>
  <div> </div>
  <div><font face="Arial" size="2">I am trying to create an active
chilled beam for a typical office space and I would like to clarify the
steps that I have tried. Firstly, I created a new layer, which is the
cooled ceiling, under wall type manager. After which, I added this new
layer to the wall type( Roof). Lastly, I defined the cooled ceiling
under each zone. If there is any errors or if I have missed out on any
steps I would greatly appreciate any remedies provided. I would also
like to find out if I were to model a passive beam, what are the
different procedures in modeling. Thank you. </font></div>
  <div> </div>
  <div><font face="Arial" size="2">Best Regards,</font></div>
  <div><font face="Arial" size="2">Sek Jun-Yang</font></div>
  <div> </div>
  <div> </div>
  <pre wrap="">
<hr size="4" width="90%">
_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users">https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users</a>
  </pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">-- 
***********************************************************************
Thermal Energy System Specialists (TESS), LLC 
David BRADLEY                      22 N. Carroll Street - Suite 370 
Partner                            Madison, WI 53703 
                                   USA
P: +1.608.274.2577 
F: +1.608.278.1475
E-mail: <a class="moz-txt-link-abbreviated" href="mailto:bradley@tess-inc.com">bradley@tess-inc.com</a> 
Web Pages:  <a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>    and      <a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a>

***********************************************************************</pre>
</body>
</html>