No, you didn't lose all your work. You can access it by opening the .bui file in a text editor. You can then correct your fault (somehow you added a adjacent wall which is only defined in one of the two zones). If you change this and save it, you should be able to open it in trnbuild. See example below.
Originally in .bui file:
WALL =FAC : SURF= 9 : AREA= 2.61 : ADJACENT=FACADE_1 : BACK
Replace by
WALL =FAC : SURF= 9 : AREA= 2.61 : BOUNDARY=IDENTICAL
Good luck!
,
Mariëlle Nuchelmans
Van: Mavi Cambronero Vázquez [mailto:maviqnk at gmail.com]
Verzonden: donderdag 22 april 2010 17:15
Aan: trnsys-users at cae.wisc.edu
Onderwerp: [TRNSYS-users] TRNBuild Error
Hi!!
I was working with TRNbuild and I saved my work, but I noticed I had something wrong.... When I tried to open the file the message that is attached appeared and it´s impossible to edit the file..... Did I lose my work in TRNBuild????
Thank you!!
Best