[TRNSYS-users] questions about Trnflow
王洋
wanghongyang1767 at gmail.com
Tue Aug 17 03:51:45 PDT 2010
Dear all,
I have set up a very simple zone only including one airlink--Large Opening.
But I run it, the list file shows Parameters for TRNFlow are missing.
Please, check defined parameters! I only define one Opening with Daily
Schedule, and I set up one Daily Schedule using Type 14, meanwhile, I define
a Output NTYPEs 207 and link Type 65 with Type 56, I want to observe Output
NTYPEs 207(total outdoor air flow into airnode). Only these, but the list
file shows Parameters for TRNFlow are missing. Please, check defined
parameters! I don't know what other Parameters are lack, if list file can
tell what are missing, that's better. Do you think how to find missing
Parameters ? Which Parameters are easy to be misses? Indeed I can not find
them.
Thanks!
Br.
wang
ps.:the listing file shows:
TRNFLOW (2003-06-04) based on COMIS 3.1
Copyright (C) 2001 EMPA
-------------------------------------------------------
Note: as soon as TRNFLOW is switched on, all couplings
between zones which are not in the air flow network and
those included in the network are reset to zero!
-------------------------------------------------------
No SET-file; using defaults
*******************************
Reading Input File *
*******************************
*******************************
Checking HVAC T-Junction data *
*******************************
*******************************
Looking for RF components *
*******************************
*** Notice at time : 0.000000
Generated by Unit : 56
Generated by Type : 56
Message : Star network calculation: every iteration step
of TRNSYS
*** Fatal Error at time : 0.000000
Generated by Unit : 56
Generated by Type : 56
Message : Parameters for TRNFlow are missing. Please,
check defined parameters!
*** An error has forced TRNSYS to abort
2010/8/16 <trnsys-users-request at cae.wisc.edu>
> Send TRNSYS-users mailing list submissions to
> trnsys-users at cae.wisc.edu
>
> To subscribe or unsubscribe via the World Wide Web, visit
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
> or, via email, send a message with subject or body 'help' to
> trnsys-users-request at cae.wisc.edu
>
> You can reach the person managing the list at
> trnsys-users-owner at cae.wisc.edu
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of TRNSYS-users digest..."
>
> Today's Topics:
>
> 1. Converting *.try into *.epw (Mavi Cambronero V?zquez)
> 2. Re: Stored variables (C++)
> (Carlos Flores | DECCW. Sydney, Australia)
> 3. Re: Stored variables (C++)
> (Carlos Flores | DECCW. Sydney, Australia)
> 4. Problem compiling with PGI Visual Fortran 10.3
> (Carlos Flores | DECCW. Sydney, Australia)
> 5. Re: Stored variables (C++)
> (Carlos Flores | DECCW. Sydney, Australia)
>
>
> ---------- 已转发邮件 ----------
> From: "Mavi Cambronero Vázquez" <maviqnk at gmail.com>
> To: trnsys-users at cae.wisc.edu
> Date: Mon, 16 Aug 2010 11:08:52 +0200
> Subject: [TRNSYS-users] Converting *.try into *.epw
> Hi!
>
> Does anyone know how to convert meteorogical files from .try into .epw? I
> found an application but it´s only valid for UK meteorogical data....
>
> Thanks in advance!
>
>
> ---------- 已转发邮件 ----------
> From: "Carlos Flores | DECCW. Sydney, Australia" <cflores at ing.uchile.cl>
> To: trnsys-users at engr.wisc.edu
> Date: Mon, 9 Aug 2010 19:19:19 +1000
> Subject: Re: [TRNSYS-users] Stored variables (C++)
> Apologies for double-posting. I just realised that my 'cflores' account
> was the one subscribed to this list. Here is my question again.
>
> --------------------------------------------------------------
>
> Hey everyone,
>
> I have TRNSYS 16 and I am programming a new module using C++. I've
> had absolutely *all* the problems that have been mentioned in the past
> with regards to stored variables (such as un-updated TRNSYS.h file) and I've
> solved most of them, but I have been unable to solve one related to
> pointers.
>
> For some reason, in TRNSYS.h the functions *setStorageVars* and *
> setStorageSize* need pointer inputs (int*, double*) to work, as opposed to
> the simple int or double variables used in FORTRAN. I have spent a lot of
> time and I have not being able to work this through, and I need to fix this
> within the next few days or it will have consequences on the project
> deadline =(
>
> Does anybody have the answer to one of these two questions?
>
> *1) Do you have any example (*.ccp) of a module programmed in C++ that
> uses stored variables?* That would probably be easiest way to understand
> how to insert the correct inputs in the *setStorageVars* function, or
>
> *2) Do you know how to insert the 'nitems' and 'stored' array in a way
> that the setStorageVars function will understand?*
>
> The template generated for C++ does not address these issues and I am
> unsure how to fix them.
>
> Any help would be highly appreciated! Thanks!
>
> Carlos Flores
> Energy Research Program
> Universidad de Chile
>
>
> ---------- 已转发邮件 ----------
> From: "Carlos Flores | DECCW. Sydney, Australia" <cflores at ing.uchile.cl>
> To: "keilholz, werner" <werner.keilholz at cstb.fr>
> Date: Wed, 11 Aug 2010 07:09:29 +1000
> Subject: Re: [TRNSYS-users] Stored variables (C++)
> Hey Werner,
>
> That is a shame. It's sad that TRNSYS does not have a proper support for
> C++, specially when they claim they do. It made me waste a couple of days
> of work.
>
> Thanks very much for your answer and for helping me not to waste my time
> any longer.
>
> Kind regards,
>
> Carlos
>
>
>
> On Mon, Aug 9, 2010 at 10:11 PM, keilholz, werner <werner.keilholz at cstb.fr
> > wrote:
>
>> Hi Carlos,
>>
>>
>>
>> The setStorageVars problem, too, has been encountered before:
>>
>> http://www.mail-archive.com/trnsys-users@engr.wisc.edu/msg01920.html
>>
>>
>>
>> Basically, my recommendation is not to use it in C or C++ - it’s a bit
>> like asking where you can get fresh hay for your car...
>>
>>
>>
>> Werner
>>
>>
>>
>> *De :* carlosfloreslenero at gmail.com [mailto:carlosfloreslenero at gmail.com]
>> *De la part de* Carlos Flores | DECCW. Sydney, Australia
>> *Envoyé :* lundi 9 août 2010 11:03
>> *À :* trnsys-users at engr.wisc.edu
>> *Objet :* Re: [TRNSYS-users] Stored variables (C++)
>>
>>
>>
>> Hey everyone,
>>
>>
>>
>> I have TRNSYS 16 and I am programming a new module using C++. I've
>> had absolutely *all* the problems that have been mentioned in the past
>> with regards to stored variables (such as un-updated TRNSYS.h file) and I've
>> solved most of them, but I have been unable to solve one related to
>> pointers.
>>
>>
>> For some reason, in TRNSYS.h the functions *setStorageVars* and *
>> setStorageSize* need pointer inputs (int*, double*) to work, as opposed
>> to the simple int or double variables used in FORTRAN. I have spent a lot
>> of time and I have not being able to work this through, and I need to fix
>> this within the next few days or it will have consequences on the project
>> deadline =(
>>
>>
>>
>> Does anybody have the answer to one of these two questions?
>>
>>
>>
>> *1) Do you have any example (*.ccp) of a module programmed in C++ that
>> uses stored variables?* That would probably be easiest way to understand
>> how to insert the correct inputs in the *setStorageVars* function, or
>>
>>
>>
>> *2) Do you know how to insert the 'nitems' and 'stored' array in a way
>> that the setStorageVars function will understand?*
>>
>>
>>
>> The template generated for C++ does not address these issues and I am
>> unsure how to fix them.
>>
>>
>>
>> Any help would be highly appreciated! Thanks!
>>
>>
>>
>> Carlos Flores
>>
>> Energy Research Program
>>
>> Universidad de Chile
>>
>
>
>
> --
> *Carlos Flores*
> Project Officer
> BSc, MSc (Mech Eng)
>
> *Department of Environment, Climate Change and Water*
> National Australian Built Environment Rating Scheme (NABERS Energy)
> Sydney, Australia
> *T:* (+61) 02 9995 5495
> *F:* (+61) 02 9995 6388
> *W:* www.nabers.com.au
>
>
>
> ---------- 已转发邮件 ----------
> From: "Carlos Flores | DECCW. Sydney, Australia" <cflores at ing.uchile.cl>
> To: trnsys-users at engr.wisc.edu
> Date: Wed, 11 Aug 2010 22:55:44 +1000
> Subject: [TRNSYS-users] Problem compiling with PGI Visual Fortran 10.3
> Hello everyone,
>
> I've got a quick question. I recently installed PGI VF 2008 (v10.3) after
> my failed attempt to use C++. I had to use PGI's as it is the version used
> in the IT department at the university.
>
> Now, TRNSYS generates a DSP file (with relevant links to TRNDll and other
> files) along with a .FOR template. The problem is that after installing GPI
> Visual Fortran, the DSP file is still not being recognised by Visual Studio
> (2008). If I try to open the file it tells me that the file is *corrupted,
> and it seems to be associated with a C++ project rather than Fortran.*
> *
> *
> *So I gues my question is: Is there any way I can fix this?*
> *
> *
> *Alternatively, if I start a new fortran project in Visual Studio from
> scratch, and I include my FOR source code. H**ow can I let Visual Studio
> know where are the libraries with the necessary functions to compile my code
> (e.g. TRNDll.dll)?*
>
> Thanks everyone!
>
> Carlos
> Energy Research Program
> Universidad de Chile
>
>
> ---------- 已转发邮件 ----------
> From: "Carlos Flores | DECCW. Sydney, Australia" <
> carlosfloreslenero at gmail.com>
> To: trnsys-users at engr.wisc.edu
> Date: Sun, 8 Aug 2010 15:26:22 +1000
> Subject: Re: [TRNSYS-users] Stored variables (C++)
> Hey everyone,
>
> I have TRNSYS 16 and I am programming a new module using C++. I've
> had absolutely *all* the problems that have been mentioned in the past
> with regards to stored variables (such as un-updated TRNSYS.h file) and I've
> solved most of them, but I have been unable to solve one related to
> pointers.
>
> For some reason, in TRNSYS.h the functions *setStorageVars* and *
> setStorageSize* need pointer inputs (int*, double*) to work, as opposed to
> the simple int or double variables used in FORTRAN. I have spent a lot of
> time and I have not being able to work this through, and I need to fix this
> within the next few days or it will have consequences on the project
> deadline =(
>
> Does anybody have the answer to one of these two questions?
>
> *1) Do you have any example (*.ccp) of a module programmed in C++ that
> uses stored variables?* That would probably be easiest way to understand
> how to insert the correct inputs in the *setStorageVars* function, or
>
> *2) Do you know how to insert the 'nitems' and 'stored' array in a way
> that the setStorageVars function will understand?*
>
> The template generated for C++ does not address these issues and I am
> unsure how to fix them.
>
> Any help would be highly appreciated! Thanks!
>
> Carlos Flores
> Energy Research Program
> Universidad de Chile
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
>