[TRNSYS-users] active layer in type 56
Kersken, Matthias
Matthias.Kersken at ibp.fraunhofer.de
Mon Jan 18 23:52:23 PST 2010
Hello Mr. Martinez!
There's a trick making it possible to do this but I must admit I had no
possibility until now to validate the results of a construction like this
with real measurement values!
- You split the wall between the two active layers, construct the wall to
the separation-zone and define one of them in each room.
- You set the outside convective heat transfer coefficients of both walls to
0.0001 (direct contact).
- Define both walls as boundary.
- You create two outputs with the outside-surface-temperature of the two
walls.
- Create an Input for these two temperatures and link the building-Type with
itself.
- Now You define the Outside-surface-temperature-Output of the wall in room
A as the boundary-condition of the wall in room B and reverse (temperature B
in room A).
This works but as I sad unfortunately I never had the possibility to
validate this concept.
Good luck,
Matthias Kersken
---
Dipl.-Ing. Matthias Kersken
Wissenschaftlicher Mitarbeiter / Abteilung Energiesysteme
Fraunhofer-Institut für Bauphysik
Institutsteil Holzkirchen
Fraunhoferstraße 10
83626 Valley
eMail: Matthias.Kersken at ibp.fraunhofer.de
Telefon 08024 / 643-204
Telefax 08024 / 643-366
www.ibp.fraunhofer.de <http://www.ibp.fraunhofer.de/>
Dipl.-Ing. Matthias Kersken
Research Associate / Department Energy Systems
Fraunhofer Institute for Building Physics
Branch Holzkirchen
Fraunhoferstraße 10
D-83626 Valley
eMail: <mailto:Matthias.Kersken at ibp.fraunhofer.de>
Matthias.Kersken at ibp.fraunhofer.de
Phone +49 8024 / 643-204
Fax +49 8024 / 643-366
<http://www.ibp.fraunhofer.de/> www.ibp.fraunhofer.de
---
_____
Von: rgaray at labein.es [mailto:rgaray at labein.es]
Gesendet: Dienstag, 19. Januar 2010 08:15
An: trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] active layer in type 56
Hello All,
I´ve been trying to create a new simulation with a wall containing two
active layers in it.
As far as I know, this is not possible. Is it correct or can I create it
somehow?
Thank you wery much.
--------------------------------------------------------------------------
Roberto Garay Martinez
Labein-Tecnalia
Unidad de Construcción y Desarrollo del Territorio
c/Geldo. Parque Tecnológico de Bizkaia
Edificio 700
48160 Derio (Bizkaia)
Tel.: 34 94 607 33 00
Fax: 34 94 607 33 49
www.labein.es
---------------------------------------------------------------------------
Visite nuestro blog:
http://www.energiaenedificacion.com
------------------------------------------------------------------------
Bilbao, 17-19 de Mayo, 2010
Open and Sustainable Building
Edificación Adaptable y Sostenible
www.OpenBuilding-2010.org
--------------------------------------------------------------------------
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100119/4ce80a91/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: smime.p7s
Type: application/x-pkcs7-signature
Size: 7103 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100119/4ce80a91/attachment-0001.bin>
More information about the TRNSYS-users
mailing list