[TRNSYS-users] NTYPE 1: TAIR & Top
hotline
hotline at transsolar.com
Mon Dec 20 02:31:12 PST 2010
Dear Wang,
in TRNBUILD you can define ZONES. These are in principle RADIATIVE ZONES
that can have ONE/SEVERAL AIRNODES. Please have a look to the Trnsys3d
Tutorial on page 20 at the bottom, there is an image showing the meaning
of radiative zone and convective airnode. If you are starting to set up
a ZONE in TRNBUILD then this automatically is a RADIATIVE ZONE with ONE
AIRNODE. TAIR represents the ideal mixed air temperature of the volume
that you define in TRNBUILD. The operative temperature (often called the
felt temperature) includes besides the TAIR also the mean surface
temperature in the zone.
Regards
Christian
TRANSSOLAR Software Team
hotline at transsolar.com
www.trnsys.de
Transsolar KlimaEngineering - Technologien für energieeffizientes Bauen
und Nutzerkomfort in Gebäuden
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart /
Amtsgericht Stuttgart - HRB 23347 / UsSt.-Id: DE152272639
Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
Dipl.Phys. Stefan Holst, Prof. Volkmar Bleicher
_____
Von: 王洋 [mailto:wanghongyang1767 at gmail.com]
Gesendet: Montag, 20. Dezember 2010 10:06
An: trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] NTYPE 1: TAIR & Top
Dear all,
I have a question about room air temperature: NTYPE 1: TAIR. As we
know, there are different room air temperature in different height of
one room. Besides that, the wall, the floor and roof temperature of the
room are also not the same. Please tell me what's meaning of NTYPE 1:
TAIR? Where is This AIRNODE? How to define This AIRNODE?
PLUS: to Operative(operation) temperature of room: How to define it?
What' meaning is Operative(operation)temperature of room? What's
difference of Operative(operation) temperature of room and NTYPE 1:
TAIR?
I saw the TRNBuild / Type56 documentation . But it only shows NTYPE 1:
TAIR: air temperature of zone. But I want to know Where is This
AIRNODE which measures aie temperature of zone? How to define This
AIRNODE? Because as we know, there are different room air temperature in
different height of one room.
to Top it shows the operative(operation) temperature of room: BUT how
to define it? What' meaning is Operative(operation)
temperature of room? What's difference of Operative(operation)
temperature of room and NTYPE 1: TAIR?
Many thanks!
Br.
wang
2010/12/17 <trnsys-users-request at cae.wisc.edu>
Send TRNSYS-users mailing list submissions to
trnsys-users at cae.wisc.edu
To subscribe or unsubscribe via the World Wide Web, visit
https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
or, via email, send a message with subject or body 'help' to
trnsys-users-request at cae.wisc.edu
You can reach the person managing the list at
trnsys-users-owner at cae.wisc.edu
When replying, please edit your Subject line so it is more specific
than "Re: Contents of TRNSYS-users digest..."
Today's Topics:
1. Re: Create a final report with TrnEdit (David BRADLEY)
2. Re: zone air temperature (NTYPE 1: TAIR) (David BRADLEY)
---------- 已转发邮件 ----------
From: David BRADLEY <d.bradley at tess-inc.com>
To: Manu <manuel.tilly at gmail.com>
Date: Fri, 17 Dec 2010 10:21:46 -0600
Subject: Re: [TRNSYS-users] Create a final report with TrnEdit
Manu,
TRNEdit is a tool that allows you to directly edit the text of the
TRNSYS input file. Before the Studio existed, people used TRNEdit to
create their input file. It doesn't really have any reporting
features. You might try selecting "Report" from the File menu in the
TRNSYS Studio. This will generate a summary text file of your
project.
Best,
David
On 12/14/2010 07:29, Manu wrote:
Hi,
I try to use TrnEdit on a project and I want to know if it's
possible to generate a final report (Word or pdf extension file)
withe graphic and text comment, juste like SimSol (french
application based on TRNSys to dimention a solar system).
Thank you
Best regards
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu
https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
---------- 已转发邮件 ----------
From: David BRADLEY <d.bradley at tess-inc.com>
To: 王洋 <wanghongyang1767 at gmail.com>
Date: Fri, 17 Dec 2010 11:21:12 -0600
Subject: Re: [TRNSYS-users] zone air temperature (NTYPE 1: TAIR)
Wang,
Information of this kind can be found in the TRNBuild / Type56
documentation (volume 05 in the Trnsys17 documentation set).
Kind Regards,
David
On 12/17/2010 07:22, 王洋 wrote:
Dear all,
I have a question about room air temperature: NTYPE 1: TAIR.
As we know, there are different room air temperature in different
height of one room. Besides that, the wall, the floor and roof
temperature of the room are also not the same. Please tell me
what's meaning of NTYPE 1: TAIR? Where is This AIRNODE? How to
define This AIRNODE?
PLUS: to Operative(operation) temperature of room: How to define
it? What' meaning is Operative(operation)temperature of room?
What's difference of Operative(operation) temperature of room and
NTYPE 1: TAIR?
Many thanks!
Br.
wang
2010/12/17 <trnsys-users-request at cae.wisc.edu>
Send TRNSYS-users mailing list submissions to
trnsys-users at cae.wisc.edu
To subscribe or unsubscribe via the World Wide Web, visit
https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
or, via email, send a message with subject or body 'help' to
trnsys-users-request at cae.wisc.edu
You can reach the person managing the list at
trnsys-users-owner at cae.wisc.edu
When replying, please edit your Subject line so it is more
specific
than "Re: Contents of TRNSYS-users digest..."
Today's Topics:
1. Re: Type 56 (David BRADLEY)
2. Re: Psychrometrics (David BRADLEY)
3. Re : Re: Psychrometrics (Jérôme Deroche)
4. error when opening sketchup (Annie Marston)
---------- 已转发邮件 ----------
From: David BRADLEY <d.bradley at tess-inc.com>
To: Abduljalil Ali Al-Abidi <abo_anas4 at yahoo.com>
Date: Thu, 16 Dec 2010 12:47:43 -0600
Subject: Re: [TRNSYS-users] Type 56
Abduljalil,
In order to change the wall layers, open TRNBuild and open
your building description file (*.bui or *.b17). Select
Typemanager: Walls from the menus at the top of the screen.
Select the appropriate wall from the drop-down list. Double
click on a layer in order to change its thickness.
Best,
David
On 12/16/2010 03:26, Abduljalil Ali Al-Abidi wrote:
Dear Trnsys user
I am a new trnsys user and I want to change the thickness of
the wall insulation in the tape 56 ( multi-zone building ).
Is it possible to change this thickness in this type ex. for
insulation = 5 cm to 20 cm step 5cm.
I would like to study the effect of insulation thick to the
performance of the system
best regards
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu
https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
---------- 已转发邮件 ----------
From: David BRADLEY <d.bradley at tess-inc.com>
To: "Jérôme Deroche" <deroche.jerome at cedre-sophia.com>
Date: Thu, 16 Dec 2010 12:50:55 -0600
Subject: Re: [TRNSYS-users] Psychrometrics
Jérôme,
What is most likely happening is that at a pressure of 1atm,
your combination of the dry bulb temperature and the absolute
humidity ratio are on the wrong side of the saturation line.
Since that is physically impossible, the psychometric routine
keeps your dry bulb temperature and resets the absolute
humidity ratio to the value it would be if the relative
humidity were 100%.
Best,
David
On 12/16/2010 04:21, wrote:
Hello,
i'm using a psychrometrics type with dry bulb temperature
and absolute humidity ratio in inputs. Pressure input is set
to 1 atm.
I have noticed that sometimes there is a difference between
the input humidity ratio and the output humidity ratio. The
difference ratio is about 1 to 12%.
Could someone explain to me why this difference happens?
Thank you
Jérôme DEROCHE
Ingénieur d'études
CEDRE
Tel: 04 92 96 03 77
Port: 06 25 11 21 93
Ophira 1, 1 place Bermond
06560 SOPHIA-ANTIPOLIS
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu
https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
---------- 已转发邮件 ----------
From: "Jérôme Deroche" <deroche.jerome at cedre-sophia.com>
To: David BRADLEY <d.bradley at tess-inc.com>
Date: Fri, 17 Dec 2010 05:08:17 -0500 (EST)
Subject: [TRNSYS-users] Re : Re: Psychrometrics
Your answers are right.
Thank you very much
Jérôme DEROCHE
Ingénieur d'études
CEDRE
Tel: 04 92 96 03 77
Port: 06 25 11 21 93
Ophira 1, 1 place Bermond
06560 SOPHIA-ANTIPOLIS
Message original Re : Re: [TRNSYS-users] Psychrometrics
De : David BRADLEY <d.bradley at tess-inc.com>
A : Jérôme Deroche <deroche.jerome at cedre-sophia.com>
Date : 2010-12-16 19:51:05
Jérôme,
What is most likely happening is that at a pressure of 1atm,
your combination of the dry bulb temperature and the absolute
humidity ratio are on the wrong side of the saturation line.
Since that is physically impossible, the psychometric routine
keeps your dry bulb temperature and resets the absolute
humidity ratio to the value it would be if the relative
humidity were 100%.
Best,
David
On 12/16/2010 04:21, wrote:
Hello,
i'm using a psychrometrics type with dry bulb temperature
and absolute humidity ratio in inputs. Pressure input is set
to 1 atm.
I have noticed that sometimes there is a difference between
the input humidity ratio and the output humidity ratio. The
difference ratio is about 1 to 12%.
Could someone explain to me why this difference happens?
Thank you
Jérôme DEROCHE
Ingénieur d'études
CEDRE
Tel: 04 92 96 03 77
Port: 06 25 11 21 93
Ophira 1, 1 place Bermond
06560 SOPHIA-ANTIPOLIS
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu
https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
---------- 已转发邮件 ----------
From: Annie Marston <A.Marston at eb-engineers.com>
To: "trnsys-users at cae.wisc.edu" <trnsys-users at cae.wisc.edu>
Date: Thu, 16 Dec 2010 14:30:35 +0000
Subject: [TRNSYS-users] error when opening sketchup
Hi,
I am using the TRNSYS 3d plugin for SketchUp V7. I have v8 but
the plugin doesn’t seem to attach to v8 (is this correct? Is
there a plugin for v8). Whenever I open sketch up I get the
following error:
Sorry… the plugin has encountered an error. This error may
cause unpredictable behavior in the plugin continue this
session with caution! It would probably be a good idea to exit
SketchUp and start again. (unfortunately this happens
everytime I open sketchup)
For help please contact…
Error:
NameError
Wrong constant name jectinfoInterface
Backtrace:
C:/Program Files (x86)/Google/Google SketchUp
7/Plugins/Trnsys3d/lib/DialogManager.rb:31:in `const_get'
C:/Program Files (x86)/Google/Google SketchUp
7/Plugins/Trnsys3d/lib/DialogManager.rb:31:in `restore_state'
C:/Program Files (x86)/Google/Google SketchUp
7/Plugins/Trnsys3d/lib/DialogManager.rb:31:in `initialize'
C:/Program Files (x86)/Google/Google SketchUp
7/Plugins/Trnsys3d/lib/AsynchProc.rb:13:in `call'
My version of the plugin is 1.0.5.362
Can you help
Thanks
Annie
Dr. A. Marston, Ph.D. LEED® AP
Building Performance Analyst
Ebert & Baumann Consulting Engineers, Inc.
An Enterprise of the Ebert-Consulting Group
734 15th Street, NW
Suite 1000
Washington, D.C. 20005, USA
Tel +1.202.608.1334
Fax +1.202.544.1434
a.marston at eb-engineers.com
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu
https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu
https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu
https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20101220/546c75a0/attachment-0005.htm>
More information about the TRNSYS-users
mailing list