[TRNSYS-users] (no subject)
Adrien JEZEQUEL - ITF
a.jezequel at itf.biz
Thu Apr 29 23:56:35 PDT 2010
Dear Salim,
To control your room temperature with a PID, you should have a look to
the example " PID- Cooling Power". This example shows you how to
maintain 20°C in your room (for cooling, not heating but it's the same).
You will then be able to adapt that example to your model with type56.
The output of your PID give what you need to maintain 20°C (your
setpoint) in your room (heating when >0, cooling when <0). Then connect
your PID output as internal gain from your thermal zone in type56 (only
>0 values for heating)
Best regards
------------------------------------------------------------------------
www.itf.biz <http://www.itf.biz>
www.itf.biz <http://www.itf.biz>
Adrien JEZEQUEL
Simulations Thermiques Dynamiques
*ITF*
62, Rue du Bolliet
73230 St Alban Leysse
FRANCE
Phone :
Fax :
Mail:
+33(0) 479 750 029
+33(0) 479 852 122
a.jezequel at itf.biz
/Afin de contribuer au respect de l'environnement, merci de n'imprimer
cet e-mail que si nécessaire
Please, consider our environmental responsability before printing this email
/
Le 29/04/2010 19:38, salim mokraoui a écrit :
>
> Dear all,
>
> As a new user, I need to know how to control the zone temperature of a
> multizone bulding (type56) using a type23 PID controller. I defined an
> input heating power in trnbuild which would be the output of type 23
> (control signal). The heating setpoint is fixed to 20 °C. The result
> was not satisfactory, as the temperature remains lower than the
> setpoit and does not oscillate.
>
> Thank you
>
> Salim MOKRAOUI
>
> Faculté des sciences de Nancy - LERMAB
>
> BP 239
>
> 54506 Vandoeuvre.
>
> Tél 03 83 68 48 47 - mél salim.mokraoui at lermab.uhp-nancy.fr
>
>
> ---------------------------------------------------------------------------------------
> Orange vous informe que cet e-mail a été contrôlé par l'anti-virus mail.
> Aucun virus connu à ce jour par nos services n'a été détecté.
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100430/66ba8a36/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: logo_itf_signature.jpg
Type: image/jpeg
Size: 2884 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100430/66ba8a36/attachment-0005.jpg>
More information about the TRNSYS-users
mailing list